Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown - for multiple arrays

2019-12-03 Thread Lloyd Hoffstatter
Al,

You may find this article and the one referenced to be helpful

https://www.purepower.com/blog/nec-690-12-rapid-shutdown-length

Best regards,

Lloyd Hoffstatter
Sunstruck Consulting

Sent from Mail for Windows 10

From: Al Frishman
Sent: Tuesday, December 3, 2019 11:42 AM
To: RE-wrenches
Subject: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown - for multiple arrays

Hey Wrenchers,
What is your interpretaion regarding NEC 2014 690.12 Rapid Shutdown of PV 
Systems on Buildings when dealing with multiple arrays separated by 4 ft paths 
on flat roofs.For example can one inverter located at the East end of an 
array be connected to solar panels on both the adjacent array to the inverter 
and a 2nd or even 3rd array located to the West separated by 4 ft paths?

I appreciate your feedback.

Al Frishman
EvolvedSolar
(917) 699-6641


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-04-16 Thread Nathan Charles
e. If the conductors are going
>> immediately into the building, as with residential and integrated systems,
>> a shutdown device would have to be within 5’ of entering the building. If
>> goes outside for a while, then inside the building, the total length could
>> be no more than 10’ and no more than 5’ inside the building­this is not
>> additive. Remember, all this is for firefighter safety.
>>
>> As Brian Mehalic and others have pointed out, the language does not
>> specify where the shutdown initiating device is to be located. The lack of
>> detail is more for flexibility than it is to give an AHJ license to make an
>> installer do anything they want.
>>
>> With grid-tie only systems (no battery backup), it would be most
>> convenient and cost effective to have a system that initiates the shutdown
>> on loss of utility. In this way, a firefighter can do what they normally
>> do, shut down utility power to the building, and the rapid shutdown would
>> automatically initiate. This does not necessitate an additional
>> disconnecting means for a load-side PV connection. The main breaker could
>> be the initiating device. For a supply-side connection, the NEC already
>> requires that the PV disconnect switch be located adjacent to the service
>> disconnecting means (article 230).
>>
>> The biggest issue with string inverters (central inverters) is that there
>> is a need to shutdown the capacitor input side of the inverter since that
>> stays energized for 5 minutes or more. The 10 seconds was to provide a
>> means to rapidly discharge the capacitors rather than requiring a relay or
>> tripping device. Doing something other than a relay will require a test
>> laboratory to evaluate the function­guess what?­we don’t have a standard
>> yet to evaluate those products. Sounds like you might want to work on that
>> committee.
>>
>> It is more complicated for battery backup systems. Midnite Solar’s
>> birdhouse products are the best I have seen so far to address this concern.
>> Since dc and ac circuits are not differentiated, battery backup systems
>> need to have a shutdown process that works independently of a utility
>> outage for obvious reasons, and it must shutdown both the dc circuits and
>> the backup ac circuits. A separate switch, like the birdhouse, would be
>> necessary that only controls these functions in an emergency situation.
>>
>> Is the language not detailed­possibly. This was done to provide
>> flexibility rather than create problems. Fire departments have been
>> requiring rooftop disconnects for years in California. These disconnects
>> are nearly worthless from a shock prevention point of view since capacitors
>> in the inverter stay charged or there are multiple disconnecting means
>> feeding each other. We have been trying to hold the fire community off of
>> rooftop disconnect requirements so we could work on a solution that
>> actually does what they want it to do. There is a long discussion on this
>> in the appendix of my “Understanding the CalFire Guidelines” document on
>> the SolarABCs website.
>>
>> The 2014 NEC language was a compromise worked out with the solar industry
>> (yes string inverter companies as well) in response to the first version of
>> the proposal which was to require module-level shutdown. This is not
>> module-level shutdown, it is PV output circuit shutdown (combiner box
>> shutdown is another way to look at it). However, the 2017 NEC cycle is this
>> year and there was a lot of talk about requiring module-level shutdown this
>> time around.
>>
>> I hope this helps. I will be writing articles for IAEI journal and other
>> periodicals on this subject since it was a very far-reaching and
>> potentially confusing new requirement in the NEC. Thanks for your interest
>> and let’s keep the constructive dialogue going on the subject. It is time
>> to get involved in the NEC update process again.
>>
>> Bill Brooks.
>>
>> *From:* re-wrenches-boun...@lists.re-wrenches.org 
>> [mailto:re-wrenches-boun...@lists.re-wrenches.org]
>> *On Behalf Of *Jeffrey Quackenbush
>> *Sent:* Thursday, January 16, 2014 1:09 AM
>> *To:* RE-wrenches
>> *Subject:* Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown
>>
>> Wrenches,
>>
>> There is no guidance in the Code text for where the shutdown should take
>> place. (1) says: "Requirements for controlled conductors shall apply only
>> to PV system conductors of more than 1.5m (5') in length inside a building,
>> or more than 3m (10') from a PV array."
&

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-04-15 Thread Dave Click
anything they want.

With grid-tie only systems (no battery backup), it would be most
convenient and cost effective to have a system that initiates the
shutdown on loss of utility. In this way, a firefighter can do
what they normally do, shut down utility power to the building,
and the rapid shutdown would automatically initiate. This does
not necessitate an additional disconnecting means for a load-side
PV connection. The main breaker could be the initiating device.
For a supply-side connection, the NEC already requires that the
PV disconnect switch be located adjacent to the service
disconnecting means (article 230).

The biggest issue with string inverters (central inverters) is
that there is a need to shutdown the capacitor input side of the
inverter since that stays energized for 5 minutes or more. The 10
seconds was to provide a means to rapidly discharge the
capacitors rather than requiring a relay or tripping device.
Doing something other than a relay will require a test laboratory
to evaluate the function­guess what?­we don't have a standard yet
to evaluate those products. Sounds like you might want to work on
that committee.

It is more complicated for battery backup systems. Midnite
Solar's birdhouse products are the best I have seen so far to
address this concern. Since dc and ac circuits are not
differentiated, battery backup systems need to have a shutdown
process that works independently of a utility outage for obvious
reasons, and it must shutdown both the dc circuits and the backup
ac circuits. A separate switch, like the birdhouse, would be
necessary that only controls these functions in an emergency
situation.

Is the language not detailed­possibly. This was done to provide
flexibility rather than create problems. Fire departments have
been requiring rooftop disconnects for years in California. These
disconnects are nearly worthless from a shock prevention point of
view since capacitors in the inverter stay charged or there are
multiple disconnecting means feeding each other. We have been
trying to hold the fire community off of rooftop disconnect
requirements so we could work on a solution that actually does
what they want it to do. There is a long discussion on this in
the appendix of my "Understanding the CalFire Guidelines"
document on the SolarABCs website.

The 2014 NEC language was a compromise worked out with the solar
industry (yes string inverter companies as well) in response to
the first version of the proposal which was to require
module-level shutdown. This is not module-level shutdown, it is
PV output circuit shutdown (combiner box shutdown is another way
to look at it). However, the 2017 NEC cycle is this year and
there was a lot of talk about requiring module-level shutdown
this time around.

I hope this helps. I will be writing articles for IAEI journal
and other periodicals on this subject since it was a very
far-reaching and potentially confusing new requirement in the
NEC. Thanks for your interest and let's keep the constructive
dialogue going on the subject. It is time to get involved in the
NEC update process again.

Bill Brooks.

*From:* re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>
[mailto:re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of
    *Jeffrey Quackenbush
*Sent:* Thursday, January 16, 2014 1:09 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

Wrenches,

There is no guidance in the Code text for where the shutdown
should take place. (1) says: "Requirements for controlled
conductors shall apply only to PV system conductors of more than
1.5m (5') in length inside a building, or more than 3m (10') from
a PV array."


So, the provisions /apply if/ the circuit 10' from the array and
5' inside a building, but no mention is made of where the
shutdown actually needs take place in the circuit. In the video
Bill Brooks suggests that the shutdown mechanism should also be
placed within this 10'/5' boundary but that is just an inference
-- nowhere in the text is this actually specified. If that was
the intent of the Code committee, then they've done a poor job
actually expressing it in English.

I'm concerned that some AHJs will interpret this to exclude all
central inverter systems (without the addition of cost-inducing
secondary DC-DC converters like Tigo) because the combiner or
junction box can be many feet from the actual beginning of a home
run under the array. Alternately, permissive AHJs could allow
this function to be fulfi

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-04-15 Thread Nathan Charles
r to the building, and the rapid shutdown would
> automatically initiate. This does not necessitate an additional
> disconnecting means for a load-side PV connection. The main breaker could
> be the initiating device. For a supply-side connection, the NEC already
> requires that the PV disconnect switch be located adjacent to the service
> disconnecting means (article 230).
>
> The biggest issue with string inverters (central inverters) is that there
> is a need to shutdown the capacitor input side of the inverter since that
> stays energized for 5 minutes or more. The 10 seconds was to provide a
> means to rapidly discharge the capacitors rather than requiring a relay or
> tripping device. Doing something other than a relay will require a test
> laboratory to evaluate the function­guess what?­we don’t have a standard
> yet to evaluate those products. Sounds like you might want to work on that
> committee.
>
> It is more complicated for battery backup systems. Midnite Solar’s
> birdhouse products are the best I have seen so far to address this concern.
> Since dc and ac circuits are not differentiated, battery backup systems
> need to have a shutdown process that works independently of a utility
> outage for obvious reasons, and it must shutdown both the dc circuits and
> the backup ac circuits. A separate switch, like the birdhouse, would be
> necessary that only controls these functions in an emergency situation.
>
> Is the language not detailed­possibly. This was done to provide
> flexibility rather than create problems. Fire departments have been
> requiring rooftop disconnects for years in California. These disconnects
> are nearly worthless from a shock prevention point of view since capacitors
> in the inverter stay charged or there are multiple disconnecting means
> feeding each other. We have been trying to hold the fire community off of
> rooftop disconnect requirements so we could work on a solution that
> actually does what they want it to do. There is a long discussion on this
> in the appendix of my “Understanding the CalFire Guidelines” document on
> the SolarABCs website.
>
> The 2014 NEC language was a compromise worked out with the solar industry
> (yes string inverter companies as well) in response to the first version of
> the proposal which was to require module-level shutdown. This is not
> module-level shutdown, it is PV output circuit shutdown (combiner box
> shutdown is another way to look at it). However, the 2017 NEC cycle is this
> year and there was a lot of talk about requiring module-level shutdown this
> time around.
>
> I hope this helps. I will be writing articles for IAEI journal and other
> periodicals on this subject since it was a very far-reaching and
> potentially confusing new requirement in the NEC. Thanks for your interest
> and let’s keep the constructive dialogue going on the subject. It is time
> to get involved in the NEC update process again.
>
> Bill Brooks.
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org]
> *On Behalf Of *Jeffrey Quackenbush
> *Sent:* Thursday, January 16, 2014 1:09 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown
>
> Wrenches,
>
> There is no guidance in the Code text for where the shutdown should take
> place. (1) says: "Requirements for controlled conductors shall apply only
> to PV system conductors of more than 1.5m (5') in length inside a building,
> or more than 3m (10') from a PV array."
>
>
> So, the provisions *apply if* the circuit 10' from the array and 5'
> inside a building, but no mention is made of where the shutdown actually
> needs take place in the circuit. In the video Bill Brooks suggests that the
> shutdown mechanism should also be placed within this 10'/5' boundary but
> that is just an inference -- nowhere in the text is this actually
> specified. If that was the intent of the Code committee, then they've done
> a poor job actually expressing it in English.
>
> I'm concerned that some AHJs will interpret this to exclude all central
> inverter systems (without the addition of cost-inducing secondary DC-DC
> converters like Tigo) because the combiner or junction box can be many feet
> from the actual beginning of a home run under the array. Alternately,
> permissive AHJs could allow this function to be fulfilled anywhere, meaning
> that the implementation won't meet the intent of the writers.
>
> I'm also concerned, as Isaac mentioned, that there are no requirements for
> how the shutdown be initiated, or that it contains of the accessibility and
> grouping requirements that are always included for disconnects. I really
> t

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-31 Thread Exeltech
Brian,

UL1741, Section 64.11 stipulates the discharge time for capacitors at less than 
five minutes.

Though the context of this Section specifically addresses capacitors that are 
accessible by some aspect of inverter disassembly, it would also be appropriate 
to extend its applicability to DC terminals across which capacitors are 
connected and are otherwise accessible by an external means, such as DC 
conductors.


Dan Lepinski



On Fri, 1/31/14, Brian Mehalic  wrote:

 Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown
 To: "RE-wrenches" 
 Date: Friday, January 31, 2014, 1:52 AM
 
 What about the capacitors on the dc side of the inverter?  My assumption has 
been that this capacitance is the reason behind the 690.17(E) labeling 
requirement.  Admittedly I don't understand the discharge capabilities of 
capacitors, but I've measured their voltage and watched it decay when 
disconnected from a power source (and heard stories about "toss the 
capacitive-laden ballast to the newbie ha ha...).  

So the question is, say for a of a roof mounted array and a ground-level string 
inverter, will additional equipment (either in the inverter or external) be 
required to isolate the PV/dc circuit conductors from the inverter in order to 
meet 690.12?  


Brian Mehalic 
NABCEP Certified Solar PV Installation Professional™ R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132


PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org



On Tue, Jan 21, 2014 at 8:45 PM, Bill Brooks  wrote:

Brian,
 
The requirement is generic. A listed contactor can meet the requirement. A 
standard is only necessary for products that want to be innovative in meeting 
the 30V, 240VA. Killing all power is an option with existing listed equipment. 
NEC 90.4 does not apply.
 
Bill.
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-30 Thread Brian Mehalic
What about the capacitors on the dc side of the inverter?  My assumption
has been that this capacitance is the reason behind the 690.17(E) labeling
requirement.  Admittedly I don't understand the discharge capabilities of
capacitors, but I've measured their voltage and watched it decay when
disconnected from a power source (and heard stories about "toss the
capacitive-laden ballast to the newbie ha ha...).

So the question is, say for a of a roof mounted array and a ground-level
string inverter, will additional equipment (either in the inverter or
external) be required to isolate the PV/dc circuit conductors from the
inverter in order to meet 690.12?


Brian Mehalic
NABCEP Certified Solar PV Installation Professional(tm) R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132

PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org


On Tue, Jan 21, 2014 at 8:45 PM, Bill Brooks  wrote:

> Brian,
>
>
>
> The requirement is generic. A listed contactor can meet the requirement. A
> standard is only necessary for products that want to be innovative in
> meeting the 30V, 240VA. Killing all power is an option with existing listed
> equipment. NEC 90.4 does not apply.
>
>
>
> Bill.
>
>
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
> re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Brian Mehalic
> *Sent:* Tuesday, January 21, 2014 2:36 PM
> *To:* RE-wrenches
> *Cc:* re-wrenches@lists.re-wrenches.org
>
> *Subject:* Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown
>
>
>
> It was suggested to me that since 690.12(5) requires the equipment to be
> listed and identified, and there is no standard for rapid shutdown
> equipment to be listed to then 90.3 (.4?...oh why isn't the NEC on my
> iPad...)says 'revert to the previous version of the NEC' and presto, no
> need to install rapid shutdown. I don't like this but the the person
> suggesting it certainly has an audience and this will appeal to installers
> looking to save on cost wherever possible.
>
> Sent from my iPad
>
>
> On Jan 21, 2014, at 5:11 PM, David Brearley <
> david.brear...@solarprofessional.com> wrote:
>
> Drake,
>
>
>
> The language in 690.12 is the compromise solution that was reached to
> ensure continued industry stability. The alternative to the combiner-level
> shutdown was module-level shutdown. It took a consolidated industry effort
> to push the module-level requirements out one more Code cycle--for the exact
> reasons that you touch on below.
>
>
>
> Not sure if this link has been published on the Wrenches list or not, but
> it provides some background on the topic:
>
>
>
> http://www.youtube.com/watch?v=sUXShMZJorQ
>
>
>
> David Brearley
>
> Senior Technical Editor, *SolarPro* magazine
>
> NABCEP Certified PV Installation Professional
>
> david.brear...@solarprofessional.com
>
> Direct: 541.261.6545
>
>
>
>
>
>
>
>
>
> On Jan 21, 2014, at 1:12 PM, re-wrenches-requ...@lists.re-wrenches.orgwrote:
>
>
>
> *From: *Drake 
>
> *Subject: **Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown*
>
> *Date: *January 21, 2014 11:36:15 AM CST
>
> *To: *RE-wrenches 
>
> *Reply-To: *RE-wrenches 
>
>
>
>
> Bill,
>
> It is good to see that energized conductors are going to be disconnected
> near the arrays. I've been an advocate of disconnecting these conductors by
> ground fault sensing equipment since ground fault detection was first
> implemented in the code. If contactors are to be installed on roofs, it
> likely won't be long before both ground faults and arc faults are
> automatically cleared.
>
> When the requirement for AC arc fault branch circuit protection was first
> put in the NEC, it was postdated to allow time for the electrical industry
> to adapt. This new remote disconnecting requirement does not provide any
> lead time.
>
> As the 2014 NEC is adopted in various jurisdictions, inspectors may feel
> that it is necessary to disallow systems without the newly required
> disconnect feature. This may result in serious problems for solar companies
> and customers, as well as manufacturers.
>
> The protection of firefighters is essential. The implementation of
> renewables is essential also. Insurance claims for weather related, global
> warming-triggered climatic disasters are rising exponentially. Extreme
> weather related events result in major loss of life and billions of dollars
> in property damage. Atmospheric CO2 levels continue to climb from the
> burning of fossil fuels. This is a crisis of global proportions.
>
> My request for cod

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-24 Thread Drake
cy either manually, or as a 
result of a fault.


Thank you,
Matt

CA Matthew Paiss, E19B
Bureau of Field Operations
San Jose Fire Department
1661 Senter Rd
San Jose, CA 95113
(831) 566-3057 c


BTW: the stakeholders who developed the consensus language in 690.12 
are listed in the NEC 2014 Report on Comments:


This comment is the result of a consensus process established among 
three groups of stakeholders: 1) CMP4 Firefighter SafetyTask Group; 
2) SEIA Codes and Standards Working Group; and 3) PV Industry Forum. 
Participants in these groups included the following individuals:


CMP4 Firefighter Safety Task Group
1. Ward Bower, CMP4 representing SEIA
2. Bill Brooks, CMP4 representing SEIA and Chair of Task Group
3. Bob Davidson, Davidson Code Concepts
4. Mark Earley, Secretary, NFPA
5. Bob James, UL
6. Matt Paiss, City of San Jose Fire Department
7. Jim Rogers, CMP4 representing IAEI
8. Todd Stafford, CMP4 representing IBEW
9. Ronnie Toomer, Chair of CMP4
10. Peter Willse, Global Asset Protection Services

SEIA Codes and Standards Working Group
1. Mark Albers, SunPower
2. Mark Baldassari, Enphase Energy
3. Ward Bower, SEIA
4. Bill Brooks, Brooks Engineering/SEIA
5. Joe Cain, Chair of SEIA Codes and Standards Working Group
6. Keith Davidson, SunTech
7. Darrel Higgs, Dow Solar
8. Lee Kraemer, First Solar
9. Carl Lenox, SunPower
10. Charles Luebke, Eaton
11. Martin Mesmer, E.ON
12. Steve Pisklak, Dow Solar13. Robert Rynar, First Solar
14. Michael Schenck, First Solar
15. John Smirnow, SEIA
16. Kris VanDerzee, First Solar
17. Leo Wu, SolarCity
18. Tilak Gopalarathnam, REFUsol Incorporated

PV Industry Forum
1. Mark Albers, SunPower
2. Greg Ball, DNV
3. Bill Brooks, Brooks Engineering, lead for 690.12
4. Mark Baldassari, Enphase Energy
5. Ward Bower, SEIA
6. Michael Coddington, NREL
7. Marv Dargatz, SolarEdge
8. Chris Flueckiger. UL
9. Joerg Grosshennig, SMA
10. Darrel Higgs, Dow Solar
11. Dan Lepinski, Exeltech
12. Carl Lenox, SunPower
13. Charles Luebke, Eaton
14. Matt Paiss, City of San Jose Fire Department
15. Steve Pisklak, Dow Solar
16. Jim Rogers, Town of Oak Bluffs
17. Jon Sharp, Ampt
18. Bhima Sheridan, SolarCity
19. John Smirnow, SEIA
20. Holly Thomas, U.S. Dept. of Energy
21. Phil Undercuffler, Outback Power
22. John Wiles, NMSU, Secretary of PV Industry Forum
23. Leo Wu, SolarCity
24. Tim Zgonena, UL


On Jan 24, 2014, at 1:00 PM, 
<mailto:re-wrenches-requ...@lists.re-wrenches.org>re-wrenches-requ...@lists.re-wrenches.org 
wrote:


From: Drake 
<<mailto:drake.chamber...@redwoodalliance.org>drake.chamber...@redwoodalliance.org>

Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown
Date: January 22, 2014 2:16:18 PM CST
To: RE-wrenches 
<<mailto:re-wrenches@lists.re-wrenches.org>re-wrenches@lists.re-wrenches.org>
Reply-To: RE-wrenches 
<<mailto:re-wrenches@lists.re-wrenches.org>re-wrenches@lists.re-wrenches.org>




David,

My sincere thanks to all of you who worked to keep the module level 
disconnect requirement out of the 2014 code cycle. That ruling 
would have amounted to a knockout punch for string and central 
inverters on buildings.


What was the driving force behind this push for immediate module 
level disconnection? There has clearly not been a rash of 
firefighter deaths due to PV systems. Although PV needs to continue 
evolving safety standards that take into account the concerns of 
firefighters, there is no crisis that would justify thwarting one 
of the few growing sectors of our economy.


The PV track record has been amazingly good. So far, I've found no 
accounts of solar related firefighter deaths or injuries. The NFPA 
statistics show that the highest cause of firefighter death is 
heart attack. 
<http://www.nfpa.org/newsandpublications/nfpa-journal/2013/july-august-2013/features/firefighter-fatalities-in-the-united-states-2012>http://www.nfpa.org/newsandpublications/nfpa-journal/2013/july-august-2013/features/firefighter-fatalities-in-the-united-states-2012 



This push for crippling regulation bears the earmark of ALEC's 
extensive and effective war on solar. As you can read in the 
following links, the massively funded, Koch brothers-linked ALEC is 
lobbying heavily, on every level, to derail solar. All who are 
associated with the solar industry need to be aware of this 
powerful lobbying campaign.


<http://www.theguardian.com/world/2013/dec/04/alec-freerider-homeowners-assault-clean-energy>http://www.theguardian.com/world/2013/dec/04/alec-freerider-homeowners-assault-clean-energy 



http://www.salon.com/2013/12/05/alec_freeriders_with_solar_panels_must_pay_for_robbing_the_system/ 



<http://beforeitsnews.com/environment/2014/01/alec-gain-an-inside-track-on-colorado-solar-2490132.html>http://beforeitsnews.com/environment/2014/01/alec-gain-an-inside-track-on-colorado-solar-2490132.html 



Is there any way that the solar community can be alerted when 
threats to our industry are being put before

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-22 Thread Drake

David,

My sincere thanks to all of you who worked to 
keep the module level disconnect requirement out 
of the 2014 code cycle. That ruling would have 
amounted to a knockout punch for string and central inverters on buildings.


What was the driving force behind this push for 
immediate module level disconnection? There has 
clearly not been a rash of firefighter deaths due 
to PV systems. Although PV needs to continue 
evolving safety standards that take into account 
the concerns of firefighters, there is no crisis 
that would justify thwarting one of the few growing sectors of our economy.


The PV track record has been amazingly good. So 
far, I've found no accounts of solar related 
firefighter deaths or injuries. The NFPA 
statistics show that the highest cause of 
firefighter death is heart attack. 
<http://www.nfpa.org/newsandpublications/nfpa-journal/2013/july-august-2013/features/firefighter-fatalities-in-the-united-states-2012>http://www.nfpa.org/newsandpublications/nfpa-journal/2013/july-august-2013/features/firefighter-fatalities-in-the-united-states-2012 



This push for crippling regulation bears the 
earmark of ALEC’s extensive and effective war on 
solar. As you can read in the following links, 
the massively funded, Koch brothers-linked ALEC 
is lobbying heavily, on every level, to derail 
solar. All who are associated with the solar 
industry need to be aware of this powerful lobbying campaign.


<http://www.theguardian.com/world/2013/dec/04/alec-freerider-homeowners-assault-clean-energy>http://www.theguardian.com/world/2013/dec/04/alec-freerider-homeowners-assault-clean-energy 



http://www.salon.com/2013/12/05/alec_freeriders_with_solar_panels_must_pay_for_robbing_the_system/ 



<http://beforeitsnews.com/environment/2014/01/alec-gain-an-inside-track-on-colorado-solar-2490132.html>http://beforeitsnews.com/environment/2014/01/alec-gain-an-inside-track-on-colorado-solar-2490132.html 



Is there any way that the solar community can be 
alerted when threats to our industry are being 
put before the NEC? Although few contractors have 
the time or money to walk away from their 
businesses and attend code writing committees, a 
substantial number might have the time to make 
phone calls and send letters or emails to code writers.


The solar industry needs a strong lobby of its own.

Drake


At 05:11 PM 1/21/2014, you wrote:

Drake,

The language in 690.12 is the compromise 
solution that was reached to ensure continued 
industry stability. The alternative to the 
combiner-level shutdown was module-level 
shutdown. It took a consolidated industry effort 
to push the module-level requirements out one 
more Code cycle—for the exact reasons that you touch on below.


Not sure if this link has been published on the 
Wrenches list or not, but it provides some background on the topic:


<http://www.youtube.com/watch?v=sUXShMZJorQ>http://www.youtube.com/watch?v=sUXShMZJorQ

David Brearley
Senior Technical Editor, SolarPro magazine
NABCEP Certified PV Installation Professional
<mailto:david.brear...@solarprofessional.com>david.brear...@solarprofessional.com
Direct: 541.261.6545





On Jan 21, 2014, at 1:12 PM, 
<mailto:re-wrenches-requ...@lists.re-wrenches.org>re-wrenches-requ...@lists.re-wrenches.org 
wrote:


From: Drake 
<<mailto:drake.chamber...@redwoodalliance.org>drake.chamber...@redwoodalliance.org>

Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown
Date: January 21, 2014 11:36:15 AM CST
To: RE-wrenches 
<<mailto:re-wrenches@lists.re-wrenches.org>re-wrenches@lists.re-wrenches.org>
Reply-To: RE-wrenches 
<<mailto:re-wrenches@lists.re-wrenches.org>re-wrenches@lists.re-wrenches.org>




Bill,

It is good to see that energized conductors are 
going to be disconnected near the arrays. I've 
been an advocate of disconnecting these 
conductors by ground fault sensing equipment 
since ground fault detection was first 
implemented in the code. If contactors are to 
be installed on roofs, it likely won't be long 
before both ground faults and arc faults are automatically cleared.


When the requirement for AC arc fault branch 
circuit protection was first put in the NEC, it 
was postdated to allow time for the electrical 
industry to adapt. This new remote 
disconnecting requirement does not provide any lead time.


As the 2014 NEC is adopted in various 
jurisdictions, inspectors may feel that it is 
necessary to disallow systems without the newly 
required disconnect feature. This may result in 
serious problems for solar companies and customers, as well as manufacturers.


The protection of firefighters is essential. 
The implementation of renewables is essential 
also. Insurance claims for weather related, 
global warming-triggered climatic disasters are 
rising exponentially. Extreme weather related 
events result in major loss of life and 
billions of dollars in property damage. 
Atmospheric CO2

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-21 Thread Bill Brooks
Mark,

 

If that relay you mention is rated for the dc voltage, current, AIR, and
temperature it will see, you are good to go. The enclosure would have to be
NEMA 4 or mounted in a vertical NEMA 3R box. Then there is always the
question of how much experience do you have with that product in that
environment in that application. That is a lot to consider.


Products that have been used for several years in listed combiner boxes have
a track record to consider.

 

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Tuesday, January 21, 2014 6:03 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

 

OK. So I will have a high rate of acceptance if it buy an Tyco vacuum relay,
and mount it in a Hoffman enclosure, and then put it on my roof?

On 1/21/2014 5:45 PM, Bill Brooks wrote:

Brian,

 

The requirement is generic. A listed contactor can meet the requirement. A
standard is only necessary for products that want to be innovative in
meeting the 30V, 240VA. Killing all power is an option with existing listed
equipment. NEC 90.4 does not apply.

 

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Brian
Mehalic
Sent: Tuesday, January 21, 2014 2:36 PM
To: RE-wrenches
Cc: re-wrenches@lists.re-wrenches.org
<mailto:re-wrenches@lists.re-wrenches.org> 
Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

 

It was suggested to me that since 690.12(5) requires the equipment to be
listed and identified, and there is no standard for rapid shutdown equipment
to be listed to then 90.3 (.4?...oh why isn't the NEC on my iPad...)says
'revert to the previous version of the NEC' and presto, no need to install
rapid shutdown. I don't like this but the the person suggesting it certainly
has an audience and this will appeal to installers looking to save on cost
wherever possible. 

Sent from my iPad


On Jan 21, 2014, at 5:11 PM, David Brearley
mailto:david.brear...@solarprofessional.com> > wrote:

Drake,

 

The language in 690.12 is the compromise solution that was reached to ensure
continued industry stability. The alternative to the combiner-level shutdown
was module-level shutdown. It took a consolidated industry effort to push
the module-level requirements out one more Code cycle-for the exact reasons
that you touch on below. 

 

Not sure if this link has been published on the Wrenches list or not, but it
provides some background on the topic:

 

http://www.youtube.com/watch?v=sUXShMZJorQ

 

David Brearley

Senior Technical Editor, SolarPro magazine

NABCEP Certified PV Installation Professional

david.brear...@solarprofessional.com
<mailto:david.brear...@solarprofessional.com> 

Direct: 541.261.6545

 

 

 

 

On Jan 21, 2014, at 1:12 PM, re-wrenches-requ...@lists.re-wrenches.org
<mailto:re-wrenches-requ...@lists.re-wrenches.org>  wrote:






From: Drake mailto:drake.chamber...@redwoodalliance.org> >

Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

Date: January 21, 2014 11:36:15 AM CST

To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org> >

Reply-To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org> >




Bill,
 
It is good to see that energized conductors are going to be disconnected
near the arrays. I've been an advocate of disconnecting these conductors by
ground fault sensing equipment since ground fault detection was first
implemented in the code. If contactors are to be installed on roofs, it
likely won't be long before both ground faults and arc faults are
automatically cleared. 
 
When the requirement for AC arc fault branch circuit protection was first
put in the NEC, it was postdated to allow time for the electrical industry
to adapt. This new remote disconnecting requirement does not provide any
lead time.  
 
As the 2014 NEC is adopted in various jurisdictions, inspectors may feel
that it is necessary to disallow systems without the newly required
disconnect feature. This may result in serious problems for solar companies
and customers, as well as manufacturers. 
 
The protection of firefighters is essential. The implementation of
renewables is essential also. Insurance claims for weather related, global
warming-triggered climatic disasters are rising exponentially. Extreme
weather related events result in major loss of life and billions of dollars
in property damage. Atmospheric CO2 levels continue to climb from the
burning of fossil fuels. This is a crisis of global proportions. 
 
My request for code writers is to please take into account the effect that
inserting new rules into the NEC may have on the stability of renewable
energy, and implement new requirements in a way that will allow for a smooth
interface.
 
Thank you, 
 
Drake 

Drake Chamberlin
Athens El

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-21 Thread Mark Frye
OK. So I will have a high rate of acceptance if it buy an Tyco vacuum 
relay, and mount it in a Hoffman enclosure, and then put it on my roof?


On 1/21/2014 5:45 PM, Bill Brooks wrote:


Brian,

The requirement is generic. A listed contactor can meet the 
requirement. A standard is only necessary for products that want to be 
innovative in meeting the 30V, 240VA. Killing all power is an option 
with existing listed equipment. NEC 90.4 does not apply.


Bill.

*From:*re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*Brian Mehalic

*Sent:* Tuesday, January 21, 2014 2:36 PM
*To:* RE-wrenches
*Cc:* re-wrenches@lists.re-wrenches.org
*Subject:* Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

It was suggested to me that since 690.12(5) requires the equipment to 
be listed and identified, and there is no standard for rapid shutdown 
equipment to be listed to then 90.3 (.4?...oh why isn't the NEC on my 
iPad...)says 'revert to the previous version of the NEC' and presto, 
no need to install rapid shutdown. I don't like this but the the 
person suggesting it certainly has an audience and this will appeal to 
installers looking to save on cost wherever possible.


Sent from my iPad


On Jan 21, 2014, at 5:11 PM, David Brearley 
<mailto:david.brear...@solarprofessional.com>> wrote:


Drake,

The language in 690.12 is the compromise solution that was reached
to ensure continued industry stability. The alternative to the
combiner-level shutdown was module-level shutdown. It took a
consolidated industry effort to push the module-level requirements
out one more Code cycle---for the exact reasons that you touch on
below.

Not sure if this link has been published on the Wrenches list or
not, but it provides some background on the topic:

http://www.youtube.com/watch?v=sUXShMZJorQ

David Brearley

Senior Technical Editor,/SolarPro/magazine

NABCEP Certified PV Installation Professional

david.brear...@solarprofessional.com
<mailto:david.brear...@solarprofessional.com>

Direct: 541.261.6545

On Jan 21, 2014, at 1:12 PM,
re-wrenches-requ...@lists.re-wrenches.org
<mailto:re-wrenches-requ...@lists.re-wrenches.org> wrote:



*From:*Drake mailto:drake.chamber...@redwoodalliance.org>>

    *Subject:**Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown*

*Date:*January 21, 2014 11:36:15 AM CST

*To:*RE-wrenches mailto:re-wrenches@lists.re-wrenches.org>>

*Reply-To:*RE-wrenches mailto:re-wrenches@lists.re-wrenches.org>>




Bill,

It is good to see that energized conductors are going to be
disconnected near the arrays. I've been an advocate of
disconnecting these conductors by ground fault sensing
equipment since ground fault detection was first implemented
in the code. If contactors are to be installed on roofs, it
likely won't be long before both ground faults and arc faults
are automatically cleared.

When the requirement for AC arc fault branch circuit
protection was first put in the NEC, it was postdated to allow
time for the electrical industry to adapt. This new remote
disconnecting requirement does not provide any lead time.

As the 2014 NEC is adopted in various jurisdictions,
inspectors may feel that it is necessary to disallow systems
without the newly required disconnect feature. This may result
in serious problems for solar companies and customers, as well
as manufacturers.

The protection of firefighters is essential. The
implementation of renewables is essential also. Insurance
claims for weather related, global warming-triggered climatic
disasters are rising exponentially. Extreme weather related
events result in major loss of life and billions of dollars in
property damage. Atmospheric CO2 levels continue to climb from
the burning of fossil fuels. This is a crisis of global
proportions.

My request for code writers is to please take into account the
effect that inserting new rules into the NEC may have on the
stability of renewable energy, and implement new requirements
in a way that will allow for a smooth interface.

Thank you,

Drake

Drake Chamberlin
/Athens Electric LLC//
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
/http://athens-electric.com/

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenche

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-21 Thread Bill Brooks
Brian,



The requirement is generic. A listed contactor can meet the requirement. A 
standard is only necessary for products that want to be innovative in meeting 
the 30V, 240VA. Killing all power is an option with existing listed equipment. 
NEC 90.4 does not apply.



Bill.



From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Brian Mehalic
Sent: Tuesday, January 21, 2014 2:36 PM
To: RE-wrenches
Cc: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown



It was suggested to me that since 690.12(5) requires the equipment to be listed 
and identified, and there is no standard for rapid shutdown equipment to be 
listed to then 90.3 (.4?...oh why isn't the NEC on my iPad...)says 'revert to 
the previous version of the NEC' and presto, no need to install rapid shutdown. 
I don't like this but the the person suggesting it certainly has an audience 
and this will appeal to installers looking to save on cost wherever possible.

Sent from my iPad


On Jan 21, 2014, at 5:11 PM, David Brearley 
mailto:david.brear...@solarprofessional.com> > wrote:

Drake,



The language in 690.12 is the compromise solution that was reached to ensure 
continued industry stability. The alternative to the combiner-level shutdown 
was module-level shutdown. It took a consolidated industry effort to push the 
module-level requirements out one more Code cycle—for the exact reasons that 
you touch on below.



Not sure if this link has been published on the Wrenches list or not, but it 
provides some background on the topic:



http://www.youtube.com/watch?v=sUXShMZJorQ



David Brearley

Senior Technical Editor, SolarPro magazine

NABCEP Certified PV Installation Professional

david.brear...@solarprofessional.com 
<mailto:david.brear...@solarprofessional.com>

Direct: 541.261.6545









On Jan 21, 2014, at 1:12 PM, re-wrenches-requ...@lists.re-wrenches.org 
<mailto:re-wrenches-requ...@lists.re-wrenches.org>  wrote:





From: Drake mailto:drake.chamber...@redwoodalliance.org> >

Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

Date: January 21, 2014 11:36:15 AM CST

To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org> >

Reply-To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org> >




Bill,

It is good to see that energized conductors are going to be disconnected near 
the arrays. I've been an advocate of disconnecting these conductors by ground 
fault sensing equipment since ground fault detection was first implemented in 
the code. If contactors are to be installed on roofs, it likely won't be long 
before both ground faults and arc faults are automatically cleared.

When the requirement for AC arc fault branch circuit protection was first put 
in the NEC, it was postdated to allow time for the electrical industry to 
adapt. This new remote disconnecting requirement does not provide any lead time.

As the 2014 NEC is adopted in various jurisdictions, inspectors may feel that 
it is necessary to disallow systems without the newly required disconnect 
feature. This may result in serious problems for solar companies and customers, 
as well as manufacturers.

The protection of firefighters is essential. The implementation of renewables 
is essential also. Insurance claims for weather related, global 
warming-triggered climatic disasters are rising exponentially. Extreme weather 
related events result in major loss of life and billions of dollars in property 
damage. Atmospheric CO2 levels continue to climb from the burning of fossil 
fuels. This is a crisis of global proportions.

My request for code writers is to please take into account the effect that 
inserting new rules into the NEC may have on the stability of renewable energy, 
and implement new requirements in a way that will allow for a smooth interface.

Thank you,

Drake

Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
http://athens-electric.com/



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org>

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>



---
This email is free from viruses and malware because avast! Antivirus protection 
is active.
http://www.avast.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-21 Thread Ray Walters

Hi Brian;

Invoking 90.4 is a decent idea; the only problem is those smarty pants 
over at Midnite have been working on their Birdhouse disconnect system 
for several years already in anticipation of this requirement.  I'm not 
up on all of this (still waiting for my copy of the 2014 Handbook)  but 
I believe their birdhouse and combiner box system meets all the new 
requirements.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 1/21/2014 3:36 PM, Brian Mehalic wrote:
It was suggested to me that since 690.12(5) requires the equipment to 
be listed and identified, and there is no standard for rapid shutdown 
equipment to be listed to then 90.3 (.4?...oh why isn't the NEC on my 
iPad...)says 'revert to the previous version of the NEC' and presto, 
no need to install rapid shutdown. I don't like this but the the 
person suggesting it certainly has an audience and this will appeal to 
installers looking to save on cost wherever possible.


Sent from my iPad

On Jan 21, 2014, at 5:11 PM, David Brearley 
<mailto:david.brear...@solarprofessional.com>> wrote:



Drake,

The language in 690.12 is the compromise solution that was reached to 
ensure continued industry stability. The alternative to the 
combiner-level shutdown was module-level shutdown. It took a 
consolidated industry effort to push the module-level requirements 
out one more Code cycle---for the exact reasons that you touch on below.


Not sure if this link has been published on the Wrenches list or not, 
but it provides some background on the topic:


http://www.youtube.com/watch?v=sUXShMZJorQ

David Brearley
Senior Technical Editor,/SolarPro/magazine
NABCEP Certified PV Installation Professional
david.brear...@solarprofessional.com 
<mailto:david.brear...@solarprofessional.com>

Direct: 541.261.6545





On Jan 21, 2014, at 1:12 PM, 
re-wrenches-requ...@lists.re-wrenches.org 
<mailto:re-wrenches-requ...@lists.re-wrenches.org> wrote:


*From:*Drake <mailto:drake.chamber...@redwoodalliance.org>>

*Subject:**Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown*
*Date:*January 21, 2014 11:36:15 AM CST
*To:*RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>>
*Reply-To:*RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>>




Bill,

It is good to see that energized conductors are going to be 
disconnected near the arrays. I've been an advocate of disconnecting 
these conductors by ground fault sensing equipment since ground 
fault detection was first implemented in the code. If contactors are 
to be installed on roofs, it likely won't be long before both ground 
faults and arc faults are automatically cleared.


When the requirement for AC arc fault branch circuit protection was 
first put in the NEC, it was postdated to allow time for the 
electrical industry to adapt. This new remote disconnecting 
requirement does not provide any lead time.


As the 2014 NEC is adopted in various jurisdictions, inspectors may 
feel that it is necessary to disallow systems without the newly 
required disconnect feature. This may result in serious problems for 
solar companies and customers, as well as manufacturers.


The protection of firefighters is essential. The implementation of 
renewables is essential also. Insurance claims for weather related, 
global warming-triggered climatic disasters are rising 
exponentially. Extreme weather related events result in major loss 
of life and billions of dollars in property damage. Atmospheric CO2 
levels continue to climb from the burning of fossil fuels. This is a 
crisis of global proportions.


My request for code writers is to please take into account the 
effect that inserting new rules into the NEC may have on the 
stability of renewable energy, and implement new requirements in a 
way that will allow for a smooth interface.


Thank you,

Drake

Drake Chamberlin
/Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
/http://athens-electric.com/


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org>


Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:
www.re-wrenches.org/etiquette.htm 
<http://www.re-wrenches.org/etiquette.htm>


Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenche

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-21 Thread Brian Mehalic
It was suggested to me that since 690.12(5) requires the equipment to be listed 
and identified, and there is no standard for rapid shutdown equipment to be 
listed to then 90.3 (.4?...oh why isn't the NEC on my iPad...)says 'revert to 
the previous version of the NEC' and presto, no need to install rapid shutdown. 
I don't like this but the the person suggesting it certainly has an audience 
and this will appeal to installers looking to save on cost wherever possible. 

Sent from my iPad

> On Jan 21, 2014, at 5:11 PM, David Brearley 
>  wrote:
> 
> Drake,
> 
> The language in 690.12 is the compromise solution that was reached to ensure 
> continued industry stability. The alternative to the combiner-level shutdown 
> was module-level shutdown. It took a consolidated industry effort to push the 
> module-level requirements out one more Code cycle—for the exact reasons that 
> you touch on below. 
> 
> Not sure if this link has been published on the Wrenches list or not, but it 
> provides some background on the topic:
> 
> http://www.youtube.com/watch?v=sUXShMZJorQ
> 
> David Brearley
> Senior Technical Editor, SolarPro magazine
> NABCEP Certified PV Installation Professional
> david.brear...@solarprofessional.com
> Direct: 541.261.6545
> 
> 
> 
> 
> 
>> On Jan 21, 2014, at 1:12 PM, re-wrenches-requ...@lists.re-wrenches.org wrote:
>> 
>> From: Drake 
>> Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown
>> Date: January 21, 2014 11:36:15 AM CST
>> To: RE-wrenches 
>> Reply-To: RE-wrenches 
>> 
>> 
>> 
>> Bill,
>>  
>> It is good to see that energized conductors are going to be disconnected 
>> near the arrays. I've been an advocate of disconnecting these conductors by 
>> ground fault sensing equipment since ground fault detection was first 
>> implemented in the code. If contactors are to be installed on roofs, it 
>> likely won't be long before both ground faults and arc faults are 
>> automatically cleared. 
>>  
>> When the requirement for AC arc fault branch circuit protection was first 
>> put in the NEC, it was postdated to allow time for the electrical industry 
>> to adapt. This new remote disconnecting requirement does not provide any 
>> lead time.  
>>  
>> As the 2014 NEC is adopted in various jurisdictions, inspectors may feel 
>> that it is necessary to disallow systems without the newly required 
>> disconnect feature. This may result in serious problems for solar companies 
>> and customers, as well as manufacturers. 
>>  
>> The protection of firefighters is essential. The implementation of 
>> renewables is essential also. Insurance claims for weather related, global 
>> warming-triggered climatic disasters are rising exponentially. Extreme 
>> weather related events result in major loss of life and billions of dollars 
>> in property damage. Atmospheric CO2 levels continue to climb from the 
>> burning of fossil fuels. This is a crisis of global proportions. 
>>  
>> My request for code writers is to please take into account the effect that 
>> inserting new rules into the NEC may have on the stability of renewable 
>> energy, and implement new requirements in a way that will allow for a smooth 
>> interface.
>>  
>> Thank you, 
>>  
>> Drake 
>> 
>> Drake Chamberlin
>> Athens Electric LLC
>> OH License 44810
>> CO License 3773
>> NABCEP Certified Solar PV 
>> 740-448-7328
>> http://athens-electric.com/
> 
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-21 Thread Drake
at committee.


It is more complicated for battery backup 
systems. Midnite Solar’s birdhouse products are 
the best I have seen so far to address this 
concern. Since dc and ac circuits are not 
differentiated, battery backup systems need to 
have a shutdown process that works independently 
of a utility outage for obvious reasons, and it 
must shutdown both the dc circuits and the 
backup ac circuits. A separate switch, like the 
birdhouse, would be necessary that only controls 
these functions in an emergency situation.


Is the language not detailed­possibly. This was 
done to provide flexibility rather than create 
problems. Fire departments have been requiring 
rooftop disconnects for years in California. 
These disconnects are nearly worthless from a 
shock prevention point of view since capacitors 
in the inverter stay charged or there are 
multiple disconnecting means feeding each other. 
We have been trying to hold the fire community 
off of rooftop disconnect requirements so we 
could work on a solution that actually does what 
they want it to do. There is a long discussion 
on this in the appendix of my “Understanding the 
CalFire Guidelines” document on the SolarABCs website.


The 2014 NEC language was a compromise worked 
out with the solar industry (yes string inverter 
companies as well) in response to the first 
version of the proposal which was to require 
module-level shutdown. This is not module-level 
shutdown, it is PV output circuit shutdown 
(combiner box shutdown is another way to look at 
it). However, the 2017 NEC cycle is this year 
and there was a lot of talk about requiring 
module-level shutdown this time around.


I hope this helps. I will be writing articles 
for IAEI journal and other periodicals on this 
subject since it was a very far-reaching and 
potentially confusing new requirement in the 
NEC. Thanks for your interest and let’s keep the 
constructive dialogue going on the subject. It 
is time to get involved in the NEC update process again.


Bill Brooks.

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] 
On Behalf Of Jeffrey Quackenbush

Sent: Thursday, January 16, 2014 1:09 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

Wrenches,

There is no guidance in the Code text for where 
the shutdown should take place. (1) says: 
"Requirements for controlled conductors shall 
apply only to PV system conductors of more than 
1.5m (5') in length inside a building, or more than 3m (10') from a PV array."



So, the provisions apply if the circuit 10' from 
the array and 5' inside a building, but no 
mention is made of where the shutdown actually 
needs take place in the circuit. In the video 
Bill Brooks suggests that the shutdown mechanism 
should also be placed within this 10'/5' 
boundary but that is just an inference -- 
nowhere in the text is this actually specified. 
If that was the intent of the Code committee, 
then they've done a poor job actually expressing it in English.


I'm concerned that some AHJs will interpret this 
to exclude all central inverter systems (without 
the addition of cost-inducing secondary DC-DC 
converters like Tigo) because the combiner or 
junction box can be many feet from the actual 
beginning of a home run under the array. 
Alternately, permissive AHJs could allow this 
function to be fulfilled anywhere, meaning that 
the implementation won't meet the intent of the writers.


I'm also concerned, as Isaac mentioned, that 
there are no requirements for how the shutdown 
be initiated, or that it contains of the 
accessibility and grouping requirements that are 
always included for disconnects. I really think 
this should be treated and categorized as a 
disconnect requirement, not a circuit 
requirement, because that is the ultimate function that's intended.


I'm surprised none of the inverter manufacturers 
have chosen to comment here, as this could 
dramatically impact the sales of central inverters.


Jeffrey Quackenbush




--
<http://www.avast.com/>
[]
<http://www.avast.com/>

This email is free from viruses and malware 
because <http://www.avast.com/>avast! Antivirus protection is active.


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-16 Thread Bill Brooks
involved in the NEC update process again.

 

Bill Brooks.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeffrey
Quackenbush
Sent: Thursday, January 16, 2014 1:09 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

 

Wrenches,

 

There is no guidance in the Code text for where the shutdown should take
place. (1) says: "Requirements for controlled conductors shall apply only to
PV system conductors of more than 1.5m (5') in length inside a building, or
more than 3m (10') from a PV array."





So, the provisions apply if the circuit 10' from the array and 5' inside a
building, but no mention is made of where the shutdown actually needs take
place in the circuit. In the video Bill Brooks suggests that the shutdown
mechanism should also be placed within this 10'/5' boundary but that is just
an inference -- nowhere in the text is this actually specified. If that was
the intent of the Code committee, then they've done a poor job actually
expressing it in English.

 

I'm concerned that some AHJs will interpret this to exclude all central
inverter systems (without the addition of cost-inducing secondary DC-DC
converters like Tigo) because the combiner or junction box can be many feet
from the actual beginning of a home run under the array. Alternately,
permissive AHJs could allow this function to be fulfilled anywhere, meaning
that the implementation won't meet the intent of the writers.

 

I'm also concerned, as Isaac mentioned, that there are no requirements for
how the shutdown be initiated, or that it contains of the accessibility and
grouping requirements that are always included for disconnects. I really
think this should be treated and categorized as a disconnect requirement,
not a circuit requirement, because that is the ultimate function that's
intended. 

 

I'm surprised none of the inverter manufacturers have chosen to comment
here, as this could dramatically impact the sales of central inverters.

 

Jeffrey Quackenbush

 



---
This email is free from viruses and malware because avast! Antivirus protection 
is active.
http://www.avast.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-16 Thread Jeffrey Quackenbush
Wrenches,

There is no guidance in the Code text for where the shutdown should take place. 
(1) says: "Requirements for controlled conductors shall apply only to PV system 
conductors of more than 1.5m (5') in length inside a building, or more than 3m 
(10') from a PV array."

So, the provisions apply if the circuit 10' from the array and 5' inside a 
building, but no mention is made of where the shutdown actually needs take 
place in the circuit. In the video Bill Brooks suggests that the shutdown 
mechanism should also be placed within this 10'/5' boundary but that is just an 
inference -- nowhere in the text is this actually specified. If that was the 
intent of the Code committee, then they've done a poor job actually expressing 
it in English.

I'm concerned that some AHJs will interpret this to exclude all central 
inverter systems (without the addition of cost-inducing secondary DC-DC 
converters like Tigo) because the combiner or junction box can be many feet 
from the actual beginning of a home run under the array. Alternately, 
permissive AHJs could allow this function to be fulfilled anywhere, meaning 
that the implementation won't meet the intent of the writers.

I'm also concerned, as Isaac mentioned, that there are no requirements for how 
the shutdown be initiated, or that it contains of the accessibility and 
grouping requirements that are always included for disconnects. I really think 
this should be treated and categorized as a disconnect requirement, not a 
circuit requirement, because that is the ultimate function that's intended. 

I'm surprised none of the inverter manufacturers have chosen to comment here, 
as this could dramatically impact the sales of central inverters.


Jeffrey Quackenbush___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-15 Thread Mark Frye
The un-controlled conductor could be up to 15 feet, 10 on the roof and 5 
in the building?


Mark Frye
Berkeley Solar Electric Systems

On 1/15/2014 2:02 PM, Daniel Young wrote:


Here is a link for a video where Mike Holt helps with an explanation 
to your question.


https://www.youtube.com/watch?v=sUXShMZJorQ

Essentially, the rapid shutdown needs to keep the energized length of 
conductors to within 10' of the array if on the roof (this rule is 
only for arrays on buildings) or within 5' of building penetration. I 
would assume that if you are 9' on the roof, you then only have 1' in 
the building before you need the shutdown device.


So micro inverters and some DC-DC optimizers should comply with the 
standard as is (since they prevent wires from being energized with _DC 
voltage_ before they even leave the array). But string inverter 
systems will need to get creative with how they address this. Midnite 
solar disco combiners with the birdhouse seem to be a possible 
solution, but they add a lot of cost to some smaller systems that 
didn't even need combiners before, let alone disconnect combiners with 
power supply cards and separate control boxes...


Hopefully a better solution for small string inverters is on the horizon.

With Regards,

Daniel Young,

NABCEP Certified PV Installation Professional^TM : Cert #031508-90

NABCEP Certified Solar Heating Installer^TM : Cert #SH031409-13

*From:*re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*Jeffrey Quackenbush

*Sent:* Tuesday, January 07, 2014 10:46 AM
*To:* 'RE-wrenches'
*Subject:* [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

I've been going through the new Code book (which is in effect now in 
Massachusetts) and found myself somewhat puzzled by the intent of the 
new "rapid shutdown" requirement in 690.12. Does anyone have insight 
into how this is supposed to be interpreted and implemented? I've put 
together a list of my own questions, given below (the numbers 
reference the new 690.12 text). Thanks!


*690.12 Rapid Shutdown*

1. Where should the rapid shutdown switch be located? (1) only says 
that the shutdown function should be installed if the circuit is 
longer than 10' or goes more than 5' into a building. If this 
condition is fulfilled, it says nothing about where the switch should 
be located. (2) says that controlled conductors should be limited to 
30V, 240W, which will only be the case downline from the switch, so 
this may mean that it should be located close to the source, i.e. on 
the roof. But this is just an inference, and one that doesn't have 
clear boundaries; every source conductor for a series connected PV 
circuit (that is not Solar Edge, Enphase , etc.) will have a higher 
voltage and wattage potential when the sun is shining /somewhere/ 
along its length, even if the disconnect is located very close to the 
array. Or does this requirement mean that all systems will need to 
have some kind of "smart" junction box, module DC-DC converter or 
module level AC inverter? Furthermore, individual modules often have 
higher voltages & wattages these days and there is no way to impose 
limits on their electrical characteristics in any field wired 
configurations. A listed AC module that sees the module leads as 
internal would be the only scenario that would be exempt.


2. (5) asks that equipment performing the shutdown should be listed 
and identified. Does that mean listed and identified for the purpose 
of this specific requirement? Or just listed and identified to limit 
voltage and wattage in 10 seconds? Does a specific UL standard exist 
for the function they have in mind? Does any equipment exist that has 
such listing and identification yet?


3. Is the rapid shutdown intended to be automatic or manual? If 
automatic, what are the parameters that would trigger the shutdown? If 
manual, are there any accessibility requirements?


4. Rapid shutdown seems more like a disconnect requirement than a 
circuit requirement. Why limit circuits to 30V, 240W, instead of just 
requiring a shutdown? Why 10 seconds, when all the disconnecting 
functions (i.e. manual disconnects, and internal AFCI, GFCI & UL 1740 
disconnects) happen in less than a second? (It hardly seems like a 
"rapid" shutdown). Why write this article into section II rather than 
section III?




No virus found in this message.
Checked by AVG - www.avg.com 
Version: 2012.0.2247 / Virus Database: 3658/6483 - Release Date: 01/07/14



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check ou

Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-15 Thread Isaac Opalinsky
Does Midnite’s Birdhouse or any combiner solutions meet the requirement to 
achieve 30V, 240 kVA within 10 seconds?  I’ve never seen a string inverter’s DC 
input terminals drop that quickly, and I’m especially curious to know how the 
string inverter manufacturers are going to cope with this, or if Midnite has 
anything to help deenergize the capacitors.

Interesting to note that 690.12 doesn’t state where the rapid shutdown should 
be initiated from, or how many steps could be required.  Could we use one 
disconnect to disconnect the conductors from the capacitors (i.e., at the 
inverter) and another to disconnect the conductors from the array (i.e., at the 
array)?  Doesn’t seem very “rapid”, but 690.12 isn’t very specific.

Isaac Opalinsky
SunPower Corporation
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-15 Thread Daniel Young
Here is a link for a video where Mike Holt helps with an explanation to your 
question.

 

https://www.youtube.com/watch?v=sUXShMZJorQ

 

Essentially, the rapid shutdown needs to keep the energized length of 
conductors to within 10’ of the array if on the roof (this rule is only for 
arrays on buildings) or within 5’ of building penetration. I would assume that 
if you are 9’ on the roof, you then only have 1’ in the building before you 
need the shutdown device.

 

So micro inverters and some DC-DC optimizers should comply with the standard as 
is (since they prevent wires from being energized with DC voltage before they 
even leave the array). But string inverter systems will need to get creative 
with how they address this. Midnite solar disco combiners with the birdhouse 
seem to be a possible solution, but they add a lot of cost to some smaller 
systems that didn’t even need combiners before, let alone disconnect combiners 
with power supply cards and separate control boxes...

 

Hopefully a better solution for small string inverters is on the horizon. 

 

With Regards,

Daniel Young, 

NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90

NABCEP Certified Solar Heating InstallerTM: Cert #SH031409-13

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeffrey 
Quackenbush
Sent: Tuesday, January 07, 2014 10:46 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

 

I've been going through the new Code book (which is in effect now in 
Massachusetts) and found myself somewhat puzzled by the intent of the new 
"rapid shutdown" requirement in 690.12. Does anyone have insight into how this 
is supposed to be interpreted and implemented? I've put together a list of my 
own questions, given below (the numbers reference the new 690.12 text). Thanks!

 

690.12 Rapid Shutdown

1.  Where should the rapid shutdown switch be located? (1) only says that the 
shutdown function should be installed if the circuit is longer than 10’ or goes 
more than 5’ into a building. If this condition is fulfilled, it says nothing 
about where the switch should be located. (2) says that controlled conductors 
should be limited to 30V, 240W, which will only be the case downline from the 
switch, so this may mean that  it should be located close to the source, i.e. 
on the roof. But this is just an inference, and one that doesn’t have clear 
boundaries; every source conductor for a series connected PV circuit (that is 
not Solar Edge, Enphase , etc.) will have a higher voltage and wattage 
potential when the sun is shining somewhere along its length, even if the 
disconnect is located very close to the array. Or does this requirement mean 
that all systems will need to have some kind of “smart” junction box, module 
DC-DC converter or module level AC inverter? Furthermore, individual modules 
often have higher voltages & wattages these days and there is no way to impose 
limits on their electrical characteristics in any field wired configurations. A 
listed AC module that sees the module leads as internal would be the only 
scenario that would be exempt.

 

2. (5) asks that equipment performing the shutdown should be listed and 
identified. Does that mean listed and identified for the purpose of this 
specific requirement? Or just listed and identified to limit voltage and 
wattage in 10 seconds? Does a specific UL standard exist for the function they 
have in mind? Does any equipment exist that has such listing and identification 
yet?

 

3. Is the rapid shutdown intended to be automatic or manual? If automatic, what 
are the parameters that would trigger the shutdown? If manual, are there any 
accessibility requirements?

 

4. Rapid shutdown seems more like a disconnect requirement than a circuit 
requirement. Why limit circuits to 30V, 240W, instead of just requiring a 
shutdown? Why 10 seconds, when all the disconnecting functions (i.e. manual 
disconnects, and internal AFCI, GFCI & UL 1740 disconnects) happen in less than 
a second? (It hardly seems like a “rapid” shutdown). Why write this article 
into section II rather than section III?

 

  _  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2247 / Virus Database: 3658/6483 - Release Date: 01/07/14

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org