Re: [RE-wrenches] Outback AC Backfeed Error

2020-12-14 Thread jay
HI Jon,

Can you tell us how long the system has been operational?  Trying to figure out 
if this is a new system or an older.

And what size generator do you have? 

If its an older system and with a big generator/big loads then there is a 
possibility of damaged/sticky relays.

jay

peltz power





> On Dec 14, 2020, at 9:07 AM, Tuss, Lones  wrote:
> 
> Hi Jon
> Not much to go on here the suggestion to look for damaged relays is probably 
> a good idea.
> Look to see if there is signs of arcing or the relay covers have a smokey 
> appearance.
> You stated the system has worked for the last week and the AGS has gone 
> through several start stop sequences and the system error has not repeated.
> It might be interesting to see if there were any warning in the event log 
> perhaps that would give more clues.
> It is difficult to be certain when the system is currently functioning.
> Sorry that is all I have.
> Take Care Sir
>  
>  
> From: RE-wrenches  <mailto:re-wrenches-boun...@lists.re-wrenches.org>> On Behalf Of Jon 
> Siegenthaler
> Sent: Friday, December 11, 2020 6:01 PM
> To: re-wrenches@lists.re-wrenches.org 
> <mailto:re-wrenches@lists.re-wrenches.org>
> Subject: [RE-wrenches] Outback AC Backfeed Error
>  
> Hey wrenches,
>  
> I have a client who has a couple of the Radian 8048's and has an error code 
> of "AC Backfeed Error GS-1". Looking at the manual it states that "Usually 
> indicates another AC power source (out of phase with the inverter) was 
> connected to the unit’s AC output. Can also occur if an out-of-phase AC 
> source is connected to the inverter’s AC input."
>  
> However when this happened the generator wasn't running and it's an off grid 
> system. Is there a way that the master is looking to the slave as another 
> power source? The system had been running fine this week, auto running the 
> generator early morning and shutting down on its own. 
>  
> Anyone seen something like this before? Thanks,
>  
> Jon Siegenthaler
> 
> 
> This email and any attachments may contain confidential information that is 
> intended only for the recipient(s). If you have received this email in error, 
> please notify the sender and delete it from your system. Any views or 
> opinions presented in this email are solely those of the author and do not 
> necessarily represent those of the company or its affiliates. This email does 
> not constitute an agreement to conduct transactions by electronic means and 
> does not create any legally binding contract or enforceable obligation in the 
> absence of a fully signed written contract. The recipient should check this 
> email and any attachments for viruses. The company accepts no liability for 
> any loss or damage caused by software viruses. If you are the intended 
> recipient and you do not wish to receive similar email(s) from us in the 
> future then please notify the sender. Please consider the environment before 
> printing.___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Outback AC Backfeed Error

2020-12-14 Thread Tuss, Lones
Hi Jon
Not much to go on here the suggestion to look for damaged relays is probably a 
good idea.
Look to see if there is signs of arcing or the relay covers have a smokey 
appearance.
You stated the system has worked for the last week and the AGS has gone through 
several start stop sequences and the system error has not repeated.
It might be interesting to see if there were any warning in the event log 
perhaps that would give more clues.
It is difficult to be certain when the system is currently functioning.
Sorry that is all I have.
Take Care Sir


From: RE-wrenches  On Behalf Of Jon 
Siegenthaler
Sent: Friday, December 11, 2020 6:01 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Outback AC Backfeed Error

Hey wrenches,

I have a client who has a couple of the Radian 8048's and has an error code of 
"AC Backfeed Error GS-1". Looking at the manual it states that "Usually 
indicates another AC power source (out of phase with the inverter) was 
connected to the unit’s AC output. Can also occur if an out-of-phase AC source 
is connected to the inverter’s AC input."

However when this happened the generator wasn't running and it's an off grid 
system. Is there a way that the master is looking to the slave as another power 
source? The system had been running fine this week, auto running the generator 
early morning and shutting down on its own.

Anyone seen something like this before? Thanks,

Jon Siegenthaler


This email and any attachments may contain confidential information that is 
intended only for the recipient(s). If you have received this email in error, 
please notify the sender and delete it from your system. Any views or opinions 
presented in this email are solely those of the author and do not necessarily 
represent those of the company or its affiliates. This email does not 
constitute an agreement to conduct transactions by electronic means and does 
not create any legally binding contract or enforceable obligation in the 
absence of a fully signed written contract. The recipient should check this 
email and any attachments for viruses. The company accepts no liability for any 
loss or damage caused by software viruses. If you are the intended recipient 
and you do not wish to receive similar email(s) from us in the future then 
please notify the sender. Please consider the environment before printing.
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Outback AC Backfeed Error

2020-12-12 Thread pgiroux
Recently had this on a project. Turns out it was two things, the cat 5 cables 
needed to be shielded so I went to Cat7 and the firmware upgrades did not take 
on one of the radians. Had to do it 3 times. System works fine now.



Peter Giroux

American Solar



From: RE-wrenches  On Behalf Of Jon 
Siegenthaler
Sent: Friday, December 11, 2020 9:01 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Outback AC Backfeed Error



Hey wrenches,



I have a client who has a couple of the Radian 8048's and has an error code of 
"AC Backfeed Error GS-1". Looking at the manual it states that "Usually 
indicates another AC power source (out of phase with the inverter) was 
connected to the unit’s AC output. Can also occur if an out-of-phase AC source 
is connected to the inverter’s AC input."



However when this happened the generator wasn't running and it's an off grid 
system. Is there a way that the master is looking to the slave as another power 
source? The system had been running fine this week, auto running the generator 
early morning and shutting down on its own.



Anyone seen something like this before? Thanks,



Jon Siegenthaler



--
This email has been checked for viruses by AVG.
https://www.avg.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Outback AC Backfeed Error

2020-12-12 Thread Barton Churchill
You could try going through the stacking sequence again to make sure they can 
synchronize properly. This is a good test of that output relay in each Radian. 
If there's a problem, you won't hear them, and they are noisy. Like the 
instructions state be sure the output breakers are open!


[cid:699e3bd7-2852-4ad0-830e-dc63c6fa2b82]Barton Churchill
Director, Power Division
2042 Stadium Drive Suite 2 • Bozeman, MT 59715 • (O) 406-587-2917 • (D) 
406-589-4493
235 E. Broadway • Jackson, WY 83001 • (O) 307-200-2210
bchurch...@energy-1.net<mailto:blans...@energy-1.net>   |
www.energy-1.net<http://www.energy-1.net/>



From: RE-wrenches  on behalf of 
Chris Worcester 
Sent: Friday, December 11, 2020 7:20 PM
To: RE-wrenches 
Subject: Re: [RE-wrenches] Outback AC Backfeed Error

Hi Jon,
I have seen this early on, when the Mate3 first came out. The slave back fed 
the master. The Mate3 didn't accept our programming, a firmware update 
corrected this glitch.



Chris Worcester
ch...@solarwindworks.com
530-448-9692

Sent from my Samsung Galaxy s9.


 Original message 
From: Jon Siegenthaler 
Date: 12/11/20 6:01 PM (GMT-08:00)
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Outback AC Backfeed Error

Hey wrenches,

I have a client who has a couple of the Radian 8048's and has an error code of 
"AC Backfeed Error GS-1". Looking at the manual it states that "Usually 
indicates another AC power source (out of phase with the inverter) was 
connected to the unit’s AC output. Can also occur if an out-of-phase AC source 
is connected to the inverter’s AC input."

However when this happened the generator wasn't running and it's an off grid 
system. Is there a way that the master is looking to the slave as another power 
source? The system had been running fine this week, auto running the generator 
early morning and shutting down on its own.

Anyone seen something like this before? Thanks,

Jon Siegenthaler
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Outback AC Backfeed Error

2020-12-11 Thread Steve Higgins
As William said... That is usually a relay issue.  In the older FX's, it
could also be a sticking issue like the hub or connections.

Steve Higgins.


On Fri, Dec 11, 2020 at 6:16 PM William Miller 
wrote:

> Jon:
>
>
>
> In the deep recess of my memory I recall this error code with FX
> inverters.  It was caused by a stuck transfer relay.  You might open the
> inverter cover and look for signs of smoke or arcing in the relay.
>
>
>
> Good luck!
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Jon Siegenthaler
> *Sent:* Friday, December 11, 2020 6:01 PM
> *To:* re-wrenches@lists.re-wrenches.org
> *Subject:* [RE-wrenches] Outback AC Backfeed Error
>
>
>
> Hey wrenches,
>
>
>
> I have a client who has a couple of the Radian 8048's and has an error
> code of "AC Backfeed Error GS-1". Looking at the manual it states that
> "Usually indicates another AC power source (out of phase with the inverter)
> was connected to the unit’s AC output. Can also occur if an out-of-phase AC
> source is connected to the inverter’s AC input."
>
>
>
> However when this happened the generator wasn't running and it's an off
> grid system. Is there a way that the master is looking to the slave as
> another power source? The system had been running fine this week, auto
> running the generator early morning and shutting down on its own.
>
>
>
> Anyone seen something like this before? Thanks,
>
>
>
> Jon Siegenthaler
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Outback AC Backfeed Error

2020-12-11 Thread Chris Worcester
Hi Jon,I have seen this early on, when the Mate3 first came out. The slave back 
fed the master. The Mate3 didn't accept our programming, a firmware update 
corrected this glitch. Chris Worcester chris@solarwindworks.com530-448-9692Sent 
from my Samsung Galaxy s9.
 Original message From: Jon Siegenthaler 
 Date: 12/11/20  6:01 PM  (GMT-08:00) To: 
re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Outback AC Backfeed 
Error Hey wrenches,I have a client who has a couple of the Radian 8048's and 
has an error code of "AC Backfeed Error GS-1". Looking at the manual it states 
that "Usually indicates another AC power source (out of phase with the 
inverter) was connected to the unit’s AC output. Can also occur if an 
out-of-phase AC source is connected to the inverter’s AC input."However when 
this happened the generator wasn't running and it's an off grid system. Is 
there a way that the master is looking to the slave as another power source? 
The system had been running fine this week, auto running the generator early 
morning and shutting down on its own. Anyone seen something like this before? 
Thanks,Jon Siegenthaler
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Outback AC Backfeed Error

2020-12-11 Thread Jerry Shafer
Wrenches
Might want to look at the hub and data cables to the inverters, bad or poor
connections can effect phases of the inverters, l have seen this manifest
it self with errors like inverter firmware issues  that in fact are bogus.
The OEM cat 5 cables are not shielded and that causes problem when they are
wrapped all around in a box. Easy to test with meters, how many times have
you just rebooted or unplugged something for it all to get better.
Anyway thats just one of many great ideas
Jerry
 NABCEP Inspector
NABCEP Installer

On Fri, Dec 11, 2020, 6:01 PM Jon Siegenthaler 
wrote:

> Hey wrenches,
>
> I have a client who has a couple of the Radian 8048's and has an error
> code of "AC Backfeed Error GS-1". Looking at the manual it states that
> "Usually indicates another AC power source (out of phase with the inverter)
> was connected to the unit’s AC output. Can also occur if an out-of-phase AC
> source is connected to the inverter’s AC input."
>
> However when this happened the generator wasn't running and it's an off
> grid system. Is there a way that the master is looking to the slave as
> another power source? The system had been running fine this week, auto
> running the generator early morning and shutting down on its own.
>
> Anyone seen something like this before? Thanks,
>
> Jon Siegenthaler
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Outback AC Backfeed Error

2020-12-11 Thread Foxfire Energy
Seem to recall something similar with early FX inverters.. Don’t recall the 
particulars but it might have had something to do with loosing their mind 
before shutting down.. maybe a shorted output.

Sent from my iPhone

On Dec 11, 2020, at 9:16 PM, William Miller  wrote:


Jon:

In the deep recess of my memory I recall this error code with FX inverters.  It 
was caused by a stuck transfer relay.  You might open the inverter cover and 
look for signs of smoke or arcing in the relay.

Good luck!

Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com<http://www.millersolar.com/>
CA Lic. 773985


From: RE-wrenches 
[mailto:re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>]
 On Behalf Of Jon Siegenthaler
Sent: Friday, December 11, 2020 6:01 PM
To: re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] Outback AC Backfeed Error

Hey wrenches,

I have a client who has a couple of the Radian 8048's and has an error code of 
"AC Backfeed Error GS-1". Looking at the manual it states that "Usually 
indicates another AC power source (out of phase with the inverter) was 
connected to the unit’s AC output. Can also occur if an out-of-phase AC source 
is connected to the inverter’s AC input."

However when this happened the generator wasn't running and it's an off grid 
system. Is there a way that the master is looking to the slave as another power 
source? The system had been running fine this week, auto running the generator 
early morning and shutting down on its own.

Anyone seen something like this before? Thanks,

Jon Siegenthaler
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Outback AC Backfeed Error

2020-12-11 Thread William Miller
Jon:



In the deep recess of my memory I recall this error code with FX
inverters.  It was caused by a stuck transfer relay.  You might open the
inverter cover and look for signs of smoke or arcing in the relay.



Good luck!



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Jon Siegenthaler
*Sent:* Friday, December 11, 2020 6:01 PM
*To:* re-wrenches@lists.re-wrenches.org
*Subject:* [RE-wrenches] Outback AC Backfeed Error



Hey wrenches,



I have a client who has a couple of the Radian 8048's and has an error code
of "AC Backfeed Error GS-1". Looking at the manual it states that "Usually
indicates another AC power source (out of phase with the inverter) was
connected to the unit’s AC output. Can also occur if an out-of-phase AC
source is connected to the inverter’s AC input."



However when this happened the generator wasn't running and it's an off
grid system. Is there a way that the master is looking to the slave as
another power source? The system had been running fine this week, auto
running the generator early morning and shutting down on its own.



Anyone seen something like this before? Thanks,



Jon Siegenthaler
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Outback AC Backfeed Error

2020-12-11 Thread Jon Siegenthaler
Hey wrenches,

I have a client who has a couple of the Radian 8048's and has an error code
of "AC Backfeed Error GS-1". Looking at the manual it states that "Usually
indicates another AC power source (out of phase with the inverter) was
connected to the unit’s AC output. Can also occur if an out-of-phase AC
source is connected to the inverter’s AC input."

However when this happened the generator wasn't running and it's an off
grid system. Is there a way that the master is looking to the slave as
another power source? The system had been running fine this week, auto
running the generator early morning and shutting down on its own.

Anyone seen something like this before? Thanks,

Jon Siegenthaler
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org