I was sent to look at another contractor's work, and found three SB5000
inverters with blown string input fuses. I was able to determine the reason
pretty quickly, and was later sent the original 1-Line, which was installed
per the drawings. The 1-Line came from a leading system integrator who
shall remain nameless.

See anything wrong?

https://www.sugarsync.com/pf/D6539806_8669786_010829

Just goes to show you - the contractor needs to take responsibility and
verify the specifications are correct, safe, and code compliant.

Jason Szumlanski
Fafco Solar
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Up for a 1-Line Riddle?

2012-08-30 Thread Andrew Truitt
Ahh yes, the old combine strings before landing on a fused DC input
terminal trick.  Sure to blow the fuse the first sunny day.  This is why
SMA created their fuse-bypass DC input terminal.  I take it the installer
was not aware of this...



For a brighter energy future,


Andrew Truitt
NABCEP Certified PV Installer™ (ID# 032407-66)

Principal
Truitt Renewable Energy Consulting

(202) 486-7507

http://www.linkedin.com/pub/andrew-truitt/8/622/713



Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
to fission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!

~William McDonough





On Thu, Aug 30, 2012 at 11:53 AM, Jason Szumlanski ja...@fafcosolar.comwrote:

 I was sent to look at another contractor's work, and found three SB5000
 inverters with blown string input fuses. I was able to determine the reason
 pretty quickly, and was later sent the original 1-Line, which was installed
 per the drawings. The 1-Line came from a leading system integrator who
 shall remain nameless.

 See anything wrong?

 https://www.sugarsync.com/pf/D6539806_8669786_010829

 Just goes to show you - the contractor needs to take responsibility and
 verify the specifications are correct, safe, and code compliant.

 Jason Szumlanski
 Fafco Solar

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Up for a 1-Line Riddle?

2012-08-30 Thread Dave Click
I've seen that one a lot, too. And not to quibble, but the 1-line 
depicts this correctly (no inline fuse shown in the inverter DC 
disconnect box), though there should be a note making this more explicit.


Speaking of sunny days turning off the system, how about the 3 30A 
inverter breakers' combined feed going into a 55A breaker. Also... a 55A 
breaker? Really? I guess the designer wanted to leave a little headroom 
to avoid scaring the 60A disconnect.


DKC

On 2012/8/30 14:35, Andrew Truitt wrote:


Ahh yes, the old combine strings before landing on a fused DC input
terminal trick.  Sure to blow the fuse the first sunny day.  This is
why SMA created their fuse-bypass DC input terminal.  I take it the
installer was not aware of this...



For a brighter energy future,


Andrew Truitt
NABCEP Certified PV Installer™ (ID# 032407-66)

Principal
Truitt Renewable Energy Consulting

(202) 486-7507 tel:%28202%29%20486-7507

http://www.linkedin.com/pub/andrew-truitt/8/622/713



Don't get me wrong: I love nuclear energy! It's just that I prefer
fusion to fission. And it just so happens that there's an enormous
fusion reactor safely banked a few million miles from us. It delivers
more than we could ever use in just about 8 minutes. And it's wireless!

~William McDonough






On Thu, Aug 30, 2012 at 11:53 AM, Jason Szumlanski ja...@fafcosolar.com
mailto:ja...@fafcosolar.com wrote:

I was sent to look at another contractor's work, and found three
SB5000 inverters with blown string input fuses. I was able to
determine the reason pretty quickly, and was later sent the original
1-Line, which was installed per the drawings. The 1-Line came from a
leading system integrator who shall remain nameless.

See anything wrong?

https://www.sugarsync.com/pf/D6539806_8669786_010829

Just goes to show you - the contractor needs to take responsibility
and verify the specifications are correct, safe, and code compliant.

Jason Szumlanski
Fafco Solar

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org
mailto:RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org http://www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Up for a 1-Line Riddle?

2012-08-30 Thread David Brearley
I'm assuming it's a balanced 3-phase interconnection, which fits with the 
reported phase current of 42 A:

(3 x 5000 W) / 208 V / 1.73 = 41.7 A

Or more simply:

24 A per inverter x 1.73 = 41.5 A

However, no one reviewing a single-line should have to guess about the service 
type

On Aug 30, 2012, at 3:12 PM, Dave Click wrote:

 I've seen that one a lot, too. And not to quibble, but the 1-line depicts 
 this correctly (no inline fuse shown in the inverter DC disconnect box), 
 though there should be a note making this more explicit.
 
 Speaking of sunny days turning off the system, how about the 3 30A inverter 
 breakers' combined feed going into a 55A breaker. Also... a 55A breaker? 
 Really? I guess the designer wanted to leave a little headroom to avoid 
 scaring the 60A disconnect.
 
 DKC
 
 On 2012/8/30 14:35, Andrew Truitt wrote:
 
 Ahh yes, the old combine strings before landing on a fused DC input
 terminal trick.  Sure to blow the fuse the first sunny day.  This is
 why SMA created their fuse-bypass DC input terminal.  I take it the
 installer was not aware of this...
 
 
 
 For a brighter energy future,
 
 
 Andrew Truitt
 NABCEP Certified PV Installer™ (ID# 032407-66)
 
 Principal
 Truitt Renewable Energy Consulting
 
 (202) 486-7507 tel:%28202%29%20486-7507
 
 http://www.linkedin.com/pub/andrew-truitt/8/622/713
 
 
 
 Don't get me wrong: I love nuclear energy! It's just that I prefer
 fusion to fission. And it just so happens that there's an enormous
 fusion reactor safely banked a few million miles from us. It delivers
 more than we could ever use in just about 8 minutes. And it's wireless!
 
 ~William McDonough
 
 
 
 
 
 
 On Thu, Aug 30, 2012 at 11:53 AM, Jason Szumlanski ja...@fafcosolar.com
 mailto:ja...@fafcosolar.com wrote:
 
I was sent to look at another contractor's work, and found three
SB5000 inverters with blown string input fuses. I was able to
determine the reason pretty quickly, and was later sent the original
1-Line, which was installed per the drawings. The 1-Line came from a
leading system integrator who shall remain nameless.
 
See anything wrong?
 
https://www.sugarsync.com/pf/D6539806_8669786_010829
 
Just goes to show you - the contractor needs to take responsibility
and verify the specifications are correct, safe, and code compliant.
 
Jason Szumlanski
Fafco Solar
 
___
List sponsored by Home Power magazine
 
List Address: RE-wrenches@lists.re-wrenches.org
mailto:RE-wrenches@lists.re-wrenches.org
 
Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules  etiquette:
www.re-wrenches.org/etiquette.htm
http://www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org http://www.members.re-wrenches.org
 
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Up for a 1-Line Riddle?

2012-08-30 Thread Dave Click
Thanks David, I was in residential mode and just saw the 240V listed in 
the OCPD table!


On 2012/8/30 16:47, David Brearley wrote:

I'm assuming it's a balanced 3-phase interconnection, which fits with the 
reported phase current of 42 A:

(3 x 5000 W) / 208 V / 1.73 = 41.7 A

Or more simply:

24 A per inverter x 1.73 = 41.5 A

However, no one reviewing a single-line should have to guess about the service 
type

On Aug 30, 2012, at 3:12 PM, Dave Click wrote:


I've seen that one a lot, too. And not to quibble, but the 1-line depicts this 
correctly (no inline fuse shown in the inverter DC disconnect box), though 
there should be a note making this more explicit.

Speaking of sunny days turning off the system, how about the 3 30A inverter 
breakers' combined feed going into a 55A breaker. Also... a 55A breaker? 
Really? I guess the designer wanted to leave a little headroom to avoid scaring 
the 60A disconnect.

DKC

On 2012/8/30 14:35, Andrew Truitt wrote:


Ahh yes, the old combine strings before landing on a fused DC input
terminal trick.  Sure to blow the fuse the first sunny day.  This is
why SMA created their fuse-bypass DC input terminal.  I take it the
installer was not aware of this...



For a brighter energy future,


Andrew Truitt
NABCEP Certified PV Installer™ (ID# 032407-66)

Principal
Truitt Renewable Energy Consulting

(202) 486-7507 tel:%28202%29%20486-7507

http://www.linkedin.com/pub/andrew-truitt/8/622/713



Don't get me wrong: I love nuclear energy! It's just that I prefer
fusion to fission. And it just so happens that there's an enormous
fusion reactor safely banked a few million miles from us. It delivers
more than we could ever use in just about 8 minutes. And it's wireless!

~William McDonough






On Thu, Aug 30, 2012 at 11:53 AM, Jason Szumlanski ja...@fafcosolar.com
mailto:ja...@fafcosolar.com wrote:

I was sent to look at another contractor's work, and found three
SB5000 inverters with blown string input fuses. I was able to
determine the reason pretty quickly, and was later sent the original
1-Line, which was installed per the drawings. The 1-Line came from a
leading system integrator who shall remain nameless.

See anything wrong?

https://www.sugarsync.com/pf/D6539806_8669786_010829

Just goes to show you - the contractor needs to take responsibility
and verify the specifications are correct, safe, and code compliant.

Jason Szumlanski
Fafco Solar

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org
mailto:RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org http://www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Up for a 1-Line Riddle?

2012-08-30 Thread Jason Szumlanski
Yep... the owner wondered why they fuses didn't blow earlier. I had to
explain that the panels are at 5% tilt and here in SW FL the sun rises to
85 degrees above the horizon come summer. There was never a problem in the
winter and spring!

The 7.69 Imp per string should have been the obvious tip-off.  2 x 7.69 =
15A.

36A max on the combined input terminal is a nice feature. As soon as I saw
the 30A discos next to the inverters I wondered why they were landing on
the fused inputs. Without the 1-line in my hand, that was a good tip-off,
too.

Jason Szumlanski
Fafco Solar



On Thu, Aug 30, 2012 at 2:35 PM, Andrew Truitt atru...@gmail.com wrote:


 Ahh yes, the old combine strings before landing on a fused DC input
 terminal trick.  Sure to blow the fuse the first sunny day.  This is why
 SMA created their fuse-bypass DC input terminal.  I take it the installer
 was not aware of this...



 For a brighter energy future,


 Andrew Truitt
 NABCEP Certified PV Installer™ (ID# 032407-66)

 Principal
 Truitt Renewable Energy Consulting

 (202) 486-7507

 http://www.linkedin.com/pub/andrew-truitt/8/622/713




 On Thu, Aug 30, 2012 at 11:53 AM, Jason Szumlanski 
 ja...@fafcosolar.comwrote:

 I was sent to look at another contractor's work, and found three SB5000
 inverters with blown string input fuses. I was able to determine the reason
 pretty quickly, and was later sent the original 1-Line, which was installed
 per the drawings. The 1-Line came from a leading system integrator who
 shall remain nameless.

 See anything wrong?

 https://www.sugarsync.com/pf/D6539806_8669786_010829

 Just goes to show you - the contractor needs to take responsibility and
 verify the specifications are correct, safe, and code compliant.

 Jason Szumlanski
 Fafco Solar


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org