Re: [Repeater-Builder] Re: Does anyone else think of Power Factor like SWR?

2008-09-22 Thread Jeff Condit
The power factor case is semantically different than the SWR case in the 
following way: With SWR, energy is flowing in both directions at near the speed 
of light.  If the reflected signal is the exact same frequency as the forward 
signal (as in the case where it is a reflection of a signal at a particular 
frequency, then there will be points along the line where the forward and 
reflects will be in phase and point along the line where they will be out of 
phase.  SWR is a ratio of the max voltage to the min voltage.  If there is no 
reflection, there is nothing to add or subtract, and so the max and min voltage 
will be the same.  The ratio (SWR) is therefore 1:1.  If all energy is 
reflected, the minimum will be zero, so that ratio of the max to the min will 
be infinite.

Now if I simultaneously measure a power line at 10 different point in a mile, I 
would detect no significant difference in power factor between the points.  
This is because the voltage anywhere on the wire is the same (san some IR 
drop), and the current into one end in the same as the current flowing out the 
other end.  Therefore, the angle between the voltage and current waveforms wil 
be the same all aong the run.

...Well, not exactly:

60 Hz has a period of 16.7ms.  On quarter wavelength is roughly where 
transmission line effects become significant.  One quarter of a period is at 
60Hz is 4.17ms.  If c=2.98x10^8 meters per second, it would travel 1241.7km in 
a quarter cycle.  (Actually, it is slightly less due to the relative delectric 
constant of air being slightly higher than that of a vacuum.)  If the distance 
between the source and the load is significantly less than this, no significant 
steady-state effects will be observable.  (Transient effects such as spikes 
could be seen if a power line broke in a windstorm.)

If I were to measure our power line at points much further apart (say thoudands 
of miles) we could indeed measure a difference because what happens is 
sufficiently delayed with respect the other points.  Thus the adjective 
semantically.  When we talk about power factor the tacit assumption is that 
the same voltage exists at all locatons of the wires and that the current in 
equals the current out (i.e. that we are talking about distances much much 
smaller than a quarter wavelength).  When we talk about SWR (or more correctly 
VSWR) we tacitly assume we are talking about transmission lines of the order of 
or longer than a quarter wavelength.

Jeff Condit


[Repeater-Builder] Re: Does anyone else think of Power Factor like SWR?

2008-09-20 Thread Nigel Johnson
Very interesting theory.  I am teaching SWR at present to my third
year college students.  Could be a good discussion point since they
have already studied power factor.  However, SWR can exist with a
purely resistive mismatched load, so it needs a bit of modification to
take all into account.

73
Nigel
ve3id



--- In Repeater-Builder@yahoogroups.com, Bob Witte K0NR [EMAIL PROTECTED]
wrote:

 --- In Repeater-Builder@yahoogroups.com, kb9bpf kb9bpf@ wrote:
 
  Since I'm way more into RF than industrial power distribution, I've 
  always been able to think of power factor on the electrical power 
  grid in terms similar to antenna system reflections, which are 
  commonly measured in terms of SWR. After all, both are AC systems 
  where the voltage and current bear a phase relationship to each 
  other. 
  
  When they are perfectly in phase the power factor is 1.0, and a 60-Hz 
  SWR meter would measure 1:1. When they are out of phase (power factor 
  1) that SWR meter would read greater than 1:1. I suspect, though I 
  haven't done the math or looked up the specific matahematical 
  definition of power factor, that it would be direcly proportional to 
  the reciprocal of the power factor. And as we know, when that happens 
  the power generating end has more difficulty delivering power 
  efficiently to the load.
  
 
 A while back I was doing some analysis of power factor to understand
 it better and I found that it has a lot in common with SWR. Both are
 focused on the issue of power transfer, so I guess we shouldn't be
 surprised. The thing they really have in common is for max power with
 AC signals, the voltage and current need to be in phase (phase angle
 of zero). 
 
 For linear systems with nice sine waves, PF = cos (phase angle)
   where phase angle = the angle between voltage and current sinusoids
 
 Wikipedia has a good explanation of PF at 
 http://en.wikipedia.org/wiki/Power_factor
 
 Play around with some typical circuits and you'll find that an SWR of
 1 also has voltage and current in phase. Again, not a surprise since
 it represents the best power transfer.
 
 This is from memory, so the usual disclaimers apply :-)
 
  73, Bob K0NR





[Repeater-Builder] Re: Does anyone else think of Power Factor like SWR?

2008-09-20 Thread w5zit
Good point Nigel.  Back in the '60s I designed a video distribution
amplifier for receiver video to tape recorders, O scopes and the like
and I matched the input impedance to prevent reflections on the video
line from distorting the signal.  The output impedance of my amplifier
was as low as I could get it, and it worked very well.

I did not design the output impedance to be 50 ohms, the impedance of
the cable we used to distribute the video.  I depended on the load to
be 50 ohms resistive to prevent any reflection.

On the other hand, the audio distribution amplifiers were not matched
on the receive end.  I also designed the output impedance of an audio
amplifier to be as low as I could get it, and was able to switch
multiple loads on the output without changing the level.  The input
impedance of the audio circuits was always 600 ohms or higher.

The power distribution grid is more like the audio and video situation
than the SWR problems we see at RF.

73 - Jim  W5ZIT

--- In Repeater-Builder@yahoogroups.com, Nigel Johnson [EMAIL PROTECTED]
wrote:

 Very interesting theory.  I am teaching SWR at present to my third
 year college students.  Could be a good discussion point since they
 have already studied power factor.  However, SWR can exist with a
 purely resistive mismatched load, so it needs a bit of modification to
 take all into account.
 
 73
 Nigel
 ve3id
 




RE: [Repeater-Builder] Re: Does anyone else think of Power Factor like SWR?

2008-09-20 Thread Gary Schafer
Yes standing waves can exist with a pure resistive load on a line but the
mismatch of the load with the line impedance creates a reactance (depending
on line length).

A transmission line must be long enough (wavelength wise) for standing waves
to exist.

A short line (wavelength wise) like an audio cable, will not exhibit
standing waves because it is too short for them to exist.

Even a short (wavelength wise) RF cable will not exhibit standing waves.
Keep in mind that the typical SWR and power meters that we use to measure
SWR with are NOT really measuring SWR. They are measuring impedance mismatch
of the internal impedance that the meter is set for, with a scale on the
meter that converts the impedance ratio to a would be SWR. 
A very long power transmission line can have standing waves on it if the
power factor problems are not kept in check.

So power factor could be thought of like SWR but only on long distribution
lines. Keep in mind that short transmission lines whether it be power, audio
or RF do not have standing waves on them when they are very short wavelength
wise.

73
Gary K4FMX 



 -Original Message-
 From: Repeater-Builder@yahoogroups.com [mailto:Repeater-
 [EMAIL PROTECTED] On Behalf Of Nigel Johnson
 Sent: Saturday, September 20, 2008 7:26 AM
 To: Repeater-Builder@yahoogroups.com
 Subject: [Repeater-Builder] Re: Does anyone else think of Power Factor
 like SWR?
 
 Very interesting theory.  I am teaching SWR at present to my third
 year college students.  Could be a good discussion point since they
 have already studied power factor.  However, SWR can exist with a
 purely resistive mismatched load, so it needs a bit of modification to
 take all into account.
 
 73
 Nigel
 ve3id
 
 
 
 --- In Repeater-Builder@yahoogroups.com, Bob Witte K0NR [EMAIL PROTECTED]
 wrote:
 
  --- In Repeater-Builder@yahoogroups.com, kb9bpf kb9bpf@ wrote:
  
   Since I'm way more into RF than industrial power distribution, I've
   always been able to think of power factor on the electrical power
   grid in terms similar to antenna system reflections, which are
   commonly measured in terms of SWR. After all, both are AC systems
   where the voltage and current bear a phase relationship to each
   other.
  
   When they are perfectly in phase the power factor is 1.0, and a 60-Hz
   SWR meter would measure 1:1. When they are out of phase (power factor
   1) that SWR meter would read greater than 1:1. I suspect, though I
   haven't done the math or looked up the specific matahematical
   definition of power factor, that it would be direcly proportional to
   the reciprocal of the power factor. And as we know, when that happens
   the power generating end has more difficulty delivering power
   efficiently to the load.
  
 
  A while back I was doing some analysis of power factor to understand
  it better and I found that it has a lot in common with SWR. Both are
  focused on the issue of power transfer, so I guess we shouldn't be
  surprised. The thing they really have in common is for max power with
  AC signals, the voltage and current need to be in phase (phase angle
  of zero).
 
  For linear systems with nice sine waves, PF = cos (phase angle)
where phase angle = the angle between voltage and current sinusoids
 
  Wikipedia has a good explanation of PF at
  http://en.wikipedia.org/wiki/Power_factor
 
  Play around with some typical circuits and you'll find that an SWR of
  1 also has voltage and current in phase. Again, not a surprise since
  it represents the best power transfer.
 
  This is from memory, so the usual disclaimers apply :-)
 
   73, Bob K0NR
 
 
 
 
 
 
 
 
 Yahoo! Groups Links
 
 
 




[Repeater-Builder] Re: Does anyone else think of Power Factor like SWR?

2008-09-19 Thread Bob Witte K0NR
--- In Repeater-Builder@yahoogroups.com, kb9bpf [EMAIL PROTECTED] wrote:

 Since I'm way more into RF than industrial power distribution, I've 
 always been able to think of power factor on the electrical power 
 grid in terms similar to antenna system reflections, which are 
 commonly measured in terms of SWR. After all, both are AC systems 
 where the voltage and current bear a phase relationship to each 
 other. 
 
 When they are perfectly in phase the power factor is 1.0, and a 60-Hz 
 SWR meter would measure 1:1. When they are out of phase (power factor 
 1) that SWR meter would read greater than 1:1. I suspect, though I 
 haven't done the math or looked up the specific matahematical 
 definition of power factor, that it would be direcly proportional to 
 the reciprocal of the power factor. And as we know, when that happens 
 the power generating end has more difficulty delivering power 
 efficiently to the load.
 

A while back I was doing some analysis of power factor to understand
it better and I found that it has a lot in common with SWR. Both are
focused on the issue of power transfer, so I guess we shouldn't be
surprised. The thing they really have in common is for max power with
AC signals, the voltage and current need to be in phase (phase angle
of zero). 

For linear systems with nice sine waves, PF = cos (phase angle)
  where phase angle = the angle between voltage and current sinusoids

Wikipedia has a good explanation of PF at 
http://en.wikipedia.org/wiki/Power_factor

Play around with some typical circuits and you'll find that an SWR of
1 also has voltage and current in phase. Again, not a surprise since
it represents the best power transfer.

This is from memory, so the usual disclaimers apply :-)

 73, Bob K0NR




[Repeater-Builder] Re: Does anyone else think of Power Factor like SWR?

2008-09-18 Thread skipp025
Normally all this is taken into the design and operation 
of the distribution grid. 

It's quite possible to have generation plants simply coast 
portions or all of their equipment on the grid as correction 
factor in hydro operation sometimes known as motoring 
the prime mover. 

In the very much smoke and mirrors grid operation I've seen 
here in Northern California... we would receive out of area 
energy purchased at a much reduced cost and pay the local 
plant a minimal amount to simply motor the line and correct 
the area PF. 

Although less common these days there are/were also a fair 
number of dyna-motor facilities set upon the grid to address 
distribution line problems. Most of the required functions 
are now address by fixed electronics (power correction 
capacitors and in some cases inductors). 

Transformers are normally thought of as RF Shunts and along 
the distribution path (grid) you have a fair number of 
low RF Impedance devices paralleled. 

Whale tale stories... 
KW hour cost for very old Hydro Plants was fixed for decades at 
about 2.5 mils of a cent. Last 1995 era cost of Nuclear energy 
from Diablo Canyon was informally quoted at 11 cents kwh. So 
of course in the Enron Days they'd motor over a hundred mega-watts 
of low cost local (clean) Sierra California hydro plants (price 
set under an old 1957 contract) so PGE could cost justify the
cash-cow Nuclear Plant at the higher cost. 

go figure... 

cheers, 
s. 

 There was a case I think in Canada where they ran into 
 this problem.  The transmission lines from one side of 
 the continent to the other was an odd multiple of a 
 quarterwave (1,250 km).  

 Since a quarter-wave acts as a impedance transformer, when 
 they put a low impedance load at the far end, the cable 
 transformed this to a high impedance at the generator end 
 and they couldn't get power into it.

 The solution?  Either fit impedance correction devices 
 along the cable, or transmit DC power and convert it back 
 to AC at the load end (they do that with a power cable 
 running between the mainland of Australia and the island
 of Tasmania).




Re: [Repeater-Builder] Re: Does anyone else think of Power Factor like SWR?

2008-09-18 Thread Gary Glaenzer
also known as 'rotary condenser' operation

Gary



- Original Message - 
From: skipp025 
To: Repeater-Builder@yahoogroups.com 
Sent: Thursday, September 18, 2008 11:24 AM
Subject: [Repeater-Builder] Re: Does anyone else think of Power Factor like SWR?


Normally all this is taken into the design and operation 
of the distribution grid. 

It's quite possible to have generation plants simply coast 
portions or all of their equipment on the grid as correction 
factor in hydro operation sometimes known as motoring 
the prime mover. 



[Repeater-Builder] Re: Does anyone else think of Power Factor like SWR?

2008-09-17 Thread Laryn Lohman
To answer the question, I don't.

Look at it this way.  The AC supply to your house, for example, is a
low impedance; it can supply hundreds of amps (the transmitter).  The
100 watt lamp (antenna/load) in your house is a relatively high
impedance compared to the supply.  There is no impedance match between
supply and load, not even close.  SWR is very high.  Do we care?  No,
we're not trying to transfer the maximum amount of power here as we do
in an antenna system, only the amount of power required by the lamp.  

Hope that helps.

Laryn K8TVZ