Hi Hugh,

This varies quite a bit all over the States.  In Colorado, they have a
distinction between an electrician and a PV installer.  Electricians can do
anything that the PV Installer can do, but not vice versa.  In order to
pull a state permit, a pv installer just needs to be listed on the
regulatory agencies website, which takes a simple one-page application, and
has more to do with business credentials than technical expertise.  The PV
installer is supposed to do only DC wiring.  The voltage does not matter
because that can mean all the way up to 600 VDC (and beyond) for PV and
battery systems above 48V nominal are restricted by the NEC.

This seems to be the case in all of the jurisdictions that I have worked
in.  You don't need any credentials to install the DC side of things.  The
DC voltage is not a significant factor in who can wire what.  For the AC
side, a master electrician license is required to pull permits that have an
AC portion of wiring.

However, often for some financial reason, such as utility incentive or to
comply with bid requirements, a NABCEP certified person is required to
oversee the DC side of things.

Hope this helps,

Cheers


On Thu, Mar 6, 2014 at 6:44 PM, Ray Walters r...@solarray.com wrote:

  New Mexico used to have a low voltage electrician.  It was for
 communications guys, and was limited to under 50 v.
 Actually pretty useless, since most systems had inverters.  Also it wasn't
 that much harder to just get a regular electrical license.
 Also, some considered even 24 v systems to be over 50 v, since the Voc in
 cold weather could exceed 50v.
 Generally, for maintenance/ battery replacement on off grid stuff, no one
 worries about it.  If you are doing new construction, pulling permits, then
 you need to have much more than just the license.
 Insurance, bonding, worker's comp, etc. are also all required.

 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer303 505-8760

 On 3/6/2014 6:33 PM, Hugh Piggott wrote:

 Me again,

  Maybe that was confusing.  Just to clarify this question, I will break
 it down as follows:

- What qualifications do you need to legally work on electrical
systems in your country/state?
- *Is the circuit voltage a factor*, and if there is a different rule
for ELV systems, then how is ELV defined?
- What other factors are applicable such as status (homeowner,
installer, paid/unpaid) and location (inside home, wet location, etc)?

  Thanks for any observations.

  Hugh

  On 5 Mar 2014, at 08:34, Hugh Piggott wrote:

  hi All,

  I am trying to find some general statements that can be made about the
 global legal position on who may or may not work on/install extra low
 voltage (ELV) systems or equipment such as batteries, PV, turbines etc.

  I understand that in the USA this is a matter for state legislation
 rather than federal.  I'd be interested to learn what rules people follow
 regarding such work and who can do it, for themselves or for money, in what
 environment (inside or outside the home for example, dry or wet etc) and at
 what voltages?  The definition of ELV seems to change depending on various
 factors, one of which is whether it is separated (floating and well
 insulated) or not.

  Many of us work with battery systems, and not everyone is a certified
 electrician.  I'd love to know some ground rules.

  thanks!

  Hugh


   Hugh Piggott
 Scoraig Wind Electric
 Dundonnell
 Ross shire
 IV23 2RE,  UK
 +44 77 1315 7600
 h...@scoraigwind.co.uk
 www.scoraigwind.co.uk




  ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  
 settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:www.re-wrenches.org/etiquette.htm

 Check out participant bios:www.members.re-wrenches.org



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 



Mac Lewis

*Yo solo sé que no sé nada. 

Re: [RE-wrenches] Extra Low Voltage

2014-03-07 Thread Mac Lewis
Hi again Hugh,

Also, in Colorado, homeowners can do any and all work that they want, as
long as they can get it passed inspection.  Oftentimes, incentives
discourage this because they need to use a licensed contractor to get the
incentive.  We have done a significant amount of business from shameful
homeowners that have tried wiring stuff up that they bought off of the
internet and couldn't get technical support to do code-compliant
installation.  We always charge a lot for this type of work.

Thanks

Thanks


On Fri, Mar 7, 2014 at 6:09 AM, Mac Lewis maclew...@gmail.com wrote:

 Hi Hugh,

 This varies quite a bit all over the States.  In Colorado, they have a
 distinction between an electrician and a PV installer.  Electricians can do
 anything that the PV Installer can do, but not vice versa.  In order to
 pull a state permit, a pv installer just needs to be listed on the
 regulatory agencies website, which takes a simple one-page application, and
 has more to do with business credentials than technical expertise.  The PV
 installer is supposed to do only DC wiring.  The voltage does not matter
 because that can mean all the way up to 600 VDC (and beyond) for PV and
 battery systems above 48V nominal are restricted by the NEC.

 This seems to be the case in all of the jurisdictions that I have worked
 in.  You don't need any credentials to install the DC side of things.  The
 DC voltage is not a significant factor in who can wire what.  For the AC
 side, a master electrician license is required to pull permits that have an
 AC portion of wiring.

 However, often for some financial reason, such as utility incentive or to
 comply with bid requirements, a NABCEP certified person is required to
 oversee the DC side of things.

 Hope this helps,

 Cheers


 On Thu, Mar 6, 2014 at 6:44 PM, Ray Walters r...@solarray.com wrote:

  New Mexico used to have a low voltage electrician.  It was for
 communications guys, and was limited to under 50 v.
 Actually pretty useless, since most systems had inverters.  Also it
 wasn't that much harder to just get a regular electrical license.
 Also, some considered even 24 v systems to be over 50 v, since the Voc in
 cold weather could exceed 50v.
 Generally, for maintenance/ battery replacement on off grid stuff, no one
 worries about it.  If you are doing new construction, pulling permits, then
 you need to have much more than just the license.
 Insurance, bonding, worker's comp, etc. are also all required.

 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer303 505-8760

 On 3/6/2014 6:33 PM, Hugh Piggott wrote:

 Me again,

  Maybe that was confusing.  Just to clarify this question, I will break
 it down as follows:

- What qualifications do you need to legally work on electrical
systems in your country/state?
- *Is the circuit voltage a factor*, and if there is a different rule
for ELV systems, then how is ELV defined?
- What other factors are applicable such as status (homeowner,
installer, paid/unpaid) and location (inside home, wet location, etc)?

  Thanks for any observations.

  Hugh

  On 5 Mar 2014, at 08:34, Hugh Piggott wrote:

  hi All,

  I am trying to find some general statements that can be made about the
 global legal position on who may or may not work on/install extra low
 voltage (ELV) systems or equipment such as batteries, PV, turbines etc.

  I understand that in the USA this is a matter for state legislation
 rather than federal.  I'd be interested to learn what rules people follow
 regarding such work and who can do it, for themselves or for money, in what
 environment (inside or outside the home for example, dry or wet etc) and at
 what voltages?  The definition of ELV seems to change depending on various
 factors, one of which is whether it is separated (floating and well
 insulated) or not.

  Many of us work with battery systems, and not everyone is a certified
 electrician.  I'd love to know some ground rules.

  thanks!

  Hugh


   Hugh Piggott
 Scoraig Wind Electric
 Dundonnell
 Ross shire
 IV23 2RE,  UK
 +44 77 1315 7600
 h...@scoraigwind.co.uk
 www.scoraigwind.co.uk




  ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  
 settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  

Re: [RE-wrenches] Extra Low Voltage

2014-03-06 Thread Hugh Piggott
Me again,

Maybe that was confusing.  Just to clarify this question, I will break it down 
as follows:
What qualifications do you need to legally work on electrical systems in your 
country/state?
Is the circuit voltage a factor, and if there is a different rule for ELV 
systems, then how is ELV defined?
What other factors are applicable such as status (homeowner, installer, 
paid/unpaid) and location (inside home, wet location, etc)?
Thanks for any observations.

Hugh

On 5 Mar 2014, at 08:34, Hugh Piggott wrote:

 hi All,
 
 I am trying to find some general statements that can be made about the global 
 legal position on who may or may not work on/install extra low voltage 
 (ELV) systems or equipment such as batteries, PV, turbines etc.
 
 I understand that in the USA this is a matter for state legislation rather 
 than federal.  I'd be interested to learn what rules people follow regarding 
 such work and who can do it, for themselves or for money, in what environment 
 (inside or outside the home for example, dry or wet etc) and at what 
 voltages?  The definition of ELV seems to change depending on various 
 factors, one of which is whether it is separated (floating and well 
 insulated) or not.
 
 Many of us work with battery systems, and not everyone is a certified 
 electrician.  I'd love to know some ground rules.
 
 thanks!
 
 Hugh
 
 
 Hugh Piggott
 Scoraig Wind Electric
 Dundonnell
 Ross shire
 IV23 2RE,  UK
 +44 77 1315 7600
 h...@scoraigwind.co.uk
 www.scoraigwind.co.uk
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Extra Low Voltage

2014-03-06 Thread Ray Walters
New Mexico used to have a low voltage electrician.  It was for 
communications guys, and was limited to under 50 v.
Actually pretty useless, since most systems had inverters.  Also it 
wasn't that much harder to just get a regular electrical license.
Also, some considered even 24 v systems to be over 50 v, since the Voc 
in cold weather could exceed 50v.
Generally, for maintenance/ battery replacement on off grid stuff, no 
one worries about it.  If you are doing new construction, pulling 
permits, then you need to have much more than just the license.

Insurance, bonding, worker's comp, etc. are also all required.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 3/6/2014 6:33 PM, Hugh Piggott wrote:

Me again,

Maybe that was confusing.  Just to clarify this question, I will break 
it down as follows:


  * What qualifications do you need to legally work on electrical
systems in your country/state?
  * *Is the circuit voltage a factor*, and if there is a different
rule for ELV systems, then how is ELV defined?
  * What other factors are applicable such as status (homeowner,
installer, paid/unpaid) and location (inside home, wet location, etc)?

Thanks for any observations.

Hugh

On 5 Mar 2014, at 08:34, Hugh Piggott wrote:


hi All,

I am trying to find some general statements that can be made about 
the global legal position on who may or may not work on/install 
extra low voltage (ELV) systems or equipment such as batteries, PV, 
turbines etc.


I understand that in the USA this is a matter for state legislation 
rather than federal.  I'd be interested to learn what rules people 
follow regarding such work and who can do it, for themselves or for 
money, in what environment (inside or outside the home for example, 
dry or wet etc) and at what voltages?  The definition of ELV seems to 
change depending on various factors, one of which is whether it is 
separated (floating and well insulated) or not.


Many of us work with battery systems, and not everyone is a certified 
electrician.  I'd love to know some ground rules.


thanks!

Hugh


Hugh Piggott
Scoraig Wind Electric
Dundonnell
Ross shire
IV23 2RE,  UK
+44 77 1315 7600
h...@scoraigwind.co.uk mailto:h...@scoraigwind.co.uk
www.scoraigwind.co.uk http://www.scoraigwind.co.uk/




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org 
mailto:RE-wrenches@lists.re-wrenches.org


Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Extra Low Voltage

2014-03-05 Thread Hugh Piggott
hi All,

I am trying to find some general statements that can be made about the global 
legal position on who may or may not work on/install extra low voltage (ELV) 
systems or equipment such as batteries, PV, turbines etc.

I understand that in the USA this is a matter for state legislation rather than 
federal.  I'd be interested to learn what rules people follow regarding such 
work and who can do it, for themselves or for money, in what environment 
(inside or outside the home for example, dry or wet etc) and at what voltages?  
The definition of ELV seems to change depending on various factors, one of 
which is whether it is separated (floating and well insulated) or not.

Many of us work with battery systems, and not everyone is a certified 
electrician.  I'd love to know some ground rules.

thanks!

Hugh


Hugh Piggott
Scoraig Wind Electric
Dundonnell
Ross shire
IV23 2RE,  UK
+44 77 1315 7600
h...@scoraigwind.co.uk
www.scoraigwind.co.uk




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org