FIRE PUMP: Urgent

2010-04-12 Thread sam b
Dear all..

We are in the process of installing *temporary fire protection* for a 30
story builing.
The pump installed is a *single diesel engine pump* (Not listed) for the
supplying water for the landing valves in each floor.The fire pump is
located in the basement floor and is barricaded .

The operation of the fire pump will be such that In case of pressure drop
due to opening of the hosereeel or landing valves the pump will start.
Now during the inspection from Client,they asked us why there is no
automatic shutoff .
*The scenario they are considering is *.
Suppose some labour accidentally opens the hosreel for anypurpose,the pump
will start running and if there is noone to stop the pump ,will it get
damaged.?
I suggested we could provide a fire alarm bell for alerting the people.
*Can we provide automatic shuttoff for the diesel pump. Is it acceptable as
per NFPA?*
Is there anyother options available or anything from NFPA to support that we
dont need automatic shutoff?

Please give your valuable inputs.

Sam
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: FIRE PUMP: Urgent

2010-04-12 Thread Bob Caputo
Since your pump is not listed, you don't comply with NFPA 20 so why does it
matter if the standard allows an automatic shut off?   For your use, the
2010 edition of NFPA states the following:

 

12.7.2.6 Sole Supply Pumps.

12.7.2.6.1 Shutdown shall be accomplished by manual or automatic means.

12.7.2.6.2 Automatic shutdown shall not be permitted where the pump
constitutes the sole source of supply of a fire sprinkler or standpipe
system or where the authority having jurisdiction

has required manual shutdown.

 

Regardless of the pump listing or other compliance issues, the answer lies
solely with the permission of the local AHJ.

Important Notice: As a member of the NFPA 13 Installation  NFPA 25
Committee's, this correspondence is not a Formal Interpretation issued
pursuant to NFPA Regulations. Any opinion expressed is the personal opinion
of the author, and does not necessarily represent the official position of
the NFPA or its Technical Committees. In addition, this correspondence is
neither intended, nor should be relied upon, to provide consultation or
services.

Bob Caputo

 

 

 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of sam b
Sent: Sunday, April 11, 2010 11:15 PM
To: sprinklerforum@firesprinkler.org
Subject: FIRE PUMP: Urgent

 

Dear all..

 

We are in the process of installing *temporary fire protection* for a 30

story builing.

The pump installed is a *single diesel engine pump* (Not listed) for the

supplying water for the landing valves in each floor.The fire pump is

located in the basement floor and is barricaded .

 

The operation of the fire pump will be such that In case of pressure drop

due to opening of the hosereeel or landing valves the pump will start.

Now during the inspection from Client,they asked us why there is no

automatic shutoff .

*The scenario they are considering is *.

Suppose some labour accidentally opens the hosreel for anypurpose,the pump

will start running and if there is noone to stop the pump ,will it get

damaged.?

I suggested we could provide a fire alarm bell for alerting the people.

*Can we provide automatic shuttoff for the diesel pump. Is it acceptable as

per NFPA?*

Is there anyother options available or anything from NFPA to support that we

dont need automatic shutoff?

 

Please give your valuable inputs.

 

Sam

___

Sprinklerforum mailing list

Sprinklerforum@firesprinkler.org

http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 

For Technical Assistance, send an email to: supp...@firesprinkler.org

 

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org

(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: FIRE PUMP: Urgent

2010-04-12 Thread sam b
Thaanx bob

I just went through the same now.

But If am not providing an automatic shutoff facility,how can I avoid  any
damage to the pump in case of mentioned scenario
From the pump supplier I cant expect anything .so from our side what we can
do to make it more safe.?

any thoughts?


Regards

Sam



On Mon, Apr 12, 2010 at 10:44 AM, Bob Caputo bcap...@cox.net wrote:

 Since your pump is not listed, you don't comply with NFPA 20 so why does it
 matter if the standard allows an automatic shut off?   For your use, the
 2010 edition of NFPA states the following:



 12.7.2.6 Sole Supply Pumps.

 12.7.2.6.1 Shutdown shall be accomplished by manual or automatic means.

 12.7.2.6.2 Automatic shutdown shall not be permitted where the pump
 constitutes the sole source of supply of a fire sprinkler or standpipe
 system or where the authority having jurisdiction

 has required manual shutdown.



 Regardless of the pump listing or other compliance issues, the answer lies
 solely with the permission of the local AHJ.

 Important Notice: As a member of the NFPA 13 Installation  NFPA 25
 Committee's, this correspondence is not a Formal Interpretation issued
 pursuant to NFPA Regulations. Any opinion expressed is the personal opinion
 of the author, and does not necessarily represent the official position of
 the NFPA or its Technical Committees. In addition, this correspondence is
 neither intended, nor should be relied upon, to provide consultation or
 services.

 Bob Caputo







 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of sam b
 Sent: Sunday, April 11, 2010 11:15 PM
 To: sprinklerforum@firesprinkler.org
 Subject: FIRE PUMP: Urgent



 Dear all..



 We are in the process of installing *temporary fire protection* for a 30

 story builing.

 The pump installed is a *single diesel engine pump* (Not listed) for the

 supplying water for the landing valves in each floor.The fire pump is

 located in the basement floor and is barricaded .



 The operation of the fire pump will be such that In case of pressure drop

 due to opening of the hosereeel or landing valves the pump will start.

 Now during the inspection from Client,they asked us why there is no

 automatic shutoff .

 *The scenario they are considering is *.

 Suppose some labour accidentally opens the hosreel for anypurpose,the pump

 will start running and if there is noone to stop the pump ,will it get

 damaged.?

 I suggested we could provide a fire alarm bell for alerting the people.

 *Can we provide automatic shuttoff for the diesel pump. Is it acceptable as

 per NFPA?*

 Is there anyother options available or anything from NFPA to support that
 we

 dont need automatic shutoff?



 Please give your valuable inputs.



 Sam

 ___

 Sprinklerforum mailing list

 Sprinklerforum@firesprinkler.org

 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



 For Technical Assistance, send an email to: supp...@firesprinkler.org



 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.orgto%3asprinklerforum-requ...@firesprinkler.org

 (Put the word unsubscribe in the subject field)

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.orgto%3asprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: FIRE PUMP: Urgent

2010-04-12 Thread Bob Caputo
While pumps are intended to start automatically (on a pressure drop) it is
intended that upon receipt of alarm indicating the pump is running, a
qualified person will be dispatched to the pump room to monitor conditions
and provide shut down after 30 minutes if the pump isn't actually needed.
This is especially true of electric motor drive pumps because it's not good
for the motor to start and stop without allowing it to run at least 10
minutes.  

Even your temporary water supply pump should have a running alarm to some
central station, job shack or similar but again, non-listed pumps are not
the subject of NFPA 20 so do whatever your local AHJ requires

insert stand disclaimer here

bc


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of sam b
Sent: Monday, April 12, 2010 12:36 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: FIRE PUMP: Urgent

Thaanx bob

I just went through the same now.

But If am not providing an automatic shutoff facility,how can I avoid  any
damage to the pump in case of mentioned scenario
From the pump supplier I cant expect anything .so from our side what we can
do to make it more safe.?

any thoughts?


Regards

Sam



On Mon, Apr 12, 2010 at 10:44 AM, Bob Caputo bcap...@cox.net wrote:

 Since your pump is not listed, you don't comply with NFPA 20 so why does
it
 matter if the standard allows an automatic shut off?   For your use, the
 2010 edition of NFPA states the following:



 12.7.2.6 Sole Supply Pumps.

 12.7.2.6.1 Shutdown shall be accomplished by manual or automatic means.

 12.7.2.6.2 Automatic shutdown shall not be permitted where the pump
 constitutes the sole source of supply of a fire sprinkler or standpipe
 system or where the authority having jurisdiction

 has required manual shutdown.



 Regardless of the pump listing or other compliance issues, the answer lies
 solely with the permission of the local AHJ.

 Important Notice: As a member of the NFPA 13 Installation  NFPA 25
 Committee's, this correspondence is not a Formal Interpretation issued
 pursuant to NFPA Regulations. Any opinion expressed is the personal
opinion
 of the author, and does not necessarily represent the official position of
 the NFPA or its Technical Committees. In addition, this correspondence is
 neither intended, nor should be relied upon, to provide consultation or
 services.

 Bob Caputo







 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of sam b
 Sent: Sunday, April 11, 2010 11:15 PM
 To: sprinklerforum@firesprinkler.org
 Subject: FIRE PUMP: Urgent



 Dear all..



 We are in the process of installing *temporary fire protection* for a 30

 story builing.

 The pump installed is a *single diesel engine pump* (Not listed) for the

 supplying water for the landing valves in each floor.The fire pump is

 located in the basement floor and is barricaded .



 The operation of the fire pump will be such that In case of pressure drop

 due to opening of the hosereeel or landing valves the pump will start.

 Now during the inspection from Client,they asked us why there is no

 automatic shutoff .

 *The scenario they are considering is *.

 Suppose some labour accidentally opens the hosreel for anypurpose,the pump

 will start running and if there is noone to stop the pump ,will it get

 damaged.?

 I suggested we could provide a fire alarm bell for alerting the people.

 *Can we provide automatic shuttoff for the diesel pump. Is it acceptable
as

 per NFPA?*

 Is there anyother options available or anything from NFPA to support that
 we

 dont need automatic shutoff?



 Please give your valuable inputs.



 Sam

 ___

 Sprinklerforum mailing list

 Sprinklerforum@firesprinkler.org

 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



 For Technical Assistance, send an email to: supp...@firesprinkler.org



 To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.orgto%3asprinklerforum-requ...@fire
sprinkler.org

 (Put the word unsubscribe in the subject field)

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.orgto%3asprinklerforum-requ...@fire
sprinkler.org
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject 

RE: OHIII

2010-04-12 Thread George Church
If it was Tuesday, it must have been Belgium.
Wouldn't have missed Copenhagen, Hartford is nice, but...

Sorry to all ya walking in Monday am to have to delete delete delete
Well past beer thirty here, time to go

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Friday, April 09, 2010 8:44 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: OHIII

Marioff was bought by UTC and is now an American company.

United Technologies Corporation

TypePublic   (NYSE: UTX)
IndustryConglomerates
Founded 1929
HeadquartersHartford, Connecticut, USA
Key people  Louis R. Chênevert, Chairman  CEO
ProductsConglomerates
Revenue   ▲ $59.8 billion USD (2008)
Net income   ▲ $4.7 billion USD (2008)
Employees   223,100 (2008)
Website utc.com

On Fri, Apr 9, 2010 at 4:38 PM, George Church for...@ptd.net wrote:
 Amen-

 Wonder if we'll have wireless heads in the future.

 Seriously- MIST. Say it like plastics in the Graduate
 (if you don't know the movie, you're not an old-timer, Mrs Robinson).
 Imagine if we could do mist with small diameter pipe (1/2?), 5 GPM flow,
 once they get a nozzle/detector combo that looks acceptably esthetic, and
 water damage will be minimized. In all seriousness, I believe that's the
 wave of the future. Maybe Mist and nitrogen (uh-oh, patent infringement)
as
 a 1-2 punch.

 Other than an excuse to go to Europe when we had money, we went to
 International fire spkr assoc conference to see what MIST stuff we could
 learn. Marioff showed video of fire tests they ran in typical office
 scenario, light hazard where we'd have installed a .1/900 with recessed
 heads, and their mist controlled the fire nicely. So its on the way, and
 they seem to be a decade ahead of us over there (Kudos, Stewart and
Alan!).
 Also in wide-spread use shipboard.




 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

RE: OHIII

2010-04-12 Thread Craig.Prahl
Sometimes a bit of recreational banter is a nice deviation from the normal 
battles we face every day.  Just make sure to mention the title subject in the 
reply somewhere to keep it official and all will be well.  ;)

Although I will say that the most recent discourse has revealed some who have 
spent way too much time inhaling fumes from the pipe dope or pvc cleaners.   
But that was probably from installing so many OHIII systems.

Now back to our regularly scheduled program...


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Monday, April 12, 2010 9:35 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: OHIII

If it was Tuesday, it must have been Belgium.
Wouldn't have missed Copenhagen, Hartford is nice, but...

Sorry to all ya walking in Monday am to have to delete delete delete Well past 
beer thirty here, time to go

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Friday, April 09, 2010 8:44 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: OHIII

Marioff was bought by UTC and is now an American company.

United Technologies Corporation

TypePublic   (NYSE: UTX)
IndustryConglomerates
Founded 1929
HeadquartersHartford, Connecticut, USA
Key people  Louis R. Chênevert, Chairman  CEO
ProductsConglomerates
Revenue   ▲ $59.8 billion USD (2008)
Net income   ▲ $4.7 billion USD (2008)
Employees   223,100 (2008)
Website utc.com

On Fri, Apr 9, 2010 at 4:38 PM, George Church for...@ptd.net wrote:
 Amen-

 Wonder if we'll have wireless heads in the future.

 Seriously- MIST. Say it like plastics in the Graduate (if you don't 
 know the movie, you're not an old-timer, Mrs Robinson).
 Imagine if we could do mist with small diameter pipe (1/2?), 5 GPM 
 flow, once they get a nozzle/detector combo that looks acceptably 
 esthetic, and water damage will be minimized. In all seriousness, I 
 believe that's the wave of the future. Maybe Mist and nitrogen (uh-oh, 
 patent infringement)
as
 a 1-2 punch.

 Other than an excuse to go to Europe when we had money, we went to 
 International fire spkr assoc conference to see what MIST stuff we 
 could learn. Marioff showed video of fire tests they ran in typical 
 office scenario, light hazard where we'd have installed a .1/900 with 
 recessed heads, and their mist controlled the fire nicely. So its on 
 the way, and they seem to be a decade ahead of us over there (Kudos, 
 Stewart and
Alan!).
 Also in wide-spread use shipboard.




 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




--
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Victaulic CPVC

2010-04-12 Thread Todd Williams
Anybody know off hand what year Vic stopped making Firelock CPVC pipe and why?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: FIRE PUMP: Urgent

2010-04-12 Thread Ron Greenman
Sam,

I don't mean to be a smart ass but follow along. You have a special
circumstance you're trying to mitigate against. Your route is to
automatically do something that is typically disallowed without
special dispensation. His greatness, the Dead One has suggested a
different tack which is essentially Biblical in scope: Render unto
NFPA what is NFPA's and unto the problem that which is the Problem's.
If you owned an airline the planes will have seats for pilot and
co-pilot. There is an expectation on the part of the manufacturer, the
regulator, and, unconsciously, the customer that both seats will be
filled. You don't get to put crash test dummies in the seats, or some
other alternative,  because you don't have a real pilot. You find
another solution. If you're required to have manual shut-down, and
there's a fear of inadvertent start-up leading to continuous run until
the pump self destructs then the OWNER will need to assure that a
qualified person is on site that can monitor and operate the pump, or
that, as Bob suggests, a pump run notification device be attached
(you'll also need a trained person on site that knows what that means
and has a procedure to deal with it: call the service company, shut it
down properly, whatever he's trained to do), or some other procedure
that allows the pump to run the required time and is then manually
shut down.

On Mon, Apr 12, 2010 at 6:19 AM, Bob Caputo bcap...@cox.net wrote:
 While pumps are intended to start automatically (on a pressure drop) it is
 intended that upon receipt of alarm indicating the pump is running, a
 qualified person will be dispatched to the pump room to monitor conditions
 and provide shut down after 30 minutes if the pump isn't actually needed.
 This is especially true of electric motor drive pumps because it's not good
 for the motor to start and stop without allowing it to run at least 10
 minutes.

 Even your temporary water supply pump should have a running alarm to some
 central station, job shack or similar but again, non-listed pumps are not
 the subject of NFPA 20 so do whatever your local AHJ requires

 insert stand disclaimer here

 bc


 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of sam b
 Sent: Monday, April 12, 2010 12:36 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: FIRE PUMP: Urgent

 Thaanx bob

 I just went through the same now.

 But If am not providing an automatic shutoff facility,how can I avoid  any
 damage to the pump in case of mentioned scenario
 From the pump supplier I cant expect anything .so from our side what we can
 do to make it more safe.?

 any thoughts?


 Regards

 Sam



 On Mon, Apr 12, 2010 at 10:44 AM, Bob Caputo bcap...@cox.net wrote:

 Since your pump is not listed, you don't comply with NFPA 20 so why does
 it
 matter if the standard allows an automatic shut off?   For your use, the
 2010 edition of NFPA states the following:



 12.7.2.6 Sole Supply Pumps.

 12.7.2.6.1 Shutdown shall be accomplished by manual or automatic means.

 12.7.2.6.2 Automatic shutdown shall not be permitted where the pump
 constitutes the sole source of supply of a fire sprinkler or standpipe
 system or where the authority having jurisdiction

 has required manual shutdown.



 Regardless of the pump listing or other compliance issues, the answer lies
 solely with the permission of the local AHJ.

 Important Notice: As a member of the NFPA 13 Installation  NFPA 25
 Committee's, this correspondence is not a Formal Interpretation issued
 pursuant to NFPA Regulations. Any opinion expressed is the personal
 opinion
 of the author, and does not necessarily represent the official position of
 the NFPA or its Technical Committees. In addition, this correspondence is
 neither intended, nor should be relied upon, to provide consultation or
 services.

 Bob Caputo







 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of sam b
 Sent: Sunday, April 11, 2010 11:15 PM
 To: sprinklerforum@firesprinkler.org
 Subject: FIRE PUMP: Urgent



 Dear all..



 We are in the process of installing *temporary fire protection* for a 30

 story builing.

 The pump installed is a *single diesel engine pump* (Not listed) for the

 supplying water for the landing valves in each floor.The fire pump is

 located in the basement floor and is barricaded .



 The operation of the fire pump will be such that In case of pressure drop

 due to opening of the hosereeel or landing valves the pump will start.

 Now during the inspection from Client,they asked us why there is no

 automatic shutoff .

 *The scenario they are considering is *.

 Suppose some labour accidentally opens the hosreel for anypurpose,the pump

 will start running and if there is noone to stop the pump ,will it get

 damaged.?

 I suggested we could provide a fire alarm bell for alerting the people.

Steam for Fire Suppression

2010-04-12 Thread Reed Roisum
I don't have much information on this yet but here goes anyway...

An owner of a manufacturing facility (I don't know what type of manufacturing) 
has in his head that he wants to use steam from his boiler for fire suppression 
(also don't know what he wants to protect).  I am basically looking for any 
information on using steam for fire suppression.  I have no experience with 
this and haven't heard of it beyond steam smothering systems for kitchen 
exhaust ducts??  Is that still used?

I am somewhat familiar with water mist systems but this sounds like a different 
animal because we would be delivering steam to a fire not forming steam when 
water droplets turn to steam at the fire.  Doesn't seem practical or even 
possible to me.  Sorry for the lack of information but that is all I have to 
share.


Thank you for any info. you have.


Reed A. Roisum, CET
Engineering Technician


Ulteig Engineers, Inc.
Building Services - Fire Protection Engineering

3350 38th Ave. S. * Fargo, ND 58104

Direct: (701)280-8580 | Cell: (701)212-8810

www.ulteig.com

Energy * Water * Built-Environment



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Steam for Fire Suppression

2010-04-12 Thread Matt Grise
Is he wanting to use a steam powered fire pump?

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS  MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Monday, April 12, 2010 10:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Steam for Fire Suppression

I don't have much information on this yet but here goes anyway...

An owner of a manufacturing facility (I don't know what type of manufacturing) 
has in his head that he wants to use steam from his boiler for fire suppression 
(also don't know what he wants to protect).  I am basically looking for any 
information on using steam for fire suppression.  I have no experience with 
this and haven't heard of it beyond steam smothering systems for kitchen 
exhaust ducts??  Is that still used?

I am somewhat familiar with water mist systems but this sounds like a different 
animal because we would be delivering steam to a fire not forming steam when 
water droplets turn to steam at the fire.  Doesn't seem practical or even 
possible to me.  Sorry for the lack of information but that is all I have to 
share.


Thank you for any info. you have.


Reed A. Roisum, CET
Engineering Technician


Ulteig Engineers, Inc.
Building Services - Fire Protection Engineering

3350 38th Ave. S. * Fargo, ND 58104

Direct: (701)280-8580 | Cell: (701)212-8810

www.ulteig.com

Energy * Water * Built-Environment



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Steam for Fire Suppression

2010-04-12 Thread Craig.Prahl
You have no standard to go by for this and no design criteria to apply.  There 
are so many variables to deal with here since steam comes in so many different 
compositions depending on application rates and temperatures, how far from the 
boiler will the steam have to travel to the hazard, what is the temperature and 
pressure at the delivery point, condensation rate, etc., etc., etc...  

Steam is nowhere near the same as water mist.

If he insists on this approach then he needs to hire a qualified ME/FPE to do 
the analysis and make the application rate determinations based on the 
condition of the steam and the hazard.  Then try to sell it as an alternative 
to the AHJ.  This is like stepping into a snake pit.  BEWARE and AVOID at all 
cost.

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Monday, April 12, 2010 11:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Steam for Fire Suppression

I don't have much information on this yet but here goes anyway...

An owner of a manufacturing facility (I don't know what type of manufacturing) 
has in his head that he wants to use steam from his boiler for fire suppression 
(also don't know what he wants to protect).  I am basically looking for any 
information on using steam for fire suppression.  I have no experience with 
this and haven't heard of it beyond steam smothering systems for kitchen 
exhaust ducts??  Is that still used?

I am somewhat familiar with water mist systems but this sounds like a different 
animal because we would be delivering steam to a fire not forming steam when 
water droplets turn to steam at the fire.  Doesn't seem practical or even 
possible to me.  Sorry for the lack of information but that is all I have to 
share.


Thank you for any info. you have.


Reed A. Roisum, CET
Engineering Technician


Ulteig Engineers, Inc.
Building Services - Fire Protection Engineering

3350 38th Ave. S. * Fargo, ND 58104

Direct: (701)280-8580 | Cell: (701)212-8810

www.ulteig.com

Energy * Water * Built-Environment



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Steam for Fire Suppression

2010-04-12 Thread Reed Roisum
Matt,

That is possible.  I am getting information second hand so  I am really in the 
dark thus far.  Just looking for any background knowledge that is out there on 
using steam for fire suppression.  I've requested more information and will 
post more when I get it.

Thanks.


Reed A. Roisum, CET

Engineering Technician



Direct: (701)280-8580
Cell: (701)212-8810





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise
Sent: Monday, April 12, 2010 10:20 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Steam for Fire Suppression

Is he wanting to use a steam powered fire pump?

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS  MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Monday, April 12, 2010 10:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Steam for Fire Suppression

I don't have much information on this yet but here goes anyway...

An owner of a manufacturing facility (I don't know what type of manufacturing) 
has in his head that he wants to use steam from his boiler for fire suppression 
(also don't know what he wants to protect).  I am basically looking for any 
information on using steam for fire suppression.  I have no experience with 
this and haven't heard of it beyond steam smothering systems for kitchen 
exhaust ducts??  Is that still used?

I am somewhat familiar with water mist systems but this sounds like a different 
animal because we would be delivering steam to a fire not forming steam when 
water droplets turn to steam at the fire.  Doesn't seem practical or even 
possible to me.  Sorry for the lack of information but that is all I have to 
share.


Thank you for any info. you have.


Reed A. Roisum, CET
Engineering Technician


Ulteig Engineers, Inc.
Building Services - Fire Protection Engineering

3350 38th Ave. S. * Fargo, ND 58104

Direct: (701)280-8580 | Cell: (701)212-8810

www.ulteig.com

Energy * Water * Built-Environment



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Steam for Fire Suppression

2010-04-12 Thread Todd Williams
Steam would probably have an impact on the fire 
plume, but since it is lighter than air, it will 
buoy to the roof and not get to the product 
below. It would likely require some low-level 
discharge to actually have any effect. A guess 
would be the  Navy may have done some research on 
this at some point. I'd go along with Craig's 
advice and avoid. Tell the guy to call you back 
and let you know how it worked out.




At 11:28 AM 4/12/2010, you wrote:
Matt,

That is possible.  I am getting information 
second hand so  I am really in the dark thus 
far.  Just looking for any background knowledge 
that is out there on using steam for fire 
suppression.  I've requested more information and will post more when I get it.

Thanks.


Reed A. Roisum, CET

Engineering Technician



Direct: (701)280-8580
Cell: (701)212-8810





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise
Sent: Monday, April 12, 2010 10:20 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Steam for Fire Suppression

Is he wanting to use a steam powered fire pump?

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS  MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Monday, April 12, 2010 10:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Steam for Fire Suppression

I don't have much information on this yet but here goes anyway...

An owner of a manufacturing facility (I don't 
know what type of manufacturing) has in his head 
that he wants to use steam from his boiler for 
fire suppression (also don't know what he wants 
to protect).  I am basically looking for any 
information on using steam for fire 
suppression.  I have no experience with this and 
haven't heard of it beyond steam smothering 
systems for kitchen exhaust ducts??  Is that still used?

I am somewhat familiar with water mist systems 
but this sounds like a different animal because 
we would be delivering steam to a fire not 
forming steam when water droplets turn to steam 
at the fire.  Doesn't seem practical or even 
possible to me.  Sorry for the lack of 
information but that is all I have to share.


Thank you for any info. you have.


Reed A. Roisum, CET
Engineering Technician


Ulteig Engineers, Inc.
Building Services - Fire Protection Engineering

3350 38th Ave. S. * Fargo, ND 58104

Direct: (701)280-8580 | Cell: (701)212-8810

www.ulteig.com

Energy * Water * Built-Environment



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Steam for Fire Suppression

2010-04-12 Thread Thom McMahon
For reasons of Temp. only this space would have to be an un-occupiable space
or the fire protection system could kill the occupants. Depending upon what
temp. and pressure (They're related) steam he's talking about, the temp of
the space will be very high. 10PSI steam is 239'F 100PSI steam is 338'F and
200PSI steam is 388'F.

When you go above 15 Psi it's med. Pressure steam, and if I remember right
over 250PSI is high pressure steam
In any case any of these exceed the ability of the human body to survive in
a space with this type of temp/pres.

Sounds like a good way to spend Decades in Court. One of the great beauties
of using water is its ability to convert/absorb so many btu's when it
changes to steam. If your using steam there is no ability to absorb BTU's,
only to displace the Ox.

(There's probably a good reason that you don't see Steam duct suppression
systems any more.)

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Monday, April 12, 2010 9:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Steam for Fire Suppression

I don't have much information on this yet but here goes anyway...

An owner of a manufacturing facility (I don't know what type of
manufacturing) has in his head that he wants to use steam from his boiler
for fire suppression (also don't know what he wants to protect).  I am
basically looking for any information on using steam for fire suppression.
I have no experience with this and haven't heard of it beyond steam
smothering systems for kitchen exhaust ducts??  Is that still used?

I am somewhat familiar with water mist systems but this sounds like a
different animal because we would be delivering steam to a fire not
forming steam when water droplets turn to steam at the fire.  Doesn't seem
practical or even possible to me.  Sorry for the lack of information but
that is all I have to share.


Thank you for any info. you have.


Reed A. Roisum, CET
Engineering Technician


Ulteig Engineers, Inc.
Building Services - Fire Protection Engineering

3350 38th Ave. S. * Fargo, ND 58104

Direct: (701)280-8580 | Cell: (701)212-8810

www.ulteig.com

Energy * Water * Built-Environment



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Steam for Fire Suppression

2010-04-12 Thread Eggen, Clarence (Dale)
FM Global has several areas that use steam as a suppressing agent.  These  
include Data Sheet 6-23, Recovery Boiler, for protection of direct contact 
evaporators, and 7-73 Dust collection.  There are several places in Data Sheet 
7-3 where steam is also used for fire suppression.  Many old textile mills 
used steam as a suppressing agent, reference to Data Sheet 7-1.

Dale Eggen, PE
Bechtel National

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Monday, April 12, 2010 8:38 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Steam for Fire Suppression

Steam would probably have an impact on the fire 
plume, but since it is lighter than air, it will 
buoy to the roof and not get to the product 
below. It would likely require some low-level 
discharge to actually have any effect. A guess 
would be the  Navy may have done some research on 
this at some point. I'd go along with Craig's 
advice and avoid. Tell the guy to call you back 
and let you know how it worked out.




At 11:28 AM 4/12/2010, you wrote:
Matt,

That is possible.  I am getting information 
second hand so  I am really in the dark thus 
far.  Just looking for any background knowledge 
that is out there on using steam for fire 
suppression.  I've requested more information and will post more when I get it.

Thanks.


Reed A. Roisum, CET

Engineering Technician



Direct: (701)280-8580
Cell: (701)212-8810





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise
Sent: Monday, April 12, 2010 10:20 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Steam for Fire Suppression

Is he wanting to use a steam powered fire pump?

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS  MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Monday, April 12, 2010 10:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Steam for Fire Suppression

I don't have much information on this yet but here goes anyway...

An owner of a manufacturing facility (I don't 
know what type of manufacturing) has in his head 
that he wants to use steam from his boiler for 
fire suppression (also don't know what he wants 
to protect).  I am basically looking for any 
information on using steam for fire 
suppression.  I have no experience with this and 
haven't heard of it beyond steam smothering 
systems for kitchen exhaust ducts??  Is that still used?

I am somewhat familiar with water mist systems 
but this sounds like a different animal because 
we would be delivering steam to a fire not 
forming steam when water droplets turn to steam 
at the fire.  Doesn't seem practical or even 
possible to me.  Sorry for the lack of 
information but that is all I have to share.


Thank you for any info. you have.


Reed A. Roisum, CET
Engineering Technician


Ulteig Engineers, Inc.
Building Services - Fire Protection Engineering

3350 38th Ave. S. * Fargo, ND 58104

Direct: (701)280-8580 | Cell: (701)212-8810

www.ulteig.com

Energy * Water * Built-Environment



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing 

RE: Steam for Fire Suppression

2010-04-12 Thread Chris Cahill
Years ago I seem to recall there was something in the annex of one of the
standards that spoke a little about steam.  Might have only been one
paragraph.  If I had to look it up I'd be looking in NFPA 2001, the CO2
standard, maybe 15?  It was more popular in the 40's and 50's.  If you can
find an NFPA handbook from that era might give you something. I'd bet the
Navy has/had experience with this. But as Craig said don't expect to find a
standard to go by.

There was one in St. Paul that protected an asphalt shingle line and it
worked very well by all accounts.  It was older than anyone working in the
plant or on the FD so I don't have particulars and they are out of business
now. 

Steam works by O2 displacement.  I don't see anything inherently wrong with
it.  But steam by itself is rather dangerous. It's certainly better than
plain water in an oven or other hot environment and blowing things up when
the water turns to steam.  But you lose the heat absorption of water to
steam like in mist and regular for sprinklers.

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: chr...@sentryfiremn.com
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Monday, April 12, 2010 10:28 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Steam for Fire Suppression

Matt,

That is possible.  I am getting information second hand so  I am really in
the dark thus far.  Just looking for any background knowledge that is out
there on using steam for fire suppression.  I've requested more information
and will post more when I get it.

Thanks.


Reed A. Roisum, CET

Engineering Technician



Direct: (701)280-8580
Cell: (701)212-8810





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise
Sent: Monday, April 12, 2010 10:20 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Steam for Fire Suppression

Is he wanting to use a steam powered fire pump?

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS  MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Monday, April 12, 2010 10:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Steam for Fire Suppression

I don't have much information on this yet but here goes anyway...

An owner of a manufacturing facility (I don't know what type of
manufacturing) has in his head that he wants to use steam from his boiler
for fire suppression (also don't know what he wants to protect).  I am
basically looking for any information on using steam for fire suppression.
I have no experience with this and haven't heard of it beyond steam
smothering systems for kitchen exhaust ducts??  Is that still used?

I am somewhat familiar with water mist systems but this sounds like a
different animal because we would be delivering steam to a fire not
forming steam when water droplets turn to steam at the fire.  Doesn't seem
practical or even possible to me.  Sorry for the lack of information but
that is all I have to share.


Thank you for any info. you have.


Reed A. Roisum, CET
Engineering Technician


Ulteig Engineers, Inc.
Building Services - Fire Protection Engineering

3350 38th Ave. S. * Fargo, ND 58104

Direct: (701)280-8580 | Cell: (701)212-8810

www.ulteig.com

Energy * Water * Built-Environment



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org

Re: Steam for Fire Suppression

2010-04-12 Thread Ed Vining
Steam has been used for firefighting aboard ship, particularly in engine
rooms.

I have had no experience with it, but you can get some info on the Internet
at Steam Fire Suppression.

Ed Vining


On Mon, Apr 12, 2010 at 8:19 AM, Reed Roisum reed.roi...@ulteig.com wrote:

 I don't have much information on this yet but here goes anyway...

 An owner of a manufacturing facility (I don't know what type of
 manufacturing) has in his head that he wants to use steam from his boiler
 for fire suppression (also don't know what he wants to protect).  I am
 basically looking for any information on using steam for fire suppression.
  I have no experience with this and haven't heard of it beyond steam
 smothering systems for kitchen exhaust ducts??  Is that still used?

 I am somewhat familiar with water mist systems but this sounds like a
 different animal because we would be delivering steam to a fire not
 forming steam when water droplets turn to steam at the fire.  Doesn't seem
 practical or even possible to me.  Sorry for the lack of information but
 that is all I have to share.


 Thank you for any info. you have.


 Reed A. Roisum, CET
 Engineering Technician


 Ulteig Engineers, Inc.
 Building Services - Fire Protection Engineering

 3350 38th Ave. S. * Fargo, ND 58104

 Direct: (701)280-8580 | Cell: (701)212-8810

 www.ulteig.com

 Energy * Water * Built-Environment



 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.orgto%3asprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
Cell 787-0465
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Steam for Fire Suppression

2010-04-12 Thread Craig.Prahl
True but these were usually in equipment spaces or ductwork and typically it's 
in the past tense as in it's not at the lead of the list of suppression agents 
for today's applications.  FMDS 7-1 dealing with textile plants even has a 
statement about steam not being considered the primary means of protection.   


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Eggen, Clarence 
(Dale)
Sent: Monday, April 12, 2010 11:50 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Steam for Fire Suppression

FM Global has several areas that use steam as a suppressing agent.  These  
include Data Sheet 6-23, Recovery Boiler, for protection of direct contact 
evaporators, and 7-73 Dust collection.  There are several places in Data Sheet 
7-3 where steam is also used for fire suppression.  Many old textile mills 
used steam as a suppressing agent, reference to Data Sheet 7-1.

Dale Eggen, PE
Bechtel National

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Monday, April 12, 2010 8:38 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Steam for Fire Suppression

Steam would probably have an impact on the fire plume, but since it is lighter 
than air, it will buoy to the roof and not get to the product below. It would 
likely require some low-level discharge to actually have any effect. A guess 
would be the  Navy may have done some research on this at some point. I'd go 
along with Craig's advice and avoid. Tell the guy to call you back and let you 
know how it worked out.




At 11:28 AM 4/12/2010, you wrote:
Matt,

That is possible.  I am getting information second hand so  I am really 
in the dark thus far.  Just looking for any background knowledge that 
is out there on using steam for fire suppression.  I've requested more 
information and will post more when I get it.

Thanks.


Reed A. Roisum, CET

Engineering Technician



Direct: (701)280-8580
Cell: (701)212-8810





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt 
Grise
Sent: Monday, April 12, 2010 10:20 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Steam for Fire Suppression

Is he wanting to use a steam powered fire pump?

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS  MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed 
Roisum
Sent: Monday, April 12, 2010 10:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Steam for Fire Suppression

I don't have much information on this yet but here goes anyway...

An owner of a manufacturing facility (I don't know what type of 
manufacturing) has in his head that he wants to use steam from his 
boiler for fire suppression (also don't know what he wants to protect).  
I am basically looking for any information on using steam for fire 
suppression.  I have no experience with this and haven't heard of it 
beyond steam smothering systems for kitchen exhaust ducts??  Is that 
still used?

I am somewhat familiar with water mist systems but this sounds like a 
different animal because we would be delivering steam to a fire not 
forming steam when water droplets turn to steam at the fire.  Doesn't 
seem practical or even possible to me.  Sorry for the lack of 
information but that is all I have to share.


Thank you for any info. you have.


Reed A. Roisum, CET
Engineering Technician


Ulteig Engineers, Inc.
Building Services - Fire Protection Engineering

3350 38th Ave. S. * Fargo, ND 58104

Direct: (701)280-8580 | Cell: (701)212-8810

www.ulteig.com

Energy * Water * Built-Environment



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email 
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field) 
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email 
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field) 
___
Sprinklerforum mailing 

RE: Steam for Fire Suppression

2010-04-12 Thread Forest Wilson
I reviewed our contract with the Sprinklerfitters Union and they have
language that they do not perform work on steam systems. So, if the
installing contractor is union, they will need to hire steamfitters to
install the steam suppression system...which may affect the labor cost of
installation. Also, some states license steam fitters so even if the
installing contractor is open shop it would affect labor cost of install.

Forest Wilson
Cherokee Fire

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Monday, April 12, 2010 11:38 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Steam for Fire Suppression

Steam would probably have an impact on the fire 
plume, but since it is lighter than air, it will 
buoy to the roof and not get to the product 
below. It would likely require some low-level 
discharge to actually have any effect. A guess 
would be the  Navy may have done some research on 
this at some point. I'd go along with Craig's 
advice and avoid. Tell the guy to call you back 
and let you know how it worked out.




At 11:28 AM 4/12/2010, you wrote:
Matt,

That is possible.  I am getting information 
second hand so  I am really in the dark thus 
far.  Just looking for any background knowledge 
that is out there on using steam for fire 
suppression.  I've requested more information and will post more when I get
it.

Thanks.


Reed A. Roisum, CET

Engineering Technician



Direct: (701)280-8580
Cell: (701)212-8810





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise
Sent: Monday, April 12, 2010 10:20 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Steam for Fire Suppression

Is he wanting to use a steam powered fire pump?

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS  MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed Roisum
Sent: Monday, April 12, 2010 10:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Steam for Fire Suppression

I don't have much information on this yet but here goes anyway...

An owner of a manufacturing facility (I don't 
know what type of manufacturing) has in his head 
that he wants to use steam from his boiler for 
fire suppression (also don't know what he wants 
to protect).  I am basically looking for any 
information on using steam for fire 
suppression.  I have no experience with this and 
haven't heard of it beyond steam smothering 
systems for kitchen exhaust ducts??  Is that still used?

I am somewhat familiar with water mist systems 
but this sounds like a different animal because 
we would be delivering steam to a fire not 
forming steam when water droplets turn to steam 
at the fire.  Doesn't seem practical or even 
possible to me.  Sorry for the lack of 
information but that is all I have to share.


Thank you for any info. you have.


Reed A. Roisum, CET
Engineering Technician


Ulteig Engineers, Inc.
Building Services - Fire Protection Engineering

3350 38th Ave. S. * Fargo, ND 58104

Direct: (701)280-8580 | Cell: (701)212-8810

www.ulteig.com

Energy * Water * Built-Environment



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Steam for Fire Suppression

2010-04-12 Thread Phelps, Mark
Steam has been used in the past for suppression of coal crusher fires in
coal fired power plants. I'm not aware of a standard for this type
design, that's why they call it SPECIAL HAZARDS. Where are the old
Grinnell guys when you need them?
Mark at Aero

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Reed
Roisum
Sent: Monday, April 12, 2010 8:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Steam for Fire Suppression

I don't have much information on this yet but here goes anyway...

An owner of a manufacturing facility (I don't know what type of
manufacturing) has in his head that he wants to use steam from his
boiler for fire suppression (also don't know what he wants to protect).
I am basically looking for any information on using steam for fire
suppression.  I have no experience with this and haven't heard of it
beyond steam smothering systems for kitchen exhaust ducts??  Is that
still used?

I am somewhat familiar with water mist systems but this sounds like a
different animal because we would be delivering steam to a fire not
forming steam when water droplets turn to steam at the fire.  Doesn't
seem practical or even possible to me.  Sorry for the lack of
information but that is all I have to share.


Thank you for any info. you have.


Reed A. Roisum, CET
Engineering Technician


Ulteig Engineers, Inc.
Building Services - Fire Protection Engineering

3350 38th Ave. S. * Fargo, ND 58104

Direct: (701)280-8580 | Cell: (701)212-8810

www.ulteig.com

Energy * Water * Built-Environment



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Jerry Pepi Has Passed

2010-04-12 Thread Mike Cabral
I just received news that Jerry Pepi passed away this morning. Someone mention 
Old Grinnell Guys in a message earlier. . . well Jerry was one of the best. 

Mike Cabral
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Steam for Fire Suppression

2010-04-12 Thread Chris Mak
As an engineering student, I worked at a hardboard mill in auckland. The 
hardboard presses had steam fire suppression systems. They were employed on a 
fairly regular basis.

 The mill itself was sprinkler protected to FM standards. Loved it when the 
sprinklers were called into action, as there was plenty of overtime on offer.

Regards


Chris Mak
Aon Sprinkler Certification
Via Blackberry
Cell +64-274-344-058


- Original Message -
From: Ed Vining [edvinin...@gmail.com]
Sent: 12/04/2010 08:55 AM MST
To: sprinklerforum@firesprinkler.org
Subject: Re: Steam for Fire Suppression



Steam has been used for firefighting aboard ship, particularly in engine
rooms.

I have had no experience with it, but you can get some info on the Internet
at Steam Fire Suppression.

Ed Vining


On Mon, Apr 12, 2010 at 8:19 AM, Reed Roisum reed.roi...@ulteig.com wrote:

 I don't have much information on this yet but here goes anyway...

 An owner of a manufacturing facility (I don't know what type of
 manufacturing) has in his head that he wants to use steam from his boiler
 for fire suppression (also don't know what he wants to protect).  I am
 basically looking for any information on using steam for fire suppression.
  I have no experience with this and haven't heard of it beyond steam
 smothering systems for kitchen exhaust ducts??  Is that still used?

 I am somewhat familiar with water mist systems but this sounds like a
 different animal because we would be delivering steam to a fire not
 forming steam when water droplets turn to steam at the fire.  Doesn't seem
 practical or even possible to me.  Sorry for the lack of information but
 that is all I have to share.


 Thank you for any info. you have.


 Reed A. Roisum, CET
 Engineering Technician


 Ulteig Engineers, Inc.
 Building Services - Fire Protection Engineering

 3350 38th Ave. S. * Fargo, ND 58104

 Direct: (701)280-8580 | Cell: (701)212-8810

 www.ulteig.com

 Energy * Water * Built-Environment



 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: supp...@firesprinkler.org

 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.orgto%3asprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




--
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
Cell 787-0465
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)



Chris Mak | Aon New Zealand
Sprinkler Certification Manager
Level 1, 4 Fred Thomas Drive,
PO Box33-1240 Takapuna  
t: +64 9 486 9761  | f: +64 9 486 0112 | m: 027 434 4058 
e: chris@aon.co.nz | w: aon.co.nz


Please consider the environment before printing this email.


This document should only be read by those persons to whom it is addressed and 
is not intended to be relied upon by any person without subsequent written 
confirmation of its contents. Accordingly, our company disclaim all 
responsibility and accept no liability (including in negligence) for the 
consequences for any person acting, or refraining from acting, on such 
information prior to the receipt by those persons of subsequent written 
confirmation.

If you have received this e-mail message in error, please notify us immediately 
by telephone. Please also destroy and delete the message from your computer. 
The Unsolicited Electronic Message Act 2007 (The Spam Act) came into effect 
from 5 September 2007. As a valued client you may receive communications from 
us from time to time, including electronic publications, invitations and 
related information. Please advise if you wish us to stop sending these 
communications to you. Otherwise we will assume you wish to continue receiving 
these communications from us. 

Any form of reproduction, dissemination, copying, disclosure, modification, 
distribution and/or publication of this e-mail message is strictly prohibited.
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Victaulic CPVC

2010-04-12 Thread J. Scott Mitchell
I'm anxious to read the why responses.

J. Scott Mitchell, P.E.

--- On Mon, 4/12/10, Todd Williams t...@fpdc.com wrote:

From: Todd Williams t...@fpdc.com
Subject: Victaulic CPVC
To: sprinklerforum@firesprinkler.org
Date: Monday, April 12, 2010, 9:11 AM

Anybody know off hand what year Vic stopped making Firelock CPVC pipe and why?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)



  
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Victaulic CPVC

2010-04-12 Thread Todd Williams
I spoke to someone today from Vic. Apparently they sold their CPVC 
line to Spears a few years ago.


At 06:56 PM 4/12/2010, you wrote:
I'm anxious to read the why responses.

J. Scott Mitchell, P.E.

--- On Mon, 4/12/10, Todd Williams t...@fpdc.com wrote:

From: Todd Williams t...@fpdc.com
Subject: Victaulic CPVC
To: sprinklerforum@firesprinkler.org
Date: Monday, April 12, 2010, 9:11 AM

Anybody know off hand what year Vic stopped making Firelock CPVC pipe and why?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)




___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Pipe Wrapping

2010-04-12 Thread Jay Jay Blocker
I thought I once saw something saying that sprinkler pipe cant be wrapped 
with pipe insulation.  Am I dreaming or does this code exist?  I cant locate it.
 
J. Blocker
EFPS
(303) 353-9712


  
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Pipe Wrapping

2010-04-12 Thread John Denhardt
I believe you were dreaming.

John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jay Jay Blocker
Sent: Monday, April 12, 2010 8:13 PM
To: sprinklerforum@firesprinkler.org
Subject: Pipe Wrapping

I thought I once saw something saying that sprinkler pipe cant be wrapped 
with pipe insulation.  Am I dreaming or does this code exist?  I cant locate it.
 
J. Blocker
EFPS
(303) 353-9712


  
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)