Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-09-09 Thread pieter offgridenterprises.org via RE-wrenches
Over the past year we have installed a handful of wildcat 15 kw generators. 
Lead times remain a challenge but so far no operational issues.
https://www.wildcatpowergen.com/
PRH

From: RE-wrenches  On Behalf Of Dana 
Orzel via RE-wrenches
Sent: Friday, September 9, 2022 7:03 AM
To: Kevin Pegg ; re-wrenches-bounces 

Cc: Dana Orzel 
Subject: Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

Good morning all if you did not catch the last email on this project the 
manufacturer is Wildcat Generators and should be in the history
I’m on vacation at the moment and operating from the phone with no Internet 
where we’re staying
Wildcat was hoping by early November to EOY to have a 15 KW and possibly a 10 
KW though not UL listed.
The 15KW is slated to get UL listing down the road Time still to be determined

Dana Orzel
C: 208.721.7003
E- d...@solarwork.com<mailto:d...@solarwork.com>


On Sep 9, 2022, at 12:52 AM, Kevin Pegg 
mailto:kp...@energyalternatives.ca>> wrote:

Hi Dana,

Touching base to see how this project is going? I could definitely sell several 
units a year of this config. Very needed.

Thanks,

Kevin Pegg
EA Energy Alternatives Ltd.
37471 Hwy 16 E
Telkwa, BC  V0J 2X2
250-846-9888
Http://www.EnergyAlternatives.ca


From: RE-wrenches 
mailto:re-wrenches-boun...@lists.re-wrenches.org>>
 On Behalf Of Dana Orzel via RE-wrenches
Sent: July-02-22 9:11 AM
To: 'RE-wrenches' 
mailto:re-wrenches@lists.re-wrenches.org>>
Cc: Dana Orzel mailto:d...@solarwork.com>>
Subject: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

I heard back Friday from the generator manufacturers executive board meeting 
Friday morning there is their response:

Hi Dana,

I spoke with the executives this morning and we’re very excited to hear what 
the demand is for this genset is. If it makes sense, we’re all in.

Please let me know if your interest in a 13KW – 1800 RPM genset – water cooled 
is of interest for you & your off grid clients. I see this as a big opportunity 
for replacing the oversized gensets that we have been forced to use  for a long 
time now.



Dana Orzel -  E - d...@solarwork.com<mailto:d...@solarwork.com> -  C - 
208.721.7003

From: RE-wrenches 
mailto:re-wrenches-boun...@lists.re-wrenches.org>>
 On Behalf Of Dana Orzel via RE-wrenches
Sent: Thursday, June 30, 2022 12:02 PM
To: 'RE-wrenches' 
mailto:re-wrenches@lists.re-wrenches.org>>
Cc: Dana Orzel mailto:d...@solarwork.com>>
Subject: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

Hey now all you off grid designer/installers,

I just had a conversation with generator manufacturer (name withheld for the 
moment), about 8-13KW water cooled gensets with UL & LP gas powered. I 
explained that there is a long time hole in the market since Onan & Kohler 
dropped their gensets for prime power in this size range.

If they made the investment to produce & UL certify a 13KW - 1800 RPM - water 
cooled – 2 wire start, prime power rated - 120/240vac genset, how many off grid 
systems are being installed with oversized gensets?

If this was available how many units would each of you be interested in per 
year? I am not asking for a commitment just a market survey for this sized unit.

If there was 20-30 companies selling 4-5+ each per year this might be a 
possibility.

Let me know either off list or on list (if this is OK ? Michael let us know) & 
I hope there is a possibility here for more appropriately sized & available 
gensets for our off grid client systems.
I will be passing along this research to the OE manufacturer. If you do not 
want your name passed along let me know for now.



Dana Orzel  Great Solar Works, Inc.
C - 208.721.7003   
d...@solarwork.com<mailto:d...@solarwork.com>
Idaho Contractor - # 028765 Idaho PV # 028374
NABCEP # 051112-136   
www.greatsolarworks.com<http://www.greatsolarworks.com/>
"Responsible Technologies for Responsible People since 1988"

P Please consider the environment before printing this email.


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-09-09 Thread Dana Orzel via RE-wrenches
Good morning all if you did not catch the last email on this project the 
manufacturer is Wildcat Generators and should be in the history 
I’m on vacation at the moment and operating from the phone with no Internet 
where we’re staying 
Wildcat was hoping by early November to EOY to have a 15 KW and possibly a 10 
KW though not UL listed.
The 15KW is slated to get UL listing down the road Time still to be determined


Dana Orzel
C: 208.721.7003
E- d...@solarwork.com

> On Sep 9, 2022, at 12:52 AM, Kevin Pegg  wrote:
> 
> 
> Hi Dana,
>  
> Touching base to see how this project is going? I could definitely sell 
> several units a year of this config. Very needed.
>  
> Thanks,
>  
> Kevin Pegg 
> EA Energy Alternatives Ltd. 
> 37471 Hwy 16 E 
> Telkwa, BC  V0J 2X2 
> 250-846-9888 
> Http://www.EnergyAlternatives.ca
>  
>  
> From: RE-wrenches  On Behalf Of 
> Dana Orzel via RE-wrenches
> Sent: July-02-22 9:11 AM
> To: 'RE-wrenches' 
> Cc: Dana Orzel 
> Subject: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY
>  
> I heard back Friday from the generator manufacturers executive board meeting 
> Friday morning there is their response:
> 
> Hi Dana,
>  
> I spoke with the executives this morning and we’re very excited to hear what 
> the demand is for this genset is. If it makes sense, we’re all in.
> 
> Please let me know if your interest in a 13KW – 1800 RPM genset – water 
> cooled is of interest for you & your off grid clients. I see this as a big 
> opportunity for replacing the oversized gensets that we have been forced to 
> use  for a long time now.
>  
>  
>  
> Dana Orzel -  E - d...@solarwork.com -  C - 208.721.7003
>  
> From: RE-wrenches  On Behalf Of 
> Dana Orzel via RE-wrenches
> Sent: Thursday, June 30, 2022 12:02 PM
> To: 'RE-wrenches' 
> Cc: Dana Orzel 
> Subject: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY
>  
> Hey now all you off grid designer/installers,
>  
> I just had a conversation with generator manufacturer (name withheld for the 
> moment), about 8-13KW water cooled gensets with UL & LP gas powered. I 
> explained that there is a long time hole in the market since Onan & Kohler 
> dropped their gensets for prime power in this size range.
>  
> If they made the investment to produce & UL certify a 13KW - 1800 RPM - water 
> cooled – 2 wire start, prime power rated - 120/240vac genset, how many off 
> grid systems are being installed with oversized gensets?
>  
> If this was available how many units would each of you be interested in per 
> year? I am not asking for a commitment just a market survey for this sized 
> unit.
>  
> If there was 20-30 companies selling 4-5+ each per year this might be a 
> possibility.
>  
> Let me know either off list or on list (if this is OK ? Michael let us know) 
> & I hope there is a possibility here for more appropriately sized & available 
> gensets for our off grid client systems.
> I will be passing along this research to the OE manufacturer. If you do not 
> want your name passed along let me know for now.
>  
>  
>  
> Dana Orzel  Great Solar Works, Inc.
> C - 208.721.7003   d...@solarwork.com
> Idaho Contractor - # 028765 Idaho PV # 028374
> NABCEP # 051112-136   www.greatsolarworks.com
> "Responsible Technologies for Responsible People since 1988" 
>  
> P Please consider the environment before printing this email.
>  
>  
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-11 Thread Chris Sparadeo via RE-wrenches
We are desperate for a dependable liquid cooled generator in the 12-16 kW
range. If quality is there, I could see us installing 10+ a year.


-Chris

On Mon, Jul 11, 2022 at 10:45 AM Christopher Warfel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> The more our local utility tries to suppress solar, the more we are taking
> people off grid, so I would estimate 3 a year for our small locale.
> On 7/10/2022 12:53 PM, Tump via RE-wrenches wrote:
>
> How many folks require UL listing to install, this may expedite delivery?
>
> On Jul 8, 2022, at 3:09 PM, Dana Orzel via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> The question was – When might these units be available?
>
> The first request from the manu. was to get a survey of how many units
> might get sold per year & responses are still trickling in slowly.
> Next Tump & I will be in a zoom meeting with the company powers that be &
> at that point they need to source & design.
> I would bet it is out aways still depending on equipment
> choices/availability, testing & UL certification etc.
>
> I would not even dare to guess but when we ca report back with a date we
> will do so.
>
>
> Dana Orzel -  E - d...@solarwork.com -  C - 208.721.7003
>
> *From:* RE-wrenches  *On
> Behalf Of *Kevin Pegg via RE-wrenches
> *Sent:* Friday, July 8, 2022 12:59 PM
> *To:* RE-wrenches 
> *Cc:* Kevin Pegg 
> *Subject:* Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS
> INQUIRY
>
> Thanks for this – there is certainly demand. I could see my company buying
> a 3-5 per year.
>
> Is there any estimate of timeline when these might be available?
>
> Kevin
>
> *From:* RE-wrenches  *On
> Behalf Of *Dana Orzel via RE-wrenches
> *Sent:* June-30-22 11:02 AM
> *To:* 'RE-wrenches' 
> *Cc:* Dana Orzel 
> *Subject:* [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY
>
> Hey now all you off grid designer/installers,
>
> I just had a conversation with generator manufacturer (name withheld for
> the moment), about 8-13KW water cooled gensets with UL & LP gas powered. I
> explained that there is a long time hole in the market since Onan & Kohler
> dropped their gensets for prime power in this size range.
>
> If they made the investment to produce & UL certify a 13KW - 1800 RPM -
> water cooled – 2 wire start, prime power rated - 120/240vac genset, how
> many off grid systems are being installed with oversized gensets?
>
> *If this was available how many units would each of you be interested in
> per year? *I am not asking for a commitment just a market survey for this
> sized unit.
>
> If there was 20-30 companies selling 4-5+ each per year this might be a
> possibility.
>
> Let me know either off list or on list (if this is OK ? Michael let us
> know) & I hope there is a possibility here for more appropriately sized &
> available gensets for our off grid client systems.
> I will be passing along this research to the OE manufacturer. If you do
> not want your name passed along let me know for now.
>
>
>
> Dana Orzel  Great Solar Works, Inc.
> *C - 208.721.7003   **d...@solarwork.com*
> 
> Idaho Contractor - # 028765 Idaho PV # 028374
> NABCEP # 051112-136   www.greatsolarworks.com
> *"Responsible Technologies for Responsible People since 1988"  *
>
> *P* Please consider the environment before printing this email.
>
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
> *tump3...@gmail.com <3...@gmail.com>*   *www.SWNL.net*
> Solarwinds Northernlights
> *   Serving Mid Coast Maine & Northern California*
> * 207-832-7574   Cl.
> 610-517-8401  *
>   *Blair "TUMP" May*
>
>
> *     MAINE'S CHARTER   *   *
> NABCEP"Certified PV Installer"*
>

Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-11 Thread Christopher Warfel via RE-wrenches
The more our local utility tries to suppress solar, the more we are 
taking people off grid, so I would estimate 3 a year for our small locale.


On 7/10/2022 12:53 PM, Tump via RE-wrenches wrote:

How many folks require UL listing to install, this may expedite delivery?
On Jul 8, 2022, at 3:09 PM, Dana Orzel via RE-wrenches 
 wrote:


The question was – When might these units be available?
The first request from the manu. was to get a survey of how many 
units might get sold per year & responses are still trickling in slowly.
Next Tump & I will be in a zoom meeting with the company powers that 
be & at that point they need to source & design.
I would bet it is out aways still depending on equipment 
choices/availability, testing & UL certification etc.
I would not even dare to guess but when we ca report back with a date 
we will do so.

Dana Orzel -  E -d...@solarwork.com-  C - 208.721.7003 //
*From:*RE-wrenches *On 
Behalf Of*Kevin Pegg via RE-wrenches

*Sent:*Friday, July 8, 2022 12:59 PM
*To:*RE-wrenches 
*Cc:*Kevin Pegg 
*Subject:*Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS 
INQUIRY
Thanks for this – there is certainly demand. I could see my company 
buying a 3-5 per year.

Is there any estimate of timeline when these might be available?
Kevin
*From:*RE-wrenches *On 
Behalf Of*Dana Orzel via RE-wrenches

*Sent:*June-30-22 11:02 AM
*To:*'RE-wrenches' 
*Cc:*Dana Orzel 
*Subject:*[RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY
Hey now all you off grid designer/installers,
I just had a conversation with generator manufacturer (name withheld 
for the moment), about 8-13KW water cooled gensets with UL & LP gas 
powered. I explained that there is a long time hole in the market 
since Onan & Kohler dropped their gensets for prime power in this 
size range.
If they made the investment to produce & UL certify a 13KW - 1800 RPM 
- water cooled – 2 wire start, prime power rated - 120/240vac genset, 
how many off grid systems are being installed with oversized gensets?
/_If this was available how many units would each of you be 
interested in per year?_/I am not asking for a commitment just a 
market survey for this sized unit.
If there was 20-30 companies selling 4-5+ each per year this might be 
a possibility.
Let me know either off list or on list (if this is OK ? Michael let 
us know) & I hope there is a possibility here for more appropriately 
sized & available gensets for our off grid client systems.
I will be passing along this research to the OE manufacturer. If you 
do not want your name passed along let me know for now.

Dana Orzel  Great Solar Works, Inc.
*C - 208.721.7003 **d...@solarwork.com* <mailto:d...@solarwork.com>**
Idaho Contractor - # 028765 Idaho PV # 028374
NABCEP # 051112-136 www.greatsolarworks.com 
<http://www.greatsolarworks.com/>

_"Responsible Technologies for Responsible People since 1988" _
**
*P*Please consider the environment before printing this email.
___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


*Tump 
mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>3...@gmail.com* 
*www.SWNL.net* 
http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>

Solarwinds Northernlights *//*
*/       Serving Mid Coast Maine & Northern California/**/
/**/   207-832-7574   Cl. 610-517-8401 /*
*//**/Blair "TUMP" May/*

*/              MAINE'S CHARTER 
/**//**/  NABCEP "Certified PV Installer"/**/
/**/
       MAINE'S CHARTER 
/**/    Trace Xantrex "Certified" Dealer / Installer"/*







___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrench

Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-11 Thread Drake Chamberlin via RE-wrenches

There is no regular pattern to our need for generators, but we could
likely sell some. 


---

On 2022-07-10 16:02, Chris Daum via RE-wrenches wrote:

I think we could sell a couple a year. 

--Chris @ the Oasis Montana 


From: RE-wrenches  On Behalf Of Tump 
via RE-wrenches
Sent: Sunday, July 10, 2022 10:54 AM
To: RE-wrenches 
Cc: Tump 
Subject: Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY 


How many folks require UL listing to install, this may expedite delivery?

On Jul 8, 2022, at 3:09 PM, Dana Orzel via RE-wrenches  wrote: 

The question was - When might these units be available? 

The first request from the manu. was to get a survey of how many units might get sold per year & responses are still trickling in slowly.  

Next Tump & I will be in a zoom meeting with the company powers that be & at that point they need to source & design.  

I would bet it is out aways still depending on equipment choices/availability, testing & UL certification etc. 

I would not even dare to guess but when we ca report back with a date we will do so. 

Dana Orzel -  E - d...@solarwork.com -  C - 208.721.7003  


From: RE-wrenches  On Behalf Of 
Kevin Pegg via RE-wrenches
Sent: Friday, July 8, 2022 12:59 PM
To: RE-wrenches 
Cc: Kevin Pegg 
Subject: Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY 

Thanks for this - there is certainly demand. I could see my company buying a 3-5 per year.  

Is there any estimate of timeline when these might be available?  

Kevin 


From: RE-wrenches  On Behalf Of Dana 
Orzel via RE-wrenches
Sent: June-30-22 11:02 AM
To: 'RE-wrenches' 
Cc: Dana Orzel 
Subject: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY 

Hey now all you off grid designer/installers, 

I just had a conversation with generator manufacturer (name withheld for the moment), about 8-13KW water cooled gensets with UL & LP gas powered. I explained that there is a long time hole in the market since Onan & Kohler dropped their gensets for prime power in this size range. 

If they made the investment to produce & UL certify a 13KW - 1800 RPM - water cooled - 2 wire start, prime power rated - 120/240vac genset, how many off grid systems are being installed with oversized gensets? 

_If this was available how many units would each of you be interested in per year? _I am not asking for a commitment just a market survey for this sized unit. 

If there was 20-30 companies selling 4-5+ each per year this might be a possibility. 

Let me know either off list or on list (if this is OK ? Michael let us know) & I hope there is a possibility here for more appropriately sized & available gensets for our off grid client systems. 

I will be passing along this research to the OE manufacturer. If you do not want your name passed along let me know for now. 

Dana Orzel  Great Solar Works, Inc.  

C - 208.721.7003   d...@solarwork.com 

Idaho Contractor - # 028765 Idaho PV # 028374 

NABCEP # 051112-136   www.greatsolarworks.com [1] 

"Responsible Technologies for Responsible People since 1988"   

P Please consider the environment before printing this email. 


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org [2]

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [3]

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ [4]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org [5]

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm [6]

Check out or update participant bios:
http://www.members.re-wrenches.org [7]



Tump [8]3...@gmail.com   www.SWNL.net [9]

Solarwinds Northernlights   __ 


_   Serving Mid Coast Maine & Northern California_
_ 207-832-7574   Cl. 610-517-8401  _ 

_  __Blair "TUMP" May_ 


  MAINE'S CHARTER 
_ NABCEP"Certified PV Installer"_ 


  MAINE'S CHARTER 
_Trace Xantrex "Certified" Dealer / Installer"_


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

L

Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-10 Thread Chris Daum via RE-wrenches
I think we could sell a couple a year.
 
--Chris @ the Oasis Montana
 
From: RE-wrenches  On Behalf Of Tump 
via RE-wrenches
Sent: Sunday, July 10, 2022 10:54 AM
To: RE-wrenches 
Cc: Tump 
Subject: Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY
 
How many folks require UL listing to install, this may expedite delivery?
On Jul 8, 2022, at 3:09 PM, Dana Orzel via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org> > 
wrote:
 
The question was – When might these units be available?
 
The first request from the manu. was to get a survey of how many units might 
get sold per year & responses are still trickling in slowly. 
Next Tump & I will be in a zoom meeting with the company powers that be & at 
that point they need to source & design. 
I would bet it is out aways still depending on equipment choices/availability, 
testing & UL certification etc.
 
I would not even dare to guess but when we ca report back with a date we will 
do so.
 
 
Dana Orzel -  E - d...@solarwork.com <mailto:d...@solarwork.com>  -  C - 
208.721.7003 
 
From: RE-wrenches mailto:re-wrenches-boun...@lists.re-wrenches.org> > On Behalf Of Kevin Pegg 
via RE-wrenches
Sent: Friday, July 8, 2022 12:59 PM
To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org> >
Cc: Kevin Pegg mailto:kp...@energyalternatives.ca> >
Subject: Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY
 
Thanks for this – there is certainly demand. I could see my company buying a 
3-5 per year. 
 
Is there any estimate of timeline when these might be available? 
 
Kevin
 
From: RE-wrenches mailto:re-wrenches-boun...@lists.re-wrenches.org> > On Behalf Of Dana Orzel 
via RE-wrenches
Sent: June-30-22 11:02 AM
To: 'RE-wrenches' mailto:re-wrenches@lists.re-wrenches.org> >
Cc: Dana Orzel mailto:d...@solarwork.com> >
Subject: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY
 
Hey now all you off grid designer/installers,
 
I just had a conversation with generator manufacturer (name withheld for the 
moment), about 8-13KW water cooled gensets with UL & LP gas powered. I 
explained that there is a long time hole in the market since Onan & Kohler 
dropped their gensets for prime power in this size range.
 
If they made the investment to produce & UL certify a 13KW - 1800 RPM - water 
cooled – 2 wire start, prime power rated - 120/240vac genset, how many off grid 
systems are being installed with oversized gensets?
 
If this was available how many units would each of you be interested in per 
year? I am not asking for a commitment just a market survey for this sized unit.
 
If there was 20-30 companies selling 4-5+ each per year this might be a 
possibility.
 
Let me know either off list or on list (if this is OK ? Michael let us know) & 
I hope there is a possibility here for more appropriately sized & available 
gensets for our off grid client systems.
I will be passing along this research to the OE manufacturer. If you do not 
want your name passed along let me know for now.
 
 
 
Dana Orzel  Great Solar Works, Inc. 
C - 208.721.7003<mailto:d...@solarwork.com> 
d...@solarwork.com
Idaho Contractor - # 028765 Idaho PV # 028374
NABCEP # 051112-136<http://www.greatsolarworks.com/> 
www.greatsolarworks.com
"Responsible Technologies for Responsible People since 1988"  
 
P Please consider the environment before printing this email.
 
 
___
List sponsored by Redwood Alliance

Pay optional member dues here:  <http://re-wrenches.org/> http://re-wrenches.org

List Address:  <mailto:RE-wrenches@lists.re-wrenches.org> 
RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
 <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/> 
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
 <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm> 
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
 <http://www.members.re-wrenches.org/> http://www.members.re-wrenches.org
 
Tump 
mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net> 
3...@gmail.com <mailto:3...@gmail.com> 
http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/> 
www.SWNL.net
Solarwinds Northernlights   
   Serving Mid Coast Maine & Northern California

Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-10 Thread Howie Michaelson via RE-wrenches
We typically do not require UL listing, but that is always good for
insurance reasons...

*Howie Michaelson**Sun Catcher*

*NABCEP Certified Solar PV Installer™*

*Solar Electric Systems Sales & Service802-272-0004*


On Sun, Jul 10, 2022 at 12:53 PM Tump via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> How many folks require UL listing to install, this may expedite delivery?
>
> On Jul 8, 2022, at 3:09 PM, Dana Orzel via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> The question was – When might these units be available?
>
> The first request from the manu. was to get a survey of how many units
> might get sold per year & responses are still trickling in slowly.
> Next Tump & I will be in a zoom meeting with the company powers that be &
> at that point they need to source & design.
> I would bet it is out aways still depending on equipment
> choices/availability, testing & UL certification etc.
>
> I would not even dare to guess but when we ca report back with a date we
> will do so.
>
>
> Dana Orzel -  E - d...@solarwork.com -  C - 208.721.7003
>
> *From:* RE-wrenches  *On
> Behalf Of *Kevin Pegg via RE-wrenches
> *Sent:* Friday, July 8, 2022 12:59 PM
> *To:* RE-wrenches 
> *Cc:* Kevin Pegg 
> *Subject:* Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS
> INQUIRY
>
> Thanks for this – there is certainly demand. I could see my company buying
> a 3-5 per year.
>
> Is there any estimate of timeline when these might be available?
>
> Kevin
>
> *From:* RE-wrenches  *On
> Behalf Of *Dana Orzel via RE-wrenches
> *Sent:* June-30-22 11:02 AM
> *To:* 'RE-wrenches' 
> *Cc:* Dana Orzel 
> *Subject:* [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY
>
> Hey now all you off grid designer/installers,
>
> I just had a conversation with generator manufacturer (name withheld for
> the moment), about 8-13KW water cooled gensets with UL & LP gas powered. I
> explained that there is a long time hole in the market since Onan & Kohler
> dropped their gensets for prime power in this size range.
>
> If they made the investment to produce & UL certify a 13KW - 1800 RPM -
> water cooled – 2 wire start, prime power rated - 120/240vac genset, how
> many off grid systems are being installed with oversized gensets?
>
> *If this was available how many units would each of you be interested in
> per year? *I am not asking for a commitment just a market survey for this
> sized unit.
>
> If there was 20-30 companies selling 4-5+ each per year this might be a
> possibility.
>
> Let me know either off list or on list (if this is OK ? Michael let us
> know) & I hope there is a possibility here for more appropriately sized &
> available gensets for our off grid client systems.
> I will be passing along this research to the OE manufacturer. If you do
> not want your name passed along let me know for now.
>
>
>
> Dana Orzel  Great Solar Works, Inc.
> *C - 208.721.7003   **d...@solarwork.com*
> 
> Idaho Contractor - # 028765 Idaho PV # 028374
> NABCEP # 051112-136   www.greatsolarworks.com
> *"Responsible Technologies for Responsible People since 1988"  *
>
> *P* Please consider the environment before printing this email.
>
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
> *tump3...@gmail.com <3...@gmail.com>*   *www.SWNL.net*
> Solarwinds Northernlights
> *   Serving Mid Coast Maine & Northern California*
> * 207-832-7574   Cl.
> 610-517-8401  *
>   *Blair "TUMP" May*
>
>
> *     MAINE'S CHARTER  *   *
> NABCEP"Certified PV Installer"*
>
>
> *   MAINE'S CHARTER   **
> Trace Xantrex "Certified" Dealer / Installer"*
>
>
>
>
&g

Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-10 Thread Tump via RE-wrenches
How many folks require UL listing to install, this may expedite delivery?
> On Jul 8, 2022, at 3:09 PM, Dana Orzel via RE-wrenches 
>  wrote:
> 
> The question was – When might these units be available?
>  
> The first request from the manu. was to get a survey of how many units might 
> get sold per year & responses are still trickling in slowly. 
> Next Tump & I will be in a zoom meeting with the company powers that be & at 
> that point they need to source & design. 
> I would bet it is out aways still depending on equipment 
> choices/availability, testing & UL certification etc.
>  
> I would not even dare to guess but when we ca report back with a date we will 
> do so.
>  
>  
> Dana Orzel -  E - d...@solarwork.com <mailto:d...@solarwork.com> -  C - 
> 208.721.7003 
>  
> From: RE-wrenches  <mailto:re-wrenches-boun...@lists.re-wrenches.org>> On Behalf Of Kevin Pegg 
> via RE-wrenches
> Sent: Friday, July 8, 2022 12:59 PM
> To: RE-wrenches  <mailto:re-wrenches@lists.re-wrenches.org>>
> Cc: Kevin Pegg  <mailto:kp...@energyalternatives.ca>>
> Subject: Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY
>  
> Thanks for this – there is certainly demand. I could see my company buying a 
> 3-5 per year. 
>  
> Is there any estimate of timeline when these might be available? 
>  
> Kevin
>  
> From: RE-wrenches  <mailto:re-wrenches-boun...@lists.re-wrenches.org>> On Behalf Of Dana Orzel 
> via RE-wrenches
> Sent: June-30-22 11:02 AM
> To: 'RE-wrenches'  <mailto:re-wrenches@lists.re-wrenches.org>>
> Cc: Dana Orzel mailto:d...@solarwork.com>>
> Subject: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY
>  
> Hey now all you off grid designer/installers,
>  
> I just had a conversation with generator manufacturer (name withheld for the 
> moment), about 8-13KW water cooled gensets with UL & LP gas powered. I 
> explained that there is a long time hole in the market since Onan & Kohler 
> dropped their gensets for prime power in this size range.
>  
> If they made the investment to produce & UL certify a 13KW - 1800 RPM - water 
> cooled – 2 wire start, prime power rated - 120/240vac genset, how many off 
> grid systems are being installed with oversized gensets?
>  
> If this was available how many units would each of you be interested in per 
> year? I am not asking for a commitment just a market survey for this sized 
> unit.
>  
> If there was 20-30 companies selling 4-5+ each per year this might be a 
> possibility.
>  
> Let me know either off list or on list (if this is OK ? Michael let us know) 
> & I hope there is a possibility here for more appropriately sized & available 
> gensets for our off grid client systems.
> I will be passing along this research to the OE manufacturer. If you do not 
> want your name passed along let me know for now.
>  
>  
>  
> Dana Orzel  Great Solar Works, Inc. 
> C - 208.721.7003   d...@solarwork.com 
> <mailto:d...@solarwork.com>
> Idaho Contractor - # 028765 Idaho PV # 028374
> NABCEP # 051112-136   www.greatsolarworks.com 
> <http://www.greatsolarworks.com/>
> "Responsible Technologies for Responsible People since 1988"  
>  
> P Please consider the environment before printing this email.
>  
>  
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> Tump 
> mailto:t...@swnl.net%22%20%5Co%20%22blocked::mailto:t...@swnl.net>3...@gmail.com
>www.SWNL.net 
> http://www.swnl

Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-08 Thread Dana Orzel via RE-wrenches
The question was - When might these units be available?

 

The first request from the manu. was to get a survey of how many units might
get sold per year & responses are still trickling in slowly. 

Next Tump & I will be in a zoom meeting with the company powers that be & at
that point they need to source & design. 

I would bet it is out aways still depending on equipment
choices/availability, testing & UL certification etc.

 

I would not even dare to guess but when we ca report back with a date we
will do so.

 

 

Dana Orzel -  E - d...@solarwork.com -  C - 208.721.7003 

 

From: RE-wrenches  On Behalf Of
Kevin Pegg via RE-wrenches
Sent: Friday, July 8, 2022 12:59 PM
To: RE-wrenches 
Cc: Kevin Pegg 
Subject: Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

 

Thanks for this - there is certainly demand. I could see my company buying a
3-5 per year. 

 

Is there any estimate of timeline when these might be available? 

 

Kevin

 

From: RE-wrenches mailto:re-wrenches-boun...@lists.re-wrenches.org> > On Behalf Of Dana Orzel
via RE-wrenches
Sent: June-30-22 11:02 AM
To: 'RE-wrenches' mailto:re-wrenches@lists.re-wrenches.org> >
Cc: Dana Orzel mailto:d...@solarwork.com> >
Subject: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

 

Hey now all you off grid designer/installers,

 

I just had a conversation with generator manufacturer (name withheld for the
moment), about 8-13KW water cooled gensets with UL & LP gas powered. I
explained that there is a long time hole in the market since Onan & Kohler
dropped their gensets for prime power in this size range.

 

If they made the investment to produce & UL certify a 13KW - 1800 RPM -
water cooled - 2 wire start, prime power rated - 120/240vac genset, how many
off grid systems are being installed with oversized gensets?

 

If this was available how many units would each of you be interested in per
year? I am not asking for a commitment just a market survey for this sized
unit.

 

If there was 20-30 companies selling 4-5+ each per year this might be a
possibility.

 

Let me know either off list or on list (if this is OK ? Michael let us know)
& I hope there is a possibility here for more appropriately sized &
available gensets for our off grid client systems.

I will be passing along this research to the OE manufacturer. If you do not
want your name passed along let me know for now.

 

 

 

Dana Orzel  Great Solar Works, Inc. 

C - 208.721.7003<mailto:d...@solarwork.com>
d...@solarwork.com

Idaho Contractor - # 028765 Idaho PV # 028374

NABCEP # 051112-136<http://www.greatsolarworks.com/>
www.greatsolarworks.com

"Responsible Technologies for Responsible People since 1988"  

 

P Please consider the environment before printing this email.

 

 

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-08 Thread Kevin Pegg via RE-wrenches
Thanks for this - there is certainly demand. I could see my company buying a 
3-5 per year.

Is there any estimate of timeline when these might be available?

Kevin

From: RE-wrenches  On Behalf Of Dana 
Orzel via RE-wrenches
Sent: June-30-22 11:02 AM
To: 'RE-wrenches' 
Cc: Dana Orzel 
Subject: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

Hey now all you off grid designer/installers,

I just had a conversation with generator manufacturer (name withheld for the 
moment), about 8-13KW water cooled gensets with UL & LP gas powered. I 
explained that there is a long time hole in the market since Onan & Kohler 
dropped their gensets for prime power in this size range.

If they made the investment to produce & UL certify a 13KW - 1800 RPM - water 
cooled - 2 wire start, prime power rated - 120/240vac genset, how many off grid 
systems are being installed with oversized gensets?

If this was available how many units would each of you be interested in per 
year? I am not asking for a commitment just a market survey for this sized unit.

If there was 20-30 companies selling 4-5+ each per year this might be a 
possibility.

Let me know either off list or on list (if this is OK ? Michael let us know) & 
I hope there is a possibility here for more appropriately sized & available 
gensets for our off grid client systems.
I will be passing along this research to the OE manufacturer. If you do not 
want your name passed along let me know for now.



Dana Orzel  Great Solar Works, Inc.
C - 208.721.7003   
d...@solarwork.com<mailto:d...@solarwork.com>
Idaho Contractor - # 028765 Idaho PV # 028374
NABCEP # 051112-136   
www.greatsolarworks.com<http://www.greatsolarworks.com/>
"Responsible Technologies for Responsible People since 1988"

P Please consider the environment before printing this email.


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-08 Thread Amos Post via RE-wrenches
I will second with 4-5 per year.  The Kohlers are what we use currently also in 
the 8-14KW range for off-grid (mostly the 14KW size).


   Amos Post
   Integrity Energy
  W 802.763.7023
   C 802.291.2188
ienergyVT.com 
Facebook 

> On Jul 6, 2022, at 9:20 AM, Luke Christy via RE-wrenches 
>  wrote:
> 
> Hi Dana,
> Following up on this, I would certainly be interested. 
> We are a  small shop but I typically sell and install 5-8 generators per 
> year. These are almost always Kohler 3600rpm 14kW units, so a 13 kW low speed 
> unit would be welcome as an option. 
> 
> Thanks!
> 
> 
>> On Jun 30, 2022, at 12:01 PM, Dana Orzel via RE-wrenches 
>> > > wrote:
>> 
>> Hey now all you off grid designer/installers,
>>  
>> I just had a conversation with generator manufacturer (name withheld for the 
>> moment), about 8-13KW water cooled gensets with UL & LP gas powered. I 
>> explained that there is a long time hole in the market since Onan & Kohler 
>> dropped their gensets for prime power in this size range.
>>  
>> If they made the investment to produce & UL certify a 13KW - 1800 RPM - 
>> water cooled – 2 wire start, prime power rated - 120/240vac genset, how many 
>> off grid systems are being installed with oversized gensets?
>>  
>> If this was available how many units would each of you be interested in per 
>> year? I am not asking for a commitment just a market survey for this sized 
>> unit.
>>  
>> If there was 20-30 companies selling 4-5+ each per year this might be a 
>> possibility.
>>  
>> Let me know either off list or on list (if this is OK ? Michael let us know) 
>> & I hope there is a possibility here for more appropriately sized & 
>> available gensets for our off grid client systems.
>> I will be passing along this research to the OE manufacturer. If you do not 
>> want your name passed along let me know for now.
>>  
>>  
>>  
>> Dana Orzel  Great Solar Works, Inc. 
>> C - 208.721.7003   d...@solarwork.com 
>> 
>> Idaho Contractor - # 028765 Idaho PV # 028374
>> NABCEP # 051112-136   www.greatsolarworks.com 
>> 
>> "Responsible Technologies for Responsible People since 1988"  
>>  
>> P Please consider the environment before printing this email.
>>  
>>  
>> ___
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> 
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org 
>> 
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> 
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
>> 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> 
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> 
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org 
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-06 Thread Luke Christy via RE-wrenches
Hi Dana,
Following up on this, I would certainly be interested. 
We are a  small shop but I typically sell and install 5-8 generators per year. 
These are almost always Kohler 3600rpm 14kW units, so a 13 kW low speed unit 
would be welcome as an option. 

Thanks!


> On Jun 30, 2022, at 12:01 PM, Dana Orzel via RE-wrenches 
>  wrote:
> 
> Hey now all you off grid designer/installers,
>  
> I just had a conversation with generator manufacturer (name withheld for the 
> moment), about 8-13KW water cooled gensets with UL & LP gas powered. I 
> explained that there is a long time hole in the market since Onan & Kohler 
> dropped their gensets for prime power in this size range.
>  
> If they made the investment to produce & UL certify a 13KW - 1800 RPM - water 
> cooled – 2 wire start, prime power rated - 120/240vac genset, how many off 
> grid systems are being installed with oversized gensets?
>  
> If this was available how many units would each of you be interested in per 
> year? I am not asking for a commitment just a market survey for this sized 
> unit.
>  
> If there was 20-30 companies selling 4-5+ each per year this might be a 
> possibility.
>  
> Let me know either off list or on list (if this is OK ? Michael let us know) 
> & I hope there is a possibility here for more appropriately sized & available 
> gensets for our off grid client systems.
> I will be passing along this research to the OE manufacturer. If you do not 
> want your name passed along let me know for now.
>  
>  
>  
> Dana Orzel  Great Solar Works, Inc. 
> C - 208.721.7003   d...@solarwork.com 
> 
> Idaho Contractor - # 028765 Idaho PV # 028374
> NABCEP # 051112-136   www.greatsolarworks.com 
> 
> "Responsible Technologies for Responsible People since 1988"  
>  
> P Please consider the environment before printing this email.
>  
>  
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> 
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> 
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> 
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
> 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> 
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> 
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-02 Thread frenergy via RE-wrenches
As an aside, maybe I've been living under a rock but I have not heard of 
1800 RPM gensets running on propane, but exclusive to diesel.  It sounds 
like that's a thing.  I'm small time off-grid here but I could easily 
see 3-4 units/year.  I'm assuming if this come to fruition, the 
manufacturer would be thinking off-grid durability, not home standby.  I 
like the water-cooled aspect of this proposal for less noise.


            I would also hope for a manufacturer that has good on the 
ground coverage for service, warranty, maintenance.


Bill

Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049

On 7/2/2022 10:58 AM, Michael Morningstar via RE-wrenches wrote:
Very Cool. We install on the average about two dozen <15kw generators 
annually. Mostly diesel and a few Honda propane. The diesels are a 
hard sell for some reason. Would love to see the return of the quality 
smaller Kohler/Onans.


On Sat, Jul 2, 2022 at 9:11 AM Dana Orzel via RE-wrenches 
 wrote:


I heard back Friday from the generator manufacturers executive
board meeting Friday morning there is their response:



Hi Dana,

I spoke with the executives this morning and we’re very excited to
hear what the demand is for this genset is. If it makes sense,
we’re all in.



Please let me know if your interest in a 13KW – 1800 RPM genset –
water cooled is of interest for you & your off grid clients. I see
this as a big opportunity for replacing the oversized gensets that
we have been forced to use  for a long time now.

Dana Orzel -  E - d...@solarwork.com -  C - 208.721.7003 //

*From:* RE-wrenches 
*On Behalf Of *Dana Orzel via RE-wrenches
*Sent:* Thursday, June 30, 2022 12:02 PM
*To:* 'RE-wrenches' 
*Cc:* Dana Orzel 
*Subject:* [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS
INQUIRY

Hey now all you off grid designer/installers,

I just had a conversation with generator manufacturer (name
withheld for the moment), about 8-13KW water cooled gensets with
UL & LP gas powered. I explained that there is a long time hole in
the market since Onan & Kohler dropped their gensets for prime
power in this size range.

If they made the investment to produce & UL certify a 13KW - 1800
RPM - water cooled – 2 wire start, prime power rated - 120/240vac
genset, how many off grid systems are being installed with
oversized gensets?

/_If this was available how many units would each of you be
interested in per year? _/I am not asking for a commitment just a
market survey for this sized unit.

If there was 20-30 companies selling 4-5+ each per year this might
be a possibility.

Let me know either off list or on list (if this is OK ? Michael
let us know) & I hope there is a possibility here for more
appropriately sized & available gensets for our off grid client
systems.

I will be passing along this research to the OE manufacturer. If
you do not want your name passed along let me know for now.

Dana Orzel  Great Solar Works, Inc.

*C - 208.721.7003 **d...@solarwork.com* <mailto:d...@solarwork.com>**

Idaho Contractor - # 028765 Idaho PV # 028374

NABCEP # 051112-136 www.greatsolarworks.com
<http://www.greatsolarworks.com/>

_"Responsible Technologies for Responsible People since 1988" _

**

*P*Please consider the environment before printing this email.

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work,
try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



--

Michael Morningstar


Morningstar Electric

PO Box 1494

Mount Shasta, CA 96067

530-921-0560

mjmornings...@gmail.com



___



--
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't 

Re: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-02 Thread Michael Morningstar via RE-wrenches
Very Cool. We install on the average about two dozen <15kw generators
annually. Mostly diesel and a few Honda propane. The diesels are a hard
sell for some reason. Would love to see the return of the quality smaller
Kohler/Onans.

On Sat, Jul 2, 2022 at 9:11 AM Dana Orzel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> I heard back Friday from the generator manufacturers executive board
> meeting Friday morning there is their response:
>
> 
>
> Hi Dana,
>
>
>
> I spoke with the executives this morning and we’re very excited to hear
> what the demand is for this genset is. If it makes sense, we’re all in.
>
> 
>
> Please let me know if your interest in a 13KW – 1800 RPM genset – water
> cooled is of interest for you & your off grid clients. I see this as a big
> opportunity for replacing the oversized gensets that we have been forced to
> use  for a long time now.
>
>
>
>
>
>
>
> Dana Orzel -  E - d...@solarwork.com -  C - 208.721.7003
>
>
>
> *From:* RE-wrenches  *On
> Behalf Of *Dana Orzel via RE-wrenches
> *Sent:* Thursday, June 30, 2022 12:02 PM
> *To:* 'RE-wrenches' 
> *Cc:* Dana Orzel 
> *Subject:* [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY
>
>
>
> Hey now all you off grid designer/installers,
>
>
>
> I just had a conversation with generator manufacturer (name withheld for
> the moment), about 8-13KW water cooled gensets with UL & LP gas powered. I
> explained that there is a long time hole in the market since Onan & Kohler
> dropped their gensets for prime power in this size range.
>
>
>
> If they made the investment to produce & UL certify a 13KW - 1800 RPM -
> water cooled – 2 wire start, prime power rated - 120/240vac genset, how
> many off grid systems are being installed with oversized gensets?
>
>
>
> *If this was available how many units would each of you be interested in
> per year? *I am not asking for a commitment just a market survey for this
> sized unit.
>
>
>
> If there was 20-30 companies selling 4-5+ each per year this might be a
> possibility.
>
>
>
> Let me know either off list or on list (if this is OK ? Michael let us
> know) & I hope there is a possibility here for more appropriately sized &
> available gensets for our off grid client systems.
>
> I will be passing along this research to the OE manufacturer. If you do
> not want your name passed along let me know for now.
>
>
>
>
>
>
>
> Dana Orzel  Great Solar Works, Inc.
>
> *C - 208.721.7003   **d...@solarwork.com*
> 
>
> Idaho Contractor - # 028765 Idaho PV # 028374
>
> NABCEP # 051112-136   www.greatsolarworks.com
>
> *"Responsible Technologies for Responsible People since 1988"  *
>
>
>
> *P* Please consider the environment before printing this email.
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

Michael Morningstar


Morningstar Electric

PO Box 1494

Mount Shasta, CA 96067

530-921-0560

mjmornings...@gmail.com
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-07-02 Thread Dana Orzel via RE-wrenches
I heard back Friday from the generator manufacturers executive board meeting
Friday morning there is their response: 



Hi Dana,

 

I spoke with the executives this morning and we're very excited to hear what
the demand is for this genset is. If it makes sense, we're all in.



Please let me know if your interest in a 13KW - 1800 RPM genset - water
cooled is of interest for you & your off grid clients. I see this as a big
opportunity for replacing the oversized gensets that we have been forced to
use  for a long time now.

 

 

 

Dana Orzel -  E - d...@solarwork.com -  C - 208.721.7003 

 

From: RE-wrenches  On Behalf Of
Dana Orzel via RE-wrenches
Sent: Thursday, June 30, 2022 12:02 PM
To: 'RE-wrenches' 
Cc: Dana Orzel 
Subject: [RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

 

Hey now all you off grid designer/installers,

 

I just had a conversation with generator manufacturer (name withheld for the
moment), about 8-13KW water cooled gensets with UL & LP gas powered. I
explained that there is a long time hole in the market since Onan & Kohler
dropped their gensets for prime power in this size range.

 

If they made the investment to produce & UL certify a 13KW - 1800 RPM -
water cooled - 2 wire start, prime power rated - 120/240vac genset, how many
off grid systems are being installed with oversized gensets?

 

If this was available how many units would each of you be interested in per
year? I am not asking for a commitment just a market survey for this sized
unit.

 

If there was 20-30 companies selling 4-5+ each per year this might be a
possibility.

 

Let me know either off list or on list (if this is OK ? Michael let us know)
& I hope there is a possibility here for more appropriately sized &
available gensets for our off grid client systems.

I will be passing along this research to the OE manufacturer. If you do not
want your name passed along let me know for now.

 

 

 

Dana Orzel  Great Solar Works, Inc. 

C - 208.721.7003<mailto:d...@solarwork.com>
d...@solarwork.com

Idaho Contractor - # 028765 Idaho PV # 028374

NABCEP # 051112-136<http://www.greatsolarworks.com/>
www.greatsolarworks.com

"Responsible Technologies for Responsible People since 1988"  

 

P Please consider the environment before printing this email.

 

 

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] WATER COOLED - 1800 RPM - 13KW GENERATORS INQUIRY

2022-06-30 Thread Dana Orzel via RE-wrenches
Hey now all you off grid designer/installers,

 

I just had a conversation with generator manufacturer (name withheld for the
moment), about 8-13KW water cooled gensets with UL & LP gas powered. I
explained that there is a long time hole in the market since Onan & Kohler
dropped their gensets for prime power in this size range.

 

If they made the investment to produce & UL certify a 13KW - 1800 RPM -
water cooled - 2 wire start, prime power rated - 120/240vac genset, how many
off grid systems are being installed with oversized gensets?

 

If this was available how many units would each of you be interested in per
year? I am not asking for a commitment just a market survey for this sized
unit.

 

If there was 20-30 companies selling 4-5+ each per year this might be a
possibility.

 

Let me know either off list or on list (if this is OK ? Michael let us know)
& I hope there is a possibility here for more appropriately sized &
available gensets for our off grid client systems.

I will be passing along this research to the OE manufacturer. If you do not
want your name passed along let me know for now.

 

 

 

Dana Orzel  Great Solar Works, Inc. 

C - 208.721.7003   d...@solarwork.com

Idaho Contractor - # 028765 Idaho PV # 028374

NABCEP # 051112-136   www.greatsolarworks.com
 

"Responsible Technologies for Responsible People since 1988"  

 

P Please consider the environment before printing this email.

 

 

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org