HI William,

I appreciate your time and input as to your thinking about this project.

However this system already exists and has been in operation for some time.  
Client has a offgrid farm with 45kva generator.  

The situation is that the main house also already runs off this generator, but 
the generator doesn’t run 24/7/365.  The other times of the year they run a 
honda 6500 at 120/240vac to power the house. The existing infrastructure of the 
farm is already set up for 120/208 3 phase and it wouldn’t be necessary or 
wanted to change all that for 7kw of inverters.

That all said, I’ll probably run the inverters at 120/240 setup, as the back up 
generator is 120/240.  And when they use the 3 phase generator its on 24 hrs a 
day.  Yes it will only use 1 inverter to battery charge, but given 24 hr charge 
time, it’ll keep up the batteries no problem.

Thanks to all,

Jay









> On Apr 2, 2020, at 11:31 AM, William Miller  wrote:
> 
> Jay:
>  
> This idea sounds wrong on many levels.  Generators are designed to be loaded 
> evenly, with some allowance for normal deviations.  Having separate loads 
> that can vary independently is asking for regulation problems.
>  
> You did not state if the generator was wound Wye or Delta.  This makes a 
> difference. 
>  
> Delta wound generators that provide 120/240 have one winding center-tapped.  
> That winding can provide only 1/3 of the rating of the generator (there is 
> some research that says the de-rate is greater).   If this is the case, your 
> two inverters can each access only 1/6 of the generator capability.  Sure you 
> might be able to draw more than 1/6, for a while...
>  
> Have you checked to see if the generator can be field re-tapped to provide 
> 120 only?  Then you could provide a generator-fed distribution and put all of 
> your 120 loads on it, providing the full generator capability.
>  
> It has come to my attention recently that two Outback FXR (or FX, I am not 
> sure) inverters can be stacked on two legs of a three-phase input power 
> source.  I had thought this was not possible.  I know it works because I 
> accidently did this.  I believe the supply was Wye configured.  It was with a 
> mobile set up built by someone else.  The inverters should have been the 
> Mobile version, and maybe this is what made this possible.  You just can't 
> use an X240 on this setup.  Consider this option if you must unbalance the 
> generator.  Try to balance the loads and charging between the inverters and 
> avoid power-save settings (you can't power-save without an X240 anyway).
>  
> I have had many customers ask me to do something that my intuition told me 
> was a bad idea.  When I was younger I might comply, and learn to regret it.  
> Good luck and stay strong.
>  
> William Miller
>  
> -Original Message-
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org 
> <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of jay
> Sent: Wednesday, April 1, 2020 4:39 PM
> To: RE-wrenches
> Subject: [RE-wrenches] magnum question
>  
> Hi All,
>  
> My question is can a single  Magnum remote run 2 inverters each as master for 
> 120v?
>  
>  
> I’ve got a client with a 3 phase generator, and I need two phases, but I 
> don’t need 240v.
>  
>  
> 1. I can’t change the generator
> 2. Two phases because I can’t load one phase that heavily.
>  
> I can do 2 Outback FXR’s each as a master,  but I’d need to have 2 Mate3S’s.
>  
> But I don’t know if magnum has that possiblity?
>  
> Thanks
>  
> jay
>  
> Peltz Power
>  
>  
>  
> ___
> List sponsored by Redwood Alliance
>  
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
>  
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>  
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>  
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>  
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>  
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wre

Re: [RE-wrenches] magnum question

2020-04-02 Thread William Miller
Jay:



This idea sounds wrong on many levels.  Generators are designed to be
loaded evenly, with some allowance for normal deviations.  Having separate
loads that can vary independently is asking for regulation problems.



You did not state if the generator was wound Wye or Delta.  This makes a
difference.



Delta wound generators that provide 120/240 have one winding
center-tapped.  That winding can provide only 1/3 of the rating of the
generator (there is some research that says the de-rate is greater).   If
this is the case, your two inverters can each access only 1/6 of the
generator capability.  Sure you might be able to draw more than 1/6, for a
while...



Have you checked to see if the generator can be field re-tapped to provide
120 only?  Then you could provide a generator-fed distribution and put all
of your 120 loads on it, providing the full generator capability.



It has come to my attention recently that two Outback FXR (or FX, I am not
sure) inverters can be stacked on two legs of a three-phase input power
source.  I had thought this was not possible.  I know it works because I
accidently did this.  I believe the supply was Wye configured.  It was with
a mobile set up built by someone else.  The inverters should have been the
Mobile version, and maybe this is what made this possible.  You just can't
use an X240 on this setup.  Consider this option if you must unbalance the
generator.  Try to balance the loads and charging between the inverters and
avoid power-save settings (you can't power-save without an X240 anyway).



I have had many customers ask me to do something that my intuition told me
was a bad idea.  When I was younger I might comply, and learn to regret
it.  Good luck and stay strong.



William Miller



-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of jay
Sent: Wednesday, April 1, 2020 4:39 PM
To: RE-wrenches
Subject: [RE-wrenches] magnum question



Hi All,



My question is can a single  Magnum remote run 2 inverters each as master
for 120v?





I’ve got a client with a 3 phase generator, and I need two phases, but I
don’t need 240v.





1. I can’t change the generator

2. Two phases because I can’t load one phase that heavily.



I can do 2 Outback FXR’s each as a master,  but I’d need to have 2
Mate3S’s.



But I don’t know if magnum has that possiblity?



Thanks



jay



Peltz Power







___

List sponsored by Redwood Alliance



List Address: RE-wrenches@lists.re-wrenches.org



Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html



List rules & etiquette:

www.re-wrenches.org/etiquette.htm



Check out or update participant bios:

www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] magnum question

2020-04-02 Thread Lones Tuss
Hi Jay
The FXR inverters do have the ability to run 2 legs of a 3phase system on a 
single Mate3(s)and a Hub10.3
Inside the Hub10.3 is a header containing 5 jumpers. These jumpers can be 
arranged so the inverters are set to a 3 phase
configuration. 
Up to 9 inverters can be used per system, up to 3 inverters per ac phase. 
Up to 6 inverters can be used with up to 3 inverters per phase on 2 of the ac 
legs a 3phase system.
For more information on the jumper locations see the Hub 10.3 quick start guide.
http://www.outbackpower.com/downloads/documents/system_management/hub/hub103_quick_start.pdf

In a 3 phase system the inverters are programmed as Master, B phase Master, C 
Phase Master or designated as a Slave inverter.
Each Master can control 2 slave inverters.
This is further explained in the FXR installation manual.
http://www.outbackpower.com/downloads/documents/inverter_chargers/fxr_vfxr_a/fxr_install.pdf
 
I hope this helps.
Take Care All






 
-Original Message-
From: RE-wrenches  On Behalf Of jay
Sent: Wednesday, April 1, 2020 4:39 PM
To: RE-wrenches 
Subject: [RE-wrenches] magnum question

Hi All,

My question is can a single  Magnum remote run 2 inverters each as master for 
120v?


I’ve got a client with a 3 phase generator, and I need two phases, but I don’t 
need 240v.


1. I can’t change the generator
2. Two phases because I can’t load one phase that heavily.

I can do 2 Outback FXR’s each as a master,  but I’d need to have 2 Mate3S’s. 

But I don’t know if magnum has that possiblity?

Thanks

jay

Peltz Power



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
https://protect2.fireeye.com/v1/url?k=d4abb431-890cfaf3-d4a8bdba-002590870bde-fe8439a98f146def=1=cc596888-1eac-4ff2-b73a-fe4a7f887cd6=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
https://protect2.fireeye.com/v1/url?k=6fb987e8-321ec92a-6fba8e63-002590870bde-aa16baf4f942a9e8=1=cc596888-1eac-4ff2-b73a-fe4a7f887cd6=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm

Check out or update participant bios:
https://protect2.fireeye.com/v1/url?k=744e5f95-29e91157-744d561e-002590870bde-8fb79a89726d0b65=1=cc596888-1eac-4ff2-b73a-fe4a7f887cd6=http%3A%2F%2Fwww.members.re-wrenches.org%2F

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] magnum question

2020-04-02 Thread Jay
Hi Dana,

That depends on the unit. 

In my case its a large generator with large loads, the inverters being just one 
of the loads. I can’t load one phase with 8kw, that would overload one phase.   
Splitting the load to 2 phases, is within the capacity of the generator and 
within the total loads

I know I can do the inverters the way I want, what I dont know is if you can 
have 2 x 120v magnum inverters both as master with a single controller. 

Jay


> On Apr 1, 2020, at 5:28 PM, Dana Orzel  wrote:
> 
> I have been informed [long ago] that not equally weighting a generators 
> output can cause excessive & uneven wear on the windings of a generator.
> Way Back in the day, folks [old wrenches] used to place an additional load 
> [hot water element, heat lamps...] on the unused leg to balance out a 240 vac 
> gen that was only using one 120v leg for inverter /battery charging on a 240 
> only generator. Simple but effective though not very fuel thrifty.
> 
> I am open to dispelling this anecdote/old wife's tale, if anyone can confirm 
> or dispute this. It makes sense to me overall.
> 
> 
> 
> Dana Orzel  Great Solar Works, Inc. 
> C - 208.721.7003   d...@solarwork.com
> Idaho Contractor - # 028765 Idaho PV # 028374
> NABCEP # 051112-136   www.solarwork.com
> "Responsible Technologies for Responsible People since 1988"  
>  Please consider the environment before printing this email.
> 
> 
> -Original Message-
> From: RE-wrenches  On Behalf Of jay
> Sent: Wednesday, April 1, 2020 5:39 PM
> To: RE-wrenches 
> Subject: [RE-wrenches] magnum question
> 
> Hi All,
> 
> My question is can a single  Magnum remote run 2 inverters each as master for 
> 120v?
> 
> 
> I’ve got a client with a 3 phase generator, and I need two phases, but I 
> don’t need 240v.
> 
> 
> 1. I can’t change the generator
> 2. Two phases because I can’t load one phase that heavily.
> 
> I can do 2 Outback FXR’s each as a master,  but I’d need to have 2 Mate3S’s. 
> 
> But I don’t know if magnum has that possiblity?
> 
> Thanks
> 
> jay
> 
> Peltz Power
> 
> 
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] magnum question

2020-04-01 Thread Dana Orzel
I have been informed [long ago] that not equally weighting a generators output 
can cause excessive & uneven wear on the windings of a generator.
Way Back in the day, folks [old wrenches] used to place an additional load [hot 
water element, heat lamps...] on the unused leg to balance out a 240 vac gen 
that was only using one 120v leg for inverter /battery charging on a 240 only 
generator. Simple but effective though not very fuel thrifty.

I am open to dispelling this anecdote/old wife's tale, if anyone can confirm or 
dispute this. It makes sense to me overall.



Dana Orzel  Great Solar Works, Inc. 
C - 208.721.7003   d...@solarwork.com
Idaho Contractor - # 028765 Idaho PV # 028374
NABCEP # 051112-136   www.solarwork.com
"Responsible Technologies for Responsible People since 1988"  
 Please consider the environment before printing this email.


-Original Message-
From: RE-wrenches  On Behalf Of jay
Sent: Wednesday, April 1, 2020 5:39 PM
To: RE-wrenches 
Subject: [RE-wrenches] magnum question

Hi All,

My question is can a single  Magnum remote run 2 inverters each as master for 
120v?


I’ve got a client with a 3 phase generator, and I need two phases, but I don’t 
need 240v.


1. I can’t change the generator
2. Two phases because I can’t load one phase that heavily.

I can do 2 Outback FXR’s each as a master,  but I’d need to have 2 Mate3S’s. 

But I don’t know if magnum has that possiblity?

Thanks

jay

Peltz Power



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] magnum question

2020-04-01 Thread jay
Hi All,

My question is can a single  Magnum remote run 2 inverters each as master for 
120v?


I’ve got a client with a 3 phase generator, and I need two phases, but I don’t 
need 240v.


1. I can’t change the generator
2. Two phases because I can’t load one phase that heavily.

I can do 2 Outback FXR’s each as a master,  but I’d need to have 2 Mate3S’s. 

But I don’t know if magnum has that possiblity?

Thanks

jay

Peltz Power



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] magnum question

2014-11-03 Thread Chris Mason
Gary,
I have an older IPAD dedicated to manuals. I use PDF Pro to transfer them
and catalogue them on the IPAD and I take that to every installation. I
have dozens of manuals on the IPAD, and as long as I take the time to
download them and catalogue them they are always available to me.

On Mon, Nov 3, 2014 at 12:26 PM, Baxter, Gary gbax...@sensata.com wrote:

  Hi Chris,



 Thanks for the thoughts. I understand about the paper manuals I always
 like to have a hard copy around and I think we kind of trained everyone on
 the SW to make sure the settings were recorded somewhere.



 There were two things that led us to put the manuals on disc (we are
 looking into USB now) cost and space. A lot of people have commented on how
 thorough Tony Boatwright (Tony wrote Trace manuals as well) is when he
 writes the manuals but unfortunately the manuals have grown in size. The
 manuals can no longer be printed on half page (8.5 x 11 folded in half)
 there are too many pages. The next option is to print a full size 8.5 x 11
 but the price per manual now is up to $6 each our cost and that is printing
 2k per print and it requires new boxes for the products so a larger manual
 can fit. Seems like trivial stuff but it adds up quickly when you are
 shipping 20k pieces per year.



 That said we understand the need for paper manuals and are looking into it
 again, we discussed offering paper manuals on a request basis.



 Thanks for the feedback,



 Gary



 *Gary Baxter*

 *Product Manager*

 Magnum | Dimensions

 2211 West Casino Rd.

 Everett, WA. 98204

 Office 425.353.8833 | Mobile 425.501.0289 | Fax. 425.353.8390



 *Please Note My New Email Address:*



 *gbax...@sensata.com gbax...@sensata.com* | www.magnumenergy.com



 *A Sensata Technologies Business Unit*









 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
 Behalf Of *Chris Schaefer
 *Sent:* Saturday, November 01, 2014 10:23 AM

 *To:* 'RE-wrenches'
 *Cc:* Santos-Buch, Alan; Boatwright, Anthony
 *Subject:* Re: [RE-wrenches] magnum question



 Gary,

 Just wanted to take the time to say thanks for the follow-up.
 I'm hoping other manufacturers will follow suit to let us know how issues
 are resolved. Sometimes us off-grid installers feel awfully lonely out
 here:).

 On a separate issue, please offer a paper manual option when
 it comes to your Remote/routers. This is necessary so that we can record
 the settings and not have to bring a laptop in to the remote locations were
 we do our work. I understand that you're trying to go green and that you
 are constantly refining your products, thus this requires a reprint and
 that is expensive. The DVD is fine for a client that may never look at it
 but as installers we need the hard copies. I'd be happy to pay an
 additional charge for these as we don't need it for every system. Thanks
 for listening.



 Christopher



 PS still waiting on your version of a 48V grid-tie/battery backup inverter
 (not AC-Coupling)



 Chris Schaefer’s

 [image: SolarWindFX]

 *Tel/Fax 585-229-2083 585-229-2083 or Cell
 585-748-1870 585-748-1870  *

 * 5115 South Hill Road ~ Canandaigua New York 14424*

 *www.solarandwindfx.com http://www.solarandwindfx.com ~ E-mail:
 ch...@solarandwindfx.com ch...@solarandwindfx.com*













 Thomas Jefferson, the author of our great Constitution, once said,
 democracy will cease to exist
 when you take away from those who are willing
 to work and give to those who would not.





 -Original Message-
 From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
 re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Baxter, Gary
 Sent: Friday, October 31, 2014 18:44
 To: RE-wrenches
 Cc: Santos-Buch, Alan; Boatwright, Anthony
 Subject: Re: [RE-wrenches] magnum question



 Follow up with Jay,



 We thought it might help others to post what we found with Jay's system.
 This was a Magnum MS4024PAE model that is 120/240 split phase input and
 output. We describe this unit as 2-2k units in series inside one unit with
 a two winding transformer basically an autoformer.



 The issue Jay was having was a Overtemp fault when charging from
 generator after an hour or so. The first tech suggested turning down the
 charge rate to 70% which solved the issue but didn't answer the question of
 why the unit was in Overtemp. The first suspicion was there was 120v into
 the inverter which will cause the transformer to run on half the windings
 and overheat at full charger output. It is perfectly acceptable to input
 120v to the MS-PAE (either leg) and it will charge and the output will be
 240v but the charge rate should be reduced. The voltage measurement to the
 input terminals was 240v so that issue was not suspected anymore.



 What Jay found was one pole of the 240v breaker from the generator was
 bad. What made it hard to troubleshoot

Re: [RE-wrenches] magnum question

2014-11-03 Thread Dan Fink
Here, we use a DropBox folder of manuals sorted by manufacturers that any
employee or sub here can access; if the site is so far off grid it has no
wifi or cell, they just have to download to their smartphone/tablet/etc
before the job. Clients get a link to just the manuals for their equipment
on Dropbox.
CDs or DVDs for docs are of almost zero use to us, I think there's only one
computer around here that even has a DVD drive anymore. USB drive or SD
card would be FAR more useful, We can read those on our smartphones.
Our most recent Magnum order last month still had paper manuals for
everything; I 3-hole punch those for the client's brain book that hangs
by their system control center by the fire extinguisher and baking soda
with EMERGENCY SHUTDOWN INSTRUCTIONS and a troubleshooting flowchart on
the cover.
Likely I'll be buying fewer 3-ring binders for clients in the near future,
or at least slimmer ones, but it's easy to include a couple pages of system
settings that can be filled in by hand by the installer, signed and dated,
right along with our battery bank inspection / maintenance forms, even if
the actual paper manuals are not there. Really prefer that clients don't
mess with system settings all that much anyway.
With systems where the client takes responsibility for battery bank
maintenance, I've found that the guilt factor of someone in charge seeing
that nobody on their staff has filled out that prominently displayed
battery maint form in awhile is a very effective motivator.
I like the dedicated old iPad idea, Chris! going to look for one used and
cheap, or a China tablet.
Sigh. Anyone here remember back in the day when your test equipment /
troubleshooting tool bag didn't include 2 different USB cords, thumb drive
full of firmware upgrades and manuals, a laptop computer and little
inverter to run it? AH well, at least we got MPPT now, 48v systems, MC4 PV
module connectors and thinner wire too.

Best;

Dan Fink
Buckville Energy
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
NABCEP / IREC / ISPQ Accredited Continuing Education Providers™
970.672.4342



On Mon, Nov 3, 2014 at 10:17 AM, Chris Mason cometenergysyst...@gmail.com
wrote:

 Gary,
 I have an older IPAD dedicated to manuals. I use PDF Pro to transfer them
 and catalogue them on the IPAD and I take that to every installation. I
 have dozens of manuals on the IPAD, and as long as I take the time to
 download them and catalogue them they are always available to me.



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] magnum question

2014-11-03 Thread jay peltz
HI All,

I've got many folks who are not very tech savy, so electronic manuals are a non 
option.
I support the idea, just make it easy to buy paper copies.
And really that includes me. I like a paper copy of the things I need.  My 
phone while it has lots of manuals is too small to really read.
I don't bring my table to the field except for known reprograming work ( 
classics).
And the batteries never go dead.

What I would suggest is  a map of how to get around.  
Back in the days of Trace and Tony would know this for sure, they used to 
include in the later years a large format map which showed the menus/ 
adjustments
Mostly this what folks need IMHO.
If they have a problem they'll call but sometimes getting them to understand 
where to go/ how to get there is difficult via phone.
But a map included with each item ( RC/ARC only really) will really help out.

Thanks

jay

peltz power


On Nov 3, 2014, at 10:50 AM, Dan Fink wrote:

 Here, we use a DropBox folder of manuals sorted by manufacturers that any 
 employee or sub here can access; if the site is so far off grid it has no 
 wifi or cell, they just have to download to their smartphone/tablet/etc 
 before the job. Clients get a link to just the manuals for their equipment on 
 Dropbox.
 CDs or DVDs for docs are of almost zero use to us, I think there's only one 
 computer around here that even has a DVD drive anymore. USB drive or SD card 
 would be FAR more useful, We can read those on our smartphones.
 Our most recent Magnum order last month still had paper manuals for 
 everything; I 3-hole punch those for the client's brain book that hangs by 
 their system control center by the fire extinguisher and baking soda with 
 EMERGENCY SHUTDOWN INSTRUCTIONS and a troubleshooting flowchart on the 
 cover. 
 Likely I'll be buying fewer 3-ring binders for clients in the near future, or 
 at least slimmer ones, but it's easy to include a couple pages of system 
 settings that can be filled in by hand by the installer, signed and dated, 
 right along with our battery bank inspection / maintenance forms, even if the 
 actual paper manuals are not there. Really prefer that clients don't mess 
 with system settings all that much anyway.
 With systems where the client takes responsibility for battery bank 
 maintenance, I've found that the guilt factor of someone in charge seeing 
 that nobody on their staff has filled out that prominently displayed battery 
 maint form in awhile is a very effective motivator.
 I like the dedicated old iPad idea, Chris! going to look for one used and 
 cheap, or a China tablet.
 Sigh. Anyone here remember back in the day when your test equipment / 
 troubleshooting tool bag didn't include 2 different USB cords, thumb drive 
 full of firmware upgrades and manuals, a laptop computer and little inverter 
 to run it? AH well, at least we got MPPT now, 48v systems, MC4 PV module 
 connectors and thinner wire too.
 
 Best;
 
 Dan Fink
 Buckville Energy
 IREC Certified Instructor™ for: 
 ~ PV Installation Professional
 ~ Small Wind Installer
 NABCEP / IREC / ISPQ Accredited Continuing Education Providers™
 970.672.4342
 
  
 
 On Mon, Nov 3, 2014 at 10:17 AM, Chris Mason cometenergysyst...@gmail.com 
 wrote:
 Gary,
 I have an older IPAD dedicated to manuals. I use PDF Pro to transfer them and 
 catalogue them on the IPAD and I take that to every installation. I have 
 dozens of manuals on the IPAD, and as long as I take the time to download 
 them and catalogue them they are always available to me.
 
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] magnum question

2014-11-03 Thread Baxter, Gary
Chris,
Good point all the manuals are available as pdf on line. We still run into 
people without internet access so paper is still their choice.

I did receive an email from a customer that said he couldn’t access our website 
because he didn’t have a computer or internet, I didn’t ask how he emailed.

Gary

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Chris Mason
Sent: Monday, November 03, 2014 9:17 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] magnum question

Gary,
I have an older IPAD dedicated to manuals. I use PDF Pro to transfer them and 
catalogue them on the IPAD and I take that to every installation. I have dozens 
of manuals on the IPAD, and as long as I take the time to download them and 
catalogue them they are always available to me.

On Mon, Nov 3, 2014 at 12:26 PM, Baxter, Gary 
gbax...@sensata.commailto:gbax...@sensata.com wrote:
Hi Chris,

Thanks for the thoughts. I understand about the paper manuals I always like to 
have a hard copy around and I think we kind of trained everyone on the SW to 
make sure the settings were recorded somewhere.

There were two things that led us to put the manuals on disc (we are looking 
into USB now) cost and space. A lot of people have commented on how thorough 
Tony Boatwright (Tony wrote Trace manuals as well) is when he writes the 
manuals but unfortunately the manuals have grown in size. The manuals can no 
longer be printed on half page (8.5 x 11 folded in half) there are too many 
pages. The next option is to print a full size 8.5 x 11 but the price per 
manual now is up to $6 each our cost and that is printing 2k per print and it 
requires new boxes for the products so a larger manual can fit. Seems like 
trivial stuff but it adds up quickly when you are shipping 20k pieces per year.

That said we understand the need for paper manuals and are looking into it 
again, we discussed offering paper manuals on a request basis.

Thanks for the feedback,

Gary

Gary Baxter
Product Manager
Magnum | Dimensions
2211 West Casino Rd.
Everett, WA. 98204
Office 425.353.8833tel:425.353.8833 | Mobile 425.501.0289tel:425.501.0289 | 
Fax. 425.353.8390tel:425.353.8390

Please Note My New Email Address:

gbax...@sensata.commailto:gbax...@sensata.com | 
www.magnumenergy.comhttp://www.magnumenergy.com/

A Sensata Technologies Business Unit




From: RE-wrenches 
[mailto:re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org]
 On Behalf Of Chris Schaefer
Sent: Saturday, November 01, 2014 10:23 AM

To: 'RE-wrenches'
Cc: Santos-Buch, Alan; Boatwright, Anthony
Subject: Re: [RE-wrenches] magnum question


Gary,

Just wanted to take the time to say thanks for the follow-up. I'm 
hoping other manufacturers will follow suit to let us know how issues are 
resolved. Sometimes us off-grid installers feel awfully lonely out here:).

On a separate issue, please offer a paper manual option when it 
comes to your Remote/routers. This is necessary so that we can record the 
settings and not have to bring a laptop in to the remote locations were we do 
our work. I understand that you're trying to go green and that you are 
constantly refining your products, thus this requires a reprint and that is 
expensive. The DVD is fine for a client that may never look at it but as 
installers we need the hard copies. I'd be happy to pay an additional charge 
for these as we don't need it for every system. Thanks for listening.



Christopher



PS still waiting on your version of a 48V grid-tie/battery backup inverter (not 
AC-Coupling)

Chris Schaefer’s
[SolarWindFX]
Tel/Fax 585-229-2083tel:585-229-2083 or Cell 
585-748-1870tel:585-748-1870
 5115 South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.comhttp://www.solarandwindfx.com ~ E-mail: 
ch...@solarandwindfx.commailto:ch...@solarandwindfx.com


[cid:image002.jpg@01CFF75C.388117F0]

[cid:image003.jpg@01CFF75C.388117F0]


[cid:image004.jpg@01CFF75C.388117F0]










Thomas Jefferson, the author of our great Constitution, once said, democracy 
will cease to exist 
when you take away from those who are willing to work and give to those 
who would not.




-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Baxter, Gary
Sent: Friday, October 31, 2014 18:44
To: RE-wrenches
Cc: Santos-Buch, Alan; Boatwright, Anthony
Subject: Re: [RE-wrenches] magnum question



Follow up with Jay,



We thought it might help others to post what we found with Jay's system. This 
was a Magnum MS4024PAE model that is 120/240 split phase input and output. We 
describe this unit as 2-2k units in series inside one unit with a two winding 
transformer basically an autoformer.



The issue Jay was having was a Overtemp fault when charging from generator 
after an hour or so. The first

Re: [RE-wrenches] magnum question

2014-11-03 Thread Baxter, Gary
Jay,
Another good idea. We have thought about a quick start guide including the 
menu map, does that sound like it would work for most? I know that's what my 
new Cannon printer came with and when I had a wireless programming question I 
had to go online for the full manual.

Gary

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of jay peltz
Sent: Monday, November 03, 2014 11:26 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] magnum question

HI All,

I've got many folks who are not very tech savy, so electronic manuals are a non 
option.
I support the idea, just make it easy to buy paper copies.
And really that includes me. I like a paper copy of the things I need.  My 
phone while it has lots of manuals is too small to really read.
I don't bring my table to the field except for known reprograming work ( 
classics).
And the batteries never go dead.

What I would suggest is  a map of how to get around.
Back in the days of Trace and Tony would know this for sure, they used to 
include in the later years a large format map which showed the menus/ 
adjustments
Mostly this what folks need IMHO.
If they have a problem they'll call but sometimes getting them to understand 
where to go/ how to get there is difficult via phone.
But a map included with each item ( RC/ARC only really) will really help out.

Thanks

jay

peltz power


On Nov 3, 2014, at 10:50 AM, Dan Fink wrote:


Here, we use a DropBox folder of manuals sorted by manufacturers that any 
employee or sub here can access; if the site is so far off grid it has no wifi 
or cell, they just have to download to their smartphone/tablet/etc before the 
job. Clients get a link to just the manuals for their equipment on Dropbox.
CDs or DVDs for docs are of almost zero use to us, I think there's only one 
computer around here that even has a DVD drive anymore. USB drive or SD card 
would be FAR more useful, We can read those on our smartphones.
Our most recent Magnum order last month still had paper manuals for everything; 
I 3-hole punch those for the client's brain book that hangs by their system 
control center by the fire extinguisher and baking soda with EMERGENCY 
SHUTDOWN INSTRUCTIONS and a troubleshooting flowchart on the cover.
Likely I'll be buying fewer 3-ring binders for clients in the near future, or 
at least slimmer ones, but it's easy to include a couple pages of system 
settings that can be filled in by hand by the installer, signed and dated, 
right along with our battery bank inspection / maintenance forms, even if the 
actual paper manuals are not there. Really prefer that clients don't mess with 
system settings all that much anyway.
With systems where the client takes responsibility for battery bank 
maintenance, I've found that the guilt factor of someone in charge seeing 
that nobody on their staff has filled out that prominently displayed battery 
maint form in awhile is a very effective motivator.
I like the dedicated old iPad idea, Chris! going to look for one used and 
cheap, or a China tablet.
Sigh. Anyone here remember back in the day when your test equipment / 
troubleshooting tool bag didn't include 2 different USB cords, thumb drive full 
of firmware upgrades and manuals, a laptop computer and little inverter to run 
it? AH well, at least we got MPPT now, 48v systems, MC4 PV module connectors 
and thinner wire too.

Best;

Dan Fink
Buckville Energy
IREC Certified Instructor(tm) for:
~ PV Installation Professional
~ Small Wind Installer
NABCEP / IREC / ISPQ Accredited Continuing Education Providers(tm)
970.672.4342



On Mon, Nov 3, 2014 at 10:17 AM, Chris Mason 
cometenergysyst...@gmail.commailto:cometenergysyst...@gmail.com wrote:
Gary,
I have an older IPAD dedicated to manuals. I use PDF Pro to transfer them and 
catalogue them on the IPAD and I take that to every installation. I have dozens 
of manuals on the IPAD, and as long as I take the time to download them and 
catalogue them they are always available to me.


___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.orgmailto:RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htmhttp://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.orghttp://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update

Re: [RE-wrenches] magnum question

2014-10-31 Thread Baxter, Gary
Follow up with Jay,

We thought it might help others to post what we found with Jay's system. This 
was a Magnum MS4024PAE model that is 120/240 split phase input and output. We 
describe this unit as 2-2k units in series inside one unit with a two winding 
transformer basically an autoformer. 

The issue Jay was having was a Overtemp fault when charging from generator 
after an hour or so. The first tech suggested turning down the charge rate to 
70% which solved the issue but didn't answer the question of why the unit was 
in Overtemp. The first suspicion was there was 120v into the inverter which 
will cause the transformer to run on half the windings and overheat at full 
charger output. It is perfectly acceptable to input 120v to the MS-PAE (either 
leg) and it will charge and the output will be 240v but the charge rate should 
be reduced. The voltage measurement to the input terminals was 240v so that 
issue was not suspected anymore. 

What Jay found was one pole of the 240v breaker from the generator was bad. 
What made it hard to troubleshoot and the reason for the post is that the 
MS-PAE will accept 120 or 240 input but always convert to 240 output. When 
measuring the input to a MS-PAE you should remove the wires from the terminal 
block and take the readings on the wires. The sense transformer on the inverter 
input will make the input look like 240v but no current on one leg will 
overheat the transformer. With the wires removed the voltage measurement will 
show there is no 240v available.

Gary

Gary Baxter
Product Manager
Magnum | Dimensions
2211 West Casino Rd.
Everett, WA. 98204
Office 425.353.8833 | Mobile 425.501.0289 | Fax. 425.353.8390

Please Note My New Email Address:

gbax...@sensata.com | www.magnumenergy.com

A Sensata Technologies Business Unit




-Original Message-
From: Baxter, Gary 
Sent: Thursday, October 23, 2014 9:50 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] magnum question

Hi Jay,
Sorry you didn't get help. Let me know what you need and I will get you an 
answer.

Gary Baxter
Product Manager
Magnum/Dimensions 

 On Oct 23, 2014, at 9:19 PM, jay peltz j...@asis.com wrote:
 
 HI All,
 
 Does anyone have a person at Magnum in engineering or higher up than tech 
 support.
 
 I've got a problem with an inverter that tech support won't or can't help 
 with.
 
 thanks
 
 jay
 
 peltz power
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] magnum question

2014-10-24 Thread Baxter, Gary
Hi Jay,
Sorry you didn't get help. Let me know what you need and I will get you an 
answer.

Gary Baxter
Product Manager
Magnum/Dimensions 

 On Oct 23, 2014, at 9:19 PM, jay peltz j...@asis.com wrote:
 
 HI All,
 
 Does anyone have a person at Magnum in engineering or higher up than tech 
 support.
 
 I've got a problem with an inverter that tech support won't or can't help 
 with.
 
 thanks
 
 jay
 
 peltz power
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] magnum question

2014-10-24 Thread Starlight Solar Power Systems,
Jay, 

Perhaps asking the question here. I have hundreds of Magnum inverter 
installations, perhaps I or others can help.

Larry
On Oct 23, 2014, at 5:44 PM, jay peltz j...@asis.com wrote:

HI All,

Does anyone have a person at Magnum in engineering or higher up than tech 
support.

I've got a problem with an inverter that tech support won't or can't help with.

thanks

jay

peltz power
___
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] magnum question

2014-10-23 Thread jay peltz
HI All,

Does anyone have a person at Magnum in engineering or higher up than tech 
support.

I've got a problem with an inverter that tech support won't or can't help with.

thanks

jay

peltz power
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org