Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-14 Thread Bryan Norkunas
Sol Ark related:

 

– we often get requests for their batteries and there seems to be a shortage at 
the moment and stock will not be available until mid to late Nov.

 

Below a response we received this morning from Sol Ark:

 

Due to the shortage we are trying to make sure batteries are being used with 
Sol-Ark systems. 

This is the only reason we carry them. Not really a supply house for batteries.

We also only recommend our batteries for back-up mostly and not really for Time 
of Use.  

Also, battery pack should be over-sized if they are going to use it for Time of 
Use. 

 

 

Bryan Norkunas

br...@pv-cables.com

 

Description: Description: PV-Cables_Logo_Transparent_Bkgnd_140x140

PV-Cables Inc. 

989 Milton Ave Ste 1D

Ferndale CA 95536

(707) 923-3000 office

www.pv-cables.com <http://www.pv-cables.com/> 

 

 Description: Description: cid:image002.jpg@01CD22E8.974B6470 Please print only 
if necessary.

 

NOTE: This email message and any attachments are for the sole use of the 
intended recipient(s) and may contain confidential and/or privileged 
information. Any unauthorized review, use, disclosure or distribution is 
prohibited. If you are not the intended recipient, please contact the sender by 
replying to this email, and destroy all copies of the original message.

 

 

 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Jason Szumlanski
Sent: Thursday, September 10, 2020 1:33 PM
To: Jeff Clearwater
Cc: RE-wrenches
Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?

 

Related question, Jeff... With the Sol-Ark, I an off-grid situation can you set 
it up to always use inveters to power loads. In other words, when the generator 
kicks in, only use the generator to charge batteries and do not bypass inveters 
to power loads directly from the generator. 

 

This is a request I get occasionally. People don't want to rely on the "dirty" 
generator power with sensitive electronics.

 

Jason

 

 

On Thu, Sep 10, 2020, 1:19 PM Jeff Clearwater  wrote:

I'm loving my first install of Sol Arks - One downside of Sol-Ark (and I can't 
find many!) is that the GEN terminal can only handle 1 of the following 3:  
Generator, AC Coupling, or Smart Load.  So if you want both a generator and AC 
coupling you have to either do a separate transfer switch for the GEN and not 
run it through the inverters - or you have to go with their internal DC MPPTif 
you do want the GEN to charge the batteries (unless you are off-grid totally 
and have no Grid in which case you might be able to run the Generator into 
Grid?  not sure about that - don't quote me!).

Anyone else with any downsides?

Best,

Jeff



Jason Szumlanski wrote on 9/10/20 4:44 AM:



There is a huge distinction in a hybrid inverter that integrates MPPT charge 
control. Eliminating all of the extraneous hardware and circuit protection 
associated with charge controllers is very appealing. The 500V input limit is 
also a game-changer in terms of wire size. I'm very interested in this approach.

 

On the flip size, an AC Coupled approach is also appealing in a lot of 
circumstances. Since Sol-Ark supports that, too, it's hard to find downsides 
other than their infancy in the industry.

 

And for what it's worth, my experience with SMA tech support recently has been 
abysmal. Long hold times and getting bounced around departments.

 

Jason Szumlanski



 

 

 

On Wed, Sep 9, 2020 at 9:50 PM Mark Frye  wrote:

The most important thing here is that no one is standing up to sing the praises 
of either SMA or Outback.

I myself have sent about 2 hours on hold over 2 days trying to get an issue 
addressed by SMA.

Re: Sol-Arc I would pay a lot extra or take some not so good aspect in exchange 
for good technical support.

On 9/9/2020 1:12 PM, Jason Szumlanski wrote:

Any tips on combining AC output from these units when stacking several of them? 
What bus/OCPD system are you using? Same question for generator/grid input. 

 

The solar MPPT inputs appear to be dead simple.

 

Jason Szumlanski

 







 

 

 

On Tue, Sep 8, 2020 at 10:45 PM MiJo Nels  wrote:

we've found SolArk to be SOLID!! .. And yes 8 inv yield about 96kW, with a TON 
of surge capabilities.. 

Joe Nelson

Project Manager C-46/C-10

Sustainable Energy Group Inc., A California Corporation

CSL# 868816

www.SustainableEnergyGroup.com 
<https://mailtrack.io/trace/link/8f0e320b52948f22a9ae9682bd3b5e9dc8d6c68f?url=http%3A%2F%2Fwww.SustainableEnergyGroup.com&userId=1613865&signature=e7d246f94af9a065>
 

530-273-4422 (Office)

530-217-8385 (Cell)



   

 

  _  

From: RE-wrenches  on behalf of 
pgir...@mindspring.com 
Sent: Tuesday, September 8, 2020 1:24:03 PM
To: 'RE-wrenches' 
Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other? 

 

I also suggest the Sol-Ark 12’s. Ext

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-10 Thread Bill Hennessy
iated with charge controllers is very appealing. The 500V input limit is 
also a game-changer in terms of wire size. I'm very interested in this 
approach. On the flip size, an AC Coupled approach is also appealing in a lot 
of circumstances. Since Sol-Ark supports that, too, it's hard to find downsides 
other than their infancy in the industry. And for what it's worth, my 
experience with SMA tech support recently has been abysmal. Long hold times and 
getting bounced around departments. Jason Szumlanski 
On Wed, Sep 9, 2020 at 9:50 PM Mark Frye  wrote:

The most important thing here is that no one is standing up to sing the praises 
of either SMA or Outback.

I myself have sent about 2 hours on hold over 2 days trying to get an issue 
addressed by SMA.

Re: Sol-Arc I would pay a lot extra or take some not so good aspect in exchange 
for good technical support.
On 9/9/2020 1:12 PM, Jason Szumlanski wrote:
Any tips on combining AC output from these units when stacking several of them? 
What bus/OCPD system are you using? Same question for generator/grid input.  
The solar MPPT inputs appear to be dead simple. Jason Szumlanski 
|   | 
| 
|   |   |   |

 |

 |

 
On Tue, Sep 8, 2020 at 10:45 PM MiJo Nels  wrote:
we've found SolArk to be SOLID!! .. And yes 8 inv yield about 96kW, with a TON 
of surge capabilities.. Joe NelsonProject Manager C-46/C-10Sustainable Energy 
Group Inc., A California CorporationCSL# 
868816www.SustainableEnergyGroup.com530-273-4422 (Office)530-217-8385 (Cell) 
  From: RE-wrenches  on behalf of 
pgir...@mindspring.com 
 Sent: Tuesday, September 8, 2020 1:24:03 PM
 To: 'RE-wrenches' 
 Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other? 
I also suggest the Sol-Ark 12's. Extremely efficient, simple to program, does a 
wonderful job in either ac coupling, stand alone or pure off grid and terrific 
customer support.

 

Peter Giroux

ASAE

 

From: RE-wrenches  On Behalf Of 
Bryan Norkunas
 Sent: Tuesday, September 8, 2020 1:50 PM
 To: 'RE-wrenches' 
 Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?

 

Sol-Arks would be possible, you can link 8 inverters.

 

Bryan 

PV-Cables

 

 

 

 

 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Chris Schaefer
 Sent: Tuesday, September 8, 2020 10:40 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?

 

I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with their 
12kw unit. Not sure what their max number of inverters are.

 

Christopher

 

On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield  
wrote:


Hey all, I'm designing a microgrid sized off-grid system for somebody, and I'm 
just wondering if anyone knows of any issues with the following designs... 

 

The client says he needs 70 kW. His load data looks pretty solid, so I'm 
sticking to using that number as a minimum, at least during the initial 
proposal stage. I only know of two possible equipment options for this size 
range...

 
   
   - I think I can use up to 10 Outback Radians, for up to an 80 kW system. Are 
there any bugs or problems with using this many inverters on one hub? I know 
I've read about issues with selling to the grid, but that's not an issue, this 
is off-grid.
   - I know that the SMA cluster box with sunny islands can allow for up to a 
72 kW system. Do you know of any bugs or problems with this system?

 

 

Are there any other options that anyone would suggest? Schneider's website says 
they can only do up to 61 kW, and Victron can only do up to 60 kW.

 

 

I know that the Outback system would yield a 240/120 Split-Phase system and 
that the SMA would yield a 208/120 3Ø system, but this doesn't really matter 
either way for this job. 

 

Thanks so much,

Kienan

 

 

Maxfield Solar 

maxfieldso...@hotmail.com

(801) 631-5584 (Cell)

___
 List sponsored by Redwood Alliance
 
 List Address:  RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address & settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive:  
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules & etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org


 

 

--

Chris Schaefer's
 
 Tel/Fax 585-229-2083 or Cell 585-748-1870 
 5115 South Hill Road ~ Canandaigua New York 14424
 www.solarandwindfx.com ~ E-mail: ch...@solarandwindfx.com



Thomas Jefferson, the author of our great Constitution, once said, "democracy" 
will cease to exist when you take away from those who are willing to work and 
give to those who would not."


|  | Virus-free.  www.avg.com |

___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-10 Thread Jason Szumlanski
Related question, Jeff... With the Sol-Ark, I an off-grid situation can you
set it up to always use inveters to power loads. In other words, when the
generator kicks in, only use the generator to charge batteries and do not
bypass inveters to power loads directly from the generator.

This is a request I get occasionally. People don't want to rely on the
"dirty" generator power with sensitive electronics.

Jason


On Thu, Sep 10, 2020, 1:19 PM Jeff Clearwater  wrote:

> I'm loving my first install of Sol Arks - One downside of Sol-Ark (and I
> can't find many!) is that the GEN terminal can only handle 1 of the
> following 3:  Generator, AC Coupling, or Smart Load.  So if you want both a
> generator and AC coupling you have to either do a separate transfer switch
> for the GEN and not run it through the inverters - or you have to go with
> their internal DC MPPTif you do want the GEN to charge the batteries
> (unless you are off-grid totally and have no Grid in which case you might
> be able to run the Generator into Grid?  not sure about that - don't quote
> me!).
>
> Anyone else with any downsides?
>
> Best,
>
> Jeff
>
>
>
> Jason Szumlanski wrote on 9/10/20 4:44 AM:
>
> There is a huge distinction in a hybrid inverter that integrates MPPT
> charge control. Eliminating all of the extraneous hardware and circuit
> protection associated with charge controllers is very appealing. The 500V
> input limit is also a game-changer in terms of wire size. I'm very
> interested in this approach.
>
> On the flip size, an AC Coupled approach is also appealing in a lot of
> circumstances. Since Sol-Ark supports that, too, it's hard to find
> downsides other than their infancy in the industry.
>
> And for what it's worth, my experience with SMA tech support recently has
> been abysmal. Long hold times and getting bounced around departments.
>
> Jason Szumlanski
>
>
>
> On Wed, Sep 9, 2020 at 9:50 PM Mark Frye  wrote:
>
>> The most important thing here is that no one is standing up to sing the
>> praises of either SMA or Outback.
>>
>> I myself have sent about 2 hours on hold over 2 days trying to get an
>> issue addressed by SMA.
>>
>> Re: Sol-Arc I would pay a lot extra or take some not so good aspect in
>> exchange for good technical support.
>> On 9/9/2020 1:12 PM, Jason Szumlanski wrote:
>>
>> Any tips on combining AC output from these units when stacking several of
>> them? What bus/OCPD system are you using? Same question for generator/grid
>> input.
>>
>> The solar MPPT inputs appear to be dead simple.
>>
>> Jason Szumlanski
>>
>>
>>
>>
>>
>>
>>
>>
>> On Tue, Sep 8, 2020 at 10:45 PM MiJo Nels 
>> wrote:
>>
>>> we've found SolArk to be SOLID!! .. And yes 8 inv yield about 96kW, with
>>> a TON of surge capabilities..
>>>
>>> Joe Nelson
>>>
>>> Project Manager C-46/C-10
>>> Sustainable Energy Group Inc., A California Corporation
>>>
>>> CSL# 868816
>>> www.SustainableEnergyGroup.com
>>> <https://mailtrack.io/trace/link/8f0e320b52948f22a9ae9682bd3b5e9dc8d6c68f?url=http%3A%2F%2Fwww.SustainableEnergyGroup.com&userId=1613865&signature=e7d246f94af9a065>
>>> 530-273-4422 (Office)
>>>
>>> 530-217-8385 (Cell)
>>>
>>> 
>>>
>>>    
>>>
>>>
>>> --
>>> *From:* RE-wrenches  on
>>> behalf of pgir...@mindspring.com 
>>> *Sent:* Tuesday, September 8, 2020 1:24:03 PM
>>> *To:* 'RE-wrenches' 
>>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>>
>>>
>>> I also suggest the Sol-Ark 12’s. Extremely efficient, simple to program,
>>> does a wonderful job in either ac coupling, stand alone or pure off grid
>>> and terrific customer support.
>>>
>>>
>>>
>>> Peter Giroux
>>>
>>> ASAE
>>>
>>>
>>>
>>> *From:* RE-wrenches  *On
>>> Behalf Of *Bryan Norkunas
>>> *Sent:* Tuesday, September 8, 2020 1:50 PM
>>> *To:* 'RE-wrenches' 
>>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>>
>>>
>>>
>>> Sol-Arks would be possible, you can link 8 inverters.
>>>
>>>
>>>
>>> *Bryan *
>>>
>>> *PV-Cables*
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>&g

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-10 Thread Dave Angelini Offgrid Solar


I am confused by the 2 different Sol Ark systems. The large one looks
like it has a DC disco/breaker and a solar disco. 

The smaller solark
looks like it has a DC breaker only. Any guidance on what else is needed to
make these useable please?  

Dave Angelini Offgrid Solar
"we go where
powerlines don't"
http://members.sti.net/offgridsolar/ [1]
e-mail
offgridso...@sti.net [2]
text 209 813 0060

On Thu, 10 Sep 2020 11:12:31
-0700, Jeff Clearwater  wrote:  Yea I'm wondering the easiest way to get a
125 AMP Midnite Inverter Bypass assembly in a simple box for 2 Sol-Arks.
Midnite would be the perfect candidate for a simple support box (e-panel
style) for Stacked Sol-Arks.

 Any ideas?

 Thanks,

 Jeff

 Dave Angelini
Offgrid Solar wrote on 9/10/20 9:37 AM:

In an all in one, the good parts
are balanced, sometimes, by a small failure making the all in one useless.
Only a complete spare will save the day, or night...Also wonder about real
world surge capacity on 1 hp pumps and big air compressors. 

I am glad to
hear that they will be making this in Texas, rather than currently only in
China. Anyone have more on this please? 

AC bypass switching is a must for
SolArk. They need a PDP or some way to make this easier. The dual mppts are
perfect for virtual tracking. I begged for a dual mppt on the new Schneider
high voltage 100a mppt :( 

I wish them good luck and take back most of my
concerns. Hope they can make it!   

Dave Angelini Offgrid Solar
"we go
where powerlines don't"
http://members.sti.net/offgridsolar/ [3]
e-mail
offgridso...@sti.net [4]
text 209 813 0060

On Thu, 10 Sep 2020 07:44:36
-0400, Jason Szumlanski  [5] wrote:  There is a huge distinction in a
hybrid inverter that integrates MPPT charge control. Eliminating all of the
extraneous hardware and circuit protection associated with charge
controllers is very appealing. The 500V input limit is also a game-changer
in terms of wire size. I'm very interested in this approach.   On the flip
size, an AC Coupled approach is also appealing in a lot of circumstances.
Since Sol-Ark supports that, too, it's hard to find downsides other than
their infancy in the industry.   And for what it's worth, my experience
with SMA tech support recently has been abysmal. Long hold times and
getting bounced around departments.   Jason Szumlanski 

  On Wed, Sep 9, 2020 at 9:50 PM Mark Frye  wrote:   

The most important
thing here is that no one is standing up to sing the praises of either SMA
or Outback. 

I myself have sent about 2 hours on hold over 2 days trying
to get an issue addressed by SMA. 

Re: Sol-Arc I would pay a lot extra or
take some not so good aspect in exchange for good technical support. On
9/9/2020 1:12 PM, Jason Szumlanski wrote:Any tips on combining AC
output from these units when stacking several of them? What bus/OCPD system
are you using? Same question for generator/grid input.The solar MPPT
inputs appear to be dead simple.   Jason Szumlanski

  On Tue,
Sep 8, 2020 at 10:45 PM MiJo Nels  wrote:   we've found SolArk to be
SOLID!! .. And yes 8 inv yield about 96kW, with a TON of surge
capabilities..   Joe Nelson Project Manager C-46/C-10 Sustainable Energy
Group Inc., A California Corporation CSL# 868816
www.SustainableEnergyGroup.com [8] 530-273-4422 (Office) 530-217-8385
(Cell)       
-
 FROM: RE-wrenches  on behalf
of pgir...@mindspring.com [10] 
 SENT: Tuesday, September 8, 2020 1:24:03
PM
 TO: 'RE-wrenches' 
 SUBJECT: Re: [RE-wrenches] Microgrid... Outback or
SMA or other?  

I also suggest the Sol-Ark 12's. Extremely efficient,
simple to program, does a wonderful job in either ac coupling, stand alone
or pure off grid and terrific customer support. 

Peter Giroux 

ASAE


FROM: RE-wrenches  ON BEHALF OF Bryan Norkunas
 SENT: Tuesday, September
8, 2020 1:50 PM
 TO: 'RE-wrenches' 
 SUBJECT: Re: [RE-wrenches]
Microgrid... Outback or SMA or other?   

Sol-Arks would be possible, you
can link 8 inverters. 

BRYAN  

PV-CABLES 

FROM: RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org [15]] ON BEHALF OF Chris
Schaefer
 SENT: Tuesday, September 8, 2020 10:40 AM
 TO: RE-wrenches

SUBJECT: Re: [RE-wrenches] Microgrid... Outback or SMA or other? 

I'd
suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with their
12kw unit. Not sure what their max number of inverters are.  

Christopher 


On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield  wrote: 

Hey all,
I'm designing a microgrid sized off-grid system for somebody, and I'm just
wondering if anyone knows of any issues with the following designs...   


The client says he needs 70 kW. His load data looks pretty solid, so I'm
sticking to using that number as a minimum, at least during the initial
proposal stage. I only know of two possible equipment options for this size
range...   

* I thin

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-10 Thread Jeff Clearwater
I'm loving my first install of Sol Arks - One downside of Sol-Ark (and I 
can't find many!) is that the GEN terminal can only handle 1 of the 
following 3: Generator, AC Coupling, or Smart Load.  So if you want both 
a generator and AC coupling you have to either do a separate transfer 
switch for the GEN and not run it through the inverters - or you have to 
go with their internal DC MPPTif you do want the GEN to charge the 
batteries (unless you are off-grid totally and have no Grid in which 
case you might be able to run the Generator into Grid?  not sure about 
that - don't quote me!).


Anyone else with any downsides?

Best,

Jeff



Jason Szumlanski wrote on 9/10/20 4:44 AM:
There is a huge distinction in a hybrid inverter that integrates MPPT 
charge control. Eliminating all of the extraneous hardware and circuit 
protection associated with charge controllers is very appealing. The 
500V input limit is also a game-changer in terms of wire size. I'm 
very interested in this approach.


On the flip size, an AC Coupled approach is also appealing in a lot of 
circumstances. Since Sol-Ark supports that, too, it's hard to find 
downsides other than their infancy in the industry.


And for what it's worth, my experience with SMA tech support recently 
has been abysmal. Long hold times and getting bounced around departments.


Jason Szumlanski

*

*


On Wed, Sep 9, 2020 at 9:50 PM Mark Frye <mailto:ma...@berkeleysolar.com>> wrote:


The most important thing here is that no one is standing up to
sing the praises of either SMA or Outback.

I myself have sent about 2 hours on hold over 2 days trying to get
an issue addressed by SMA.

Re: Sol-Arc I would pay a lot extra or take some not so good
aspect in exchange for good technical support.

On 9/9/2020 1:12 PM, Jason Szumlanski wrote:

Any tips on combining AC output from these units when stacking
several of them? What bus/OCPD system are you using? Same
question for generator/grid input.

The solar MPPT inputs appear to be dead simple.

Jason Szumlanski







*

*


On Tue, Sep 8, 2020 at 10:45 PM MiJo Nels
mailto:spaceshipnels...@gmail.com>>
wrote:

we've found SolArk to be SOLID!! .. And yes 8 inv yield about
96kW, with a TON of surge capabilities..

Joe Nelson

Project Manager C-46/C-10
Sustainable Energy Group Inc., A California Corporation

CSL# 868816
www.SustainableEnergyGroup.com

<https://mailtrack.io/trace/link/8f0e320b52948f22a9ae9682bd3b5e9dc8d6c68f?url=http%3A%2F%2Fwww.SustainableEnergyGroup.com&userId=1613865&signature=e7d246f94af9a065>
530-273-4422 (Office)

530-217-8385 (Cell)



   



*From:* RE-wrenches
mailto:re-wrenches-boun...@lists.re-wrenches.org>> on behalf
of pgir...@mindspring.com <mailto:pgir...@mindspring.com>
mailto:pgir...@mindspring.com>>
*Sent:* Tuesday, September 8, 2020 1:24:03 PM
*To:* 'RE-wrenches' mailto:re-wrenches@lists.re-wrenches.org>>
*Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or
other?

I also suggest the Sol-Ark 12’s. Extremely efficient, simple
to program, does a wonderful job in either ac coupling, stand
alone or pure off grid and terrific customer support.

Peter Giroux

ASAE

*From:*RE-wrenches mailto:re-wrenches-boun...@lists.re-wrenches.org>> *On
Behalf Of *Bryan Norkunas
*Sent:* Tuesday, September 8, 2020 1:50 PM
    *To:* 'RE-wrenches' mailto:re-wrenches@lists.re-wrenches.org>>
*Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or
other?

Sol-Arks would be possible, you can link 8 inverters.

*Bryan *

*PV-Cables*

*From:*RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf
Of *Chris Schaefer
*Sent:* Tuesday, September 8, 2020 10:40 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or
other?

I'd suggest giving the crew at Sol-Ark a quick call @
972-575-8875 with their 12kw unit. Not sure what their max
number of inverters are.

Christopher

On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield
mailto:maxfieldso...@hotmail.com>> wrote:

Hey all, I'm designing a microgrid sized off-grid system
for somebody, and I'm just wondering if anyone knows of
any issues with the following designs...

The client says he needs 70 kW. His load data looks
pretty solid, so I'm sticking to using that number as a

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-10 Thread Jeff Clearwater
Yea I'm wondering the easiest way to get a 125 AMP Midnite Inverter 
Bypass assembly in a simple box for 2 Sol-Arks.  Midnite would be the 
perfect candidate for a simple support box (e-panel style) for Stacked 
Sol-Arks.


Any ideas?

Thanks,

Jeff

Dave Angelini Offgrid Solar wrote on 9/10/20 9:37 AM:


In an all in one, the good parts are balanced,  sometimes,  by a small 
failure making the all in one useless. Only a complete spare will save 
the day, or night...Also wonder about real world surge capacity on 1 
hp pumps and big air compressors.


I am glad to hear that they will be making this in Texas, rather than 
currently only in China. Anyone have more on this please?


AC bypass switching is a must for SolArk. They need a PDP or some way 
to make this easier. The dual mppts are perfect for virtual tracking. 
I begged for a dual mppt on the new Schneider high voltage 100a mppt :(


I wish them good luck and take back most of my concerns. Hope they can 
make it!


  
*Dave Angelini Offgrid Solar "we go where powerlines don't" 
http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net 
<mailto:offgridso...@sti.net> text 209 813 0060*


On Thu, 10 Sep 2020 07:44:36 -0400, Jason Szumlanski 
 wrote:


There is a huge distinction in a hybrid inverter that integrates MPPT 
charge control. Eliminating all of the extraneous hardware and 
circuit protection associated with charge controllers is very 
appealing. The 500V input limit is also a game-changer in terms of 
wire size. I'm very interested in this approach.
On the flip size, an AC Coupled approach is also appealing in a lot 
of circumstances. Since Sol-Ark supports that, too, it's hard to find 
downsides other than their infancy in the industry.
And for what it's worth, my experience with SMA tech support recently 
has been abysmal. Long hold times and getting bounced around departments.

Jason Szumlanski

On Wed, Sep 9, 2020 at 9:50 PM Mark Frye <mailto:ma...@berkeleysolar.com>> wrote:


The most important thing here is that no one is standing up to
sing the praises of either SMA or Outback.

I myself have sent about 2 hours on hold over 2 days trying to
get an issue addressed by SMA.

Re: Sol-Arc I would pay a lot extra or take some not so good
aspect in exchange for good technical support.

On 9/9/2020 1:12 PM, Jason Szumlanski wrote:

Any tips on combining AC output from these units when stacking
several of them? What bus/OCPD system are you using? Same
question for generator/grid input.
The solar MPPT inputs appear to be dead simple.
Jason Szumlanski




On Tue, Sep 8, 2020 at 10:45 PM MiJo Nels
mailto:spaceshipnels...@gmail.com>>
wrote:

we've found SolArk to be SOLID!! .. And yes 8 inv yield
about 96kW, with a TON of surge capabilities..
Joe Nelson
Project Manager C-46/C-10
Sustainable Energy Group Inc., A California Corporation
CSL# 868816
www.SustainableEnergyGroup.com

<https://mailtrack.io/trace/link/8f0e320b52948f22a9ae9682bd3b5e9dc8d6c68f?url=http%3A%2F%2Fwww.SustainableEnergyGroup.com&userId=1613865&signature=e7d246f94af9a065>
530-273-4422 (Office)
530-217-8385 (Cell)

   

*From:* RE-wrenches
mailto:re-wrenches-boun...@lists.re-wrenches.org>> on
behalf of pgir...@mindspring.com
<mailto:pgir...@mindspring.com> mailto:pgir...@mindspring.com>>
*Sent:* Tuesday, September 8, 2020 1:24:03 PM
        *To:* 'RE-wrenches' mailto:re-wrenches@lists.re-wrenches.org>>
*Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or
other?

I also suggest the Sol-Ark 12's. Extremely efficient, simple
to program, does a wonderful job in either ac coupling,
stand alone or pure off grid and terrific customer support.

Peter Giroux

ASAE

*From:*RE-wrenches
mailto:re-wrenches-boun...@lists.re-wrenches.org>> *On
Behalf Of *Bryan Norkunas
*Sent:* Tuesday, September 8, 2020 1:50 PM
    *To:* 'RE-wrenches' mailto:re-wrenches@lists.re-wrenches.org>>
*Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or
other?

Sol-Arks would be possible, you can link 8 inverters.

*Bryan *

*PV-Cables*

*From:*RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
    Behalf Of *Chris Schaefer
        *Sent:* Tuesday, September 8, 2020 10:40 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or
other?

I'd suggest giving the crew at Sol-Ark a quick call @
972-575-8875 with their 12k

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-10 Thread Dave Angelini Offgrid Solar


In an all in one, the good parts are balanced, sometimes, by a small
failure making the all in one useless. Only a complete spare will save the
day, or night...Also wonder about real world surge capacity on 1 hp pumps
and big air compressors. 

I am glad to hear that they will be making this
in Texas, rather than currently only in China. Anyone have more on this
please? 

AC bypass switching is a must for SolArk. They need a PDP or some
way to make this easier. The dual mppts are perfect for virtual tracking. I
begged for a dual mppt on the new Schneider high voltage 100a mppt :( 

I
wish them good luck and take back most of my concerns. Hope they can make
it!   

Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridso...@sti.net
[2]
text 209 813 0060

On Thu, 10 Sep 2020 07:44:36 -0400, Jason Szumlanski
wrote:  There is a huge distinction in a hybrid inverter that
integrates MPPT charge control. Eliminating all of the extraneous hardware
and circuit protection associated with charge controllers is very
appealing. The 500V input limit is also a game-changer in terms of wire
size. I'm very interested in this approach.   On the flip size, an AC
Coupled approach is also appealing in a lot of circumstances. Since Sol-Ark
supports that, too, it's hard to find downsides other than their infancy in
the industry.   And for what it's worth, my experience with SMA tech
support recently has been abysmal. Long hold times and getting bounced
around departments.   Jason Szumlanski  
  On Wed, Sep
9, 2020 at 9:50 PM Mark Frye  wrote:   

The most important thing here is
that no one is standing up to sing the praises of either SMA or Outback.


I myself have sent about 2 hours on hold over 2 days trying to get an
issue addressed by SMA. 

Re: Sol-Arc I would pay a lot extra or take some
not so good aspect in exchange for good technical support. On 9/9/2020 1:12
PM, Jason Szumlanski wrote:Any tips on combining AC output from these
units when stacking several of them? What bus/OCPD system are you using?
Same question for generator/grid input.The solar MPPT inputs appear to
be dead simple.   Jason Szumlanski

  On Tue, Sep 8, 2020 at
10:45 PM MiJo Nels  wrote:   we've found SolArk to be SOLID!! .. And yes 8
inv yield about 96kW, with a TON of surge capabilities.. 
   Joe Nelson
 
Project Manager C-46/C-10 Sustainable Energy Group Inc., A California
Corporation
  CSL# 868816 www.SustainableEnergyGroup.com [5] 530-273-4422
(Office)
  530-217-8385 (Cell)
  
     

-

FROM: RE-wrenches  on behalf of pgir...@mindspring.com [7] 
 SENT: Tuesday,
September 8, 2020 1:24:03 PM
 TO: 'RE-wrenches' 
 SUBJECT: Re:
[RE-wrenches] Microgrid... Outback or SMA or other?  

I also suggest
the Sol-Ark 12's. Extremely efficient, simple to program, does a wonderful
job in either ac coupling, stand alone or pure off grid and terrific
customer support. 

Peter Giroux 

ASAE 

FROM: RE-wrenches  ON BEHALF OF
Bryan Norkunas
 SENT: Tuesday, September 8, 2020 1:50 PM
 TO: 'RE-wrenches'

 SUBJECT: Re: [RE-wrenches] Microgrid... Outback or SMA or other?  


Sol-Arks would be possible, you can link 8 inverters. 

BRYAN 


PV-CABLES 

FROM: RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org [12]] ON BEHALF OF Chris
Schaefer
 SENT: Tuesday, September 8, 2020 10:40 AM
 TO: RE-wrenches

SUBJECT: Re: [RE-wrenches] Microgrid... Outback or SMA or other? 

I'd
suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with their
12kw unit. Not sure what their max number of inverters are.  

Christopher 


On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield  wrote: 

Hey all,
I'm designing a microgrid sized off-grid system for somebody, and I'm just
wondering if anyone knows of any issues with the following designs...   


The client says he needs 70 kW. His load data looks pretty solid, so I'm
sticking to using that number as a minimum, at least during the initial
proposal stage. I only know of two possible equipment options for this size
range...   

* I think I can use up to 10 Outback Radians, for up to an
80 kW system. Are there any bugs or problems with using this many inverters
on one hub? I know I've read about issues with selling to the grid, but
that's not an issue, this is off-grid.
* I know that the SMA cluster box
with sunny islands can allow for up to a 72 kW system. Do you know of any
bugs or problems with this system?

Are there any other options that anyone
would suggest? Schneider's website says they can only do up to 61 kW, and
Victron can only do up to 60 kW.   

I know that the Outback system would
yield a 240/120 Split-Phase system and that the SMA would yield a 208/120
3Ø system, but this doesn't really matter either way for this job.   


Thanks

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-10 Thread penobscotsolar
We've had great luck using the Tigo (and SMA) optimizers with SolArk to
conform to NEC2017 and CEC2018.


> There is a huge distinction in a hybrid inverter that integrates MPPT
> charge control. Eliminating all of the extraneous hardware and circuit
> protection associated with charge controllers is very appealing. The 500V
> input limit is also a game-changer in terms of wire size. I'm very
> interested in this approach.
>
> On the flip size, an AC Coupled approach is also appealing in a lot of
> circumstances. Since Sol-Ark supports that, too, it's hard to find
> downsides other than their infancy in the industry.
>
> And for what it's worth, my experience with SMA tech support recently has
> been abysmal. Long hold times and getting bounced around departments.
>
> Jason Szumlanski
>
>
>
> On Wed, Sep 9, 2020 at 9:50 PM Mark Frye  wrote:
>
>> The most important thing here is that no one is standing up to sing the
>> praises of either SMA or Outback.
>>
>> I myself have sent about 2 hours on hold over 2 days trying to get an
>> issue addressed by SMA.
>>
>> Re: Sol-Arc I would pay a lot extra or take some not so good aspect in
>> exchange for good technical support.
>> On 9/9/2020 1:12 PM, Jason Szumlanski wrote:
>>
>> Any tips on combining AC output from these units when stacking several
>> of
>> them? What bus/OCPD system are you using? Same question for
>> generator/grid
>> input.
>>
>> The solar MPPT inputs appear to be dead simple.
>>
>> Jason Szumlanski
>>
>>
>>
>>
>>
>>
>>
>>
>> On Tue, Sep 8, 2020 at 10:45 PM MiJo Nels 
>> wrote:
>>
>>> we've found SolArk to be SOLID!! .. And yes 8 inv yield about 96kW,
>>> with
>>> a TON of surge capabilities..
>>>
>>> Joe Nelson
>>>
>>> Project Manager C-46/C-10
>>> Sustainable Energy Group Inc., A California Corporation
>>>
>>> CSL# 868816
>>> www.SustainableEnergyGroup.com
>>> <https://mailtrack.io/trace/link/8f0e320b52948f22a9ae9682bd3b5e9dc8d6c68f?url=http%3A%2F%2Fwww.SustainableEnergyGroup.com&userId=1613865&signature=e7d246f94af9a065>
>>> 530-273-4422 (Office)
>>>
>>> 530-217-8385 (Cell)
>>>
>>> 
>>>
>>>    
>>>
>>>
>>> --
>>> *From:* RE-wrenches  on
>>> behalf of pgir...@mindspring.com 
>>> *Sent:* Tuesday, September 8, 2020 1:24:03 PM
>>> *To:* 'RE-wrenches' 
>>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>>
>>>
>>> I also suggest the Sol-Ark 12’s. Extremely efficient, simple to
>>> program,
>>> does a wonderful job in either ac coupling, stand alone or pure off
>>> grid
>>> and terrific customer support.
>>>
>>>
>>>
>>> Peter Giroux
>>>
>>> ASAE
>>>
>>>
>>>
>>> *From:* RE-wrenches  *On
>>> Behalf Of *Bryan Norkunas
>>> *Sent:* Tuesday, September 8, 2020 1:50 PM
>>> *To:* 'RE-wrenches' 
>>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>>
>>>
>>>
>>> Sol-Arks would be possible, you can link 8 inverters.
>>>
>>>
>>>
>>> *Bryan *
>>>
>>> *PV-Cables*
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
>>> ] *On Behalf Of *Chris
>>> Schaefer
>>> *Sent:* Tuesday, September 8, 2020 10:40 AM
>>> *To:* RE-wrenches
>>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>>
>>>
>>>
>>> I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with
>>> their 12kw unit. Not sure what their max number of inverters are.
>>>
>>>
>>>
>>> Christopher
>>>
>>>
>>>
>>> On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield
>>> 
>>> wrote:
>>>
>>> Hey all, I'm designing a microgrid sized off-grid system for somebody,
>>> and I'm just wondering if anyone knows of any issues with the following
>>> designs...
>>>
>>>
>>>
>>> The client says he needs 70 kW. His load data l

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-10 Thread Jason Szumlanski
There is a huge distinction in a hybrid inverter that integrates MPPT
charge control. Eliminating all of the extraneous hardware and circuit
protection associated with charge controllers is very appealing. The 500V
input limit is also a game-changer in terms of wire size. I'm very
interested in this approach.

On the flip size, an AC Coupled approach is also appealing in a lot of
circumstances. Since Sol-Ark supports that, too, it's hard to find
downsides other than their infancy in the industry.

And for what it's worth, my experience with SMA tech support recently has
been abysmal. Long hold times and getting bounced around departments.

Jason Szumlanski



On Wed, Sep 9, 2020 at 9:50 PM Mark Frye  wrote:

> The most important thing here is that no one is standing up to sing the
> praises of either SMA or Outback.
>
> I myself have sent about 2 hours on hold over 2 days trying to get an
> issue addressed by SMA.
>
> Re: Sol-Arc I would pay a lot extra or take some not so good aspect in
> exchange for good technical support.
> On 9/9/2020 1:12 PM, Jason Szumlanski wrote:
>
> Any tips on combining AC output from these units when stacking several of
> them? What bus/OCPD system are you using? Same question for generator/grid
> input.
>
> The solar MPPT inputs appear to be dead simple.
>
> Jason Szumlanski
>
>
>
>
>
>
>
>
> On Tue, Sep 8, 2020 at 10:45 PM MiJo Nels 
> wrote:
>
>> we've found SolArk to be SOLID!! .. And yes 8 inv yield about 96kW, with
>> a TON of surge capabilities..
>>
>> Joe Nelson
>>
>> Project Manager C-46/C-10
>> Sustainable Energy Group Inc., A California Corporation
>>
>> CSL# 868816
>> www.SustainableEnergyGroup.com
>> <https://mailtrack.io/trace/link/8f0e320b52948f22a9ae9682bd3b5e9dc8d6c68f?url=http%3A%2F%2Fwww.SustainableEnergyGroup.com&userId=1613865&signature=e7d246f94af9a065>
>> 530-273-4422 (Office)
>>
>> 530-217-8385 (Cell)
>>
>> 
>>
>>    
>>
>>
>> --
>> *From:* RE-wrenches  on
>> behalf of pgir...@mindspring.com 
>> *Sent:* Tuesday, September 8, 2020 1:24:03 PM
>> *To:* 'RE-wrenches' 
>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>
>>
>> I also suggest the Sol-Ark 12’s. Extremely efficient, simple to program,
>> does a wonderful job in either ac coupling, stand alone or pure off grid
>> and terrific customer support.
>>
>>
>>
>> Peter Giroux
>>
>> ASAE
>>
>>
>>
>> *From:* RE-wrenches  *On
>> Behalf Of *Bryan Norkunas
>> *Sent:* Tuesday, September 8, 2020 1:50 PM
>> *To:* 'RE-wrenches' 
>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>
>>
>>
>> Sol-Arks would be possible, you can link 8 inverters.
>>
>>
>>
>> *Bryan *
>>
>> *PV-Cables*
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
>> ] *On Behalf Of *Chris
>> Schaefer
>> *Sent:* Tuesday, September 8, 2020 10:40 AM
>> *To:* RE-wrenches
>> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>>
>>
>>
>> I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with
>> their 12kw unit. Not sure what their max number of inverters are.
>>
>>
>>
>> Christopher
>>
>>
>>
>> On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield 
>> wrote:
>>
>> Hey all, I'm designing a microgrid sized off-grid system for somebody,
>> and I'm just wondering if anyone knows of any issues with the following
>> designs...
>>
>>
>>
>> The client says he needs 70 kW. His load data looks pretty solid, so I'm
>> sticking to using that number as a minimum, at least during the initial
>> proposal stage. I only know of two possible equipment options for this size
>> range...
>>
>>
>>
>>1. I think I can use up to 10 Outback Radians, for up to an 80 kW
>>system. Are there any bugs or problems with using this many inverters on
>>one hub? I know I've read about issues with selling to the grid, but 
>> that's
>>not an issue, this is off-grid.
>>2. I know that the SMA cluster box with sunny islands can allow for
>>up to a 72 kW system. Do you know of any bugs or problems with this 
>> system?
>>
>>
>>
>>
>>
>> Are there any o

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-10 Thread penobscotsolar
Hey Bill,
   They're still small enough that, at least so far, there is no hold music!
And we combine ac outputs with an "ac combiner panel" simply a single
phase or three phase panel, with each inverter feeding a breaker in that
panel and ensuring that we use either a main breaker that can be back fed
or a panel with feed through lugs. It is simple and safe and code
compliant.


Daryl





> OK, I'll bite.  I use SMA and Outback almost exclusively.  SMA for
> grid-tie so I can't vouch for SI for Off-grid and I don't seem to have
> the same wait problem with SMA, its usually 10-20 minutes.
>
>              And Outback well they're not perfect but I've been
> using there stuff since day 1 (thanks Bob-O), still using FX3524 ser#
> 0007 and been installing since they were Trace. Service?  well, let's
> just say it varies but I've been willing to put up with it.  The WORST
> part of of Outback service calls is the music they pipe in on
> 'hold'...its enough to make you hang up.
>
>              Sol-ark, the new kid on the block sounds slick and I'm
> genuinely tempted, specs look great..wonder what their 'hold' music is
> like?
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
>
> On 9/9/2020 6:49 PM, Mark Frye wrote:
>>
>> The most important thing here is that no one is standing up to sing
>> the praises of either SMA or Outback.
>>
>> I myself have sent about 2 hours on hold over 2 days trying to get an
>> issue addressed by SMA.
>>
>> Re: Sol-Arc I would pay a lot extra or take some not so good aspect in
>> exchange for good technical support.
>>
>> On 9/9/2020 1:12 PM, Jason Szumlanski wrote:
>>> Any tips on combining AC output from these units when stacking
>>> several of them? What bus/OCPD system are you using? Same question
>>> for generator/grid input.
>>>
>>> The solar MPPT inputs appear to be dead simple.
>>>
>>> Jason Szumlanski
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>
>
>
> --
> This email has been checked for viruses by Avast antivirus software.
> https://www.avast.com/antivirus
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-10 Thread Mac Lewis
The largest we've done is a 4 stack of 8k Radians and a 6 stack of Sunny
Islands with the Mutlicluster box.  They both have worked fine and there
are advantages to each approach.

An advantage to a multicluster approach is that you can have smaller and
segmented battery banks that don't require custom DC bussing.  Each cluster
master manages the battery bank.  The solar input can go straight into the
multicluster box since AC coupling works very well with SMA equipment.

Things get very busy with a Radian system quickly.  We had to use a custom
bussing system to combine the battery banks at around 1500A and miles of
4/0 cable to feed more bussing for the solar input and Radian connection.

Regarding getting the AC in and out of the Radian, we opted to use
dedicated panelboards for both the input and the output with double pole
60A breakers feeding in and out of each Radian.  It's also a good idea to
have a bypass switch upstream of the AC input panelboard that can bypass
the system if needed.

Both of these systems worked well but took a lot of planning for the
spatial layout and took a lot of wall space, much more than we initially
thought.

Good Luck and let us know which approach you take.

On Wed, Sep 9, 2020 at 10:20 PM frenergy  wrote:

> OK, I'll bite.  I use SMA and Outback almost exclusively.  SMA for
> grid-tie so I can't vouch for SI for Off-grid and I don't seem to have the
> same wait problem with SMA, its usually 10-20 minutes.
>
> And Outback well they're not perfect but I've been using
> there stuff since day 1 (thanks Bob-O), still using FX3524 ser# 0007 and
> been installing since they were Trace.  Service?  well, let's just say it
> varies but I've been willing to put up with it.  The WORST part of of
> Outback service calls is the music they pipe in on 'hold'...its enough to
> make you hang up.
>
> Sol-ark, the new kid on the block sounds slick and I'm
> genuinely tempted, specs look great..wonder what their 'hold' music is like?
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049www.frenergy.net
>
> On 9/9/2020 6:49 PM, Mark Frye wrote:
>
> The most important thing here is that no one is standing up to sing the
> praises of either SMA or Outback.
>
> I myself have sent about 2 hours on hold over 2 days trying to get an
> issue addressed by SMA.
>
> Re: Sol-Arc I would pay a lot extra or take some not so good aspect in
> exchange for good technical support.
> On 9/9/2020 1:12 PM, Jason Szumlanski wrote:
>
> Any tips on combining AC output from these units when stacking several of
> them? What bus/OCPD system are you using? Same question for generator/grid
> input.
>
> The solar MPPT inputs appear to be dead simple.
>
> Jason Szumlanski
>
>
>
>
>
>
>
>
> --
> [image: Avast logo] 
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com 
>
> <#m_3055688145284475229_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-09 Thread frenergy
OK, I'll bite.  I use SMA and Outback almost exclusively.  SMA for 
grid-tie so I can't vouch for SI for Off-grid and I don't seem to have 
the same wait problem with SMA, its usually 10-20 minutes.


            And Outback well they're not perfect but I've been 
using there stuff since day 1 (thanks Bob-O), still using FX3524 ser# 
0007 and been installing since they were Trace. Service?  well, let's 
just say it varies but I've been willing to put up with it.  The WORST 
part of of Outback service calls is the music they pipe in on 
'hold'...its enough to make you hang up.


            Sol-ark, the new kid on the block sounds slick and I'm 
genuinely tempted, specs look great..wonder what their 'hold' music is like?


Bill

Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net

On 9/9/2020 6:49 PM, Mark Frye wrote:


The most important thing here is that no one is standing up to sing 
the praises of either SMA or Outback.


I myself have sent about 2 hours on hold over 2 days trying to get an 
issue addressed by SMA.


Re: Sol-Arc I would pay a lot extra or take some not so good aspect in 
exchange for good technical support.


On 9/9/2020 1:12 PM, Jason Szumlanski wrote:
Any tips on combining AC output from these units when stacking 
several of them? What bus/OCPD system are you using? Same question 
for generator/grid input.


The solar MPPT inputs appear to be dead simple.

Jason Szumlanski











--
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-09 Thread Mark Frye
The most important thing here is that no one is standing up to sing the 
praises of either SMA or Outback.


I myself have sent about 2 hours on hold over 2 days trying to get an 
issue addressed by SMA.


Re: Sol-Arc I would pay a lot extra or take some not so good aspect in 
exchange for good technical support.


On 9/9/2020 1:12 PM, Jason Szumlanski wrote:
Any tips on combining AC output from these units when stacking several 
of them? What bus/OCPD system are you using? Same question for 
generator/grid input.


The solar MPPT inputs appear to be dead simple.

Jason Szumlanski







*

*


On Tue, Sep 8, 2020 at 10:45 PM MiJo Nels <mailto:spaceshipnels...@gmail.com>> wrote:


we've found SolArk to be SOLID!! .. And yes 8 inv yield about
96kW, with a TON of surge capabilities..

Joe Nelson

Project Manager C-46/C-10
Sustainable Energy Group Inc., A California Corporation

CSL# 868816
www.SustainableEnergyGroup.com

<https://mailtrack.io/trace/link/a79a94610bdfe9a8c1b0480229481ccc0945e36a?url=http%3A%2F%2Fwww.SustainableEnergyGroup.com&userId=1613865&signature=628892195b38f17d>
530-273-4422 (Office)

530-217-8385 (Cell)



   



*From:* RE-wrenches mailto:re-wrenches-boun...@lists.re-wrenches.org>> on behalf of
pgir...@mindspring.com <mailto:pgir...@mindspring.com>
mailto:pgir...@mindspring.com>>
*Sent:* Tuesday, September 8, 2020 1:24:03 PM
*To:* 'RE-wrenches' mailto:re-wrenches@lists.re-wrenches.org>>
    *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?

I also suggest the Sol-Ark 12’s. Extremely efficient, simple to
program, does a wonderful job in either ac coupling, stand alone
or pure off grid and terrific customer support.

Peter Giroux

ASAE

*From:*RE-wrenches mailto:re-wrenches-boun...@lists.re-wrenches.org>> *On Behalf Of
*Bryan Norkunas
*Sent:* Tuesday, September 8, 2020 1:50 PM
*To:* 'RE-wrenches' mailto:re-wrenches@lists.re-wrenches.org>>
*Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?

Sol-Arks would be possible, you can link 8 inverters.

*Bryan *

*PV-Cables*

*From:*RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*Chris Schaefer
*Sent:* Tuesday, September 8, 2020 10:40 AM
    *To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?

I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875
with their 12kw unit. Not sure what their max number of inverters are.

Christopher

On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield
mailto:maxfieldso...@hotmail.com>> wrote:

Hey all, I'm designing a microgrid sized off-grid system for
somebody, and I'm just wondering if anyone knows of any issues
with the following designs...

The client says he needs 70 kW. His load data looks pretty
solid, so I'm sticking to using that number as a minimum, at
least during the initial proposal stage. I only know of two
possible equipment options for this size range...

 1. I think I can use up to 10 Outback Radians, for up to an
80 kW system. Are there any bugs or problems with using
this many inverters on one hub? I know I've read about
issues with selling to the grid, but that's not an issue,
this is off-grid.
 2. I know that the SMA cluster box with sunny islands can
allow for up to a 72 kW system. Do you know of any bugs or
problems with this system?

Are there any other options that anyone would suggest?
Schneider's website says they can only do up to 61 kW, and
Victron can only do up to 60 kW.

I know that the Outback system would yield a 240/120
Split-Phase system and that the SMA would yield a 208/120 3Ø
system, but this doesn't really matter either way for this job.

Thanks so much,

Kienan

*Maxfield Solar*

*maxfieldso...@hotmail.com* <mailto:maxfieldso...@hotmail.com>

*(801) 631-5584 (Cell)***

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

<https://mailtrack.io/trace/link/37324a803ab135ce4f6abd4943a96852954122c7?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=422bba15ca9ac17c>

List-Archive:
 

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-09 Thread Jason Szumlanski
Any tips on combining AC output from these units when stacking several of
them? What bus/OCPD system are you using? Same question for generator/grid
input.

The solar MPPT inputs appear to be dead simple.

Jason Szumlanski




On Tue, Sep 8, 2020 at 10:45 PM MiJo Nels 
wrote:

> we've found SolArk to be SOLID!! .. And yes 8 inv yield about 96kW, with a
> TON of surge capabilities..
>
> Joe Nelson
>
> Project Manager C-46/C-10
> Sustainable Energy Group Inc., A California Corporation
>
> CSL# 868816
> www.SustainableEnergyGroup.com
> <https://mailtrack.io/trace/link/a79a94610bdfe9a8c1b0480229481ccc0945e36a?url=http%3A%2F%2Fwww.SustainableEnergyGroup.com&userId=1613865&signature=628892195b38f17d>
> 530-273-4422 (Office)
>
> 530-217-8385 (Cell)
>
> 
>
>    
>
>
> --
> *From:* RE-wrenches  on behalf
> of pgir...@mindspring.com 
> *Sent:* Tuesday, September 8, 2020 1:24:03 PM
> *To:* 'RE-wrenches' 
> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>
>
> I also suggest the Sol-Ark 12’s. Extremely efficient, simple to program,
> does a wonderful job in either ac coupling, stand alone or pure off grid
> and terrific customer support.
>
>
>
> Peter Giroux
>
> ASAE
>
>
>
> *From:* RE-wrenches  *On
> Behalf Of *Bryan Norkunas
> *Sent:* Tuesday, September 8, 2020 1:50 PM
> *To:* 'RE-wrenches' 
> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>
>
>
> Sol-Arks would be possible, you can link 8 inverters.
>
>
>
> *Bryan *
>
> *PV-Cables*
>
>
>
>
>
>
>
>
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
> ] *On Behalf Of *Chris Schaefer
> *Sent:* Tuesday, September 8, 2020 10:40 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>
>
>
> I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with
> their 12kw unit. Not sure what their max number of inverters are.
>
>
>
> Christopher
>
>
>
> On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield 
> wrote:
>
> Hey all, I'm designing a microgrid sized off-grid system for somebody, and
> I'm just wondering if anyone knows of any issues with the following
> designs...
>
>
>
> The client says he needs 70 kW. His load data looks pretty solid, so I'm
> sticking to using that number as a minimum, at least during the initial
> proposal stage. I only know of two possible equipment options for this size
> range...
>
>
>
>1. I think I can use up to 10 Outback Radians, for up to an 80 kW
>system. Are there any bugs or problems with using this many inverters on
>one hub? I know I've read about issues with selling to the grid, but that's
>not an issue, this is off-grid.
>2. I know that the SMA cluster box with sunny islands can allow for up
>to a 72 kW system. Do you know of any bugs or problems with this system?
>
>
>
>
>
> Are there any other options that anyone would suggest? Schneider's website
> says they can only do up to 61 kW, and Victron can only do up to 60 kW.
>
>
>
>
>
> I know that the Outback system would yield a 240/120 Split-Phase system
> and that the SMA would yield a 208/120 3Ø system, but this doesn't really
> matter either way for this job.
>
>
>
> Thanks so much,
>
> Kienan
>
>
>
>
>
> *Maxfield Solar*
>
> *maxfieldso...@hotmail.com* 
>
> *(801) 631-5584 (Cell)*
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/37324a803ab135ce4f6abd4943a96852954122c7?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=422bba15ca9ac17c>
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/2190cd706faec5c590faf0036321741ce879e7c1?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=6ef73e07203fddf4>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/87baaab45bd57bc31753a44cdc40e0e4a60915e2?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=9c9c3d731088>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> &

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-09 Thread penobscotsolar
What do you see, Dave? We have 6 12 kW and two 8 kW installed so far in
the Bahamas and two here in Maine, all with Fortress batteries, and I
cannot be more pleased. I do wish they had a remote monitor panel for
easier at home monitoring and I guess I would rather they had their own
monitoring system instead of Powerview, but compared to others I am
thrilled at the ease of installation and programming, zero service calls
and wireless connectivity for monitoring over the internet.

Thanks,
Daryl



>
>
> Due diligence on Sol Arc. I would look at them harder if I were you!
>
>
> Dave Angelini Offgrid Solar
> "we go where powerlines
> don't"
> http://members.sti.net/offgridsolar/ [1]
> e-mail offgridso...@sti.net
> [2]
> text 209 813 0060
>
> On Wed, 9 Sep 2020 15:32:51 +, Kienan Maxfield
> wrote: Thank you all so much for the suggestions!! I hadn't thought of
> SolArk, but I'll have to include that in my proposals. It sounds like
> they've really gathered quite a following.   Thanks, Kienan
>  MAXFIELD
> SOLAR maxfieldso...@hotmail.com [3]  (801) 631-5584 (CELL)
>
> -
>  FROM: RE-wrenches  on behalf of Jay
>  SENT:
> Tuesday, September 8, 2020 8:50 PM
>  TO: RE-wrenches
>  SUBJECT: Re:
> [RE-wrenches] Microgrid... Outback or SMA or other? Hi Joe   A
> correction   Both the 8 and 12kw are 9 kw inverters In off grid mode
> according to the specs.For grid selling the 12kw is 12 kw.Jay
> Peltz
> power
>  On Sep 8, 2020, at 7:45 PM, MiJo Nels  wrote:
>  we've found
> SolArk to be SOLID!! .. And yes 8 inv yield about 96kW, with a TON of
> surge
> capabilities..
>Joe Nelson
>   Project Manager C-46/C-10 Sustainable
> Energy Group Inc., A California Corporation
>   CSL# 868816
> www.SustainableEnergyGroup.com [4] 530-273-4422 (Office)
>   530-217-8385
> (Cell)
>   
>      
>
> -----
>  FROM: RE-wrenches  on
> behalf of pgir...@mindspring.com
>  SENT: Tuesday, September 8, 2020 1:24:03
> PM
>  TO: 'RE-wrenches'
>  SUBJECT: Re: [RE-wrenches] Microgrid... Outback or
> SMA or other?
>
> I also suggest the Sol-Ark 12's. Extremely efficient,
> simple to program, does a wonderful job in either ac coupling, stand alone
> or pure off grid and terrific customer support.
>
> Peter Giroux
>
> ASAE
>
>
> FROM: RE-wrenches  ON BEHALF OF Bryan Norkunas
>  SENT: Tuesday, September
> 8, 2020 1:50 PM
>  TO: 'RE-wrenches'
>  SUBJECT: Re: [RE-wrenches]
> Microgrid... Outback or SMA or other?
>
> Sol-Arks would be possible, you
> can link 8 inverters.
>
> BRYAN
>
> PV-CABLES
>
> FROM: RE-wrenches
> [mailto:re-wrenches-boun...@lists.re-wrenches.org [5]] ON BEHALF OF Chris
> Schaefer
>  SENT: Tuesday, September 8, 2020 10:40 AM
>  TO: RE-wrenches
>
> SUBJECT: Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>
> I'd
> suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with their
> 12kw unit. Not sure what their max number of inverters are.
>
> Christopher
>
>
> On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield  wrote:
>
> Hey all,
> I'm designing a microgrid sized off-grid system for somebody, and I'm just
> wondering if anyone knows of any issues with the following designs...
>
>
> The client says he needs 70 kW. His load data looks pretty solid, so I'm
> sticking to using that number as a minimum, at least during the initial
> proposal stage. I only know of two possible equipment options for this
> size
> range...
>
>   * I think I can use up to 10 Outback Radians, for up to an
> 80 kW system. Are there any bugs or problems with using this many
> inverters
> on one hub? I know I've read about issues with selling to the grid, but
> that's not an issue, this is off-grid.
>   * I know that the SMA cluster box
> with sunny islands can allow for up to a 72 kW system. Do you know of any
> bugs or problems with this system?
>
> Are there any other options that anyone
> would suggest? Schneider's website says they can only do up to 61 kW, and
> Victron can only do up to 60 kW.
>
> I know that the Outback system would
> yield a 240/120 Split-Phase system and that the SMA would yield a 208/120
> 3Ø system, but this doesn't really matter either way for this job.
>
>
> Thanks so much,
>
> Kienan
>
> MAXFIELD SOLAR
>
>
> maxfieldso...@hotmail.com [7]
>
> (801) 631-5584 (CELL)
>
>
> ___
>  List sponsored by
> Redwood Alliance
>
>  List Address:  RE-wrenches@lists.re-wrenches.org [8]
>
>

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-09 Thread Dave Angelini Offgrid Solar


Due diligence on Sol Arc. I would look at them harder if I were you! 


Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridso...@sti.net
[2]
text 209 813 0060

On Wed, 9 Sep 2020 15:32:51 +, Kienan Maxfield 
wrote: Thank you all so much for the suggestions!! I hadn't thought of
SolArk, but I'll have to include that in my proposals. It sounds like
they've really gathered quite a following.   Thanks, Kienan 
 MAXFIELD
SOLAR maxfieldso...@hotmail.com [3]  (801) 631-5584 (CELL)

-
 FROM: RE-wrenches  on behalf of Jay 
 SENT:
Tuesday, September 8, 2020 8:50 PM
 TO: RE-wrenches 
 SUBJECT: Re:
[RE-wrenches] Microgrid... Outback or SMA or other? Hi Joe   A
correction   Both the 8 and 12kw are 9 kw inverters In off grid mode
according to the specs.For grid selling the 12kw is 12 kw.Jay Peltz
power 
 On Sep 8, 2020, at 7:45 PM, MiJo Nels  wrote:
 we've found
SolArk to be SOLID!! .. And yes 8 inv yield about 96kW, with a TON of surge
capabilities.. 
   Joe Nelson
  Project Manager C-46/C-10 Sustainable
Energy Group Inc., A California Corporation
  CSL# 868816
www.SustainableEnergyGroup.com [4] 530-273-4422 (Office)
  530-217-8385
(Cell)
  
     

-
 FROM: RE-wrenches  on
behalf of pgir...@mindspring.com 
 SENT: Tuesday, September 8, 2020 1:24:03
PM
 TO: 'RE-wrenches' 
 SUBJECT: Re: [RE-wrenches] Microgrid... Outback or
SMA or other?  

I also suggest the Sol-Ark 12's. Extremely efficient,
simple to program, does a wonderful job in either ac coupling, stand alone
or pure off grid and terrific customer support. 

Peter Giroux 

ASAE


FROM: RE-wrenches  ON BEHALF OF Bryan Norkunas
 SENT: Tuesday, September
8, 2020 1:50 PM
 TO: 'RE-wrenches' 
 SUBJECT: Re: [RE-wrenches]
Microgrid... Outback or SMA or other?   

Sol-Arks would be possible, you
can link 8 inverters. 

BRYAN  

PV-CABLES 

FROM: RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org [5]] ON BEHALF OF Chris
Schaefer
 SENT: Tuesday, September 8, 2020 10:40 AM
 TO: RE-wrenches

SUBJECT: Re: [RE-wrenches] Microgrid... Outback or SMA or other? 

I'd
suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with their
12kw unit. Not sure what their max number of inverters are.  

Christopher 


On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield  wrote: 

Hey all,
I'm designing a microgrid sized off-grid system for somebody, and I'm just
wondering if anyone knows of any issues with the following designs...   


The client says he needs 70 kW. His load data looks pretty solid, so I'm
sticking to using that number as a minimum, at least during the initial
proposal stage. I only know of two possible equipment options for this size
range...   

* I think I can use up to 10 Outback Radians, for up to an
80 kW system. Are there any bugs or problems with using this many inverters
on one hub? I know I've read about issues with selling to the grid, but
that's not an issue, this is off-grid.
* I know that the SMA cluster box
with sunny islands can allow for up to a 72 kW system. Do you know of any
bugs or problems with this system?

Are there any other options that anyone
would suggest? Schneider's website says they can only do up to 61 kW, and
Victron can only do up to 60 kW.   

I know that the Outback system would
yield a 240/120 Split-Phase system and that the SMA would yield a 208/120
3Ø system, but this doesn't really matter either way for this job.   


Thanks so much,   

Kienan   

MAXFIELD SOLAR  


maxfieldso...@hotmail.com [7]

(801) 631-5584 (CELL)   


___
 List sponsored by
Redwood Alliance

 List Address:  RE-wrenches@lists.re-wrenches.org [8]


Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [9]


List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org [10]


List rules ">Chris Schaefer's

 Tel/Fax 585-229-2083 or Cell 585-748-1870 

5115 South Hill Road ~ Canandaigua New York 14424
 www.solarandwindfx.com
[13] ~ E-mail: _ch...@solarandwindfx.com [14]_ 

Thomas Jefferson, the
author of our great Constitution, once said, "democracy" will cease to
exist when you take away from those who are willing to work and give to
those who would not."

 [15]
Virus-free.  www.avg.com [16]

 
___
 List sponsored by Redwood
Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change
listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List
rules & etiquette:
 www.re-wrenches.org/et

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-09 Thread Kienan Maxfield
Thank you all so much for the suggestions!! I hadn't thought of SolArk, but 
I'll have to include that in my proposals. It sounds like they've really 
gathered quite a following.

Thanks,
Kienan


Maxfield Solar
maxfieldso...@hotmail.com<mailto:maxfieldso...@hotmail.com>
(801) 631-5584 (Cell)

From: RE-wrenches  on behalf of Jay 

Sent: Tuesday, September 8, 2020 8:50 PM
To: RE-wrenches 
Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?

Hi Joe

A correction

Both the 8 and 12kw are 9 kw inverters
In off grid mode according to the specs.

For grid selling the 12kw is 12 kw.

Jay
Peltz power

On Sep 8, 2020, at 7:45 PM, MiJo Nels  wrote:


we've found SolArk to be SOLID!! .. And yes 8 inv yield about 96kW, with a TON 
of surge capabilities..

Joe Nelson

Project Manager C-46/C-10
Sustainable Energy Group Inc., A California Corporation

CSL# 868816
www.SustainableEnergyGroup.com<http://www.SustainableEnergyGroup.com>
530-273-4422 (Office)

530-217-8385 (Cell)



   



From: RE-wrenches  on behalf of 
pgir...@mindspring.com 
Sent: Tuesday, September 8, 2020 1:24:03 PM
To: 'RE-wrenches' 
Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?


I also suggest the Sol-Ark 12’s. Extremely efficient, simple to program, does a 
wonderful job in either ac coupling, stand alone or pure off grid and terrific 
customer support.



Peter Giroux

ASAE



From: RE-wrenches  On Behalf Of 
Bryan Norkunas
Sent: Tuesday, September 8, 2020 1:50 PM
To: 'RE-wrenches' 
Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?



Sol-Arks would be possible, you can link 8 inverters.



Bryan

PV-Cables













From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Chris Schaefer
Sent: Tuesday, September 8, 2020 10:40 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?



I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with their 
12kw unit. Not sure what their max number of inverters are.



Christopher



On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield 
mailto:maxfieldso...@hotmail.com>> wrote:

Hey all, I'm designing a microgrid sized off-grid system for somebody, and I'm 
just wondering if anyone knows of any issues with the following designs...



The client says he needs 70 kW. His load data looks pretty solid, so I'm 
sticking to using that number as a minimum, at least during the initial 
proposal stage. I only know of two possible equipment options for this size 
range...



  1.  I think I can use up to 10 Outback Radians, for up to an 80 kW system. 
Are there any bugs or problems with using this many inverters on one hub? I 
know I've read about issues with selling to the grid, but that's not an issue, 
this is off-grid.
  2.  I know that the SMA cluster box with sunny islands can allow for up to a 
72 kW system. Do you know of any bugs or problems with this system?





Are there any other options that anyone would suggest? Schneider's website says 
they can only do up to 61 kW, and Victron can only do up to 60 kW.





I know that the Outback system would yield a 240/120 Split-Phase system and 
that the SMA would yield a 208/120 3Ø system, but this doesn't really matter 
either way for this job.



Thanks so much,

Kienan





Maxfield Solar

maxfieldso...@hotmail.com<mailto:maxfieldso...@hotmail.com>

(801) 631-5584 (Cell)

___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>




--

Chris Schaefer’s
<http://www.solarandwindfx.com/>



Tel/Fax 585-229-2083 or Cell 585-748-1870
5115 South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.com<http://www.solarandwindfx.com> ~ E-mail: 
ch...@solarandwindfx.com<mailto:ch...@solarandwindfx.com>



Thomas Jefferson, the author of our great Constitution, once said, "democracy" 
will cease to exist when you take away from those who are willing to work and 
give to those who would not."

[https://ipmcdn.avast.com/images/icons/icon-envelope-tick-green-avg-v1.png]<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 Virus-free. 
www.avg.com<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign

Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-08 Thread Jay
Hi Joe

A correction

Both the 8 and 12kw are 9 kw inverters
In off grid mode according to the specs. 

For grid selling the 12kw is 12 kw.  

Jay
Peltz power

> On Sep 8, 2020, at 7:45 PM, MiJo Nels  wrote:
> 
> 
> we've found SolArk to be SOLID!! .. And yes 8 inv yield about 96kW, with a 
> TON of surge capabilities.. 
> 
> Joe Nelson
> 
> Project Manager C-46/C-10
> Sustainable Energy Group Inc., A California Corporation
> 
> CSL# 868816
> www.SustainableEnergyGroup.com
> 530-273-4422 (Office)
> 
> 530-217-8385 (Cell)
> 
> 
> 
>    
> 
> 
> From: RE-wrenches  on behalf of 
> pgir...@mindspring.com 
> Sent: Tuesday, September 8, 2020 1:24:03 PM
> To: 'RE-wrenches' 
> Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>  
> I also suggest the Sol-Ark 12’s. Extremely efficient, simple to program, does 
> a wonderful job in either ac coupling, stand alone or pure off grid and 
> terrific customer support.
>  
> Peter Giroux
> ASAE
>  
> From: RE-wrenches  On Behalf Of 
> Bryan Norkunas
> Sent: Tuesday, September 8, 2020 1:50 PM
> To: 'RE-wrenches' 
> Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>  
> Sol-Arks would be possible, you can link 8 inverters.
>  
> Bryan
> PV-Cables
>  
>  
>  
>  
>  
>  
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On 
> Behalf Of Chris Schaefer
> Sent: Tuesday, September 8, 2020 10:40 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?
>  
> I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with their 
> 12kw unit. Not sure what their max number of inverters are.
>  
> Christopher
>  
> On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield  
> wrote:
> Hey all, I'm designing a microgrid sized off-grid system for somebody, and 
> I'm just wondering if anyone knows of any issues with the following 
> designs... 
>  
> The client says he needs 70 kW. His load data looks pretty solid, so I'm 
> sticking to using that number as a minimum, at least during the initial 
> proposal stage. I only know of two possible equipment options for this size 
> range...
>  
> I think I can use up to 10 Outback Radians, for up to an 80 kW system. Are 
> there any bugs or problems with using this many inverters on one hub? I know 
> I've read about issues with selling to the grid, but that's not an issue, 
> this is off-grid.
> I know that the SMA cluster box with sunny islands can allow for up to a 72 
> kW system. Do you know of any bugs or problems with this system?
>  
>  
> Are there any other options that anyone would suggest? Schneider's website 
> says they can only do up to 61 kW, and Victron can only do up to 60 kW.
>  
>  
> I know that the Outback system would yield a 240/120 Split-Phase system and 
> that the SMA would yield a 208/120 3Ø system, but this doesn't really matter 
> either way for this job. 
>  
> Thanks so much,
> Kienan
>  
>  
> Maxfield Solar
> maxfieldso...@hotmail.com
> (801) 631-5584 (Cell)
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 
>  
> --
> Chris Schaefer’s
> 
> 
> Tel/Fax 585-229-2083 or Cell 585-748-1870 
> 5115 South Hill Road ~ Canandaigua New York 14424
> www.solarandwindfx.com ~ E-mail: ch...@solarandwindfx.com
> 
> 
> 
> Thomas Jefferson, the author of our great Constitution, once said, 
> "democracy" will cease to exist when you take away from those who are willing 
> to work and give to those who would not."
> 
> 
>   Virus-free. www.avg.com
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-08 Thread MiJo Nels
we've found SolArk to be SOLID!! .. And yes 8 inv yield about 96kW, with a TON 
of surge capabilities..

Joe Nelson

Project Manager C-46/C-10
Sustainable Energy Group Inc., A California Corporation

CSL# 868816
www.SustainableEnergyGroup.com<http://www.SustainableEnergyGroup.com>
530-273-4422 (Office)

530-217-8385 (Cell)



   



From: RE-wrenches  on behalf of 
pgir...@mindspring.com 
Sent: Tuesday, September 8, 2020 1:24:03 PM
To: 'RE-wrenches' 
Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?


I also suggest the Sol-Ark 12’s. Extremely efficient, simple to program, does a 
wonderful job in either ac coupling, stand alone or pure off grid and terrific 
customer support.



Peter Giroux

ASAE



From: RE-wrenches  On Behalf Of 
Bryan Norkunas
Sent: Tuesday, September 8, 2020 1:50 PM
To: 'RE-wrenches' 
Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?



Sol-Arks would be possible, you can link 8 inverters.



Bryan

PV-Cables













From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Chris Schaefer
Sent: Tuesday, September 8, 2020 10:40 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?



I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with their 
12kw unit. Not sure what their max number of inverters are.



Christopher



On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield 
mailto:maxfieldso...@hotmail.com>> wrote:

Hey all, I'm designing a microgrid sized off-grid system for somebody, and I'm 
just wondering if anyone knows of any issues with the following designs...



The client says he needs 70 kW. His load data looks pretty solid, so I'm 
sticking to using that number as a minimum, at least during the initial 
proposal stage. I only know of two possible equipment options for this size 
range...



  1.  I think I can use up to 10 Outback Radians, for up to an 80 kW system. 
Are there any bugs or problems with using this many inverters on one hub? I 
know I've read about issues with selling to the grid, but that's not an issue, 
this is off-grid.
  2.  I know that the SMA cluster box with sunny islands can allow for up to a 
72 kW system. Do you know of any bugs or problems with this system?





Are there any other options that anyone would suggest? Schneider's website says 
they can only do up to 61 kW, and Victron can only do up to 60 kW.





I know that the Outback system would yield a 240/120 Split-Phase system and 
that the SMA would yield a 208/120 3Ø system, but this doesn't really matter 
either way for this job.



Thanks so much,

Kienan





Maxfield Solar

maxfieldso...@hotmail.com<mailto:maxfieldso...@hotmail.com>

(801) 631-5584 (Cell)

___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>




--

Chris Schaefer’s
[Image removed by sender.]<http://www.solarandwindfx.com/>
Tel/Fax 585-229-2083 or Cell 585-748-1870
5115 South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.com<http://www.solarandwindfx.com> ~ E-mail: 
ch...@solarandwindfx.com<mailto:ch...@solarandwindfx.com>

[Image removed by sender.]

Thomas Jefferson, the author of our great Constitution, once said, "democracy" 
will cease to exist when you take away from those who are willing to work and 
give to those who would not."

[https://ipmcdn.avast.com/images/icons/icon-envelope-tick-green-avg-v1.png]<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 Virus-free. 
www.avg.com<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-08 Thread pgiroux
I also suggest the Sol-Ark 12’s. Extremely efficient, simple to program, does a 
wonderful job in either ac coupling, stand alone or pure off grid and terrific 
customer support.



Peter Giroux

ASAE



From: RE-wrenches  On Behalf Of 
Bryan Norkunas
Sent: Tuesday, September 8, 2020 1:50 PM
To: 'RE-wrenches' 
Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?



Sol-Arks would be possible, you can link 8 inverters.



Bryan

PV-Cables













From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Chris Schaefer
Sent: Tuesday, September 8, 2020 10:40 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?



I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with their 
12kw unit. Not sure what their max number of inverters are.



Christopher



On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield  
wrote:

Hey all, I'm designing a microgrid sized off-grid system for somebody, and I'm 
just wondering if anyone knows of any issues with the following designs...



The client says he needs 70 kW. His load data looks pretty solid, so I'm 
sticking to using that number as a minimum, at least during the initial 
proposal stage. I only know of two possible equipment options for this size 
range...



1.  I think I can use up to 10 Outback Radians, for up to an 80 kW system. 
Are there any bugs or problems with using this many inverters on one hub? I 
know I've read about issues with selling to the grid, but that's not an issue, 
this is off-grid.
2.  I know that the SMA cluster box with sunny islands can allow for up to 
a 72 kW system. Do you know of any bugs or problems with this system?





Are there any other options that anyone would suggest? Schneider's website says 
they can only do up to 61 kW, and Victron can only do up to 60 kW.





I know that the Outback system would yield a 240/120 Split-Phase system and 
that the SMA would yield a 208/120 3Ø system, but this doesn't really matter 
either way for this job.



Thanks so much,

Kienan





Maxfield Solar

 <mailto:maxfieldso...@hotmail.com> maxfieldso...@hotmail.com

(801) 631-5584 (Cell)

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>






--

Chris Schaefer’s
 <http://www.solarandwindfx.com/>
Tel/Fax 585-229-2083 or Cell 585-748-1870
5115 South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.com <http://www.solarandwindfx.com>  ~ E-mail: 
ch...@solarandwindfx.com <mailto:ch...@solarandwindfx.com>



Thomas Jefferson, the author of our great Constitution, once said, "democracy" 
will cease to exist when you take away from those who are willing to work and 
give to those who would not."



--
This email has been checked for viruses by AVG.
https://www.avg.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-08 Thread Bryan Norkunas
Sol-Arks would be possible, you can link 8 inverters.

 

Bryan 

PV-Cables

 

 

 

 

 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Chris Schaefer
Sent: Tuesday, September 8, 2020 10:40 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Microgrid... Outback or SMA or other?

 

I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with their 
12kw unit. Not sure what their max number of inverters are.

 

Christopher

 

On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield  
wrote:

Hey all, I'm designing a microgrid sized off-grid system for somebody, and I'm 
just wondering if anyone knows of any issues with the following designs... 

 

The client says he needs 70 kW. His load data looks pretty solid, so I'm 
sticking to using that number as a minimum, at least during the initial 
proposal stage. I only know of two possible equipment options for this size 
range...

 

1.  I think I can use up to 10 Outback Radians, for up to an 80 kW system. 
Are there any bugs or problems with using this many inverters on one hub? I 
know I've read about issues with selling to the grid, but that's not an issue, 
this is off-grid.
2.  I know that the SMA cluster box with sunny islands can allow for up to 
a 72 kW system. Do you know of any bugs or problems with this system?

 

 

Are there any other options that anyone would suggest? Schneider's website says 
they can only do up to 61 kW, and Victron can only do up to 60 kW.

 

 

I know that the Outback system would yield a 240/120 Split-Phase system and 
that the SMA would yield a 208/120 3Ø system, but this doesn't really matter 
either way for this job. 

 

Thanks so much,

Kienan

 

 

Maxfield Solar 

 <mailto:maxfieldso...@hotmail.com> maxfieldso...@hotmail.com

(801) 631-5584 (Cell)

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




 

-- 

Chris Schaefer’s
 <http://www.solarandwindfx.com> Image removed by sender.
Tel/Fax 585-229-2083 or Cell 585-748-1870 
5115 South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.com ~ E-mail: ch...@solarandwindfx.com

Image removed by sender.

Thomas Jefferson, the author of our great Constitution, once said, "democracy" 
will cease to exist when you take away from those who are willing to work and 
give to those who would not."

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-08 Thread Chris Schaefer
I'd suggest giving the crew at Sol-Ark a quick call @ 972-575-8875 with
their 12kw unit. Not sure what their max number of inverters are.

Christopher

On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield 
wrote:

> Hey all, I'm designing a microgrid sized off-grid system for somebody, and
> I'm just wondering if anyone knows of any issues with the following
> designs...
>
> The client says he needs 70 kW. His load data looks pretty solid, so I'm
> sticking to using that number as a minimum, at least during the initial
> proposal stage. I only know of two possible equipment options for this size
> range...
>
>
>1. I think I can use up to 10 Outback Radians, for up to an 80 kW
>system. Are there any bugs or problems with using this many inverters on
>one hub? I know I've read about issues with selling to the grid, but that's
>not an issue, this is off-grid.
>
>2. I know that the SMA cluster box with sunny islands can allow for up
>to a 72 kW system. Do you know of any bugs or problems with this system?
>
>
>
> Are there any other options that anyone would suggest? Schneider's website
> says they can only do up to 61 kW, and Victron can only do up to 60 kW.
>
>
> I know that the Outback system would yield a 240/120 Split-Phase system
> and that the SMA would yield a 208/120 3Ø system, but this doesn't really
> matter either way for this job.
>
> Thanks so much,
> Kienan
>
>
> *Maxfield Solar*
> *maxfieldso...@hotmail.com* 
> * (801) 631-5584 (Cell) *
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 

Chris Schaefer’s


*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
 ~ E-mail: ch...@solarandwindfx.com
*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Microgrid... Outback or SMA or other?

2020-09-08 Thread Kienan Maxfield
Hey all, I'm designing a microgrid sized off-grid system for somebody, and I'm 
just wondering if anyone knows of any issues with the following designs...

The client says he needs 70 kW. His load data looks pretty solid, so I'm 
sticking to using that number as a minimum, at least during the initial 
proposal stage. I only know of two possible equipment options for this size 
range...


  1.  I think I can use up to 10 Outback Radians, for up to an 80 kW system. 
Are there any bugs or problems with using this many inverters on one hub? I 
know I've read about issues with selling to the grid, but that's not an issue, 
this is off-grid.

  2.  I know that the SMA cluster box with sunny islands can allow for up to a 
72 kW system. Do you know of any bugs or problems with this system?


Are there any other options that anyone would suggest? Schneider's website says 
they can only do up to 61 kW, and Victron can only do up to 60 kW.


I know that the Outback system would yield a 240/120 Split-Phase system and 
that the SMA would yield a 208/120 3Ø system, but this doesn't really matter 
either way for this job.

Thanks so much,
Kienan


Maxfield Solar
maxfieldso...@hotmail.com
(801) 631-5584 (Cell)
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org