Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-03-09 Thread Ray Walters

HI Chris;

Just to be clear, the cables are not going to fail just because they 
aren't code compliant; unless you meant they would fail an inspection.  
I've included a picture of my own service rated at 150 amps.  Using 
table 310.15(B)7 (which I believe is the correct table for sizing the 
service conductors, not 310.B16 or 17), My side is 2/0 aluminum, but the 
utility side is #4 aluminum.  The utility is not held to NEC 
requirements, but a fire isn't starting just because they're grossly 
undersized by NEC standards.  NEC has huge safety factors, which are 
appropriate for wires hidden in walls that are expected to last the life 
of the house.
Finally, to be code compliant with a supply side 60 A connection, I 
believe the service conductors would need to be 3/0 Cu or 250 MCM 
Aluminum.  That would correspond to a 225 A service (x 120%) or 270 
amps, leaving 5 amps to spare.  As Dave mentioned, replacing the service 
conductors would probably not be a reasonable option.  Downsizing the 
main breaker to 175 A, would also work (175 + 60 < 200 x 120%) and since 
some of the loads are being transferred to the 60A breaker, downsizing 
the main should be compliant.



R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified, Licensed Contractor
808 269-7491

On 3/9/2013 8:17 AM, Christopher Warfel wrote:
Had a couple of minutes here, so with the load side connection, the 
200 amp breaker would operate to protect all conductors. With a supply 
side connection, the battery charger could be pulling 60 amps, the 
main panel 200, and the service conductors sized for 240 amps would 
fail. 2/0 in free air is rated for 265A T310.15(B)(17), but would you 
say that T310.(B)(16) applies for service conductors and then 2/0 is 175?


I am really starting to hate solar.
On 2/28/2013 10:21 AM, Dave Click wrote:
As a note, supply side connections have an extra complication with 
battery backup systems. With a regular GT inverter you're just 
pushing current into that interconnection point and you can work out 
easily that you won't have any overcurrent issues unless you made a 
big mistake and your inverter output exceeds the rating of your 
service conductors. However, with a battery system you're also 
potentially pulling current from that point. Before the battery 
inverter is installed your main breaker protects your service 
conductors, but if the inverter is pulling in 60A and the main 
breaker is also operating near its capacity, you could have >240A 
running over 200A service conductors with no breakers tripping. You 
would overwhelm the capacity of the service [230.23(A)] and no 
breakers would trip. You could fix this by replacing your service 
conductors back to the transformer (I'm just saying that it's an 
option) or downsizing the main breaker, and at that point you're 
probably better off just making it a load side connection. I'd go 
load side and argue with the AHJ to use the 2011 update mentioned 
earlier.


Dave

On 2013/2/28 9:55, Garrison Riegel wrote:


Allen,

The benefit I see would be to allow for a code compliant load side 
connection on a 200A panel with a 200A MB, where the AHJ is on the 
2008 NEC or older and will not listen to your good logic.  I don't 
think this would always be the best option, but if backup loads and 
inverter output were less than 32A then a 40A OCPD in the main panel 
should be fine?  Since it sounds like the 60A breaker in the main 
panel is not a safety issue, but a design consideration, I suppose I 
would just prefer flexibility when possible.


That said, this AHJ is on the 2008, and the loads will be less than 
30A, but based on this conversation I plan to go with a 60A and try 
to convince the AHJ that it will be code compliant in their future!


Thanks,

Garrison

*From:*re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*Allan Sindelar

*Sent:* Thursday, February 28, 2013 8:14 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

Garrison,
I don't know why it's not listed as 60A max, but my own internal 
logic would ask why it should be. The only benefit I could see for 
using smaller than a 60A breaker would be to allow use of #8 
conductors (allowed with a 40A or 50A breaker) instead of the #6 
necessary with a 60A breaker. And of course, you could use a 40A 
breaker with #6 conductors, so theoretically it would be fine. I 
just fail to see any benefit to doing so.

Allan

*Allan Sindelar*
al...@positiveenergysolar.com <mailto:al...@positiveenergysolar.com>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
*Positive Energy, Inc.*
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
*505 424-1112*
www.positiveenergysolar.com <http://www.positiveenergysolar.com/&

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-03-09 Thread Christopher Warfel
Had a couple of minutes here, so with the load side connection, the 200 
amp breaker would operate to protect all conductors. With a supply side 
connection, the battery charger could be pulling 60 amps, the main panel 
200, and the service conductors sized for 240 amps would fail. 2/0 in 
free air is rated for 265A T310.15(B)(17), but would you say that 
T310.(B)(16) applies for service conductors and then 2/0 is 175?


I am really starting to hate solar.
On 2/28/2013 10:21 AM, Dave Click wrote:
As a note, supply side connections have an extra complication with 
battery backup systems. With a regular GT inverter you're just pushing 
current into that interconnection point and you can work out easily 
that you won't have any overcurrent issues unless you made a big 
mistake and your inverter output exceeds the rating of your service 
conductors. However, with a battery system you're also potentially 
pulling current from that point. Before the battery inverter is 
installed your main breaker protects your service conductors, but if 
the inverter is pulling in 60A and the main breaker is also operating 
near its capacity, you could have >240A running over 200A service 
conductors with no breakers tripping. You would overwhelm the capacity 
of the service [230.23(A)] and no breakers would trip. You could fix 
this by replacing your service conductors back to the transformer (I'm 
just saying that it's an option) or downsizing the main breaker, and 
at that point you're probably better off just making it a load side 
connection. I'd go load side and argue with the AHJ to use the 2011 
update mentioned earlier.


Dave

On 2013/2/28 9:55, Garrison Riegel wrote:


Allen,

The benefit I see would be to allow for a code compliant load side 
connection on a 200A panel with a 200A MB, where the AHJ is on the 
2008 NEC or older and will not listen to your good logic.  I don't 
think this would always be the best option, but if backup loads and 
inverter output were less than 32A then a 40A OCPD in the main panel 
should be fine?  Since it sounds like the 60A breaker in the main 
panel is not a safety issue, but a design consideration, I suppose I 
would just prefer flexibility when possible.


That said, this AHJ is on the 2008, and the loads will be less than 
30A, but based on this conversation I plan to go with a 60A and try 
to convince the AHJ that it will be code compliant in their future!


Thanks,

Garrison

*From:*re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*Allan Sindelar

*Sent:* Thursday, February 28, 2013 8:14 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

Garrison,
I don't know why it's not listed as 60A max, but my own internal 
logic would ask why it should be. The only benefit I could see for 
using smaller than a 60A breaker would be to allow use of #8 
conductors (allowed with a 40A or 50A breaker) instead of the #6 
necessary with a 60A breaker. And of course, you could use a 40A 
breaker with #6 conductors, so theoretically it would be fine. I just 
fail to see any benefit to doing so.

Allan

*Allan Sindelar*
al...@positiveenergysolar.com <mailto:al...@positiveenergysolar.com>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
*Positive Energy, Inc.*
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
*505 424-1112*
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>

On 2/28/2013 6:27 AM, Garrison Riegel wrote:

Thanks Allen for clarifying why a 60A is required.  I was
wondering.  The spec does list a surge current of 9000W so I
thought that may be the rationale, but even that would only
require a 50A, and since this surge occurs during 'stand-alone
mode' it didn't seem to apply to the OCPD at the main panel. 
Your explanation makes more sense, but I wonder why then they

don't list the AC input breaker size as 60A /max/.  If you have
few backup loads, and are not on the 2011 NEC, a 40A could
theoretically be fine?

Thanks all for your thoughts, much appreciated.

Garrison

*From:*re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*Allan Sindelar
    *Sent:* Wednesday, February 27, 2013 6:08 PM
    *To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side
Connection

August,
The 60A breaker is intended to allow grid power to pass through
to the loads in excess of the inverter's stand-alone output. The
point of 705.12 (moved in the 2011 NEC from 690.64 (B)(2)) is to
differentiate between load pass-through current and sell current.

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-03-03 Thread Gary Willett

William - You're correct, I was confused - thanks for setting me straight!

Regards,  Gary

On 3/1/13 1:05 PM, William Miller wrote:

Gary:

I think you are a little confused about the operating modes of the XW 
inverter:


In the AC Passthru mode, no battery charging occurs.  Below is the 
passage from the manual that describes this:


/The AC connected to the AC1 or AC2 input is passing directly through 
the Xantrex XW
Series Inverter/Charger to the loads. The batteries are not being 
charged in this state.


/In the normal transfer mode, battery charging does occur.  It is my 
clear understanding that the Xantrex SW and XW inverters and the 
Outback FX and Radian inverters will regulate battery charging so that 
the charger circuit uses only excess amperage available.  For 
example:  If the input breaker size is programmed for 60 amps and 
there is 60 amps of load, 0 amps of AC will be used for battery 
charging.  If the load decreases to 50 amps, 10 amps of AC will be 
used for battery charging, etc..  Therefore, the OCPD does _not_ need 
to be sized to accommodate both uses of input AC.


Below is a passage from the XW Operating Manual that describes this:

/In addition, the battery charger can reduce its charging current to 
the batteries
so the combined charge AC current and total load current does not 
exceed the

capacity of the generator or trip its output breakers or fuses.

/Extending this discussion beyond the current topic (pun intended), we 
need to understand what happens if the connected loads exceed the 
input breaker rating.  Here the game changes.  The FX inverter can not 
prevent the overload from passing to the input breaker, possibly 
tripping it.  The SW, XW and Radian inverters can provide "Generator 
Support."  Do not confuse Generator Support with Generator Remote 
start functions.  Generator Support allows the inverter to sync to, 
and assist the AC input source in powering loads.  To use the example 
above:  If the load rises to 70 amps, the inverter draws energy from 
the batteries to provide the last 10 amps.


Below is the passage from the XW manual that describes this:

/AC2 Breaker:  Sets the AC2 (Gen) breaker size, based on the size of 
the installed AC breaker. The
breaker size must not exceed the capacity of the generator. The 
Xantrex XW Series
Inverter/Charger limits the maximum input current to this setting by 
derating its charging
current to an equivalent of 80% of the AC breaker size. If the 
connected loads exceed the
AC2 breaker setting, the AC breaker trips. The breaker may not trip if 
Gen Support is
enabled and Gen Amps is configured not to exceed the generator's rated 
output current.


/I hope this information is relevant, correct and helpful.

Sincerely,

William Miller




At 08:24 AM 3/1/2013, you wrote:

Larry:

In the case of the Xantrex XW Series, while in the "AC Pass-Thru" 
Mode, the internal transfer switch relay connects the protected loads 
directly to the AC1 grid input. The XW internal battery charger is 
then activated to recharge the battery bank.


The OCPD(s) through which the protected load amps and charging amps 
are passing must be sized to accommodate both at the same time.


Regards,

Gary Willett
Icarus Solar



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-03-01 Thread William Miller

Gary:

I think you are a little confused about the operating modes of the XW inverter:

In the AC Passthru mode, no battery charging occurs.  Below is the passage 
from the manual that describes this:


The AC connected to the AC1 or AC2 input is passing directly through the 
Xantrex XW
Series Inverter/Charger to the loads. The batteries are not being charged 
in this state.


In the normal transfer mode, battery charging does occur.  It is my clear 
understanding that the Xantrex SW and XW inverters and the Outback FX and 
Radian inverters will regulate battery charging so that the charger circuit 
uses only excess amperage available.  For example:  If the input breaker 
size is programmed for 60 amps and there is 60 amps of load, 0 amps of AC 
will be used for battery charging.  If the load decreases to 50 amps, 10 
amps of AC will be used for battery charging, etc..  Therefore, the OCPD 
does not need to be sized to accommodate both uses of input AC.


Below is a passage from the XW Operating Manual that describes this:

In addition, the battery charger can reduce its charging current to the 
batteries

so the combined charge AC current and total load current does not exceed the
capacity of the generator or trip its output breakers or fuses.

Extending this discussion beyond the current topic (pun intended), we need 
to understand what happens if the connected loads exceed the input breaker 
rating.  Here the game changes.  The FX inverter can not prevent the 
overload from passing to the input breaker, possibly tripping it.  The SW, 
XW and Radian inverters can provide "Generator Support."  Do not confuse 
Generator Support with Generator Remote start functions.  Generator Support 
allows the inverter to sync to, and assist the AC input source in powering 
loads.  To use the example above:  If the load rises to 70 amps, the 
inverter draws energy from the batteries to provide the last 10 amps.


Below is the passage from the XW manual that describes this:

AC2 Breaker:  Sets the AC2 (Gen) breaker size, based on the size of the 
installed AC breaker. The
breaker size must not exceed the capacity of the generator. The Xantrex XW 
Series
Inverter/Charger limits the maximum input current to this setting by 
derating its charging
current to an equivalent of 80% of the AC breaker size. If the connected 
loads exceed the
AC2 breaker setting, the AC breaker trips. The breaker may not trip if Gen 
Support is
enabled and Gen Amps is configured not to exceed the generator's rated 
output current.


I hope this information is relevant, correct and helpful.

Sincerely,

William Miller




At 08:24 AM 3/1/2013, you wrote:

Larry:

In the case of the Xantrex XW Series, while in the "AC Pass-Thru" Mode, 
the internal transfer switch relay connects the protected loads directly 
to the AC1 grid input. The XW internal battery charger is then activated 
to recharge the battery bank.


The OCPD(s) through which the protected load amps and charging amps are 
passing must be sized to accommodate both at the same time.


Regards,

Gary Willett
Icarus Solar
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-03-01 Thread Roy Butler

  
  
Garrison and Ross,

Although there are times that the buss bar
  rating may be higher than the main breaker
rating, the difficulty is in
obtaining documentation to verify that.
Sometimes it states the rating clearly on the panel label but that seems to be
  the exception, not the rule.

   
  
  Roy Butler
NABCEP Certified Small Wind Installer®
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV & wind installer
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807
607-324-9747  www.four-winds-energy.com

Join us at the 9th Annual Small Wind Conference
A Gathering of Installers, Manufacturers, Dealers, & Distributors
June 18 and 19, 2013 in Stevens Point, Wisconsin
www.smallwindconference.com

Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.



  On 3/1/2013 11:54 AM, Garrison Reigel wrote:


  
  
  Good point Ross.  The panel is marked
as a 200A with no indication that the bus has a higher rating,
so I've assumed 200A.  I considered downsizing the MB, but it's
an discontinued panel, and filled to capacity so not exactly
ideal.

Thanks,

Garrison

  
  From:
  re-wrenches-boun...@lists.re-wrenches.org
  [re-wrenches-boun...@lists.re-wrenches.org] on behalf of
  Ross Taylor [wind.trai...@gmail.com]
  Sent: Thursday, February 28, 2013 9:24 PM
  To: re-wrenches@lists.re-wrenches.org
      Subject: Re: [RE-wrenches] Conductor Sizing for
      Supply Side Connection

  
  Hi Garrison,


This is a great discussion and I think I've read all
  the responses. If I missed this question, please forgive
  me.  But, in your original post you refer to a 200 amp
  service.  I don't, though, see mention of the rating of
  the bus bars.  The bus bars may be rated for something
  more than 200 amps, depending upon the panel, even if
  they're protected by a 200 amp main disconnect.  If so,
  that would increase your backfeed breaker sizing options.


Best wishes, 


Ross Taylor


  

  
  
  
  
  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-03-01 Thread Garrison Reigel
Good point Ross.  The panel is marked as a 200A with no indication that the bus 
has a higher rating, so I've assumed 200A.  I considered downsizing the MB, but 
it's an discontinued panel, and filled to capacity so not exactly ideal.

Thanks,

Garrison

From: re-wrenches-boun...@lists.re-wrenches.org 
[re-wrenches-boun...@lists.re-wrenches.org] on behalf of Ross Taylor 
[wind.trai...@gmail.com]
Sent: Thursday, February 28, 2013 9:24 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

Hi Garrison,

This is a great discussion and I think I've read all the responses. If I missed 
this question, please forgive me.  But, in your original post you refer to a 
200 amp service.  I don't, though, see mention of the rating of the bus bars.  
The bus bars may be rated for something more than 200 amps, depending upon the 
panel, even if they're protected by a 200 amp main disconnect.  If so, that 
would increase your backfeed breaker sizing options.

Best wishes,

Ross Taylor

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-03-01 Thread Gary Willett

Larry:

In the case of the Xantrex XW Series, while in the "AC Pass-Thru" Mode, 
the internal transfer switch relay connects the protected loads directly 
to the AC1 grid input. The XW internal battery charger is then activated 
to recharge the battery bank.


The OCPD(s) through which the protected load amps and charging amps are 
passing must be sized to accommodate both at the same time.


Regards,

Gary Willett
Icarus Solar


On 3/1/13 8:40 AM, wire...@gmail.com wrote:


Gary,

I thought most inverters share power. So if the inverter has a 60A 
transfer switch and all of that is needed for loads then none for 
charging and as load demand decreases, charging increases.


Larry Liesner
Elektron Solar

On Feb 28, 2013 11:33 AM, <mailto:g...@icarussolarservices.com>> wrote:


Garrison, et al:

Another consideration when sizing the POCC OCPD (either load side
or supply side) is charging current when the grid power returns
and the battery bank is near the LBCO voltage.

Bulk charging current and AC pass-through current both must be
considered when sizing the POCC OCPD.

Regards,

Gary Willett

Icarus Solar

On Thu, 28 Feb 2013 10:04:51 -0600, Garrison Riegel
mailto:garri...@solarserviceinc.com>> wrote:

Great point Dave.  It crossed my mind that it was technically
possible, but figured since I would be removing loads off the
main panel it was highly unlikely.  Thanks for the code
reference. I'll go load side, and be prepared for some
discussion.

Thanks,

Garrison

*From:*re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>
[mailto:re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf
Of *Dave Click
*Sent:* Thursday, February 28, 2013 9:21 AM
*To:* re-wrenches@lists.re-wrenches.org
<mailto:re-wrenches@lists.re-wrenches.org>
    *Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side
Connection

As a note, supply side connections have an extra complication
with battery backup systems. With a regular GT inverter you're
just pushing current into that interconnection point and you
can work out easily that you won't have any overcurrent issues
unless you made a big mistake and your inverter output exceeds
the rating of your service conductors. However, with a battery
system you're also potentially pulling current from that
point. Before the battery inverter is installed your main
breaker protects your service conductors, but if the inverter
is pulling in 60A and the main breaker is also operating near
its capacity, you could have >240A running over 200A service
conductors with no breakers tripping. You would overwhelm the
capacity of the service [230.23(A)] and no breakers would
trip. You could fix this by replacing your service conductors
back to the transformer (I'm just saying that it's an option)
or downsizing the main breaker, and at that point you're
probably better off just making it a load side connection. I'd
go load side and argue with the AHJ to use the 2011 update
mentioned earlier.

Dave

On 2013/2/28 9:55, Garrison Riegel wrote:

Allen,

The benefit I see would be to allow for a code compliant
load side connection on a 200A panel with a 200A MB, where
the AHJ is on the 2008 NEC or older and will not listen to
your good logic.  I don't think this would always be the
best option, but if backup loads and inverter output were
less than 32A then a 40A OCPD in the main panel should be
fine?  Since it sounds like the 60A breaker in the main
panel is not a safety issue, but a design consideration, I
suppose I would just prefer flexibility when possible.

That said, this AHJ is on the 2008, and the loads will be
less than 30A, but based on this conversation I plan to go
with a 60A and try to convince the AHJ that it will be
code compliant in their future!

Thanks,

Garrison

*From:*re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Allan Sindelar
*Sent:* Thursday, February 28, 2013 8:14 AM
    *To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Conductor Sizing for Supply
Side Connection

Garrison,
I don't know why it's not listed as 60A max, but my own
   

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-03-01 Thread wirewiz
Gary,

I thought most inverters share power. So if the inverter has a 60A transfer
switch and all of that is needed for loads then none for charging and as
load demand decreases, charging increases.

Larry Liesner
Elektron Solar
On Feb 28, 2013 11:33 AM,  wrote:

> Garrison, et al:
>
>
>
> Another consideration when sizing the POCC OCPD (either load side or
> supply side) is charging current when the grid power returns and the
> battery bank is near the LBCO voltage.
>
>
>
> Bulk charging current and AC pass-through current both must be considered
> when sizing the POCC OCPD.
>
>
>
> Regards,
>
>
>
> Gary Willett
>
> Icarus Solar
>
> On Thu, 28 Feb 2013 10:04:51 -0600, Garrison Riegel <
> garri...@solarserviceinc.com> wrote:
>
>  Great point Dave.  It crossed my mind that it was technically possible,
> but figured since I would be removing loads off the main panel it was
> highly unlikely.  Thanks for the code reference.  I’ll go load side, and be
> prepared for some discussion.
>
>
>
>
>
> Thanks,
>
>
>
>
>
> Garrison
>
>
>
>
>
>
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
> re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Dave Click
> *Sent:* Thursday, February 28, 2013 9:21 AM
> *To:* re-wrenches@lists.re-wrenches.org
> *Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side Connection
>
>
>
>
>
> As a note, supply side connections have an extra complication with battery
> backup systems. With a regular GT inverter you're just pushing current into
> that interconnection point and you can work out easily that you won't have
> any overcurrent issues unless you made a big mistake and your inverter
> output exceeds the rating of your service conductors. However, with a
> battery system you're also potentially pulling current from that point.
> Before the battery inverter is installed your main breaker protects your
> service conductors, but if the inverter is pulling in 60A and the main
> breaker is also operating near its capacity, you could have >240A running
> over 200A service conductors with no breakers tripping. You would overwhelm
> the capacity of the service [230.23(A)] and no breakers would trip. You
> could fix this by replacing your service conductors back to the transformer
> (I'm just saying that it's an option) or downsizing the main breaker, and
> at that point you're probably better off just making it a load side
> connection. I'd go load side and argue with the AHJ to use the 2011 update
> mentioned earlier.
>
> Dave
>
>
>
> On 2013/2/28 9:55, Garrison Riegel wrote:
>
>
>
> Allen,
>
>
>
>
>
>
>
> The benefit I see would be to allow for a code compliant load side
> connection on a 200A panel with a 200A MB, where the AHJ is on the 2008 NEC
> or older and will not listen to your good logic.  I don’t think this would
> always be the best option, but if backup loads and inverter output were
> less than 32A then a 40A OCPD in the main panel should be fine?  Since it
> sounds like the 60A breaker in the main panel is not a safety issue, but a
> design consideration, I suppose I would just prefer flexibility when
> possible.
>
>
>
>
>
>
>
> That said, this AHJ is on the 2008, and the loads will be less than 30A,
> but based on this conversation I plan to go with a 60A and try to convince
> the AHJ that it will be code compliant in their future!
>
>
>
>
>
>
>
> Thanks,
>
>
>
>
>
>
>
> Garrison
>
>
>
>
>
>
>
>
>
>
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [
> mailto:re-wrenches-boun...@lists.re-wrenches.org]
> *On Behalf Of *Allan Sindelar
> *Sent:* Thursday, February 28, 2013 8:14 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side Connection
>
>
>
>
>
>
>
> Garrison,
> I don't know why it's not listed as 60A max, but my own internal logic
> would ask why it should be. The only benefit I could see for using smaller
> than a 60A breaker would be to allow use of #8 conductors (allowed with a
> 40A or 50A breaker) instead of the #6 necessary with a 60A breaker. And of
> course, you could use a 40A breaker with #6 conductors, so theoretically it
> would be fine. I just fail to see any benefit to doing so.
> Allan
>
>
>
> *Allan Sindelar*
> al...@positiveenergysolar.com
> NABCEP Certified Photovoltaic Installer
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder and Chief Technology Officer
> *Positive Energy, Inc.*
> 320

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-28 Thread gary
Garrison, et al:
 
Another consideration when sizing the POCC OCPD (either load side or supply
side) is charging current when the grid power returns and the battery bank is
near the LBCO voltage. 
 
Bulk charging current and AC pass-through current both must be considered
when sizing the POCC OCPD.
 
Regards,
 
Gary Willett
Icarus SolarOn Thu, 28 Feb 2013 10:04:51 -0600, Garrison Riegel
 wrote:


Great point Dave.  It crossed my mind that it was technically
possible, but figured since I would be removing loads off the main panel it was
highly unlikely.  Thanks for the code reference.  I’ll go load side, and be
prepared for some discussion.
 

 
Thanks,
 

 
Garrison
 

 

 


From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave
ClickSent: Thursday, February 28, 2013 9:21 AMTo:
re-wrenches@lists.re-wrenches.orgSubject: Re: [RE-wrenches] Conductor
Sizing for Supply Side Connection
 

 
As a note, supply side
connections have an extra complication with battery backup systems. With a
regular GT inverter you're just pushing current into that interconnection point
and you can work out easily that you won't have any overcurrent issues unless
you made a big mistake and your inverter output exceeds the rating of your
service conductors. However, with a battery system you're also potentially
pulling current from that point. Before the battery inverter is installed your
main breaker protects your service conductors, but if the inverter is pulling in
60A and the main breaker is also operating near its capacity, you could have
>240A running over 200A service conductors with no breakers tripping. You
would overwhelm the capacity of the service [230.23(A)] and no breakers would
trip. You could fix this by replacing your service conductors back to the
transformer (I'm just saying that it's an option) or downsizing the main
breaker, and at that point you're probably better off just making it a load side
connection. I'd go load side and argue with the AHJ to use the 2011 update
mentioned earlier.Dave
 

On 2013/2/28 9:55, Garrison Riegel wrote:
 

Allen,
 
 
 
The benefit I see would be to allow for a code compliant load side
connection on a 200A panel with a 200A MB, where the AHJ is on the 2008 NEC or
older and will not listen to your good logic.  I don’t think this would
always be the best option, but if backup loads and inverter output were less
than 32A then a 40A OCPD in the main panel should be fine?  Since it sounds
like the 60A breaker in the main panel is not a safety issue, but a design
consideration, I suppose I would just prefer flexibility when possible.
 
 
 
That said, this AHJ is on the 2008, and the loads will be less than
30A, but based on this conversation I plan to go with a 60A and try to convince
the AHJ that it will be code compliant in their future!
 
 
 
Thanks,
 
 
 
Garrison
 
 
 
 
 


From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
Allan SindelarSent: Thursday, February 28, 2013 8:14
AMTo: RE-wrenchesSubject: Re: [RE-wrenches] Conductor
Sizing for Supply Side Connection
 
 
 

Garrison,I don't
know why it's not listed as 60A max, but my own internal logic would ask why it
should be. The only benefit I could see for using smaller than a 60A breaker
would be to allow use of #8 conductors (allowed with a 40A or 50A breaker)
instead of the #6 necessary with a 60A breaker. And of course, you could use a
40A breaker with #6 conductors, so theoretically it would be fine. I just fail
to see any benefit to doing so.Allan
 

Allan Sindelaral...@positiveenergysolar.comNABCEP Certified
Photovoltaic InstallerNABCEP Certified Technical Sales ProfessionalNew
Mexico EE98J Journeyman ElectricianFounder and Chief Technology
OfficerPositive Energy, Inc.3209 Richards Lane (note new
address)Santa Fe, New Mexico 87507505 424-1112www.positiveenergysolar.com
 
 
 
 
 
On 2/28/2013 6:27 AM, Garrison Riegel wrote:
 

Thanks Allen for clarifying why a 60A is required.  I was
wondering.  The spec does list a surge current of 9000W so I thought that may
be the rationale, but even that would only require a 50A, and since this surge
occurs during ‘stand-alone mode’ it didn’t seem to apply to the OCPD at
the main panel.  Your explanation makes more sense, but I wonder why then they
don’t list the AC input breaker size as 60A max.  If you have few
backup loads, and are not on the 2011 NEC, a 40A could theoretically be
fine?
 
 
 
Thanks all for your thoughts, much appreciated.
 
 
 
Garrison
 
 
 
 
 


From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
Allan SindelarSent: Wednesday, February 27, 2013 6:08
PMTo: RE-wrenchesSubject: Re: [RE-wrenches] Conductor
Sizing for Supply Side Connection
 
 
 

August,The 60A
breaker is intended to allow grid power to pass through to the loads in excess

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-28 Thread Garrison Riegel
Great point Dave.  It crossed my mind that it was technically possible, but
figured since I would be removing loads off the main panel it was highly
unlikely.  Thanks for the code reference.  I'll go load side, and be
prepared for some discussion.

 

Thanks,

 

Garrison 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Click
Sent: Thursday, February 28, 2013 9:21 AM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

 

As a note, supply side connections have an extra complication with battery
backup systems. With a regular GT inverter you're just pushing current into
that interconnection point and you can work out easily that you won't have
any overcurrent issues unless you made a big mistake and your inverter
output exceeds the rating of your service conductors. However, with a
battery system you're also potentially pulling current from that point.
Before the battery inverter is installed your main breaker protects your
service conductors, but if the inverter is pulling in 60A and the main
breaker is also operating near its capacity, you could have >240A running
over 200A service conductors with no breakers tripping. You would overwhelm
the capacity of the service [230.23(A)] and no breakers would trip. You
could fix this by replacing your service conductors back to the transformer
(I'm just saying that it's an option) or downsizing the main breaker, and at
that point you're probably better off just making it a load side connection.
I'd go load side and argue with the AHJ to use the 2011 update mentioned
earlier.

Dave

On 2013/2/28 9:55, Garrison Riegel wrote:

Allen,

 

The benefit I see would be to allow for a code compliant load side
connection on a 200A panel with a 200A MB, where the AHJ is on the 2008 NEC
or older and will not listen to your good logic.  I don't think this would
always be the best option, but if backup loads and inverter output were less
than 32A then a 40A OCPD in the main panel should be fine?  Since it sounds
like the 60A breaker in the main panel is not a safety issue, but a design
consideration, I suppose I would just prefer flexibility when possible.

 

That said, this AHJ is on the 2008, and the loads will be less than 30A, but
based on this conversation I plan to go with a 60A and try to convince the
AHJ that it will be code compliant in their future!

 

Thanks,

 

Garrison

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Thursday, February 28, 2013 8:14 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

 

Garrison,
I don't know why it's not listed as 60A max, but my own internal logic would
ask why it should be. The only benefit I could see for using smaller than a
60A breaker would be to allow use of #8 conductors (allowed with a 40A or
50A breaker) instead of the #6 necessary with a 60A breaker. And of course,
you could use a 40A breaker with #6 conductors, so theoretically it would be
fine. I just fail to see any benefit to doing so.
Allan

Allan Sindelar
 <mailto:al...@positiveenergysolar.com> al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>  

 

 

On 2/28/2013 6:27 AM, Garrison Riegel wrote:

Thanks Allen for clarifying why a 60A is required.  I was wondering.  The
spec does list a surge current of 9000W so I thought that may be the
rationale, but even that would only require a 50A, and since this surge
occurs during 'stand-alone mode' it didn't seem to apply to the OCPD at the
main panel.  Your explanation makes more sense, but I wonder why then they
don't list the AC input breaker size as 60A max.  If you have few backup
loads, and are not on the 2011 NEC, a 40A could theoretically be fine?

 

Thanks all for your thoughts, much appreciated.

 

Garrison

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Wednesday, February 27, 2013 6:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

 

August,
The 60A breaker is intended to allow grid power to pass through to the loads
in excess of the inverter's stand-alone output. The point of 705.12 (moved
in the 2011 NEC from 690.64 (B)(2)) is to differentiate between load
pass-through current and sell current. The amount of current fed into the
grid is (4500/230 =) 19.56A, while the amount that can be taken from the
grid a

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-28 Thread Dave Click
As a note, supply side connections have an extra complication with 
battery backup systems. With a regular GT inverter you're just pushing 
current into that interconnection point and you can work out easily that 
you won't have any overcurrent issues unless you made a big mistake and 
your inverter output exceeds the rating of your service conductors. 
However, with a battery system you're also potentially pulling current 
from that point. Before the battery inverter is installed your main 
breaker protects your service conductors, but if the inverter is pulling 
in 60A and the main breaker is also operating near its capacity, you 
could have >240A running over 200A service conductors with no breakers 
tripping. You would overwhelm the capacity of the service [230.23(A)] 
and no breakers would trip. You could fix this by replacing your service 
conductors back to the transformer (I'm just saying that it's an option) 
or downsizing the main breaker, and at that point you're probably better 
off just making it a load side connection. I'd go load side and argue 
with the AHJ to use the 2011 update mentioned earlier.


Dave

On 2013/2/28 9:55, Garrison Riegel wrote:


Allen,

The benefit I see would be to allow for a code compliant load side 
connection on a 200A panel with a 200A MB, where the AHJ is on the 
2008 NEC or older and will not listen to your good logic.  I don't 
think this would always be the best option, but if backup loads and 
inverter output were less than 32A then a 40A OCPD in the main panel 
should be fine?  Since it sounds like the 60A breaker in the main 
panel is not a safety issue, but a design consideration, I suppose I 
would just prefer flexibility when possible.


That said, this AHJ is on the 2008, and the loads will be less than 
30A, but based on this conversation I plan to go with a 60A and try to 
convince the AHJ that it will be code compliant in their future!


Thanks,

Garrison

*From:*re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*Allan Sindelar

*Sent:* Thursday, February 28, 2013 8:14 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

Garrison,
I don't know why it's not listed as 60A max, but my own internal logic 
would ask why it should be. The only benefit I could see for using 
smaller than a 60A breaker would be to allow use of #8 conductors 
(allowed with a 40A or 50A breaker) instead of the #6 necessary with a 
60A breaker. And of course, you could use a 40A breaker with #6 
conductors, so theoretically it would be fine. I just fail to see any 
benefit to doing so.

Allan

*Allan Sindelar*
al...@positiveenergysolar.com <mailto:al...@positiveenergysolar.com>
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
*Positive Energy, Inc.*
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
*505 424-1112*
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>

On 2/28/2013 6:27 AM, Garrison Riegel wrote:

Thanks Allen for clarifying why a 60A is required.  I was
wondering. The spec does list a surge current of 9000W so I
thought that may be the rationale, but even that would only
require a 50A, and since this surge occurs during 'stand-alone
mode' it didn't seem to apply to the OCPD at the main panel.  Your
explanation makes more sense, but I wonder why then they don't
list the AC input breaker size as 60A /max/.  If you have few
backup loads, and are not on the 2011 NEC, a 40A could
theoretically be fine?

Thanks all for your thoughts, much appreciated.

Garrison

*From:*re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*Allan Sindelar
    *Sent:* Wednesday, February 27, 2013 6:08 PM
    *To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side
Connection

August,
The 60A breaker is intended to allow grid power to pass through to
the loads in excess of the inverter's stand-alone output. The
point of 705.12 (moved in the 2011 NEC from 690.64 (B)(2)) is to
differentiate between load pass-through current and sell current.
The amount of current fed into the grid is (4500/230 =) 19.56A,
while the amount that can be taken from the grid and passed
through to the load is much greater. If you were limited to a 40A
breaker in order to maintain 120% of a 200A main bus, you'd be
prone to nuisance trips under large cumulative loads.

Allan

*Allan Sindelar*
al...@positiveenergysolar.com <mailto:al...@positiveenergysolar.com>
NABCEP Certified Photovoltaic Installer
NABCEP Certifie

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-28 Thread Garrison Riegel
Allen,

 

The benefit I see would be to allow for a code compliant load side
connection on a 200A panel with a 200A MB, where the AHJ is on the 2008 NEC
or older and will not listen to your good logic.  I don't think this would
always be the best option, but if backup loads and inverter output were less
than 32A then a 40A OCPD in the main panel should be fine?  Since it sounds
like the 60A breaker in the main panel is not a safety issue, but a design
consideration, I suppose I would just prefer flexibility when possible.

 

That said, this AHJ is on the 2008, and the loads will be less than 30A, but
based on this conversation I plan to go with a 60A and try to convince the
AHJ that it will be code compliant in their future!

 

Thanks,

 

Garrison

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Thursday, February 28, 2013 8:14 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

 

Garrison,
I don't know why it's not listed as 60A max, but my own internal logic would
ask why it should be. The only benefit I could see for using smaller than a
60A breaker would be to allow use of #8 conductors (allowed with a 40A or
50A breaker) instead of the #6 necessary with a 60A breaker. And of course,
you could use a 40A breaker with #6 conductors, so theoretically it would be
fine. I just fail to see any benefit to doing so.
Allan

Allan Sindelar
 <mailto:al...@positiveenergysolar.com> al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>  

 

 

On 2/28/2013 6:27 AM, Garrison Riegel wrote:

Thanks Allen for clarifying why a 60A is required.  I was wondering.  The
spec does list a surge current of 9000W so I thought that may be the
rationale, but even that would only require a 50A, and since this surge
occurs during 'stand-alone mode' it didn't seem to apply to the OCPD at the
main panel.  Your explanation makes more sense, but I wonder why then they
don't list the AC input breaker size as 60A max.  If you have few backup
loads, and are not on the 2011 NEC, a 40A could theoretically be fine?

 

Thanks all for your thoughts, much appreciated.

 

Garrison

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Wednesday, February 27, 2013 6:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

 

August,
The 60A breaker is intended to allow grid power to pass through to the loads
in excess of the inverter's stand-alone output. The point of 705.12 (moved
in the 2011 NEC from 690.64 (B)(2)) is to differentiate between load
pass-through current and sell current. The amount of current fed into the
grid is (4500/230 =) 19.56A, while the amount that can be taken from the
grid and passed through to the load is much greater. If you were limited to
a 40A breaker in order to maintain 120% of a 200A main bus, you'd be prone
to nuisance trips under large cumulative loads.

Allan

Allan Sindelar
 <mailto:al...@positiveenergysolar.com> al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>  

 

 

 

 






___
List sponsored by Home Power magazine
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-28 Thread Allan Sindelar

  
  
Garrison,
  I don't know why it's not listed as 60A max, but my own internal
  logic would ask why it should be. The only benefit I could see for
  using smaller than a 60A breaker would be to allow use of #8
  conductors (allowed with a 40A or 50A breaker) instead of the #6
  necessary with a 60A breaker. And of course, you could use a 40A
  breaker with #6 conductors, so theoretically it would be fine. I
  just fail to see any benefit to doing so.
  Allan
  
  


Allan Sindelar
al...@positiveenergysolar.com
  NABCEP Certified Photovoltaic
Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



 
  On 2/28/2013 6:27 AM, Garrison Riegel wrote:


  
  
  
  
Thanks Allen
for clarifying why a 60A is required.  I was wondering.  The
spec does list a surge current of 9000W so I thought that
may be the rationale, but even that would only require a
50A, and since this surge occurs during ‘stand-alone mode’
it didn’t seem to apply to the OCPD at the main panel.  Your
explanation makes more sense, but I wonder why then they
don’t list the AC input breaker size as 60A max.  If
you have few backup loads, and are not on the 2011 NEC, a
40A could theoretically be fine?
 
Thanks all for
your thoughts, much appreciated.
 
Garrison
 
 

  
From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On
  Behalf Of Allan Sindelar
Sent: Wednesday, February 27, 2013 6:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Conductor Sizing for
        Supply Side Connection
  

 

  August,
The 60A breaker is intended to allow grid power to pass
through to the loads in excess of the inverter's stand-alone
output. The point of 705.12 (moved in the 2011 NEC from
690.64 (B)(2)) is to differentiate between load pass-through
current and sell current. The amount of current fed into the
grid is (4500/230 =) 19.56A, while the amount that can be
taken from the grid and passed through to the load is much
greater. If you were limited to a 40A breaker in order to
maintain 120% of a 200A main bus, you'd be prone to nuisance
trips under large cumulative loads.

Allan
  
Allan Sindelar
  al...@positiveenergysolar.com
  NABCEP Certified
Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com
  
 
 
  


   

 
  
  
  
  
  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-28 Thread Garrison Riegel
Thanks Allen for clarifying why a 60A is required.  I was wondering.  The
spec does list a surge current of 9000W so I thought that may be the
rationale, but even that would only require a 50A, and since this surge
occurs during 'stand-alone mode' it didn't seem to apply to the OCPD at the
main panel.  Your explanation makes more sense, but I wonder why then they
don't list the AC input breaker size as 60A max.  If you have few backup
loads, and are not on the 2011 NEC, a 40A could theoretically be fine?

 

Thanks all for your thoughts, much appreciated.

 

Garrison

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Wednesday, February 27, 2013 6:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

 

August,
The 60A breaker is intended to allow grid power to pass through to the loads
in excess of the inverter's stand-alone output. The point of 705.12 (moved
in the 2011 NEC from 690.64 (B)(2)) is to differentiate between load
pass-through current and sell current. The amount of current fed into the
grid is (4500/230 =) 19.56A, while the amount that can be taken from the
grid and passed through to the load is much greater. If you were limited to
a 40A breaker in order to maintain 120% of a 200A main bus, you'd be prone
to nuisance trips under large cumulative loads.

Allan

Allan Sindelar
 <mailto:al...@positiveenergysolar.com> al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>  

 

 

 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-27 Thread August Goers
Alan,



Thanks for the clarification. I believe you and Jeremy are talking about
the exception listed on the last paragraph of 705.12(D)(2). I've never used
that rule but it is good to know about. When we do battery backup we
typically route the critical loads through an external transfer switch
rather than through the battery inverter but this definitely has the
potential to open up doors and potentially reduce equipment cost.



Best,



August





August Goers



Luminalt Energy Corporation

1320 Potrero Avenue

San Francisco, CA 94110

m: 415.559.1525

o: 415.641.4000

aug...@luminalt.com



*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Allan Sindelar
*Sent:* Wednesday, February 27, 2013 4:08 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side Connection



August,
The 60A breaker is intended to allow grid power to pass through to the
loads in excess of the inverter's stand-alone output. The point of 705.12
(moved in the 2011 NEC from 690.64 (B)(2)) is to differentiate between load
pass-through current and sell current. The amount of current fed into the
grid is (4500/230 =) 19.56A, while the amount that can be taken from the
grid and passed through to the load is much greater. If you were limited to
a 40A breaker in order to maintain 120% of a 200A main bus, you'd be prone
to nuisance trips under large cumulative loads.

Allan

*Allan Sindelar*
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
*Positive Energy, Inc.*
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
*505 424-1112*
www.positiveenergysolar.com





On 2/27/2013 4:23 PM, August Goers wrote:

Jeremy,



Good point. Even under the 2008 NEC 690.64(B)(2) you can install up to a 40
Amp breaker on the load side as long as it is on the opposite side of the
input feed per 690.64(B)(7). Garrison, do you need a 60 A breaker?



I haven't used this product myself, but if the continuous output power is
indeed 4500 W then you'd be fine with a 25 or 30 A breaker.



Best,



August



*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *All Solar, Inc.
*Sent:* Wednesday, February 27, 2013 1:50 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side Connection



There is an exception in NEC2011 regarding the point of connection. This
may not apply, but you could avoid the supply side.  4500W / 240V = 18.75 x
1.25 = 23.4A, well under the 120% rule. reference 705.12(D)(2)



Jeremy

All Solar

CO,USA

- Original Message -

*From:* Garrison Riegel 

*To:* 'RE-wrenches' 

*Sent:* Wednesday, February 27, 2013 2:15 PM

*Subject:* [RE-wrenches] Conductor Sizing for Supply Side Connection



Wrenches,



On an upcoming job we have a Xantrex XW4548 interconnecting with a 200A
service, and I’d very much appreciate some advice if y’all are willing.



Since the inverter output OCPD is required to be 60A we are looking at a
supply side connection, and I have two questions:



1.   Before the point of interconnection the inverter output circuit
will first pass through the XW Power Distribution Panel and inverter
bypass, which is essentially a 60A breaker.  The service disconnect for the
supply side connection will also be fused at 60A.  Does the 120% rule apply
to the conductor between these two OCPDs?  Or since this is a supply side
connection in accordance with 690.64(A), 690.64(B)(2) will not apply? [this
AHJ is on the 2008 NEC]



2.   Can anyone recommend a reliable insulation piercing tap
connector?  Or would you recommend something else entirely for a
residential supply side connection?



Thanks in advance,



Garrison

847-677-0950

Solar Service Inc.




--

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___

List sponsored by Home Power magazine



List Address: RE-wrenches@lists.re-wrenches.org



Change email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm



Check out participant bios:

www.members.re-wrenches.org
___
List sponsored by Home Power magazi

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-27 Thread Allan Sindelar

  
  
August,
  The 60A breaker is intended to allow grid power to pass through to
  the loads in excess of the inverter's stand-alone output. The
  point of 705.12 (moved in the 2011 NEC from 690.64 (B)(2)) is to
  differentiate between load pass-through current and sell current.
  The amount of current fed into the grid is (4500/230 =) 19.56A,
  while the amount that can be taken from the grid and passed
  through to the load is much greater. If you were limited to a 40A
  breaker in order to maintain 120% of a 200A main bus, you'd be
  prone to nuisance trips under large cumulative loads.
  
  Allan
  
  


Allan Sindelar
al...@positiveenergysolar.com
  NABCEP Certified Photovoltaic
Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



 
  On 2/27/2013 4:23 PM, August Goers wrote:


  
  
  
  
Jeremy, 
 
Good point.
Even under the 2008 NEC 690.64(B)(2) you can install up to a
40 Amp breaker on the load side as long as it is on the
opposite side of the input feed per 690.64(B)(7). Garrison,
do you need a 60 A breaker?
 
I haven't used
this product myself, but if the continuous output power is
indeed 4500 W then you'd be fine with a 25 or 30 A breaker.
 
Best,
 
August
 

  
From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]
On Behalf Of All Solar, Inc.
Sent: Wednesday, February 27, 2013 1:50 PM
To: RE-wrenches
        Subject: Re: [RE-wrenches] Conductor Sizing for
    Supply Side Connection
  

 

  
There
  is an exception in NEC2011 regarding the point of
  connection. This may not apply, but you could avoid the
  supply side.  4500W / 240V = 18.75 x 1.25 = 23.4A, well
  under the 120% rule. reference 705.12(D)(2)


   


  Jeremy


  All
  Solar


  CO,USA


  
-
Original Message - 
  
  
From:
Garrison Riegel
  
  
  
To:
'RE-wrenches'
  
  
  
Sent:
Wednesday, February 27, 2013 2:15 PM
  
  
    Subject:
    [RE-wrenches] Conductor Sizing for Supply Side
Connection
  
  
 
  
  Wrenches,
   
  On an upcoming job we have a Xantrex
XW4548 interconnecting with a 200A service, and I’d very
much appreciate some advice if y’all are willing.  
   
  Since the inverter output OCPD is
required to be 60A we are looking at a supply side
connection, and I have two questions:
   
  
1.   Before the
point of interconnection the inverter output circuit will
first pass through the XW Power Distribution Panel and
inverter bypass, which is essentially a 60A breaker.  The
service disconnect for the supply side connection will also
be fused at 60A.  Does the 120% rule apply to the conductor
between these two OCPDs?  Or since this is a supply side
connection in accordance with 690.64(A), 690.64(B)(2) will
not apply? [this AHJ is on the 2008 NEC]
   
  2.   Can anyone
recommend a reliable insulation piercing tap connector?  Or
would you recommend something else entirely for a
residential supply side connection?
   
  Thanks in advance,
   
  Garrison
  847-677-0950
  Solar Service Inc.
  
 
   
  
  

  ___
  List sponsored by Home Power magazine
  
  List Address: RE-wrenches@lists.re-wrenches.org
  
  Change email address & settings:
  http://lists.re-wrenches.org/optio

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-27 Thread August Goers
Jeremy,



Good point. Even under the 2008 NEC 690.64(B)(2) you can install up to a 40
Amp breaker on the load side as long as it is on the opposite side of the
input feed per 690.64(B)(7). Garrison, do you need a 60 A breaker?



I haven't used this product myself, but if the continuous output power is
indeed 4500 W then you'd be fine with a 25 or 30 A breaker.



Best,



August



*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *All Solar, Inc.
*Sent:* Wednesday, February 27, 2013 1:50 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Conductor Sizing for Supply Side Connection



There is an exception in NEC2011 regarding the point of connection. This
may not apply, but you could avoid the supply side.  4500W / 240V = 18.75 x
1.25 = 23.4A, well under the 120% rule. reference 705.12(D)(2)



Jeremy

All Solar

CO,USA

- Original Message -

*From:* Garrison Riegel 

*To:* 'RE-wrenches' 

*Sent:* Wednesday, February 27, 2013 2:15 PM

*Subject:* [RE-wrenches] Conductor Sizing for Supply Side Connection



Wrenches,



On an upcoming job we have a Xantrex XW4548 interconnecting with a 200A
service, and I’d very much appreciate some advice if y’all are willing.



Since the inverter output OCPD is required to be 60A we are looking at a
supply side connection, and I have two questions:



1.   Before the point of interconnection the inverter output circuit
will first pass through the XW Power Distribution Panel and inverter
bypass, which is essentially a 60A breaker.  The service disconnect for the
supply side connection will also be fused at 60A.  Does the 120% rule apply
to the conductor between these two OCPDs?  Or since this is a supply side
connection in accordance with 690.64(A), 690.64(B)(2) will not apply? [this
AHJ is on the 2008 NEC]



2.   Can anyone recommend a reliable insulation piercing tap
connector?  Or would you recommend something else entirely for a
residential supply side connection?



Thanks in advance,



Garrison

847-677-0950

Solar Service Inc.




--

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-27 Thread Garrison Riegel
Thanks August.  I couldn't get the attachment to open, but I see what you're
saying.  You do bring up a good point about the AHJ as well.  Few here have
seen solar, and fewer are familiar with 690 so anything out of the ordinary
usually gets flagged.

 

As Jeremy points out the 2011 NEC would allow this as a load side
connection, so maybe I should spend my energy trying to convince them to let
us follow the current Code instead.

 

Thanks much,

 

Garrison

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
Sent: Wednesday, February 27, 2013 3:43 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

 

Hi Garrison,

 

In my opinion you only need to size the conductors to the overcurrent
protection. Bill Brooks addressed a similar question of mine a few months
ago - I've attached the email here. If you do a node analysis (ie see what
would happen under both normal operation and fault conditions at any given
point) you'll see that the current at any given point along the wire path
will never exceed the breaker ratings on either side (or the higher of the
two if they're different). It is a different story from what the 120% rule
is addressing - in that case the current feeding into a busbar has the
potential of being supplied by both the main breaker and the solar breaker
thus potentially exceeding the bus capacity.

 

I've used insulation piercing connectors from Burndy and Ilso with good
results. Ilsco is called KUP-L-TAP and part number IPC-4/0-2/0 is a common
one. You'll need to find the part number that best matches your wire size.

 

It's a bit of a separate issue, but I've found that many jurisdictions are
very critical of supply side connections and can start to ask questions
about whether the whole setup is listed for the purpose. It is nearly
impossible to get the manufacturer to list the entire service and line tap
in my experience. You might want to look into that if you think your
jurisdiction might have similar concerns. 

 

Good luck!

 

Best,

 

August

 

 

August Goers

 

Luminalt Energy Corporation

1320 Potrero Avenue

San Francisco, CA 94110

m: 415.559.1525

o: 415.641.4000

aug...@luminalt.com

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Garrison
Riegel
Sent: Wednesday, February 27, 2013 1:15 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Conductor Sizing for Supply Side Connection

 

Wrenches,

 

On an upcoming job we have a Xantrex XW4548 interconnecting with a 200A
service, and I'd very much appreciate some advice if y'all are willing.  

 

Since the inverter output OCPD is required to be 60A we are looking at a
supply side connection, and I have two questions:

 

1.   Before the point of interconnection the inverter output circuit
will first pass through the XW Power Distribution Panel and inverter bypass,
which is essentially a 60A breaker.  The service disconnect for the supply
side connection will also be fused at 60A.  Does the 120% rule apply to the
conductor between these two OCPDs?  Or since this is a supply side
connection in accordance with 690.64(A), 690.64(B)(2) will not apply? [this
AHJ is on the 2008 NEC]

 

2.   Can anyone recommend a reliable insulation piercing tap connector?
Or would you recommend something else entirely for a residential supply side
connection?

 

Thanks in advance,

 

Garrison

847-677-0950

Solar Service Inc.

 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-27 Thread All Solar, Inc.
There is an exception in NEC2011 regarding the point of connection. This may 
not apply, but you could avoid the supply side.  4500W / 240V = 18.75 x 1.25 = 
23.4A, well under the 120% rule. reference 705.12(D)(2)

Jeremy
All Solar
CO,USA
  - Original Message - 
  From: Garrison Riegel 
  To: 'RE-wrenches' 
  Sent: Wednesday, February 27, 2013 2:15 PM
  Subject: [RE-wrenches] Conductor Sizing for Supply Side Connection


  Wrenches,

   

  On an upcoming job we have a Xantrex XW4548 interconnecting with a 200A 
service, and I'd very much appreciate some advice if y'all are willing.  

   

  Since the inverter output OCPD is required to be 60A we are looking at a 
supply side connection, and I have two questions:

   

  1.   Before the point of interconnection the inverter output circuit will 
first pass through the XW Power Distribution Panel and inverter bypass, which 
is essentially a 60A breaker.  The service disconnect for the supply side 
connection will also be fused at 60A.  Does the 120% rule apply to the 
conductor between these two OCPDs?  Or since this is a supply side connection 
in accordance with 690.64(A), 690.64(B)(2) will not apply? [this AHJ is on the 
2008 NEC]

   

  2.   Can anyone recommend a reliable insulation piercing tap connector?  
Or would you recommend something else entirely for a residential supply side 
connection?

   

  Thanks in advance,

   

  Garrison

  847-677-0950

  Solar Service Inc.

   

   



--


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Change email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-27 Thread August Goers
Hi Garrison,



In my opinion you only need to size the conductors to the overcurrent
protection. Bill Brooks addressed a similar question of mine a few months
ago - I've attached the email here. If you do a node analysis (ie see what
would happen under both normal operation and fault conditions at any given
point) you'll see that the current at any given point along the wire path
will never exceed the breaker ratings on either side (or the higher of the
two if they're different). It is a different story from what the 120% rule
is addressing - in that case the current feeding into a busbar has the
potential of being supplied by both the main breaker and the solar breaker
thus potentially exceeding the bus capacity.



I've used insulation piercing connectors from Burndy and Ilso with good
results. Ilsco is called KUP-L-TAP and part number IPC-4/0-2/0 is a common
one. You'll need to find the part number that best matches your wire size.



It's a bit of a separate issue, but I've found that many jurisdictions are
very critical of supply side connections and can start to ask questions
about whether the whole setup is listed for the purpose. It is nearly
impossible to get the manufacturer to list the entire service and line tap
in my experience. You might want to look into that if you think your
jurisdiction might have similar concerns.



Good luck!



Best,



August





August Goers



Luminalt Energy Corporation

1320 Potrero Avenue

San Francisco, CA 94110

m: 415.559.1525

o: 415.641.4000

aug...@luminalt.com





*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Garrison Riegel
*Sent:* Wednesday, February 27, 2013 1:15 PM
*To:* 'RE-wrenches'
*Subject:* [RE-wrenches] Conductor Sizing for Supply Side Connection



Wrenches,



On an upcoming job we have a Xantrex XW4548 interconnecting with a 200A
service, and I’d very much appreciate some advice if y’all are willing.



Since the inverter output OCPD is required to be 60A we are looking at a
supply side connection, and I have two questions:



1.   Before the point of interconnection the inverter output circuit
will first pass through the XW Power Distribution Panel and inverter
bypass, which is essentially a 60A breaker.  The service disconnect for the
supply side connection will also be fused at 60A.  Does the 120% rule apply
to the conductor between these two OCPDs?  Or since this is a supply side
connection in accordance with 690.64(A), 690.64(B)(2) will not apply? [this
AHJ is on the 2008 NEC]



2.   Can anyone recommend a reliable insulation piercing tap
connector?  Or would you recommend something else entirely for a
residential supply side connection?



Thanks in advance,



Garrison

847-677-0950

Solar Service Inc.
--- Begin Message ---
Andy, August, and Eric,

 

There will likely be significant changes in the 2014 NEC to clarify the
situation you are discussing. Fault current has very little to do with
this issue. 

 

The key distinction was used in my proposal to the 2014 NEC that removed
the statement "and conductor" in 705.12(D) since conductors are treated
very differently in the NEC. We in 690 are the ones that got this messed
up. The issue with conductors are taps. With two sources feeding a tap,
the sum of the feeder breakers would have to be taken into account in
sizing the tap. This does NOT mean that the tap is a full size conductor.
The tap rule determines the size and the new proposal simply requires you
to use both the feeder breaker and the PV breaker in sizing the tap. This
assumes that both breakers are feeding the tap in the event of fault on
the tap and that there would be no problem clearing that fault. If fault
current was used as an argument for oversizing (it is wrong), it only has
relevance in the tap scenario. A fault in a feeder with no taps does not
allow the sum of the currents to flow anywhere but where the fault is-the
rest of the conductor is undamaged in a fault.

 

As was pointed out, in a fault, the PV inverter will shut down in a few
cycles leaving no contribution from the inverter anyway. Don't even bother
thinking about high impedance faults-the NEC does little to deal with
these types of faults other than to require ground fault protectors on all
services 1000A and up.

 

Sizing a conductor for the sum of two breakers on opposite ends of a
feeder seems to be what the code says, but it is totally ABSURD from a
technical point of view. John's articles were merely pointing out that the
code language seems to be telling us to do this, regardless of whether it
makes technical sense. The 2014 NEC will do away with this craziness.

 

Bill.

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Andrew
Truitt
Sent: Monday, May 07, 2012 11:24 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] 120% Ru

[RE-wrenches] Conductor Sizing for Supply Side Connection

2013-02-27 Thread Garrison Riegel
Wrenches,

 

On an upcoming job we have a Xantrex XW4548 interconnecting with a 200A
service, and I'd very much appreciate some advice if y'all are willing.  

 

Since the inverter output OCPD is required to be 60A we are looking at a
supply side connection, and I have two questions:

 

1.   Before the point of interconnection the inverter output circuit
will first pass through the XW Power Distribution Panel and inverter bypass,
which is essentially a 60A breaker.  The service disconnect for the supply
side connection will also be fused at 60A.  Does the 120% rule apply to the
conductor between these two OCPDs?  Or since this is a supply side
connection in accordance with 690.64(A), 690.64(B)(2) will not apply? [this
AHJ is on the 2008 NEC]

 

2.   Can anyone recommend a reliable insulation piercing tap connector?
Or would you recommend something else entirely for a residential supply side
connection?

 

Thanks in advance,

 

Garrison

847-677-0950

Solar Service Inc.

 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org