RE: AHJ requires Concealed Sprinklers

2021-11-10 Thread Mike Stossel via Sprinklerforum
Yes, we have a jurisdiction that does not permit the use of concealed 
sprinklers.  

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum  On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Wednesday, November 10, 2021 9:21 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: travis.m...@mfpdesign.com
Subject: AHJ requires Concealed Sprinklers

Has anyone run into a jurisdiction where they mandate the type of sprinkler to 
be used?  We have one local jurisdiction that mandates concealed sprinklers in 
R2 occupancies.  It is in their amended codes.  We hadn't done an R2 in this 
jurisdiction in many years.  This came up new.  I was wondering if anyone else 
has jurisdictions that impose only a certain type of sprinkler.

Travis Mack, CFPS, CWBSP, RME-G, COC, SET Senior Engineering Manager MFP Design
480-505-9271 ext. 700 C: 480-272-2471
travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Dry System Size

2021-11-01 Thread Mike Stossel via Sprinklerforum
The FDT program will work with a single loop.

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum  On Behalf 
Of Brian Harris via Sprinklerforum
Sent: Monday, November 1, 2021 10:06 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Brian Harris ; travis.m...@mfpdesign.com
Subject: RE: Dry System Size

So that begs to question what are you supposed to do it you have a looped 
system?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-Original Message-
From: Sprinklerforum  On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Monday, November 01, 2021 9:59 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: travis.m...@mfpdesign.com
Subject: Re: Dry System Size

If I recall correctly, it may work for a loop, depending on configuration, but 
it is not listed for loops. Only listed for tree systems.


Travis Mack, CFPS, CWBSP, RME-G, COC, SET

Senior Engineering Manager

MFP Design

480-505-9271 ext. 700 C: 480-272-2471

travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>

www.mfpdesign.com<http://www.mfpdesign.com/>



Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>


From: Sprinklerforum  on behalf 
of cliff--- via Sprinklerforum 
Sent: Monday, November 1, 2021 6:55:52 AM
To: sprinklerforum@lists.firesprinkler.org 

Cc: cl...@fire-design.com 
Subject: RE: Dry System Size

Brian,

Unless they have changed the program in the last year or so, the FDT software 
will not work if your mains are looped. I believe it only works on a 'tree' 
type system.

Cliff Whitfield, SET
President

Fire Design, Inc.
940 Summerbrooke Drive
Tallahassee, FL 32312
Ph: 828-284-4772



cl...@fire-design.com
www.fire-design.com<http://www.fire-design.com>

-Original Message-
From: Sprinklerforum  On Behalf 
Of Brian Harris via Sprinklerforum
Sent: Monday, November 1, 2021 9:51 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Brian Harris 
Subject: RE: Dry System Size

Travis-
Thanks as always.


Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-Original Message-
From: Sprinklerforum  On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Monday, November 01, 2021 9:44 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: travis.m...@mfpdesign.com
Subject: Re: Dry System Size

Tyco FDT is only software for this.


Travis Mack, CFPS, CWBSP, RME-G, COC, SET

Senior Engineering Manager

MFP Design

480-505-9271 ext. 700 C:
480-272-2471

travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>

www.mfpdesign.com<http://www.mfpdesign.com><http://www.mfpdesign.com/<http://www.mfpdesign.com>>



Send large files to us via:
https://www.hightail.com/u/MFPDesign<https://www.hightail.com/u/MFPDesign><https://na01.safelinks.protection.outlo
ok.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7<http://ok.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7>
C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0
%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D
=0>


From: Sprinklerforum  on behalf 
of Brian Harris via Sprinklerforum 
Sent: Monday, November 1, 2021 6:42:38 AM
To: sprinklerforum@lists.firesprinkler.org

Cc: Brian Harris 
Subject: Dry System Size

I assume with a dry system size of 1200 gallons my options are to add a 2nd dry 
valve and have (2) 600 gallon system with quick opening devices or run delivery 
time calc's and see if by chance it's under 60 seconds? If the latter is true 
what do most use to run theses calc's?

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/<http://bvssystemsinc.com><http://bvssystemsinc.com<http://bvssystemsinc.com>>>
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or>
g>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
___
Sprinklerfo

RE: Supervised Air Manual Dry Standpipe

2021-10-22 Thread Mike Stossel via Sprinklerforum
In NYC we put a 2 1/2" FHV right next to the FDC with a pressure gauge.  When 
they arrive they use the 2 1/2" FHV as a dump valve and can see the pressure 
that is left in the system at a single location. 

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum  On Behalf 
Of BRUCE VERHEI via Sprinklerforum
Sent: Friday, October 22, 2021 1:53 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: BRUCE VERHEI ; Moschello, Joe 

Subject: RE: Supervised Air Manual Dry Standpipe

I’m not familiar with NYC’s requirement. I do know FF’s hate waiting for air to 
discharge and they get a constant stream of water. Even flat, ostensibly dry 
hose has a lot of air in it. I mean the lines between the engine and the FDC. 
Then there’s all the air in the standpipe. Pressurize the dry standpipe and the 
wait is longer. 

You all seen dry spk system trip test. Even after a decent stream there’s a 
little air spitting. Nozzle reaction from a sprinkler head? Meh. From a 200 gpm 
solid stream nozzle? Nozzle reaction matters, especially if it’s bouncing 
around. Keep at 25? I’d suppose amongst concerns is time to bleed line, and 
start to attack fire.

Best.

Bruce Verhei

> On 10/21/2021 8:30 AM Moschello, Joe via Sprinklerforum 
>  wrote:
> 
>  
> It's an FDNY DOB local law amendment NYC made back in 2010 as a result of the 
> Deutsche Bank fire in 2007 where 2 FF's died and 100 FF's were injured in a 7 
> alarm construction site fire.
> 
> Joseph Moschello
> Lieutenant/Fire Protection Subcode Official Summit Fire Department
> 396 Broad Street
> Summit, NJ 07901
> 908-277-9360
>  
> 
> 
> 
> 
> -Original Message-
> From: Sprinklerforum 
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
> Failla, Daniel via Sprinklerforum
> Sent: Thursday, October 21, 2021 10:13 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Failla, Daniel
> Subject: RE: Supervised Air Manual Dry Standpipe
> 
> CAUTION: This email has originated from outside of the organization. Do not 
> click links or open attachments unless you recognize the sender and know the 
> content is safe.
> 
> 
> 
> Good morning,
> 
> Can someone please provide the actual NFPA 14, code reference for this 
> requirement?
> 
> Thank you for the assistance.
> 
> Sincerely,
> 
> Daniel S. Failla Jr. | Deputy Fire Marshal Charleston Fire Department 
> Fire Marshal Division
> 2 George Street, Suite 3800 | Charleston, SC 29401
> T:(843) 724-5960 | F:(843) 720-5857 |  fail...@charleston-sc.gov  |  
> www.charleston-sc.gov/fire
> 
> 
> 
> 
> 
> -Original Message-
> From: Sprinklerforum  
> On Behalf Of Henry Fontana via Sprinklerforum
> Sent: Wednesday, October 20, 2021 10:47 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Henry Fontana ; cw bamford 
> 
> Subject: Re: Supervised Air Manual Dry Standpipe
> 
> CAUTION: This email originated outside of the City of Charleston. Do not 
> click links or open attachments unless you recognize the sender and know the 
> content is safe.
> 
> 
> If you want the big east coast city rule. Here it is.
> 
> “ Pressure shall be maintained in the standpipe and cross connections at all 
> times and shall not exceed 25 psig (172 kPag) by utilizing nitrogen or an air 
> compressor with an air dryer”
> 
> Henry Fontana
> Operations Manager (NYC)
> Johnson Controls Fire Protection
> 100 Lighting Way| St#402|Secaucus|NJ 
> 07094
> Cell: 201-210-9873
> henry.font...@jci.com<mailto:henry.font...@jci.com>
> 
> 
> On Oct 20, 2021, at 9:18 PM, cw bamford via Sprinklerforum 
>  wrote:
> 
> Can somebody on East Coast big city please respond?
> 
> What about  using a PS15   Nominal System Pressure 15 psi  low pressure
> switch on the dry system standpipe?
> 
> On Wed, Oct 20, 2021 at 2:08 PM Mike Morey via Sprinklerforum < 
> sprinklerforum@lists.firesprinkler.org> wrote:
> 
> I don’t know that their is an express limit other than minimum 7psi.  That 
> said for safety reasons if you have an air source capable of anything close 
> to that I’d come up with something to regulate it.  Doesn’t 13 limit air 
> testing to 60 psi for safety?  Air pressure is much more dangerous than water 
> as far as amount of energy stored.
> 
> 
> Mike Morey
> 
> CFPS 3229 • NICET S.E.T. 123677
> 
> Project Manager • Fire Protection Group Shambaugh & Son, LP an EMCOR 
> Company
> 
> 7614 Opportunity Drive • Fort Wayne, IN • 46825
> 
> direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991 email 
> mmo...@shambaugh.com
> 
> [Image]
> 
> 
>

RE: Overhead / Friction Loss

2020-01-29 Thread Mike Stossel via Sprinklerforum
Could you please also share your spreadsheet with me?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of jaycs7919--- via Sprinklerforum
Sent: Wednesday, January 29, 2020 6:13 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: jaycs7...@gmail.com; Brian Harris 
Subject: Overhead / Friction Loss

I sent you an excel sheet I put together for our estimators to use to determine 
if they would need a pump or not based on design and water flows they obtained.

Jay Stough
NICET IV LAYOUT
NICET III ITM


On Tuesday, January 28, 2020, 2:09:21 PM EST, Brian Harris via Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:



What’s a good “ballpark” number to include for pressure loss due to friction 
when guesstimating system demand? I figure EHP, Elevation, Underground, BFP. 
Any help would be greatly appreciated.



Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com<http://bvssystemsinc.com/>

Phone: 704.896.9989

Fax: 704.896.1935


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: inside hose - Standpipes

2020-01-07 Thread Mike Stossel via Sprinklerforum
Are you looking for section 12.8.5?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Tuesday, January 7, 2020 2:12 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G 
Subject: inside hose - Standpipes

I have an AHJ that is requesting inside hose allowance to be provided at the 
standpipe hose valves.  I recall there being standards in 13 or 14 that states 
you are not required to provided inside hose allowances because of standpipes.  
Can someone help me locate.

It would not normally be an issue, but we have a tank that is already sized (by 
others) and this project has car stackers so the inside hose for the duration 
would cause significant issues.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
fax: 866-430-6107
tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>
www.mfpdesign.com

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Software Platform

2019-12-26 Thread Mike Stossel via Sprinklerforum
It sound like most of the forum is running AutoSprink, but I am looking to see 
if anyone on the forum was a SprinkCAD Classic user and switched over to 
SprinkCAD 3D.

Thanks,


Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 13D CAD and Calc Program

2019-11-08 Thread Mike Stossel via Sprinklerforum
I am using AutoCad 2019 – SprinkCAD – ThinkPad p72 with the following build out:
●  Intel® Xeon® E-2176M 6 core processor with vPro™ (2.70GHz, up to 4.40GHz 
with Turbo Boost Technology, 12MB Cache)
●  Windows 10 Pro for Workstations 64
●  Windows 10 Pro for Workstations 64 English
●  17.3” UHD 4K (3840 x 2160) IPS anti-glare, 400nits
●  32GB (16GB + 16GB) DDR4 2400MHz ECC
●  NVIDIA Quadro P4200 8GB
●  IR & 720p HD Camera with Microphone
●  Backlit Keyboard with Number Pad - English
●  Fingerprint Reader
●  Fingerprint
●  Hardware dTPM
●  Hardware dTPM2.0 Enabled
●  1TB Solid State Drive PCIe-NVMe OPAL2.0 M.2
●  1TB Hard Disk Drive, 7200rpm, SATA3, 2.5"
●  2TB
●  Smart Card Reader
●  6 cell Li-Polymer 99Wh
●  230W AC Adapter (3pin) - US
●  Intel® 9560 vPro 802.11AC (2 x 2) & Bluetooth 5.0
●  vPro Certified
●  17.3" UHD (3840 x 2160) LED, IPS, Anti-glare, non-Touch, with IR-Camera, 
with Mic, with WLAN
●  Intel Xeon E-2176M Processor (12MB Cache, up to 4.40 GHz), NVIDIA Quadro 
P4200 8GB GDRR5

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of firstin--- via Sprinklerforum
Sent: Friday, November 8, 2019 8:07 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: firs...@aol.com
Subject: 13D CAD and Calc Program

Hello all,

I've been drawing 13D systems by hand on reflective ceiling plans for years. 
I'm now looking for recommendations for a CAD program for 13D systems, 
something simple and inexpensive if possible.

I've been using Hydronics to run the calculations. There is a problem with this 
program when trying to plug in a pump. I would like to know who is using what 
as far a as calculation program. Any recommendations on computer drawing and 
calculation programs.

Thanks all!
Owen Evans
Sent from my iPhone
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Ex cov under OH Door

2019-08-23 Thread Mike Stossel via Sprinklerforum
NFPA 2013 2019 - 11.3.2 (8) Extended coverage sprinklers installed to protect 
areas below a single overhead door(s)

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Travis Mack via Sprinklerforum
Sent: Friday, August 23, 2019 5:13 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Travis Mack 
Subject: Ex cov under OH Door

Question has been brought up. Can you use ex cov sidewall listed for light 
hazard under overhead door in an ordinary hazard building?

I was under the impression it was not an issue. There is wording in section on 
standard spray sidewall that you can. But the same wording is not in the 
section under ex cov sidewall sprinklers. Since location has meaning, it made 
me question.



Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com<http://www.mfpdesign,com>
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Flex Heads

2019-07-18 Thread Mike Stossel
I have not heard of any issues, several of my clients use them.  Many of my 
clients have started switching over to Victaulic's CC so that the entire system 
is grooved.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Thomas Reinhardt
Sent: Thursday, July 18, 2019 3:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Flex Heads

I know that flex heads are listed and approved. I'm sure this topic has come up 
before. Anyone have any problems with using flex heads?

Tom Reinhardt
Fire Inspector/Plan Reviewer
Skokie Fire Department
7424 Niles Center Road
Skokie, IL 60077
Office: 847-982-5342
thomas.reinha...@skokie.org<mailto:thomas.reinha...@skokie.org>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sleeping rooms in a hospital

2019-06-28 Thread Mike Stossel
I have always done QR.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Friday, June 28, 2019 3:46 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Sleeping rooms in a hospital

Residential sprinklers or QR?  I-2 occupancy.  Specs call for residential. I've 
always done these as QR.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: PDF to DWG programs

2019-06-18 Thread Mike Stossel
Do you have an earlier version of AutoCAD?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of J H
Sent: Tuesday, June 18, 2019 1:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: PDF to DWG programs

Hello everybody,
Does anyone have any recommendation for a free or low cost program to convert 
PDF to DWG format? I tried the trial version of Autocad 2019 and really liked 
their  PDFIMPORT function but I can't afford to upgrade so am looking for other 
alternatives. I have some old software that will do it but the results aren't 
near the quality of Autocad2019.

Thanks,
J
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Water Test From Storage Tank

2019-05-17 Thread Mike Stossel
Vince and Glen sorry for the inconvenience.  Next time I will try and keep my 
dumb questions to myself so that your head doesn’t explode.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Glen Buelow, Inc.
Sent: Thursday, May 16, 2019 12:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Water Test From Storage Tank

Vince,
I can't! I am afraid my head will explode.
[https://docs.google.com/uc?export=download=0B7SYmRowbxfLWWlIRHA2UmJqaFE=0B7SYmRowbxfLMHpWaGVTRjhPR0NMN3BtUVZrZWNoZlFFZzBzPQ]

Glen Buelow
Glen W. Buelow, Inc.
Fire Protection Design and Consulting
Cleveland 330.220.7201 ● Akron 330.665.4439


On Thu, May 16, 2019 at 12:42 PM Vince Sabolik 
mailto:vi...@wtfp.net>> wrote:
You didn't look at the dumb answers?
On May 16, 2019, "Glen Buelow, Inc." 
mailto:gwb...@gmail.com>> wrote:
Vince,
Nioce answer to dumb question
[https://docs.google.com/uc?export=download=0B7SYmRowbxfLWWlIRHA2UmJqaFE=0B7SYmRowbxfLMHpWaGVTRjhPR0NMN3BtUVZrZWNoZlFFZzBzPQ]

Glen Buelow
Glen W. Buelow, Inc.
Fire Protection Design and Consulting
Cleveland 330.220.7201 ● Akron 330.665.4439


On Wed, May 15, 2019 at 2:26 PM Vince Sabolik 
mailto:vi...@wtfp.net>> wrote:
Height x .434 = Starting psi at top.

Less friction loss at flow (pick a flow)

Your flow test complete with a K factor!






On 5/15/2019 11:27 AM, Mike Stossel wrote:
I have an existing building with a sprinkler system that is supplied by a 
gravity tank located on the roof.  They are modifying the first floor of the 
building that will require hydraulic calculations.  Is it possible to 
mathematically create a waterflow test  accurately, or do you need to actually 
perform a water flow test at the 1st floor level?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>



___

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

--
[cid:image005.jpg@01D50C80.B0DB7FE0]
11351 Pearl Road /  Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601

Vince Sabolik
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Vince Sabolik
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Water Test From Storage Tank

2019-05-15 Thread Mike Stossel
Perfect, thank you.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Steve Mackinnon
Sent: Wednesday, May 15, 2019 11:51 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Water Test From Storage Tank

I do a lot of this work in NYC and we just use the gravity pressure as the 
static number and drop 1 psi for residual pressure. Then divide the gravity 
tank volume by your hazard (i.e. light = 30 minutes, and ord haz = 40 minutes) 
for the flow number.

Steven


From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Wednesday, May 15, 2019 11:31 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Water Test From Storage Tank

Computer models do it all the time.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."


From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Mike Stossel
Sent: Wednesday, May 15, 2019 8:27 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Water Test From Storage Tank

I have an existing building with a sprinkler system that is supplied by a 
gravity tank located on the roof.  They are modifying the first floor of the 
building that will require hydraulic calculations.  Is it possible to 
mathematically create a waterflow test  accurately, or do you need to actually 
perform a water flow test at the 1st floor level?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Water Test From Storage Tank

2019-05-15 Thread Mike Stossel
I have an existing building with a sprinkler system that is supplied by a 
gravity tank located on the roof.  They are modifying the first floor of the 
building that will require hydraulic calculations.  Is it possible to 
mathematically create a waterflow test  accurately, or do you need to actually 
perform a water flow test at the 1st floor level?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] EC Heads and open Grid Ceilings

2019-05-07 Thread Mike Stossel
I could be completely off base with this, but does your ceiling need to follow 
open grid ceilings?  The thought crossing my mind is a 2"x4" hung on its edge 
spaced a couple feet apart or more of a ceiling grid system installed without 
the tiles.  Would the three times rule apply instead of the open grid rules?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Kyle.Montgomery
Sent: Tuesday, May 7, 2019 1:17 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] EC Heads and open Grid Ceilings

I think you do, unless somehow your EC heads meet that spacing criteria (which 
would be a horribly inefficient use of EC sprinklers). But I'm hoping someone 
will disagree with me and have a good answer as to why you don't.

-Kyle M

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of James Crawford
Sent: Tuesday, May 7, 2019 9:34 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] EC Heads and open Grid Ceilings

We have an existing building that has extended coverage heads installed, the 
tenant improvement involves floating wood grated ceilings that are more than 
70% open and will be about 18" below the sprinkler head. Light hazard occupancy.

NFPA #13 (2013) section 8.15.14 Open Grid Ceilings does not make mention of EC 
heads.

Do we need to change all the heads in this area to standard coverage heads?



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca<mailto:jcrawf...@phaserfire.ca>
Web www.phaserfire.ca<http://www.phaserfire.ca>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Grooved Coupling for CPVC

2019-04-04 Thread Mike Stossel
I just heard back from Victaulic and they said the following:

"You can use and 004, which is 75 with an 005 gasket. You can use the 75 
submittal  and I believe it is UL/FM approved."

Hope this helps.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Mike Hairfield
Sent: Thursday, April 4, 2019 12:11 PM
To: Sprinklerforum 
Subject: Grooved Coupling for CPVC

I have a local AHJ asking for a data sheet that states that a standard grooved 
coupling is
U/L listed and/or FM approved for that use.

Have any of you guys ever seen this?

Thanks,

Mike
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] RE: Antifreeze temperature requirements

2019-03-14 Thread Mike Stossel
Being from Pennsylvania I consult with Punxsutawney Phil.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Kyle.Montgomery
Sent: Thursday, March 14, 2019 1:51 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] RE: Antifreeze temperature requirements

No one uses the old Farmer’s Almanac anymore?

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of tston...@comcast.net<mailto:tston...@comcast.net>
Sent: Thursday, March 14, 2019 10:21 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] RE: Antifreeze temperature requirements

Todd,

NOAH should be able to help with that information.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

   117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968
 tston...@comcast.net<mailto:tston...@comcast.net>



From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Fpdcdesign
Sent: Thursday, March 14, 2019 1:19 PM
To: Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: Antifreeze temperature requirements

Yes, I’m using the “A” word. I have a client that is asking be about using the 
new Tyco antifreeze solution for a project. Reading through the literature, it 
states that it is not good for temperatures below -10F. My question is where do 
we find information to determine what is the projected minimum temperature for 
a particular location?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: QR for OH

2019-03-07 Thread Mike Stossel
I would use quick response everywhere.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Brian Harris
Sent: Thursday, March 7, 2019 10:49 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: QR for OH

Quick poll:
Just wondering what the consensus is when doing an office building where the 
majority of the heads are QR pendents in LH areas. Do you use SR pendents in 
the few rooms that are OH or do you just use QR to keep it simple?  I doubt 
here's much of a cost savings if any.

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: OS "flow rates"

2019-03-05 Thread Mike Stossel
What about showing him the equivalent length chart in NFPA 13 for gate valves?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Rocci 3 Cetani
Sent: Tuesday, March 5, 2019 3:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: OS "flow rates"

So we swapped out a broken OS valve at the hospital and the OSHPD inspector 
is insisting he wants the "flow rates"  ( I assume he means friction loss) from 
the existing and new OS valve. OS valve cutsheets  don't have a friction 
loss chart because the loss is so minimal. Does anyone have any ideas on how to 
explain this to an OSHPD inspector, he have already told him this but he is 
just stuck on wanting to know the "flow rates"

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590


roc...@norcalfire.com<mailto:roc...@norcalfire.com>
www.norcalfire.com<http://www.norcalfire.com/>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information
belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Car Lifts

2019-01-30 Thread Mike Stossel
NFPA 13, 2016 now gives us guidance and tells us to protect the area as Extra 
Hazard Group II with an overhead system only.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of John Irwin
Sent: Wednesday, January 30, 2019 6:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Car Lifts

Currently working on a high end condo development. The owners have individual 
garages with an option to have a lift installed so that they can get an 
additional car in.

I am sure you know where this is going ... sprinklers under the lift or no? I 
don't know of any code references that directly address this situation.

What say you?

John Irwin

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten." - Benjamin Franklin

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Hydrostatic Test Gauge

2019-01-21 Thread Mike Stossel
I have an New York City inspector stating that it is required by code that a 
600psi gauge is used when performing a 300psi standpipe test.  I have looked at 
every code book that I can think of and cannot find any such requirement.  Does 
anyone know of any code requirement for this?di

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Back to back floor controls.

2018-11-06 Thread Mike Stossel
You are absolutely right, it always helps when you read the entire question and 
don’t jump to a conclusion.  My apologizes for the incorrect information.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of cl...@fire-design.com
Sent: Tuesday, November 6, 2018 3:53 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Back to back floor controls.

I thought Todd said this was a 2-story building?

I’d use the check valves but more for good ‘engineering practice’.  I’m not 
certain that they are ‘required’, based on the info Todd provided.

Just my opinion.

Cliff Whitfield, SET
President

Fire Design, Inc.
184 Comfort Place
Burnsville, NC 28714
Ph: 828-284-4772

[Description: New FDI Logo-4.jpg]

cl...@fire-design.com<mailto:cl...@fire-design.com>
www.fire-design.com<http://www.fire-design.com/>

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of John Denhardt
Sent: Tuesday, November 6, 2018 3:49 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Back to back floor controls.

I agree. Check valves are required.

John
John August Denhardt, P.E.
Strickland Fire Protection

On Nov 6, 2018, at 3:41 PM, Mike Stossel 
mailto:m...@knssprinkler.com>> wrote:
If I am understanding you question correctly, check valves are required.

8.16.1.5 Floor Control Valve Assemblies.
8.16.1.5.1* Multistory buildings exceeding two stories in height shall be 
provided with a floor control valve, check valve, main drain valve, and flow 
switch for isolation, control, and annunciation of water flow on each floor 
level.

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Fpdcdesign
Sent: Tuesday, November 6, 2018 3:38 PM
To: Sprinklerforum 
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: Back to back floor controls.

I am working on an existing two story plus attic wood frame building. The 
engineer is requiring zone control assemblies (butterfly valve plus riser 
manifold) for every level including the attic. I have designed it so there is a 
bull head tee at the top of a 4” riser with the assemblies on either side of 
the tee. Given that the flow switches are going to be in close proximity, 
should I install a check valve between the butterfly valve and the manifold?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

[https://ipmcdn.avast.com/images/icons/icon-envelope-tick-round-orange-animated-no-repeat-v1.gif]<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=icon>

Virus-free. 
www.avast.com<https://www.avast.com/sig-email?utm_medium=email_source=link_campaign=sig-email_content=emailclient_term=link>


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Back to back floor controls.

2018-11-06 Thread Mike Stossel
Sorry, I also made the assumption that your total floor area exceeded the 
square footage.

8.16.1.5.3 The floor control valve, check valve, main drain valve, and flow 
switch required by 8.16.1.6.3 shall not be required where the total area of all 
floors combined does not exceed the system protection area limitations of 8.2.1.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Fpdcdesign
Sent: Tuesday, November 6, 2018 3:38 PM
To: Sprinklerforum 
Subject: Back to back floor controls.

I am working on an existing two story plus attic wood frame building. The 
engineer is requiring zone control assemblies (butterfly valve plus riser 
manifold) for every level including the attic. I have designed it so there is a 
bull head tee at the top of a 4” riser with the assemblies on either side of 
the tee. Given that the flow switches are going to be in close proximity, 
should I install a check valve between the butterfly valve and the manifold?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Back to back floor controls.

2018-11-06 Thread Mike Stossel
If I am understanding you question correctly, check valves are required.

8.16.1.5 Floor Control Valve Assemblies.
8.16.1.5.1* Multistory buildings exceeding two stories in height shall be 
provided with a floor control valve, check valve, main drain valve, and flow 
switch for isolation, control, and annunciation of water flow on each floor 
level.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Fpdcdesign
Sent: Tuesday, November 6, 2018 3:38 PM
To: Sprinklerforum 
Subject: Back to back floor controls.

I am working on an existing two story plus attic wood frame building. The 
engineer is requiring zone control assemblies (butterfly valve plus riser 
manifold) for every level including the attic. I have designed it so there is a 
bull head tee at the top of a 4” riser with the assemblies on either side of 
the tee. Given that the flow switches are going to be in close proximity, 
should I install a check valve between the butterfly valve and the manifold?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Obstructions in Light Hazard Attic

2018-10-25 Thread Mike Stossel
It is part of TYCO’s requirements in their listing that when the sprinklers are 
installed on pipes greater than 2-1/2” they need to be on sprigs.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Travis Mack
Sent: Thursday, October 25, 2018 11:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Obstructions in Light Hazard Attic

The sections you quote, I believe, are for isolated obstructions. I would think 
your 4” pipe is a continuous obstruction.  So, I’m not certain it applies.

Additionally, i don’t think the attic sprinklers are SSU. I think you would 
need to look at the extended coverage rules. That exemption is not located in 
8.8 either.

I think you may be changing stuff.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Oct 25, 2018, at 8:32 AM, Richard Mote 
mailto:spri...@aol.com>> wrote:
We have an attic where the designer placed TYCO BB head directly on a 4" line 
running at the peak. They should have been on sprigs but it wasn't caught in 
the design stage.

NFPA 13, 2007 in section 8.6.5.2.1.4 States that for light and ordinary hazard 
occupancies structural members only shall be considered when applying the 
requirements of 8.6.5.2.1.3.
8.6.5.2.1.8 States The requirement of 8.6.5.2.1.3 shall not apply to sprinkler 
pipe less than 3 in. (80 mm) in diameter.
So which is it? In light and ordinary hazard can you ignore the non structural 
obstructions and only apply them in extra hazard occupancies? This seems like a 
circular argument.

Excerpt from NFPA 13 below to save looking it up.

8.6.5.2.1.3* Minimum Distance from Obstructions.
(A) Unless the requirements of 8.6.5.2.1.4 through 8.6.5.2.1.9 are met, 
sprinklers shall be positioned away from obstructions a minimum distance of 
three times the maximum dimension of the obstruction (e.g., structural members, 
pipe, columns, and fixtures).
(B) The maximum clear distance required shall be 24 in. (609 mm) in accordance 
with Figure 8.6.5.2.1.3(B).
8.6.5.2.1.4* For light and ordinary hazard occupancies, structural members only 
shall be considered when applying the requirements of 8.6.5.2.1.3.
8.6.5.2.1.5 Sprinklers shall be permitted to be spaced on opposite sides of the 
obstruction where the distance from the centerline of the obstruction to the 
sprinklers does not exceed one-half the allowable distance between sprinklers. 
8.6.5.2.1.6 Sprinklers shall be permitted to be located one half the distance 
between the obstructions where the obstruction consists of open trusses 20 in. 
(0.51 m) or greater a part [24 in. (0.61 m) on center], provided that all truss 
members are not greater than 4 in. (102 mm) (nominal) in width.
8.6.5.2.1.7 Sprinklers shall be permitted to be installed on the centerline of 
a truss or bar joist or directly above a beam, provided that the truss chord or 
beam dimension is not more than 8 in. (203 mm) and the sprinkler deflector is 
located at least 6 in. (152 mm) above the structural member and where the 
sprinkler is positioned at a distance three times greater than the maximum 
dimension of the web members away from the web members.
8.6.5.2.1.8 The requirements of 8.6.5.2.1.3 shall not apply to sprinkler system 
piping less than 3 in. (80 mm) in diameter

A.8.6.5.2.1.4 It is the intent of this section to exempt nonstructural elements 
in light and ordinary hazard occupancies from the obstruction criteria commonly 
called the “Three Times Rule.” However, the other obstruction rules, including 
the “Beam Rule” (see 8.6.5.1.2) and the “Wide Obstruction Rule” (see 
8.6.5.3.3), still apply. If an obstruction is so close to a sprinkler that 
water cannot spray on both sides, it is effectively a continuous obstruction as 
far as the sprinkler is concerned and the Beam Rule should be applied.
It is not the intent of this section to permit the use of fixtures and 
architectural features or treatments to conceal, obscure, or otherwise obstruct 
sprinkler discharge. The requirement should be applied in accordance with the 
performance objectives in 8.6.5.1.

Richard L. Mote
On Behalf of
Rowe Sprinkler Systems
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Big Ass Fans

2018-10-23 Thread Mike Stossel
11.1.7* High Volume Low Speed (HVLS) Fans. The installation of HVLS fans in 
buildings equipped with sprinklers, including ESFR sprinklers, shall comply 
with the following:
(1) The maximum fan diameter shall be 24 ft (7.3 m).
(2) The HVLS fan shall be centered approximately between four adjacent 
sprinklers.
(3) The vertical clearance from the HVLS fan to sprinkler deflector shall be a 
minimum of 3 ft (0.9 m).
(4) All HVLS fans shall be interlocked to shut down immediately upon receiving 
a waterflow signal from the alarm
A.11.1.7 A series of 10 full-scale fire tests and limited-scale testing were 
conducted to determine the impact of HVLS fan operation on the performance of 
sprinkler systems. The project, sponsored by the Property Insurance Research 
Group (PIRG) and other industry groups, was coordinated by the Fire Protection 
Research Foundation (FPRF). The complete test report, High Volume/Low Speed Fan 
and Sprinkler Operation
- Ph. 2 Final Report (2011), is available from the FPRF. Both control mode 
density area and early suppression fast response sprinklers were tested. 
Successful results were obtained when the HVLS fan was shut down upon the 
activation of the first sprinkler followed by a 90-second delay. Other methods 
of fan shutdown were also tested including shutdown by activation of air 
sampling-type detection and ionization-type smoke detectors. Earlier fan 
shutdown resulted in less commodity damage.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Mike Hairfield
Sent: Tuesday, October 23, 2018 6:03 AM
To: Sprinkler Forum 
Subject: Big Ass Fans


Local AHJ stated that if the fan is 20' wide (10' blades) it's an obstruction, 
these are 24' wide.



These are located in a warehouse with ESFR sprinkler systems.



How does one go about protecting the area below the Big Ass Fans to eliminate

the obstructions?



Thanks,



Mike
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sidewalls in Extra Hazard Occupancies

2018-09-26 Thread Mike Stossel
I am hopeful that in the future they will be able to expand on the criteria.  
In most of my projects they stack (3) or more cars, and in this case they are 
stacking (5).  It would be nice to have a solid direction to run in, but as for 
now we are putting a bandage on it with sidewalls between at each level.  Most 
of the fire sub-code officials have us do it as ordinary hazard group I, this 
is the first time that they have requested an extra hazard group II.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Steve Leyton
Sent: Wednesday, September 26, 2018 1:26 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sidewalls in Extra Hazard Occupancies

City of San Diego also enforces EH2.   Surprise - it's in the book.  Since 
we're using 2016 out here, we're already taking that for granted: A.5.4.2(9).

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Wednesday, September 26, 2018 10:03 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Sidewalls in Extra Hazard Occupancies

Thank you, that was extremely helpful.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Gus Olson
Sent: Wednesday, September 26, 2018 12:56 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Sidewalls in Extra Hazard Occupancies

The City of San Francisco has requirements just like you said.  Check out 
Administrative Bulletin 4.25

[cid:image007.png@01D4559D.A41D0A20]
Regards,
Gus Olson



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Wednesday, September 26, 2018 12:14 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Sidewalls in Extra Hazard Occupancies

I have a fire subcode official that is requesting sidewall sprinklers to be 
located at each level of an automobile car stacker.  The car stacker will have 
(4) levels of sidewalls located between each car and then an upright overhead 
system.  They are also requesting that the system be protected in accordance 
with extra hazard group II.  I could not find any allowance or sidewall 
sprinkler that is listed for extra hazard protection.  Does anyone know of a 
sidewall that is listed for extra hazard?

Thanks,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sidewalls in Extra Hazard Occupancies

2018-09-26 Thread Mike Stossel
Thank you, that was extremely helpful.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Gus Olson
Sent: Wednesday, September 26, 2018 12:56 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sidewalls in Extra Hazard Occupancies

The City of San Francisco has requirements just like you said.  Check out 
Administrative Bulletin 4.25

[cid:image004.png@01D45599.3A8C56A0]
Regards,
Gus Olson



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Wednesday, September 26, 2018 12:14 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Sidewalls in Extra Hazard Occupancies

I have a fire subcode official that is requesting sidewall sprinklers to be 
located at each level of an automobile car stacker.  The car stacker will have 
(4) levels of sidewalls located between each car and then an upright overhead 
system.  They are also requesting that the system be protected in accordance 
with extra hazard group II.  I could not find any allowance or sidewall 
sprinkler that is listed for extra hazard protection.  Does anyone know of a 
sidewall that is listed for extra hazard?

Thanks,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Sidewalls in Extra Hazard Occupancies

2018-09-26 Thread Mike Stossel
I have a fire subcode official that is requesting sidewall sprinklers to be 
located at each level of an automobile car stacker.  The car stacker will have 
(4) levels of sidewalls located between each car and then an upright overhead 
system.  They are also requesting that the system be protected in accordance 
with extra hazard group II.  I could not find any allowance or sidewall 
sprinkler that is listed for extra hazard protection.  Does anyone know of a 
sidewall that is listed for extra hazard?

Thanks,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Type V Construction & Hangers

2018-09-25 Thread Mike Stossel
Had this occur once a couple years ago in New Jersey.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of MFP Design, LLC
Sent: Tuesday, September 25, 2018 5:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Type V Construction & Hangers

Has anyone run into situations where the AHJ is requiring the structural 
engineer on a project to provide a sealed criteria letter for the project 
indicating the maximum hanger spacing based on pipe size and structural member? 
 We are seeing one local jurisdiction start to require this.

[MFP_logo_F]
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com>

http://www.mfpdesign.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D=0>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D=0>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Omission of sprinklers in hotel bathrooms

2018-09-24 Thread Mike Stossel
I believe they should be considered separate bathrooms as permitted by section 
3.3.2 and A.3.3.2.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Fox, Duane T. (FireMarshal)
Sent: Monday, September 24, 2018 10:48 AM
To: 'sprinklerforum@lists.firesprinkler.org' 

Subject: Omission of sprinklers in hotel bathrooms

I have a hotel project where the designer has placed a door inside the bathroom 
between the sink and toilet/shower.  The bathroom is over 55 sqft, however, 
with the placement of the door inside the bathroom each area on either side of 
the door is less than 55 sqft.  NFPA 13 – 8.15.8.1 states bathrooms under 55 
sqft are exempt (with other criteria met) and the appendix for that section 
states a door is not required in order to omit sprinkler as long as the 
bathroom complies with the definition for compartment. I assume the door in the 
appendix is between the bathroom and the living space.  My question: is adding 
a door inside the bathroom, making two areas within the bathroom, a viable 
design to allow the sprinklers to be omitted?

In my opinion the bathroom square footage is the entire area within the 
bathroom space no matter how many doors are used. Therefore, the space would 
need coverage.

Duane T. Fox, Jr., CFPS, CFI, CFPE
Asst Chief, Technical Services
DE State Fire Marshal’s Office
302-856-5298


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Fire Truck Supply @ FDC

2018-08-24 Thread Mike Stossel
You can include the city supply.  I typically set a fire pump up at the 
exterior of the building at the FDC location

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Jerry Van Kolken
Sent: Friday, August 24, 2018 4:23 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Truck Supply @ FDC

Is it just 150psi or is it 150 + city supply?

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bruce Verhei
Sent: Monday, September 12, 2016 2:19 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Fire Truck Supply @ FDC

Oh, and starting at something lower than eventual EP is more than adequate to 
let you find open standpipe ports, and close them. Why flood the stairwell more 
than necessary?

BV

On Sep 12, 2016, at 14:06, Bruce Verhei 
mailto:bver...@comcast.net>> wrote:
Most FD's use 150 psi as a near universal starting point. It's what an FDC 
basically says "start me at".

If nozzle is not too high above FDC this isn't too bad. If nozzle is a number 
of floors up the operator will be ready to provide water before its needed. And 
it gets all of the now compressed air out of the system.

But once water is flowing, the pump operator will do field calc's to get the 
appropriate real pressure. Our standard 1 3/4 hose packs used 135 psi for 
friction loss and nozzle pressure. I suspect cities with bigger footprint 
buildings would use a 200' instead of 150' hose pack, getting you back to ~150 
psi at gated wye (2 1/2" X 1 1/2" X 1 1/2") I know an alternative is 50' 2 1/2" 
then wye, then standpipe bundles.

Our standard was for head pressure was 5 psi per floor. For all you three 
significant digit folks, this actually works out pretty close for 10-12' 
storeys.

Field calc also includes friction loss between engine and FDC.

And our standard calc included 25 psi for friction loss in the standpipe 
system. I later decided that this was way too much, but fire experience belied 
the numbers. The scheme we used did not result in too high nozzle pressure. 
Usually more pressure was requested by radio. Eventually I decided that hose 
lines were much more liable to have kinks in this setting compared to homes, 
restaurants, repair garages and so on. Compare a kink to a 1" 90 in a 1 1/2" 
sprinkler line. Lots of friction loss in a very short run.

So I didn't send a note to Training telling them no, we weren't seeing 25 psi 
f.l. in a five story standpipe at 200 gpm.

NP + attack line FL + HP + 25 for standpipe and FDC + FL from engine to FDC = EP

To recap,
-150 psi to get water flowing,
-connect second 2 1/2" line to FDC and get it charged,
-do field hydraulics, increase engine pressure, and reset relief valve ( or 
governor)
-adjust up 20 psi per each request from attack companies. 20 psi is about 
minimum that is noticeable. During active fire fighting you will not get a 
request for less.

After control, at some point pressure will be adjusted way down, per request.

This is one FD's practice. It works well in low rise.

Best

Bruce Verhei

On Sep 12, 2016, at 13:00, Brian Harris 
mailto:bhar...@bvssystemsinc.com>> wrote:
Thanks guys, much appreciated.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: Monday, September 12, 2016 3:21 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Fire Truck Supply @ FDC

Is there a “standard” GPM @ PSI used for a standpipe calc with regard to what 
the fire truck will provide? I called the local AHJ and all he would say is 
they provide 150psi, didn’t know the gpm or even the hose size for that matter. 
Any help would be greatly appreciated.

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Reaming of pipe

2018-08-10 Thread Mike Stossel
According to NFPA 13 it is to minimize the reduction of the inside diameter and 
pieces dislodging and causing obstructions.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Hinson, Ryan
Sent: Thursday, August 9, 2018 8:46 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Schoenecker, Anthony (Tony) 
Subject: Reaming of pipe

What is the forum consensus on why threaded sprinkler piping is reamed.  I 
always did it as a fitter.  We have always required it in our specifications.  
I have never really thought about the ‘why’ though.  Is it as simple as 
removing the burr created when the pipe is cut and any potential ‘Klingons’ 
that might get sent downstream to a discharge device OR is this the proverbial 
“It’s always been done this way”?  The excerpts included below are what I could 
find on it with bolding added by me.

I’m not seeing where reaming is necessary for sprinkler piping.

NFPA 13 (2016) Section 6.5.1.1 states:

All threaded pipe and fittings shall have threads cut to ASME 
B1.20.1, Pipe Threads, General Purpose (Inch).

ASTM A135-09 Section 13 – Workmanship, Finish, and Appearance, states the 
following:

13.2.3 Ends, Threaded Pipe—Each end of threaded pipe shall be reamed to remove 
all burrs.  All threads shall be in accordance with the American National 
Standard Pipe Threads (Note 6) and cut so as to make a tight joint when the 
pipe is tested at the mill to the specified internal hydrostatic pressure…

NOTE 6—A complete description of the American National Standard Pipe Threads 
applicable to pipe, valves, and fittings is contained in ASME B1.20.1...

ASTM A53-10 Section 11 – End Finish:

11.2 If ordered with threaded ends, the pipe ends shall be provided with a 
thread in accordance with the gaging practice and tolerances of ANSI B1.20.1…

Reaming is not mentioned.

ASME B1.20.1-13 – Pipe Threads, General Purpose (Inch), does not mention 
reaming pipe.  Figure 3 and Table 2 do not show a reamed edge of the male end 
of the threaded pipe.

The following are the only ASTM or ASME pipe standard references I can find 
requiring reaming of pipe:

ASTM B0828-16 – Standard Practice for Making Capillary Joints by Soldering of 
Copper and Copper Alloy Tubing:

6.2 Reaming:
6.2.1 Ream all cut tube ends to the full inside diameter of the tube to remove 
the small burr created by the cutting operation.  Failure to remove this rough 
edge by reaming is a leading cause of erosion-corrosion that occurs as a result 
of local turbulence and increased local flow velocity in the tube.  A properly 
reamed piece of tube provides a smooth surface for better flow.

ASTM A589-06(12) – Standard Specification for Seamless and Welded Carbon Steel 
Water-Well Pipe – This does not apply.

Thoughts?

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Senior Fire Protection Engineer, Fire Protection Engineering Group
O 952-656-3662 \  M 320-250-5404 \  F 952-229-2923
rhin...@burnsmcd.com<mailto:rhin...@burnsmcd.com>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437

[cid:image001.png@01D024F0.1D126480]<https://www.linkedin.com/company/burns-&-mcdonnell>
  [cid:image002.png@01D024F0.1D126480] 
<https://www.facebook.com/BurnsMcDonnell>   
[cid:image003.png@01D024F0.1D126480] <https://twitter.com/BurnsMcDonnell>   
[cid:image004.png@01D024F0.1D126480] <https://www.youtube.com/user/burnsmcd>   
[cid:image005.png@01D024F0.1D126480] <http://www.burnsmcdblog.com/>   
[cid:image006.png@01D024F0.1D126480] 
<https://www.linkedin.com/profile/public-profile-settings?trk=prof-edit-edit-public_profile>
Proud to be one of FORTUNE’s 100 Best Companies to Work For
Please consider the environment before printing this email.
*Registered in: LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout
This email and any attachments are solely for the use of the addressed 
recipients and
may contain privileged client communication or privileged work product. If you 
are not the
intended recipient and receive this communication, please contact the sender by 
phone at
816-333-9400, and delete and purge this email from your email system and 
destroy any
other electronic or printed copies. Thank you for your cooperation.
[Logo_1_Primary_2Color_sm]
Create Amazing.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Remote Control Butterfly Valve

2018-08-03 Thread Mike Stossel
Does anyone know who makes a remote control butterfly valve listed for fire 
protection?  I have checked several of the manufacturers and have had no luck 
as of yet.

Thanks, for the help.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Flow Switch Maximum Surge

2018-07-31 Thread Mike Stossel
From my understanding what they are referring to is city water surges and the 
potential for false alarms.  If you anticipate surges to be greater you would 
install a retard chamber.  I don’t believe it is referring to the system in an 
actual flow situation.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of James Litvak
Sent: Tuesday, July 31, 2018 9:59 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Flow Switch Maximum Surge

All flow switch cut sheets show a maximum surge of 18 fps. Does this mean the 
velocity of my system at the flow switch has to have a max velocity of 18 fps?
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: HVLS Fan clearance

2018-07-27 Thread Mike Stossel
Would the AHJ possibly accept a disconnect for the fans when the sprinklers 
activate?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Matt Grise
Sent: Friday, July 27, 2018 12:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: HVLS Fan clearance

Any chance they could use some other type of fan that is not specifically HVLS?

Matt


From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Steve Leyton
Sent: Friday, July 27, 2018 11:13 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HVLS Fan clearance

Actually, this is a built condition (based on APPROVED PLANS, which doesn’t 
seem to matter much in some jurisdictions) and the unyielding inspector is 
insisting on dropping the fans.  Can’t affordably revise the sprinklers.

SL

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Friday, July 27, 2018 7:43 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: HVLS Fan clearance

It looks like the FPRF report that was used to guide NFPA 13 11.1.7 was 
entirely focused on high-piled storage, so it does seem like the requirements 
would be overkill here.

Most of the test failed when too many sprinklers opened. Would the AHJ be open 
to allowing the fans to be higher if you gave a larger design area? That could 
counter the main ‘failure’ source of the testing.

Matt


From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Steve Leyton
Sent: Thursday, July 26, 2018 7:02 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: HVLS Fan clearance

Good evening Forumites:

NFPA 13, 11.1.7 mandates that sprinklers be spaced symmetrically to a High 
Velocity/Low Speed fan, which may be up to 24’ in diameter, and sprinkler 
deflectors must be at least 3’ above the blades.

We are working on the redevelopment an industrial building with a wide loading 
dock that’s covered by an overhang with a ceiling at 11’-6” that will be a 
gathering space.  Several 8’ fans are positioned exactly centered between the 
sprinklers that are extended coverage and no closer to the edge of the blade 
pattern than 6’.  The AHJ is requiring that the 3’ must be observed and the 
fans look ridiculous hanging down at 8’-0” AFF.   So long as sprinklers are 
outside of conventional fan blade circles, there’s no minimum vertical 
deflector clearance in the obstruction criteria for spray and residential 
sprinklers and it seems to me that the 3’ clearance is overkill in this 
particular application.

Does anyone have any experience or are there any other studies out there 
besides the one from NFPA/FPRF that shed light on the acceptability of 
sprinklers at less than 3’ vertically above blades where the sprinklers are 
outside the blade circle?

Steve L.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Fire Proofing joists

2018-07-25 Thread Mike Stossel
Would it need to extend the entire length of the bar joist or is the 30% based 
on the entire area of the joist?  When the final bar returned to the deck it 
was creating an open triangle at the ends of the joist so the bay is not 
created and would connect to the adjacent bay.  Does this still comply with the 
30%?

Thanks,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Roland Huggins
Sent: Wednesday, July 25, 2018 3:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Fire Proofing joists

I'll take a shot at this but note I’m shooting from the hip (translation - 
leaves me an out incase there is something I think of later or a Forumite 
comment that might chnage my opinion).  Allow me to start with stating that 
this requirement has been in the standard longer than my short tenure on NFPA 
13 so I can’t elaborate on why 30% was the selected line in the sand.  It is a 
reasonable number though when viewed more so through the perspective of the 
impact on the discharge pattern (versus activation).

Fortunately the question is why is there a difference between the integrity of 
the boundary between regular obstructed construction and its sub-family panel 
construction.  I might add that we did bring this issue on panel construction 
to the attention of the committee.  When we have structural members greater 
than 7.5 ft apart but they form a pocket that is no greater than 300 sf, it’s 
going to capture heat and impact the activation of the sprinklers.  Since the 
ability to capture heat is a function of the integrity of the boundaries, there 
you go.

NFPA dictated caveat: this opinion is mine (and maybe mine alone) and should 
not be considered a formal interpretation of NFPA or any of its technical 
committees.

Roland

Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.
Dallas, TX
http://www.firesprinkler.org<http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




On Jul 25, 2018, at 9:26 AM, Kyle.Montgomery 
mailto:kmontgom...@aerofire.com>> wrote:

Somewhat of a sidetrack:

Can someone explain to me why bar joists with fire proofing can be considered 
obstructed construction when they are 69% open, with no apparent restrictions 
on joist spacing, depth, etc but for panel construction "there should be no 
unfilled penetrations in the cross-sectional area of the bounding structural 
members, including the interface at the roof"?

-Kyle M

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Fire Proofing joists

2018-07-25 Thread Mike Stossel
Out of curiosity as I have never seen fireproofing done in this way.  Could you 
consider it as obstructed construction or just an obstruction?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Prahl, Craig/GVL
Sent: Wednesday, July 25, 2018 10:24 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Fire Proofing joists

When it’s sprayed solid like that it’s an obstruction since it interferes with 
the discharge pattern.

When I’ve dealt with it, the GC wanted us to place all our hangers on the 
joists before they were sprayed so we didn’t damage the integrity of the 
coating by chipping it away to place clamps.  Be sure they don’t stick you with 
repair costs from you having to get through that stuff to place beam clamps.



Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Phillips, Mark
Sent: Wednesday, July 25, 2018 10:15 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] Fire Proofing joists

Greetings
I would like to get options on a trend we have been seeing in our area of the 
country.
Fire proofers have been utilizing a system of mesh secured to open joists then 
spraying on fire proofing. The joists can either be closely spaced or 5 to 7 
feet apart.

The question is should the mesh then be considered a solid obstruction? There 
is no consistency on the spay insulation it’s just spray and go. We are also 
being told by the GC that we must wait to hang till the fire proofing is 
complete and we cannot be located in the joists. (picture attached)

I would like to hear opinions and others experiences with this situation.

Thanks in advance


Sent from 
Mail<https://urldefense.proofpoint.com/v2/url?u=https-3A__go.microsoft.com_fwlink_-3FLinkId-3D550986=DwMFaQ=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI=9g3YkXH_KWe9tuUgCaH0ezuQimPIr14lVpqPdDon1N4=6OHYVzdEkp-rqgLcLINMzFCTPr93lxdu1M0JrRDF7nQ=>
 for Windows 10

[cid:image002.jpg@01D42403.21B13370]

Mark​



Phillips


Vice President of Fire Protection

,

Kirlin Carolinas, LLC



t: 919-526-1584

 |

m: 919-610-0490


mphill...@jjkllc.com<mailto:mphill...@jjkllc.com>

 |

https://kirlingroup.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__kirlingroup.com_=DwMFaQ=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI=9g3YkXH_KWe9tuUgCaH0ezuQimPIr14lVpqPdDon1N4=_AIcjetubLiHbRYD-urw2wD3nwDoMUVzvcJD7xwxqmI=>


8000 Brownleigh Dr

,

Raleigh

,

NC



27617



[cid:image003.png@01D42403.21B13370]<https://urldefense.proofpoint.com/v2/url?u=https-3A__twitter.com_KirlinGroup=DwMFaQ=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI=9g3YkXH_KWe9tuUgCaH0ezuQimPIr14lVpqPdDon1N4=6A5yPbug14iivLxqin37xxfzXWQS-tnfLCBzh41TuZY=>


[cid:image004.png@01D42403.21B13370]<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.facebook.com_kirlinllc=DwMFaQ=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI=9g3YkXH_KWe9tuUgCaH0ezuQimPIr14lVpqPdDon1N4=eEPNrmUz_VsZyQKLpqey-nrrB_JIO2Ox8hRcJcuNyo4=>


[cid:image005.png@01D42403.21B13370]<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.linkedin.com_company_133201_=DwMFaQ=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI=9g3YkXH_KWe9tuUgCaH0ezuQimPIr14lVpqPdDon1N4=Pthw0wm2fIf5PWFexzvbhRRevVxmK_8s-8kwEntNkRc=>






[cid:image006.jpg@01D42403.21B13370]<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.surveymonkey.com_r_KirlinCarolinaSurvey=DwMFaQ=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI=9g3YkXH_KWe9tuUgCaH0ezuQimPIr14lVpqPdDon1N4=E4tEecbsT0gruViHuNZEXcEwYatv6-sDyBkiu7b0weY=>

[cid:image007.jpg@01D42403.21B13370]<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.kirlingroup.com_join-2Dour-2Dteam-2Dcareers_-23opportunity=DwMFaQ=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI=9g3YkXH_KWe9tuUgCaH0ezuQimPIr14lVpqPdDon1N4=wew5e2SoOmDef4VxFVh88fyk80LaEyx0Z2NfVY7fQcw=>

[cid:image008.jpg@01D42403.21B13370]<https://urldefense.proofpoint.com/v2/url?u=https-3A__kirlingroup.com_=DwMFaQ=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI=9g3YkXH_KWe9tuUgCaH0ezuQimPIr14lVpqPdDon1N4=_AIcjetubLiHbRYD-urw2wD3nwDoMUVzvcJD7xwxqmI=>







NOTICE - This communication may contain confidential and privileged information 
that 

RE: Robotic Parking

2018-07-13 Thread Mike Stossel
Travis is definitely right.  We have a concept we use in NYC, as we run into 
this all the time, and in fact I am working on a building right now that is 
four level stackers.  With that being said it is always a best guess without 
the guidance and the EOR should guide you.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Travis Mack
Sent: Friday, July 13, 2018 11:47 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Robotic Parking

You are going to have to get the EOR that created your “engineered” drawing 
involved to give you a hazard since it doesn’t seem to be addressed in NFPA 13.

You may want to try to contact the company that designed the robotic car system 
and see if they can give any guidance.

I bet your EOR has a comment to design to NFPA 13 and figures he is off the 
hook. Just kick it back to them.

It’s Friday. Make it his weekend project to do his job of giving the proper 
criteria. I bet that goes over well.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Jul 13, 2018, at 8:40 AM, John Irwin 
mailto:jo...@cfcsystems.com>> wrote:
This is 7 levels of cars stacked vertically. We are in the 2013 edition of NFPA 
13.



John Irwin, C.E.T. – jo...@cfcsystems.com<mailto:jo...@cfcsystems.com>
Commercial Fire and Communications
Fire Sprinkler Specialist – NICET ID: 134153
Cell: 727-282-9243

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack
Sent: Friday, July 13, 2018 11:38 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Robotic Parking

If this is the “car stackers” mentioned in 2016 edition, then it is only for 2 
levels high.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Jul 13, 2018, at 8:35 AM, Nick Maneen 
mailto:nman...@sentryfp.com>> wrote:
2016 Edition of 13 calls these Extra Hazard. These are a challenge to say the 
least. Good luck. I wish I had a better answer for you.
Nick Maneen
704-791-7789

On Fri, Jul 13, 2018, 11:33 AM John Irwin 
mailto:jo...@cfcsystems.com>> wrote:
Anyone have any experience with these new robotic parking buildings? My 
“engineered” plans are pretty bad. No hazard is given. I am going to assume the 
same as a parking garage? I don’t see this as being too challenging, but I am 
wondering if there is some huge pitfall that I am not aware of. It’s pretty 
much 7 floors of this ….



The top floor doesn’t show the center area protected. I’m wondering if it needs 
to be …

John Irwin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Robotic Parking

2018-07-13 Thread Mike Stossel
NFPA does not have any guidance for stackers that high, like Travis had said it 
is only good up to two.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of John Irwin
Sent: Friday, July 13, 2018 11:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Robotic Parking

This is 7 levels of cars stacked vertically. We are in the 2013 edition of NFPA 
13.



John Irwin, C.E.T. – jo...@cfcsystems.com<mailto:jo...@cfcsystems.com>
Commercial Fire and Communications
Fire Sprinkler Specialist – NICET ID: 134153
Cell: 727-282-9243

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack
Sent: Friday, July 13, 2018 11:38 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Robotic Parking

If this is the “car stackers” mentioned in 2016 edition, then it is only for 2 
levels high.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Jul 13, 2018, at 8:35 AM, Nick Maneen 
mailto:nman...@sentryfp.com>> wrote:
2016 Edition of 13 calls these Extra Hazard. These are a challenge to say the 
least. Good luck. I wish I had a better answer for you.
Nick Maneen
704-791-7789

On Fri, Jul 13, 2018, 11:33 AM John Irwin 
mailto:jo...@cfcsystems.com>> wrote:
Anyone have any experience with these new robotic parking buildings? My 
“engineered” plans are pretty bad. No hazard is given. I am going to assume the 
same as a parking garage? I don’t see this as being too challenging, but I am 
wondering if there is some huge pitfall that I am not aware of. It’s pretty 
much 7 floors of this ….

[cid:image003.png@01D41A9E.74D94CE0]

The top floor doesn’t show the center area protected. I’m wondering if it needs 
to be …

John Irwin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Robotic Parking

2018-07-13 Thread Mike Stossel
Is this regarding stackers on multiple levels or a stacker that has (7) levels 
of cars?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of John Irwin
Sent: Friday, July 13, 2018 11:34 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Robotic Parking

Anyone have any experience with these new robotic parking buildings? My 
"engineered" plans are pretty bad. No hazard is given. I am going to assume the 
same as a parking garage? I don't see this as being too challenging, but I am 
wondering if there is some huge pitfall that I am not aware of. It's pretty 
much 7 floors of this 

[cid:image002.png@01D41A9D.ACCCD640]

The top floor doesn't show the center area protected. I'm wondering if it needs 
to be ...

John Irwin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Airline feeds to freezers

2018-07-03 Thread Mike Stossel
Yes it would be an upright 25.2, and your right all of the storage and 
discharge requirements appear to be based on FMG.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Mike Stossel
Sent: Tuesday, July 3, 2018 2:36 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Airline feeds to freezers

I believe it was Viking and as far as I know they are still made.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Matt Grise
Sent: Tuesday, July 3, 2018 2:34 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Airline feeds to freezers

Do they still make the ESFR that is specially listed for use with anti-freeze? 
I can’t remember who made that system…

Matt

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Ben Young
Sent: Tuesday, July 03, 2018 1:28 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Airline feeds to freezers

Mike, I assume you mean the V4603 25.2K upright, correct?
That won't fly as the AHJ does not recognize FMG protection schemes unless they 
meet or exceed NFPA. Its a whole thing that will not likely change, so this is 
a non-option.
Matt,
You can use bottled nitrogen (and we were planning on doing that to initially 
fill the system instead of the quick fill on the N2 generator) but per my 
reading of 7.9.2.7 you still have to run a line thru the freezer for ice plug 
checks.
I'm with you, it makes no sense since you should never see an ice plug with N2, 
but the code is the code.


Benjamin Young

On Tue, Jul 3, 2018 at 2:19 PM, Mike Stossel 
mailto:m...@knssprinkler.com>> wrote:
Ben,

Would it help in anyway if you used the Victaulic LP46 heads?  You maybe able 
to protect the freezers and the dry storage areas with the same dry pipe valve 
without in-rack sprinklers.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Ben Young
Sent: Tuesday, July 3, 2018 2:03 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Airline feeds to freezers

I'm doing a blast freezer that sits about 150 feet remotely from where the 
riser is located.
I'm doing a DIPA with IRAS. If you really want to know, its a class 3 commodity 
stored in multiple-row racks 26' wide. Bldg is 25 feet to roof, storage height 
is 20 feet.
This is in the northeast, so running ESFR is a non-starter.

This is being done under the 2013 edition of the code, and I'm having some 
issues with trying to comply with the stuff in 7.9, especially 7.9.2.7
First, my DIPA requires the air tie-in to be fed from the system trim (DDX) so 
using figure 7.9.2.7.1.1(a) is out. So my air supply run just doubled in length.
Now, there are other freezers on the way to this freezer that are a lot closer. 
Could I put my air lines in that freezer and still meet the intent of 7.9.2.7, 
or is this going to be too confusing to have the ice plug check lines in 
another location?
Please do not suggest relocating the pre-action valve closer to the freezer, 
this isn't an option for the owner.
Secondly, who thought it was OK to allow nitrogen systems to only require one 
ice plug check line? If the N2 system can't keep up with the demand or has 
other issues it will start pumping in the same moist air direct from its air 
compressor and be no different. I don't get that, but OK.
I'm pretty much 100% committed at this point to using a Dry Air Pack since I 
don't have to run an intake line over to the cooler either. I haven't seen 
anything on this being allowed on N2 systems unless they're listed for freezer 
use. Does that exist?
Here's some other info:
We are also doing a dry system for a dry-goods storage warehouse that sits next 
to the new freezer. Both are only connected to other freezers and coolers on 
the property, so there is no other room or place to put our valves besides the 
existing pump room. We are also running all this bulk pipe outside! Mainly 
along exposed exterior building columns (don't know how that happens, but I'm 
not going to look a gift horse in the mouth) and then we will have to install a 
couple of pipe stands. This is all galvanized, and will be the two mains: one 
for dry and one for DIPA. Owner doesn't want DIPA for the dry goods warehouse 
because of detection and expense for IRAS detection.
And of course, estimator didn't figure on ru

RE: Airline feeds to freezers

2018-07-03 Thread Mike Stossel
I believe it was Viking and as far as I know they are still made.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Matt Grise
Sent: Tuesday, July 3, 2018 2:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Airline feeds to freezers

Do they still make the ESFR that is specially listed for use with anti-freeze? 
I can’t remember who made that system…

Matt

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Ben Young
Sent: Tuesday, July 03, 2018 1:28 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Airline feeds to freezers

Mike, I assume you mean the V4603 25.2K upright, correct?
That won't fly as the AHJ does not recognize FMG protection schemes unless they 
meet or exceed NFPA. Its a whole thing that will not likely change, so this is 
a non-option.
Matt,
You can use bottled nitrogen (and we were planning on doing that to initially 
fill the system instead of the quick fill on the N2 generator) but per my 
reading of 7.9.2.7 you still have to run a line thru the freezer for ice plug 
checks.
I'm with you, it makes no sense since you should never see an ice plug with N2, 
but the code is the code.


Benjamin Young

On Tue, Jul 3, 2018 at 2:19 PM, Mike Stossel 
mailto:m...@knssprinkler.com>> wrote:
Ben,

Would it help in anyway if you used the Victaulic LP46 heads?  You maybe able 
to protect the freezers and the dry storage areas with the same dry pipe valve 
without in-rack sprinklers.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Ben Young
Sent: Tuesday, July 3, 2018 2:03 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Airline feeds to freezers

I'm doing a blast freezer that sits about 150 feet remotely from where the 
riser is located.
I'm doing a DIPA with IRAS. If you really want to know, its a class 3 commodity 
stored in multiple-row racks 26' wide. Bldg is 25 feet to roof, storage height 
is 20 feet.
This is in the northeast, so running ESFR is a non-starter.

This is being done under the 2013 edition of the code, and I'm having some 
issues with trying to comply with the stuff in 7.9, especially 7.9.2.7
First, my DIPA requires the air tie-in to be fed from the system trim (DDX) so 
using figure 7.9.2.7.1.1(a) is out. So my air supply run just doubled in length.
Now, there are other freezers on the way to this freezer that are a lot closer. 
Could I put my air lines in that freezer and still meet the intent of 7.9.2.7, 
or is this going to be too confusing to have the ice plug check lines in 
another location?
Please do not suggest relocating the pre-action valve closer to the freezer, 
this isn't an option for the owner.
Secondly, who thought it was OK to allow nitrogen systems to only require one 
ice plug check line? If the N2 system can't keep up with the demand or has 
other issues it will start pumping in the same moist air direct from its air 
compressor and be no different. I don't get that, but OK.
I'm pretty much 100% committed at this point to using a Dry Air Pack since I 
don't have to run an intake line over to the cooler either. I haven't seen 
anything on this being allowed on N2 systems unless they're listed for freezer 
use. Does that exist?
Here's some other info:
We are also doing a dry system for a dry-goods storage warehouse that sits next 
to the new freezer. Both are only connected to other freezers and coolers on 
the property, so there is no other room or place to put our valves besides the 
existing pump room. We are also running all this bulk pipe outside! Mainly 
along exposed exterior building columns (don't know how that happens, but I'm 
not going to look a gift horse in the mouth) and then we will have to install a 
couple of pipe stands. This is all galvanized, and will be the two mains: one 
for dry and one for DIPA. Owner doesn't want DIPA for the dry goods warehouse 
because of detection and expense for IRAS detection.
And of course, estimator didn't figure on running any extra air line piping 
since he threw an N2 system on there! So no I'm trying to figure out a cost 
efficient way of meeting the code on this one. Oh wait, isn't that what we do 
every day anyway?
And hey, if you can't help me out on this one, no sweat (haha) and enjoy our 
4th of July tomorrow.!
Thanks all,
Ben Young


Benjamin Young

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.o

RE: Airline feeds to freezers

2018-07-03 Thread Mike Stossel
Ben,

Would it help in anyway if you used the Victaulic LP46 heads?  You maybe able 
to protect the freezers and the dry storage areas with the same dry pipe valve 
without in-rack sprinklers.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Ben Young
Sent: Tuesday, July 3, 2018 2:03 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Airline feeds to freezers

I'm doing a blast freezer that sits about 150 feet remotely from where the 
riser is located.
I'm doing a DIPA with IRAS. If you really want to know, its a class 3 commodity 
stored in multiple-row racks 26' wide. Bldg is 25 feet to roof, storage height 
is 20 feet.
This is in the northeast, so running ESFR is a non-starter.

This is being done under the 2013 edition of the code, and I'm having some 
issues with trying to comply with the stuff in 7.9, especially 7.9.2.7
First, my DIPA requires the air tie-in to be fed from the system trim (DDX) so 
using figure 7.9.2.7.1.1(a) is out. So my air supply run just doubled in length.
Now, there are other freezers on the way to this freezer that are a lot closer. 
Could I put my air lines in that freezer and still meet the intent of 7.9.2.7, 
or is this going to be too confusing to have the ice plug check lines in 
another location?
Please do not suggest relocating the pre-action valve closer to the freezer, 
this isn't an option for the owner.

Secondly, who thought it was OK to allow nitrogen systems to only require one 
ice plug check line? If the N2 system can't keep up with the demand or has 
other issues it will start pumping in the same moist air direct from its air 
compressor and be no different. I don't get that, but OK.
I'm pretty much 100% committed at this point to using a Dry Air Pack since I 
don't have to run an intake line over to the cooler either. I haven't seen 
anything on this being allowed on N2 systems unless they're listed for freezer 
use. Does that exist?

Here's some other info:
We are also doing a dry system for a dry-goods storage warehouse that sits next 
to the new freezer. Both are only connected to other freezers and coolers on 
the property, so there is no other room or place to put our valves besides the 
existing pump room. We are also running all this bulk pipe outside! Mainly 
along exposed exterior building columns (don't know how that happens, but I'm 
not going to look a gift horse in the mouth) and then we will have to install a 
couple of pipe stands. This is all galvanized, and will be the two mains: one 
for dry and one for DIPA. Owner doesn't want DIPA for the dry goods warehouse 
because of detection and expense for IRAS detection.
And of course, estimator didn't figure on running any extra air line piping 
since he threw an N2 system on there! So no I'm trying to figure out a cost 
efficient way of meeting the code on this one. Oh wait, isn't that what we do 
every day anyway?
And hey, if you can't help me out on this one, no sweat (haha) and enjoy our 
4th of July tomorrow.!
Thanks all,
Ben Young


Benjamin Young
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Fire Department Connections

2018-06-22 Thread Mike Stossel
I believe Potter Roemer carries them.  I have previously gotten one rated for 
500psi from them.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of James Crawford
Sent: Friday, June 22, 2018 1:21 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Fire Department Connections

Can anyone point me in the right direction.

We are looking for a fire department connection that is listed for more than 
300 pounds.


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca<mailto:jcrawf...@phaserfire.ca>
Web www.phaserfire.ca<http://www.phaserfire.ca>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 3" FDC

2018-06-01 Thread Mike Stossel
This is typical for my New York City clients.  Most of them use a 3"x3"x6" 
flush mount made by Croker.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Michael Goodis
Sent: Friday, June 1, 2018 3:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: 3" FDC

They don't make one, and the cloest you will find is a 3"" pipe to the FDC 
Snoot/Connection.   But it will still be 2 ½".

Good luck.

Michael Goodis
Salesman, Project Manager
IL#000635   NICET#135586
Key Fire Protection Enterprises LLC
3200 Mike Padgett HWY
Augusta, GA 30906
Office- (706) 790-3473
Cell- (706) 220-8822
Fax: (706) 738-2119



From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Richard Mote
Sent: Friday, June 1, 2018 3:28 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: 3" FDC

Here's another one for the books AHJ requires a 3" Siamese Fire Department 
Connection. I've checked Manufactures so far and am sticking out. Below is the 
exact text of their response. Anyone got any brilliant ideas?



A. The required Fire Department Connection (FDC) for Plymouth Township is a 
Siamese 3" female
NST with covers. The location indicated is acceptable.

Richard Mote
Design Manager
[http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg]
W: 877.324.ROWE  *  F: 570.837.6335  *  C:570.541.2685
PO Box 407  *  7993 US Route 522, Suite 1  *  Middleburg, PA 17842
505A Cornerstone Court  *  Hillsborough, NC 27278
RoweSprinkler.com  *  
rich...@rowesprinkler.com<mailto:rich...@rowesprinkler.com>

*** Confidentiality Notice ***
This email and any attachments thereto may contain information that is 
privileged and confidential and is intended only for the use of the addressee. 
If the reader of the message is not the intended recipient or an authorized 
representative of the intended recipient, you are hereby notified that any 
dissemination of this communication is strictly prohibited. If you have 
received this communication in error, please notify us immediately by e-mail at 
rich...@rowesprinkler.com<mailto:rich...@rowesprinkler.com> or by telephone at 
570-837-7647 and delete the message and any attachments permanently from your 
system.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Ceiling Grids and Flex Drops

2018-05-30 Thread Mike Stossel
In the installation manual it specifically says for use on ceiling suspension 
systems installed in accordance with ASTM C635 and ASTM C636.  Is the AHJ 
looking for something specific or did they not read the installation manual?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of Richard Mote
Sent: Wednesday, May 30, 2018 11:59 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Ceiling Grids and Flex Drops

I have a AHJ that is questioning the use of Flex Drops especially the Victaulic 
ones. He says that they are so flexible that when a sprinkler goes off the jet 
effect is going to lift the sprinkler up through the ceiling. I told him that 
the drops are mechanically attached to the ceiling grid and in order to lift up 
they would have to lift the entire weight of the ceiling grid, ceiling tiles, 
the lights and HVAC diffusers. His answer prove, it either by letter from the 
manufacturer or from someone a lot higher up the food chain than either he or I 
am. Or something specific in NFPA 13 that says he is wrong.

Richard Mote
Design Manager
[http://www.rowesprinkler.com/emailsig/Email_Sig_Logo.jpg]
W: 877.324.ROWE  *  F: 570.837.6335
PO Box 407 * 7993 US Route 522, Suite 1 * Middleburg, PA 17842
505 A Cornerstone Court * Hillsborough, NC 27278
RoweSprinkler.com  *  
rich...@rowesprinkler.com<mailto:rich...@rowesprinkler.com>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: ESFR closer than 8'

2018-05-30 Thread Mike Stossel
Is the building 30'0" high or lower?  If so would expanding your spacing to 
12'0" help?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum  On Behalf 
Of JD Gamble
Sent: Wednesday, May 30, 2018 11:07 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: ESFR closer than 8'

I need some clarity on this one 

Spacing ESFR 25.2K PNTs on 10 x 10 spacing in 30' bays @ 16" below ceiling.  
Line are equally spaced 5' from center of 36" deep beams.  I have an area where 
a full height wall is 11'-6" from a beam requiring an additional row of ESFR.  
When spacing the additional sprinklers at 8' between branch lines it places the 
additional sprinklers less than 8' from the adjacent line along the other side 
of the solid steel beam.  Is the beam sufficient (only 20" below the sprinkler) 
to prevent skipping?  Can I be less than minimum spacing (64sq.ft.) with the 
beam separating sprinklers?

Scratching my head here.

Life Safety Solutions of Sheridan

JD Gamble
jgam...@lssofsheridan.com<mailto:jgam...@lssofsheridan.com>
(307) 763-3361

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sprinkler 1/2" Extension Nipples

2018-05-14 Thread Mike Stossel
Yes, I believe the language was added in the 2016 edition section 6.4.8 
allowing up to a 2" single fitting length without including them in the 
hydraulic calculation.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Mike Hairfield
Sent: Monday, May 14, 2018 9:37 AM
To: Sprinkler Forum <sprinklerforum@lists.firesprinkler.org>
Subject: Sprinkler 1/2" Extension Nipples


Are 1/2" Sprinkler Extension Nipples allowed in NFPA-13 to be used when 
changing out

existing concealed sprinklers with new concealed sprinklers?
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Software

2018-05-10 Thread Mike Stossel
I am having a tremendous amount of problems performing 3D coordination's.  It 
is taking me approximately 3 times longer than the old flat way of a standard 
coordination overlay.  I know a lot of you are using AutoSprink and HydraCAD, 
but I am not.  I am a SprinkCAD user and at this time cannot switch to another 
platform.  I use Navisworks Freedom viewer to see the clash locations, and do 
the best I can to measure and move out of the way and submit the new model to 
see if I guessed right.  I did not switch to SprinkCAD 3D as of yet as I have 
not had time to build a brand new database that incorporates products other 
than what TYCO supports.  In all honesty I don't know that it would make any 
difference as it appears that I would be doing the same guess work that I am 
doing now.

Does anyone else on the forum use SprinkCAD or have you all switched over?  If 
you are a SprinkCAD user did you switch to the 3D version and was it helpful 
and worth all the time of constructing a new database?  Does anyone have any 
helpful hints on how to speed up the process or is it just me or the software 
that I am using?  I am OK with hearing that it is just me, that means that I 
just have to work harder at it and constructive criticism is always welcome.  
It just seems that something that was supposed to be better, it is much more 
difficult and time consuming and that you almost can't charge enough money to 
cover the time it takes.  I know I have to embrace it as this is the future, 
but I am really struggling with it.

Thanks and any help that anyone can offer would be greatly appreciated.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Supply calculation for manual-wet standpipe

2018-04-17 Thread Mike Stossel
Yes, you can add in the water supply to the suction side of the pump.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Matt Grise
Sent: Tuesday, April 17, 2018 9:46 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Supply calculation for manual-wet standpipe

Is that 150psi of pressure boost? So if you put in 50psi, you can get 200 @ 
1000 out?

Matt


From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Mike Stossel
Sent: Tuesday, April 17, 2018 8:44 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Supply calculation for manual-wet standpipe

I believe to be certified under the guidelines of NFPA 1901 the minimum the 
pumper would supply is 150psi @1,000gpm, 200psi @ 750gpm and 250psi @ 500gpm.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Travis Mack
Sent: Tuesday, April 17, 2018 9:41 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Supply calculation for manual-wet standpipe

Demand was only 750. Typically pumper truck will deliver more psi at only 750 
gpm.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Apr 17, 2018, at 6:35 AM, Rocci 3 Cetani 
<roc...@norcalfire.com<mailto:roc...@norcalfire.com>> wrote:
Looks like hydra cad and also looks like he is over the standard pumper trucks  
150 PSI…..unless your pumper trucks pump more than 150 PSI I would have him 
look at it again

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590


roc...@norcalfire.com<mailto:roc...@norcalfire.com>
www.norcalfire.com<http://www.norcalfire.com/>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information
belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Matt Grise
Sent: Tuesday, April 17, 2018 6:20 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Supply calculation for manual-wet standpipe

What software package is it?

Matt



From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Dewayne Martinez
Sent: Tuesday, April 17, 2018 7:39 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Dewayne Martinez 
<dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>>
Subject: RE: Supply calculation for manual-wet standpipe

I am not used to seeing this calc program so I may be looking at this wrong but 
I don’t see a water supply on this graph.


Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/


From: Dewayne Martinez 
<dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>>
Sent: Tuesday, April 17, 2018 6:42 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Dewayne Martinez 
<dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>>
Subject: RE: Supply calculation for manual-wet standpipe

I initially put in a supply of 150psi at 1000gpm and then modify it until I get 
a 0 PSI cushion.

Dewayne Martinez
Fire Protection Design Manager

TO

RE: Supply calculation for manual-wet standpipe

2018-04-17 Thread Mike Stossel
I believe to be certified under the guidelines of NFPA 1901 the minimum the 
pumper would supply is 150psi @1,000gpm, 200psi @ 750gpm and 250psi @ 500gpm.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Travis Mack
Sent: Tuesday, April 17, 2018 9:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Supply calculation for manual-wet standpipe

Demand was only 750. Typically pumper truck will deliver more psi at only 750 
gpm.
Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Apr 17, 2018, at 6:35 AM, Rocci 3 Cetani 
<roc...@norcalfire.com<mailto:roc...@norcalfire.com>> wrote:
Looks like hydra cad and also looks like he is over the standard pumper trucks  
150 PSI…..unless your pumper trucks pump more than 150 PSI I would have him 
look at it again

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590


roc...@norcalfire.com<mailto:roc...@norcalfire.com>
www.norcalfire.com<http://www.norcalfire.com/>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may 
contain confidential information
belonging to the sender. The information is intended only for the use of 
individual or entity named above. If you are not the intended recipient, or the 
employee or agent responsible to deliver this message to the intended 
recipient, you are hereby notified that any disclosure, copying or taking of 
any action in reliance on the contents of this information is strictly 
prohibited. If you have received this transmission in error, please immediately 
notify us by telephone to arrange for return of the documents.

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Matt Grise
Sent: Tuesday, April 17, 2018 6:20 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Supply calculation for manual-wet standpipe

What software package is it?

Matt



From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Dewayne Martinez
Sent: Tuesday, April 17, 2018 7:39 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Dewayne Martinez 
<dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>>
Subject: RE: Supply calculation for manual-wet standpipe

I am not used to seeing this calc program so I may be looking at this wrong but 
I don’t see a water supply on this graph.


Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/


From: Dewayne Martinez 
<dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>>
Sent: Tuesday, April 17, 2018 6:42 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Dewayne Martinez 
<dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>>
Subject: RE: Supply calculation for manual-wet standpipe

I initially put in a supply of 150psi at 1000gpm and then modify it until I get 
a 0 PSI cushion.

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/


From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Matt Grise
Sent: Tuesday, April 17, 2018 6:26 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Supply calculation for manual-wet standpipe

When you say that  you tweak it to find the actual demand – does your software 
not tell you the psi input required to supply the hose demand you request at 
the standpipe outlets? I usually see ‘required pressure’ as an output of the 
software no matter what the input is.

Matt


From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Dewayne Martinez
S

RE: Residential water storage

2018-03-20 Thread Mike Stossel
This is true, but it is an unrequired secondary supply for the house.  The 
house has a public water supply that is primary to the residence, the fire pump 
would only be used in the case of an emergency.  

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Phong - Indochine Engineering
Sent: Monday, March 19, 2018 10:51 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

Note at the time that water of the swimming pool is being drained out for 
replacing, there will be no water supplied to the fire pump.

Regards,
Le Vu Phong
Mobile:  +84 (0) 902 363 525

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: 19 March, 2018 9:42 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

Yes. You could get your water supply and positive pressure to the pump at the 
same time.  I would assume a house that size would have a big enough pool to 
satisfy the demand of the system.   

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of John Irwin
Sent: Monday, March 19, 2018 10:38 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

Are you suggesting I use the pool as my water supply?

John Irwin
DynaFire Inc.

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Mike Stossel
Sent: Monday, March 19, 2018 10:36 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

I assume a house that large has a swimming pool.  Is the pump equipment located 
in a pool house or in the basement?  If it is in the basement you maybe able to 
cut a tee into one of the lines to gain a supply to a standard residential pump.

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of John Irwin
Sent: Monday, March 19, 2018 10:33 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

Yeah .. that's a concern I have as well.

John Irwin
DynaFire Inc.

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Matt Grise
Sent: Monday, March 19, 2018 10:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

When I hear 'hurricane', I also think swampy soil. It might be worth looking 
into the logistics of a buried tank. It would be a bummer if it popped out of 
the ground during a hurricane.

Matt


-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Vince Sabolik
Sent: Monday, March 19, 2018 9:25 AM
To: sprinklerforum@lists.firesprinkler.org; John Irwin <john.ir...@dynafire.com>
Subject: Re: Residential water storage

Bury a pressure tank

On 3/19/2018 9:41 AM, John Irwin wrote:
> I swear after 25 years in sprinklers I am amazed at how often new 
> situations are still presented to me …
>
>
>
> Here’s my situation … 22,000 sqft single family home. The owners lost 
> water completely in the last hurricane and want to make sure that the 
> new sprinkler system will continue to have a water supply if this 
> happens again. So they want to bury a grey water tank in the yard 
> that’s specifically for fire sprinkler supply. What considerations do 
> I even start with on this? It’s a 13D system, so do I have to take 
> NFPA 22 into consideration? How do I get water out of an underground 
> tank? Standard well pump? Should I not even bother with a city supply 
> if I am feeding off of a tank? Obviously money doesn’t seem to be a 
> consideration …
>
>
>
>
>
>
>
>
>
>
>
> John Irwin
>
> Fire Sprinkler Specialist
>
> DynaFire, Inc.
>
> 727-282-9243 – Cell
>
>
>
> *“A customer is the most important visitor on our premises. He is not 
> dependent on us. We are dependent on him. He is not an interruption on 
> our work. He is the purpose of it. He is not an outsider on our 
> business. He is a part of it. We are not doing him a favour by serving 
> him. He is doing us a favour by giving us an opportunity to do so.”*
> -- next part -- An HTML attachment was 
> scrubbed...
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
> er.org/attachments/20180319/3cc2de75/attachment.html>
> ___

RE: Residential water storage

2018-03-19 Thread Mike Stossel
Yes. You could get your water supply and positive pressure to the pump at the 
same time.  I would assume a house that size would have a big enough pool to 
satisfy the demand of the system.   

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of John Irwin
Sent: Monday, March 19, 2018 10:38 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

Are you suggesting I use the pool as my water supply?

John Irwin
DynaFire Inc.

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Mike Stossel
Sent: Monday, March 19, 2018 10:36 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

I assume a house that large has a swimming pool.  Is the pump equipment located 
in a pool house or in the basement?  If it is in the basement you maybe able to 
cut a tee into one of the lines to gain a supply to a standard residential pump.

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of John Irwin
Sent: Monday, March 19, 2018 10:33 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

Yeah .. that's a concern I have as well.

John Irwin
DynaFire Inc.

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Matt Grise
Sent: Monday, March 19, 2018 10:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

When I hear 'hurricane', I also think swampy soil. It might be worth looking 
into the logistics of a buried tank. It would be a bummer if it popped out of 
the ground during a hurricane.

Matt


-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Vince Sabolik
Sent: Monday, March 19, 2018 9:25 AM
To: sprinklerforum@lists.firesprinkler.org; John Irwin <john.ir...@dynafire.com>
Subject: Re: Residential water storage

Bury a pressure tank

On 3/19/2018 9:41 AM, John Irwin wrote:
> I swear after 25 years in sprinklers I am amazed at how often new 
> situations are still presented to me …
>
>
>
> Here’s my situation … 22,000 sqft single family home. The owners lost 
> water completely in the last hurricane and want to make sure that the 
> new sprinkler system will continue to have a water supply if this 
> happens again. So they want to bury a grey water tank in the yard 
> that’s specifically for fire sprinkler supply. What considerations do 
> I even start with on this? It’s a 13D system, so do I have to take 
> NFPA 22 into consideration? How do I get water out of an underground 
> tank? Standard well pump? Should I not even bother with a city supply 
> if I am feeding off of a tank? Obviously money doesn’t seem to be a 
> consideration …
>
>
>
>
>
>
>
>
>
>
>
> John Irwin
>
> Fire Sprinkler Specialist
>
> DynaFire, Inc.
>
> 727-282-9243 – Cell
>
>
>
> *“A customer is the most important visitor on our premises. He is not 
> dependent on us. We are dependent on him. He is not an interruption on 
> our work. He is the purpose of it. He is not an outsider on our 
> business. He is a part of it. We are not doing him a favour by serving 
> him. He is doing us a favour by giving us an opportunity to do so.”*
> -- next part -- An HTML attachment was 
> scrubbed...
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
> er.org/attachments/20180319/3cc2de75/attachment.html>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
>


-- 

11351 Pearl Road /  Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601

/
Vince Sabolik /

-- next part --
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180319/8985db05/attachment.html>
-- next part --
A non-text attachment was scrubbed...
Name: 20914 x WTFP Logo NEW1.jpg
Type: image/jpeg
Size: 30521 bytes
Desc: not available
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180319/8985db05/attachment.jpg>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listin

RE: Residential water storage

2018-03-19 Thread Mike Stossel
I assume a house that large has a swimming pool.  Is the pump equipment located 
in a pool house or in the basement?  If it is in the basement you maybe able to 
cut a tee into one of the lines to gain a supply to a standard residential pump.

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of John Irwin
Sent: Monday, March 19, 2018 10:33 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

Yeah .. that's a concern I have as well.

John Irwin
DynaFire Inc.

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Matt Grise
Sent: Monday, March 19, 2018 10:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

When I hear 'hurricane', I also think swampy soil. It might be worth looking 
into the logistics of a buried tank. It would be a bummer if it popped out of 
the ground during a hurricane.

Matt


-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Vince Sabolik
Sent: Monday, March 19, 2018 9:25 AM
To: sprinklerforum@lists.firesprinkler.org; John Irwin <john.ir...@dynafire.com>
Subject: Re: Residential water storage

Bury a pressure tank

On 3/19/2018 9:41 AM, John Irwin wrote:
> I swear after 25 years in sprinklers I am amazed at how often new 
> situations are still presented to me …
>
>
>
> Here’s my situation … 22,000 sqft single family home. The owners lost 
> water completely in the last hurricane and want to make sure that the 
> new sprinkler system will continue to have a water supply if this 
> happens again. So they want to bury a grey water tank in the yard 
> that’s specifically for fire sprinkler supply. What considerations do 
> I even start with on this? It’s a 13D system, so do I have to take 
> NFPA 22 into consideration? How do I get water out of an underground 
> tank? Standard well pump? Should I not even bother with a city supply 
> if I am feeding off of a tank? Obviously money doesn’t seem to be a 
> consideration …
>
>
>
>
>
>
>
>
>
>
>
> John Irwin
>
> Fire Sprinkler Specialist
>
> DynaFire, Inc.
>
> 727-282-9243 – Cell
>
>
>
> *“A customer is the most important visitor on our premises. He is not 
> dependent on us. We are dependent on him. He is not an interruption on 
> our work. He is the purpose of it. He is not an outsider on our 
> business. He is a part of it. We are not doing him a favour by serving 
> him. He is doing us a favour by giving us an opportunity to do so.”*
> -- next part -- An HTML attachment was 
> scrubbed...
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
> er.org/attachments/20180319/3cc2de75/attachment.html>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
>


-- 

11351 Pearl Road /  Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601

/
Vince Sabolik /

-- next part --
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180319/8985db05/attachment.html>
-- next part --
A non-text attachment was scrubbed...
Name: 20914 x WTFP Logo NEW1.jpg
Type: image/jpeg
Size: 30521 bytes
Desc: not available
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180319/8985db05/attachment.jpg>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Residential water storage

2018-03-19 Thread Mike Stossel
I don't know if this will be helpful, but a company by the name of NAFFCO makes 
a small vertical turbine fire pump with a flow of 50gpm and a pressure range 
from 42-188psi.

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of John Irwin
Sent: Monday, March 19, 2018 9:51 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Residential water storage

Nope. I offered that. They are adamant that they don't give up any floor
space.¯\_(ツ)_/¯

John Irwin
DynaFire Inc.

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Travis Mack
Sent: Monday, March 19, 2018 9:47 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Residential water storage

Instead of underground tank, can you sell them on a Talco Home Hydrant tank and 
pump system? They have a small foot print.

Put an automatic float valve on it and you have your city supply being used 
should it be available.

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Mar 19, 2018, at 6:41 AM, John Irwin <john.ir...@dynafire.com> wrote:
>
> I swear after 25 years in sprinklers I am amazed at how often new 
> situations are still presented to me …
>
>
>
> Here’s my situation … 22,000 sqft single family home. The owners lost 
> water completely in the last hurricane and want to make sure that the 
> new sprinkler system will continue to have a water supply if this 
> happens again. So they want to bury a grey water tank in the yard 
> that’s specifically for fire sprinkler supply. What considerations do 
> I even start with on this? It’s a 13D system, so do I have to take 
> NFPA 22 into consideration? How do I get water out of an underground 
> tank? Standard well pump? Should I not even bother with a city supply 
> if I am feeding off of a tank? Obviously money doesn’t seem to be a 
> consideration …
>
>
>
>
>
>
>
>
>
>
>
> John Irwin
>
> Fire Sprinkler Specialist
>
> DynaFire, Inc.
>
> 727-282-9243 – Cell
>
>
>
> *“A customer is the most important visitor on our premises. He is not 
> dependent on us. We are dependent on him. He is not an interruption on 
> our work. He is the purpose of it. He is not an outsider on our 
> business. He is a part of it. We are not doing him a favour by serving 
> him. He is doing us a favour by giving us an opportunity to do so.”*
> -- next part -- An HTML attachment was 
> scrubbed...
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkl
> er.org/attachments/20180319/3cc2de75/attachment.html>
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
-- next part --
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180319/7e94da13/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Extended Coverage O-H Dry Sidewall Sprinklers

2018-03-15 Thread Mike Stossel
To the best of my knowledge TYCO is the only one.

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Mike Hairfield
Sent: Thursday, March 15, 2018 9:42 AM
To: Sprinkler Forum <sprinklerforum@lists.firesprinkler.org>
Subject: Extended Coverage O-H Dry Sidewall Sprinklers

Who else makes a Extended Coverage Ordinary Hazard Dry Sidewall sprinkler 
besides TYCO?


Mike
-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/3eb1cb2d/attachment.html>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


New Sprinkler Design

2018-03-13 Thread Mike Stossel
I was asked to do a presentation next week on the basic design of fire 
sprinkler systems.  They essentially are asking for an overview touching on the 
entire thought process we go through when developing the system.  Going from 
hazard type, sprinkler selection, type of system and layout (tree, loop, grid), 
basic hydraulics and so on.  Does anyone happen to have any power points or 
other documents that will help guide me through this presentation?  They are 
asking for the presentation to last approximately one hour.  Any help that 
anyone can give me with this would be greatly appreciated.

Thanks,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

-- next part --
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180313/444a70d6/attachment.html>
-- next part --
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 8535 bytes
Desc: image001.png
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180313/444a70d6/attachment.png>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Glazing Protection with standard spray

2018-02-13 Thread Mike Stossel
Not sure if this will help you in anyway, but what about section D.1.1.1.1 in 
NFPA 13.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jerry Van Kolken
Sent: Tuesday, February 13, 2018 6:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Glazing Protection with standard spray

The door is part of the assembly but, I just found out this is the area where 
they were intending to Std Spray in lieu of WS.

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Prahl, Craig/GVL
Sent: Tuesday, February 13, 2018 3:06 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Glazing Protection with standard spray

There isn't any prescribed protection for door glazing.  There is a window 
sprinkler, I think it was by Tyco that when installed per its listing was 
considered equivalent to 2-hour protection but that was for fixed glazing and 
with some restrictions.

Is this door part of a fire rated assembly or area separation?


Craig L. Prahl
Fire Protection Group Lead/SME
Direct - 864.920.7540
Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>
http://www.jacobs.com<http://www.jacobs.com/>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jerry Van Kolken
Sent: Tuesday, February 13, 2018 5:58 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Glazing Protection with standard spray [EXTERNAL]

Okay, Is been about a decade since I've dealt glazing protection. Is there any 
information on protecting window with standard spray sprinklers. I've been told 
this was direction was approved by the AHJ.

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Help Finding ESFR upright greater than K17

2018-02-12 Thread Mike Stossel
You may also want to look at the Victaulic LP-46 (model V4603).  It has a 25.2 
K-Factor although it does have specific guidelines on how and when it can be 
used, but it may fit your needs.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Nicky Marshall
Sent: Monday, February 12, 2018 2:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Help Finding ESFR upright greater than K17

Most of the responses do not seem to have answered your question if you are 
specifically looking for an upright ESFR sprinkler.

To my knowledge, the K17 Tyco TY7126 is the biggest upright ESFR unless you go 
Extended Coverage K25: TY9128 and Viking VK595.
If you can go standard response (CMSA) then there are more choices. K17: 
TY7153, TY7151, VK580 and Reliable RA1124.  Then K25 VK598 and Victaulic V4603.


Nicky Marshall
Southern Regional Manager
PROTECH DESIGN LIMITED
Specialist Fire Protection Consultants
Phone: +64 (0)3 579 5577 extn 2  Mobile: +64 (0)21 433 488  Email: 
ni...@protechdesign.co.nz<mailto:ni...@protechdesign.co.nz>  Skype: 
nicky-marshall Web :www.protechdesign.co.nz
Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ Postal: PO Box 4022, 
Redwood Village, Blenheim 7242, NZ

"I always wondered why somebody doesn't do something about that. Then I 
realised I was somebody" Lily Tomlin

From: Jeff Polke [mailto:jpo...@gcioutdoor.com]
Sent: Tuesday, 13 February 2018 5:30 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Help Finding ESFR upright greater than K17

Good morning all.  I am looking for an expert in ESFR sprinkler heads to help 
me find a ESFR upright head with at least a K factor 17(not 16.8).  There does 
not seem to be other companies that make these ESFR other Tyco. Please let me 
know.  Thanks.

Jeffrey Polke
Co-President
jpo...@gcioutdoor.com<mailto:jpo...@gcioutdoor.com>


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Small Air Compressor?

2018-01-04 Thread Mike Stossel
I believe GAST makes a tankless 1/6HP that goes to 90 gallons. It should be 
model number 1LAA-46S-M100GX.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of BILL MENSTER
Sent: Thursday, January 4, 2018 2:24 PM
To: sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: Small Air Compressor?


Does anyone know of a small air compressor available for a pre-action system?  
I have a very small pre-action system (3 heads) with only 5 gallon capacity.  
The smallest riser mount compressor I can find is for up to 110 gal.

Looking to save a few bucks if possible.



Thanks



Bill Menster
WFM Consulting
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Underground Main Between 2 Attached Building Areas

2017-12-11 Thread Mike Stossel
Yes, I have done this on many occasions, especially in large warehouses.  I 
have run the underground main into the pump room, after the pump drop down and 
run underground to multiple riser locations.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Wayne Cordiner
Sent: Monday, December 11, 2017 10:05 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Underground Main Between 2 Attached Building Areas

Good morning Forum,

I have a situation I've never come across before that I'm hoping someone here 
may have.

We are working on a Phase 2 addition of a school. Essentially we have a 
rectangular shaped building in existence (fully sprinklered) and a new 
rectangular building being added on the end, to form a letter T if you will. 
Current incoming service is in the existing building at the furthest corner 
away from the new building area. Originally phase 2 was proposed to have the 
sprinkler mains come back to this fire service room but now they do not want to 
open ceilings to do so and the existing main is not sized for this new area. 
The owners/architects have proposed teeing off the existing main after the back 
flow preventer, dropping below the floor and elbowing back outside. They then 
want to run this main underground along side the building and then pop back 
into the new space when it penetrates the foundation wall at the intersection 
of the new wall.

The idea of installing mains so come into, then back out of, and then into a 
building again seems like a bad plan to me.
After looking throughout the codes (IBC 2015, NFPA 13 2013, 14 2013, etc) I 
can't seem to find anything stating this would not be permitted.
From what we can tell now, and it may change, this will end up as 1 building so 
the idea of another service will face resistance with this AHJ.
Has anyone ever come across a situation like this before?

Regards,
Wayne T. Cordiner Jr.
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: compressor size

2017-11-08 Thread Mike Stossel
The air compressor are sized by the system capacity, and each manufacturer will 
give you sizing charts.  For instance one of the manufacturers states that a 
system with a capacity of 125 gallons will need their 1/6hp air compressor. So 
basically select a manufacturer and go to their sizing charts.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of James Crawford
Sent: Wednesday, November 8, 2017 3:57 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: compressor size

Is there an easy equation out there to see how many CFM I require to fill a dry 
system, I am sizing an air compressor and would like to ensure I do not over or 
undersize it.


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca<mailto:jcrawf...@phaserfire.ca>
Web www.phaserfire.ca<http://www.phaserfire.ca>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Standpipe Pressure Question.

2017-11-01 Thread Mike Stossel
So the building does not have a sprinkler system?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Thomas Reinhardt
Sent: Wednesday, November 1, 2017 3:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Standpipe Pressure Question.

The highest story is above 30 feet. Thus are adopted IFC chapter 9 section 
905.3.1 apply. Standpipes to be automatic wet. Thanks

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: Wednesday, November 01, 2017 2:22 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Standpipe Pressure Question.

How many stories is the building?   I'm going the same way as Nick did with his 
question.

Yes, 100 PSI came in 1993.

SML

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Don Casey
Sent: Wednesday, November 01, 2017 12:21 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Standpipe Pressure Question.

When did 14 bring in the 100psi requirement?  93? (or is my imagination running 
in the wrong direction).  If the building was constructed prior to the 100psi 
requirement, is there an argument that you're maintaining the level of 
performance of the originally designed system?

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Thomas Reinhardt
Sent: 2017/11/01 3:09 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Standpipe Pressure Question.

Question for the forum. I have a complete renovation of a school. They are 
required to have 3 standpipes installed. The designers approached me and asked 
if one of the standpipes could have a reduced pressure. The reason is because 
then they would have to upgrade the electrical power to the pump. This in turn 
would make them upgrade the power for the backup generator. This would create 
an economic  problem for the school district. In researching NFPA 14. I found 
that the minimum residual pressure at 2.5 in. should be 100psi for each 
standpipe. Am I interpreting this correct. They asked that 1 standpipe be only 
65psi (doesn't sound correct). NFPA 14 says that standpipes shall provide 250 
gallons. All standpipie hose connections to be class 1 systems. Am I missing 
something. Thanks

Tom Reinhardt
Fire Inspector/Plan Reviewer
Skokie Fire Department
7424 Niles Center Road
Skokie, IL 60077
Office: 847-982-5342
thomas.reinha...@skokie.org<mailto:thomas.reinha...@skokie.org>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Standpipe Pressure Question.

2017-11-01 Thread Mike Stossel
It has been my experience that the pressure requirement between 65psi and 
100psi varies from city to city and state to state.  Is the building a high 
rise? Can the standpipes be classified as manual wet and not automatic and be 
based on the pumper trucks capabilities from the FDC instead of the fire pumps?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Thomas Reinhardt
Sent: Wednesday, November 1, 2017 3:09 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Standpipe Pressure Question.

Question for the forum. I have a complete renovation of a school. They are 
required to have 3 standpipes installed. The designers approached me and asked 
if one of the standpipes could have a reduced pressure. The reason is because 
then they would have to upgrade the electrical power to the pump. This in turn 
would make them upgrade the power for the backup generator. This would create 
an economic  problem for the school district. In researching NFPA 14. I found 
that the minimum residual pressure at 2.5 in. should be 100psi for each 
standpipe. Am I interpreting this correct. They asked that 1 standpipe be only 
65psi (doesn't sound correct). NFPA 14 says that standpipes shall provide 250 
gallons. All standpipie hose connections to be class 1 systems. Am I missing 
something. Thanks

Tom Reinhardt
Fire Inspector/Plan Reviewer
Skokie Fire Department
7424 Niles Center Road
Skokie, IL 60077
Office: 847-982-5342
thomas.reinha...@skokie.org<mailto:thomas.reinha...@skokie.org>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Hose valve location

2017-10-25 Thread Mike Stossel
In the 2007 edition of NFPA 14 it is section 7.3.1.1.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com
Sent: Wednesday, October 25, 2017 10:58 AM
To: Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: Hose valve location

I was asked about Code (or Standard) requirements for the height of a 2-1/2" 
hose valve off the floor. I couldn't find anything in either 14 or IFC. I 
assume there would be something somewhere.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NYC Standpipe

2017-10-24 Thread Mike Stossel
Great, thank you.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Wayne Cordiner
Sent: Tuesday, October 24, 2017 5:42 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NYC Standpipe

Mike,

Using the 4” on the lower height areas is correct.
I have done this in the past without issue from the FDNY or NYC DOB.
Regards,

Wayne T. Cordiner, Jr.
917-426-5844
fpdrawi...@gmail.com<mailto:fpdrawi...@gmail.com>

On Oct 24, 2017, at 17:09, Kyle.Montgomery 
<kmontgom...@aerofire.com<mailto:kmontgom...@aerofire.com>> wrote:
I would think 4” would be allowable for the shorter standpipes, but I’ve never 
worked in NYC so my thoughts probably aren’t worth much.

You are going to run calcs to prove that 4” would work hydraulically, right?

Kyle Montgomery
 
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
kmontgom...@aerofire.com<mailto:kmontgom...@aerofire.com>



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Tuesday, October 24, 2017 1:16 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] NYC Standpipe

In New York City they have the following requirement:

7.6.1 Delete and replace with the following: Class I and Class III standpipes 
in buildings with floor heights less than 150 feet (45 720 mm) above grade 
plane shall be at least 4 inches (100 mm) in size. Standpipes in buildings with 
floor heights greater than 150 (45 720 mm) feet above grade plane
shall be no less than 6 inches (150 mm) in diameter.

I am currently doing a project that is greater than 150’0” in height, so I  
know that my main standpipes will be 6”, but I have a couple areas of the 
building that only go up 50’ that will also require standpipes.  Can the areas 
of the building that are less than 150’ in height have 4” standpipes, or 
because they state building and not standpipe, all of the standpipes will need 
to be 6” regardless off height?  I have always designed it as all since they 
state building, but wanted to see what everyone else thinks.

Thanks in advance for the help.

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


NYC Standpipe

2017-10-24 Thread Mike Stossel
In New York City they have the following requirement:

7.6.1 Delete and replace with the following: Class I and Class III standpipes 
in buildings with floor heights less than 150 feet (45 720 mm) above grade 
plane shall be at least 4 inches (100 mm) in size. Standpipes in buildings with 
floor heights greater than 150 (45 720 mm) feet above grade plane
shall be no less than 6 inches (150 mm) in diameter.

I am currently doing a project that is greater than 150'0" in height, so I  
know that my main standpipes will be 6", but I have a couple areas of the 
building that only go up 50' that will also require standpipes.  Can the areas 
of the building that are less than 150' in height have 4" standpipes, or 
because they state building and not standpipe, all of the standpipes will need 
to be 6" regardless off height?  I have always designed it as all since they 
state building, but wanted to see what everyone else thinks.

Thanks in advance for the help.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Clean Room Sprinkler Options

2017-10-17 Thread Mike Stossel
Could you use the Viking VK462 Mirage Quick Response Concealed Pendent MRI 
Sprinkler.  In can be used in hazards up to ordinary group II and is 
specifically listed for neutral and negative pressure plenums.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larrimer, Peter A
Sent: Tuesday, October 17, 2017 3:16 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Clean Room Sprinkler Options

Can anyone please assist with a recommendation for a “clean room” sprinkler 
where the clean rooms are designed to be negative pressure (for compounding 
dangerous drugs).

The concealed sprinkler cut sheets that I’ve looked at online generally say 
that the concealed heads cannot be used in negative pressure rooms (positive 
pressure plenums) and this is the type of room design that we require.  The 
FlexHead cleanroom ceiling sprinkler connection doesn’t appear to be easy to 
clean after installation.

What type of quick response sprinkler could be used in a negative pressure room 
that is readily and easily cleanable?  Users wanted to used concealed 
sprinklers as they thought that the concealed sprinklers would be easy to wipe 
down when necessary, but we don’t want to violate the installation instructions 
on the cut sheets that state that the concealed sprinklers can’t be used with 
positive pressure plenums (negative pressure rooms).

Thanks in advance.

Pete Larrimer
VA

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Reed A. Roisum, SET
Sent: Tuesday, October 17, 2017 2:02 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] NFPA 13 edition in Wisconsin

I am finding conflicting answers as to what edition of NFPA 13 is applicable in 
Wisconsin.  It appears as though IBC 2009 is the applicable building code, 
which references NFPA 13, 2007 edition.  However, I have in my notes that NFPA 
13, 2010 edition is the applicable edition for some reason.  It may be because 
I believe NFPA 1, 2012 edition is the adopted fire code and that would 
reference NFPA 13, 2010 edition??

Can anyone point me to something definitive for Wisconsin’s applicable edition 
of NFPA 13?

Thank you.

Reed



Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Schedule 10 vs Schedule 40 pipe

2017-10-03 Thread Mike Stossel
In my opinion if the schedule 40 is going to be grooved than it would probably 
be worth it, but if they are going to thread the schedule 40 than schedule 10 
will most likely outlast the 40. I am basing this on schedule 10 grooved piping 
having a better corrosion resistance ration than threaded schedule 40.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: Tuesday, October 3, 2017 1:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Schedule 10 vs Schedule 40 pipe

Hello Forumites:

We are working to develop a bid package for a pair of large freezers and 
coolers used for food stuffs storage on racks to 35'. The freezers are to be 
-10 degrees and the coolers will be 31 degrees. The sprinklers systems will be 
double interlock pre-action with Protecto-wire detection and CMSA sprinklers.

My question: The owner is asking for a recommendation on whether to spec 
schedule 10 or schedule 40 piping. The concern is long term serviceability of 
the piping system. My initial thought is that due to the constant low ambient 
temperatures corrosion would be seriously inhibited for two reasons; any 
condensate in the pipe would be in frozen form and the low temps would inhibit 
microbial growth. So my thought is that schedule 10 pipe would last the 20 year 
expected service life of the system. However, I would like to get the thoughts 
of the forum participants, is the cost of schedule 40 warranted or would 
schedule 10 service just as well in this application?

Thanks in advance for your responses.

John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Removing Dry Sprinklers

2017-09-28 Thread Mike Stossel
What about using a pipe?  Take a pipe with an I.D. capable of going over an 18" 
wrench and measure the distance down to the hanging hole at the bottom of the 
wrench.  Drill a hole at that point and through bolt it so you can't lose the 
wrench.  Slide the pipe out to the dry pendent and hook it to loosen.  Once you 
loosen it a little bit you should be able to take it out the rest of the way 
with a head wrench.  

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of proud-texan
Sent: Thursday, September 28, 2017 2:23 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Removing Dry Sprinklers

We have a freezer that we need to change some Dry Sprinklers. 
Unfortunately, there is less than 12" clear space above it so no way to get a 
man above it to wrench the head loose.  When we try to remove it with a head 
wrench, it refuses to budge.  If we break the head, we will be up the 
proverbial creek.  Does anyone have any ideas short of disassembling the 
freezer to change heads?

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Flight Simulator Bldg

2017-09-20 Thread Mike Stossel
Don’t know if this will help, but FM Data Sheet 7-3 is for flight simulators.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com
Sent: Wednesday, September 20, 2017 10:11 AM
To: Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: Re: Flight Simulator Bldg

I'm sure there will be a lot of electronics inside. Since you have a pilot in 
an enclosed space, are there any systems inside for life safety?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)



On Sep 20, 2017 at 10:06 AM, mailto:tston...@comcast.net>> wrote:

Matt, Todd,

I have no info on the simulators. I am assuming no combustible construction 
with a pilot inside.



I do agree with E H Grp 2. Not sure that really applies in this case. While 
pilot training is going on there is also a manned computer room over seeing the 
simulator.



 Regards,

G. Tim Stone

G. Tim Stone Consulting, LLC

117 Old Stage Rd.

Essex Junction, VT. 05452

Cell: (802) 373-0638

tston...@comcast.net<mailto:tston...@comcast.net>
On September 20, 2017 at 9:29 AM Matt Grise 
<m...@afpsprink.com<mailto:m...@afpsprink.com>> wrote:

What is in the simulators? Could there be a shielded fire in there?



Matt





From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Prahl, Craig/GVL
Sent: Wednesday, September 20, 2017 8:27 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Flight Simulator Bldg



Are these servo motor articulated or use hydraulic fluids?



If there are no hydraulic fluids or other contributing hazards, the building 
may be able to classified as an F-2 occupancy and no sprinklers required.



You might also investigate the possibility of a water mist or hybrid water mist 
system in lieu of sprinklers for such an occupancy but that will take some 
analysis and engineering work to determine suitability or viability of the 
option.



Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of TIM STONE
Sent: Wednesday, September 20, 2017 9:23 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Fwd: Flight Simulator Bldg [EXTERNAL]



What occupancy should be considered?

Steel building, 25' high with Flight Simulators inside. Engineer has asked that 
no sprinklers be installed directly over simulators which are about 22' in 
diameter. I need to use extended coverage. Occupancy not specified. I am 
leaning toward Ordinary Hazard 1 as minimum.

Am I on the right track or could I consider Light Hazard?

Cheers,

G. Tim Stone

G. Tim Stone Consulting, LLC

117 Old Stage Rd.

Essex Junction, VT. 05452

Cell: (802) 373-0638

tston...@comcast.net<mailto:tston...@comcast.net>


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___ Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Liability Question

2017-09-17 Thread Mike Stossel
Thank you all very much for your recommendations, I have found them very 
helpful and I will be applying them to my current and future projects.  I am in 
the same boat as Wayne Cordiner and primarily design in New York City, and he 
is completely right in saying it is a different animal in itself.  Like many 
have mentioned, I believe I will have to weigh if the request is meeting or 
exceeding the code or if it has the potential of harming others.  If it is the 
latter, document my concerns to the engineer or architect of record, and if all 
else fails respectfully walk away from the project.  At the end of the day what 
Travis said is completely true, "Keeping my integrity and knowing I've done the 
best I can is worth more than a few dollars from a job."

Thanks again to everyone and if anyone has more comments they are always 
appreciated, I like to hear what everyone has to say.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Drucker
Sent: Sunday, September 17, 2017 12:51 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Liability Question

In New Jersey permit applications and design documents are required to 
demonstrate compliance with the adopted codes and standards applicable to the 
project. For example an FM design is paralleled with NFPA-13 calculation 
methods to demonstrate code compliance. Furthermore  documents prepared by 
other than the design professional (ie the primary achitect or engineer) are 
required to be accompanied by a letter from the design professional that they 
have reviewed and are acceptable for submission for permit purposes. Bottom 
line the project architect and/or engineer are ultimately responsibile.

Last but not least as our municipal attorneys reiterate, be sure your position 
is defensible in court.

Hope that helps, not sure what the regulations are in your state.

John Drucker
Assistant Construction Official
Fire & Electrical Subcode Official
Building Inspector
Borough of Red Bank, NJ
Cell/Text 732-904-6823
On Sep 17, 2017 12:14 AM, Ed Vining 
<edkvin...@gmail.com<mailto:edkvin...@gmail.com>> wrote:
Howsabout suggesting to the engineer that he run the design past the building 
and code authorities prior to submitting it, to be sure they will accept it.  
He would probably be told that he can design in more than is required by code, 
but the final design must also meet the codes.  Even if the authorities accept 
less, I would consult with my insurance company, to get their viewpoint.

On Sat, Sep 16, 2017 at 4:37 AM, Mike Stossel 
<m...@knssprinkler.com<mailto:m...@knssprinkler.com>> wrote:
I am not looking to start a debate between NICET and engineers, but I have a 
question about liability and would very much value the forums opinion.  The 
particulars behind the disagreement really are not important as I have had 
various issues come up in the past and would like to know how to handle it 
going forward.
I am working on a project that NFPA and IBC are specific on a particular layout 
and designed the area as such.  The engineer of record for the project has 
reviewed the area and told me to do it a different way.  I researched what he 
is asking to do and found no documentation that this is an acceptable means of 
protection.  I contacted the engineer and said that my layout was as per NFPA 
and IBC requirements and that I could not find anything regarding his method of 
design.  His response was that NFPA and IBC are just merely the minimal level 
of protection and that his way is better than what NFPA and IBC are requiring 
and will provide a higher level of protection.  When I asked what he was basing 
his opinion on, his response was because I am an engineer and I said so.
This is the issue I am concerned about.  I am a NICET Level IV in water based 
systems layout and fully understand and realize that I am not an engineer and 
understand that my place is behind them.  However, I have previously been hired 
as a professional witness and it appears in court it really doesn't matter to 
the judge one way or another.  Once you are deemed by the court as a 
professional in your field it appears that you are viewed and judged in the 
same fashion no matter the title you carry.
So back to the original scenario.  He is the engineer of record for the project 
and I do not know one way or the other if his request will enhance or hinder 
the system.  Would anyone recommend getting a hold harmless agreement in the 
event that his method is actually a detriment to the system or is it enough 
that he is the engineer of record and the liability is all his.

Any and all opinions are very much appreciated.  I would just really like to 
know how the forum would handle this in the very law suit happy environment 
that 

Liability Question

2017-09-16 Thread Mike Stossel
I am not looking to start a debate between NICET and engineers, but I have a 
question about liability and would very much value the forums opinion.  The 
particulars behind the disagreement really are not important as I have had 
various issues come up in the past and would like to know how to handle it 
going forward.
I am working on a project that NFPA and IBC are specific on a particular layout 
and designed the area as such.  The engineer of record for the project has 
reviewed the area and told me to do it a different way.  I researched what he 
is asking to do and found no documentation that this is an acceptable means of 
protection.  I contacted the engineer and said that my layout was as per NFPA 
and IBC requirements and that I could not find anything regarding his method of 
design.  His response was that NFPA and IBC are just merely the minimal level 
of protection and that his way is better than what NFPA and IBC are requiring 
and will provide a higher level of protection.  When I asked what he was basing 
his opinion on, his response was because I am an engineer and I said so.
This is the issue I am concerned about.  I am a NICET Level IV in water based 
systems layout and fully understand and realize that I am not an engineer and 
understand that my place is behind them.  However, I have previously been hired 
as a professional witness and it appears in court it really doesn't matter to 
the judge one way or another.  Once you are deemed by the court as a 
professional in your field it appears that you are viewed and judged in the 
same fashion no matter the title you carry.
So back to the original scenario.  He is the engineer of record for the project 
and I do not know one way or the other if his request will enhance or hinder 
the system.  Would anyone recommend getting a hold harmless agreement in the 
event that his method is actually a detriment to the system or is it enough 
that he is the engineer of record and the liability is all his.

Any and all opinions are very much appreciated.  I would just really like to 
know how the forum would handle this in the very law suit happy environment 
that we live in today.

Thanks in advance for all comments.

Best regards,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Parking under 13R system

2017-08-25 Thread Mike Stossel
I have had this scenario come up several times and I have always protected it.  
I based this primarily on the living space being above the parking area.  My 
thought process was to consider it as an area outside the dwelling unit which 
sends me to NFPA 13.  In NFPA 13 in section A.8.15.7.2 (2007 edition) this 
scenario is addressed by the following “However, areas under exterior ceilings 
where the building is sprinklered should be protected due to the occupancy 
above.”


Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com
Sent: Friday, August 25, 2017 6:30 AM
To: Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: Parking under 13R system

I am looking at a 3 story apartment building that is going to be protected by a 
13R system. Under one wing, the main level will be open for parking with 2 
floors of apartments above. 13R addresses garages but not open (on 2 sides) 
parking areas. A number of years ago, I did a similar arrangement, but it was a 
13 system and the space was protected by a dry system. Thought on if sprinklers 
are required?

I know there was a thread or 2 about this, but only found the one about 
sprinklers under train tracks.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 10" pipe with 1.0 CRR

2017-08-11 Thread Mike Stossel
It has always been my understanding that the corrosion resistance ratio 
benchmark of (1) is based on threaded schedule 40 steel, so I believe any other 
pipe type would have a better or worse ratio, but not the same.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: Friday, August 11, 2017 8:39 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: dmarti...@total-mechanical.com
Subject: 10" pipe with 1.0 CRR

Anyone know of 10in non-sch40 pipe that has a CRR of 1?  Have a project where 
the EOR is insisting on this.  They also have a 100lb maximum point load per 
hanger…..but that is a conversation for another day!
Thanks,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI  53072
dmarti...@total-mechanical.com<mailto:dmarti...@total-mechanical.com>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/

[Consecutive Honors 2012-2017]


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Parking Under MTA Tracks

2017-06-29 Thread Mike Stossel
That is an approach I never thought of, I focused on the tracks and not the 
concept of the structure.  Like you said , I am not sure what occupancy group 
it would fall under, but technically a structure no different than any other 
building.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Wayne Cordiner
Sent: Thursday, June 29, 2017 2:00 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Parking Under MTA Tracks

Mike,

NYC BC 903.2.10.3 Parking Garages, states an automatic sprinkler system shall 
be provided throughout buildings classified as enclosed parking garages in 
accordance with section 406.4 or where open or enclosed parking garage is 
located beneath other occupancy groups.
I wish I could tell you which occupancy group elevated train tracks fall under 
but regardless the only exception is an R-3 so automatic sprinklers appear to 
be required.
I've attached a link to the BC site. Hope this helps.

https://www1.nyc.gov/site/buildings/codes/2014-construction-codes.page
Regards,

Wayne T. Cordiner, Jr.
917-426-5844


On Jun 27, 2017, at 19:22, Mike Stossel 
<m...@knssprinkler.com<mailto:m...@knssprinkler.com>> wrote:
Does anyone know of an NFPA code that addresses parking under train tracks?  I 
have a customer in New York City that is going to rent the space under the 
tracks for parking.  One of the requirements that New York City has made is 
that proper fire protection is provided, but gave no indication as to what this 
is.  I checked NFPA 130 thinking that standpipes maybe required, but I could 
not find any information pertaining to this scenario.  Any ideas or direction 
is greatly appreciated, and thank you in advance for the help.



Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Parking Under MTA Tracks

2017-06-29 Thread Mike Stossel
The city owns the tracks and the property underneath.  My client would be 
leasing the property underneath the tracks for additional parking.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Kyle.Montgomery
Sent: Thursday, June 29, 2017 2:09 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Parking Under MTA Tracks

I would expect that the need for a standpipe would be dependent upon the 
accessibility to fire trucks and location of adjacent hydrants. If the truck 
can drive along the length of the track and there are hydrants every 
couple-hundred feet, why would you need a standpipe?

As far as the design criteria, I would be surprised if they didn’t want 
something more “overkill” than the standard parking protection (OH1), 
considering the risk to the structure. Would column protection be advisable in 
this scenario?

Maybe a dumb question: Is the city the owner of the train/tracks, or is your 
customer?

Kyle Montgomery
 [cid:image001.gif@01CAA0CE.8D8066F0]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
kmontgom...@aerofire.com<mailto:kmontgom...@aerofire.com>



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Wayne Cordiner
Sent: Thursday, June 29, 2017 11:00 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Parking Under MTA Tracks

Mike,

NYC BC 903.2.10.3 Parking Garages, states an automatic sprinkler system shall 
be provided throughout buildings classified as enclosed parking garages in 
accordance with section 406.4 or where open or enclosed parking garage is 
located beneath other occupancy groups.
I wish I could tell you which occupancy group elevated train tracks fall under 
but regardless the only exception is an R-3 so automatic sprinklers appear to 
be required.
I've attached a link to the BC site. Hope this helps.

https://www1.nyc.gov/site/buildings/codes/2014-construction-codes.page
Regards,

Wayne T. Cordiner, Jr.
917-426-5844


On Jun 27, 2017, at 19:22, Mike Stossel 
<m...@knssprinkler.com<mailto:m...@knssprinkler.com>> wrote:
Does anyone know of an NFPA code that addresses parking under train tracks?  I 
have a customer in New York City that is going to rent the space under the 
tracks for parking.  One of the requirements that New York City has made is 
that proper fire protection is provided, but gave no indication as to what this 
is.  I checked NFPA 130 thinking that standpipes maybe required, but I could 
not find any information pertaining to this scenario.  Any ideas or direction 
is greatly appreciated, and thank you in advance for the help.



Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Heating cable and 1" wrap.

2017-06-14 Thread Mike Stossel
I’m not sure if the sprinkler will work for your application, but have you 
looked at Victaulic’s LP-46 sprinkler?  If I remember right it can be used on a 
dry system and depending upon what commodity you are protecting it can be used 
in buildings up to 45’0”  high with storage up to 40’0”.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com
Sent: Tuesday, June 13, 2017 8:30 PM
To: Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: RE: Heating cable and 1" wrap.

I gave it the 90 second overview. This was not a detailed analysis. I assumed a 
50 degree temperature differential (+40 to -10?). I'm not even sure where this 
place is.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)



On Jun 13, 2017 at 8:16 PM, <Mark.Phelps<mailto:mphe...@aerofire.com>> wrote:
Hey Todd,
On your power calculations, what minimum ambient temperature did you use for 
the water filled pipe.

Mark at Aero
602 820-7894

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com>
Sent: Tuesday, June 13, 2017 4:50 PM
To: Sprinklerforum
Subject: RE: Heating cable and 1" wrap.

Pentairthermal.com has information that you can use to estimate the power 
demand. I went through some numbers (with a lot of assumptions) and came up 
with around 11 kW of power required. Wait until he sees that cost. I think this 
guy is a looney.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)




On Jun 13, 2017 at 6:49 PM, mailto:atir...@atcofirepro.com>> wrote:
About 4000 Ft. of pipe, 300 sprinklers.

Art

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: Tuesday, June 13, 2017 6:42 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Heating cable and 1" wrap.

Well, one thing is for sure, your customer would be on AEP’s (American Electric 
Power) Christmas card list the first time they powered the trace system up! 
Hundreds of feet of resistance heating cable…what a “peak” demand that would 
set.

John Paulsen – SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P – 614-782-2438
F – 614-782-2374
C – 614-348-8206



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack, SET
Sent: Tuesday, June 13, 2017 6:25 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Heating cable and 1" wrap.


Yeah...I had some one tell me it was like $5/ft for the materials.  Now, using 
Professor Greenman's qualitative formula, it would be about $10/ft + all the 
extras :-) I don't know how accurate or not, but that sure would keep me from 
doing an entire system in it.

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com>



http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign

LinkedIn: https://www.linkedin.com/in/travismack
On 6/13/2017 3:08 PM, rongreenman . wrote:
Just figure a lot per foot, double it, and then add on the extras.

On Tue, Jun 13, 2017 at 3:05 PM, Art Tiroly 
<atir...@atcofirepro.com<mailto:atir...@atcofirepro.com>> wrote:
Thanks.
How do you determine the cost of operating a heat trace system?
That is important to convey

Ary

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Jeff Normand
Sent: Tuesday, June 13, 2017 5:27 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Heating cable and 1" wrap.

If ceiling is too costly wait until you see the price of heat tracing an entire 
system.



On Tue, Jun 13, 2017 at 4:20 PM, Art Tiroly 
<atir...@atcofirepro.com<mailto:atir...@atcofirepro.com>> wrote:
They need store packaging material, idle pallets.

Ceiling is also too costly.

Art

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Matt Grise
Sent: Tuesday, June 13, 2017 5:16 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Heating cable and 1" wrap.

What are they storing?

Could they put in a false ceiling?

Matt


From: 

RE: CPVC Piping

2017-06-09 Thread Mike Stossel
I totally agree with you on all the points you made.  The space is conditioned 
so the thermal expansion would be almost none existent.  I could not find 
anything establishing an allowable limit, is it merely up to the installer to 
decide what the allowable expansion is?

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Hinson, Ryan
Sent: Friday, June 9, 2017 1:43 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: CPVC Piping

What is your expected temperature delta?  Since CPVC is installed in heated 
spaces, is there going to be that significant of a change in temperature?  
Where is the water supply coming from?  In a conditioned space, CPVC piping 
system with no flow is going to have negligible thermal expansion IMO.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Senior Fire Protection Engineer
O 952-656-3662 \  M 320-250-5404  \  F 952-229-2923
rhin...@burnsmcd.com<mailto:rhin...@burnsmcd.com>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437
*Registered in: MD, MN, PA, & TX
**NICET IV - Water-Based Systems Layout

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Friday, June 09, 2017 11:57 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: CPVC Piping

I just recently had the question asked of me of, when do you need to install a 
thermal expansion loop in CPVC piping?  I searched all of the manufacturers 
that I could think of and they all appear to say basically the same thing, in 
long straight runs of pipe.  No one specifically defines what that length would 
be and likewise I could not find an allowable expansion amount.  For instance 
an expansion of  ½" or 1" is acceptable or at 1" expansion you will need one.   
I can understand not defining a specific length of run since each geographic 
area has different temperature changes which would affect the expansion, but I 
would have thought that they would define an expansion threshold.  Any guidance 
that can be given would be greatly appreciated.

Best regards,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


CPVC Piping

2017-06-09 Thread Mike Stossel
I just recently had the question asked of me of, when do you need to install a 
thermal expansion loop in CPVC piping?  I searched all of the manufacturers 
that I could think of and they all appear to say basically the same thing, in 
long straight runs of pipe.  No one specifically defines what that length would 
be and likewise I could not find an allowable expansion amount.  For instance 
an expansion of  ½" or 1" is acceptable or at 1" expansion you will need one.   
I can understand not defining a specific length of run since each geographic 
area has different temperature changes which would affect the expansion, but I 
would have thought that they would define an expansion threshold.  Any guidance 
that can be given would be greatly appreciated.

Best regards,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: sprinklers in deactivated buildings with freeze potential

2017-05-25 Thread Mike Stossel
I had this occur once in the past and we received permission from the AHJ to 
make it an anti-freeze system.  It was less expensive  than putting in the dry 
valves, pitching the pipe, taking out all of the drops, etc... The AHJ was fine 
with the anti-freeze in this instance since the building was going to be 
completely unoccupied.  The only thing they did was tag the building  in their 
files that this arrangement had to be revisited in the event that a new tenant 
takes occupancy. They also had wanted signs installed on all of the exterior 
doors alerting the fire fighters and anyone that enters that the system was 
anti-freeze.  The other thing we had to do was change out the backflow to an 
RPZ.  

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Foltz, Stuart D CIV USARMY CEERD-CERL (US)
Sent: Thursday, May 25, 2017 10:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: sprinklers in deactivated buildings with freeze potential


An owner is deactivating a group of buildings and wants to preserve them for 
future use. My group has been asked to make recommendations and model the 
economic impacts. Because these recommendation may be used in nearly any 
climate, we would like to recommend complete shutoff of all water but are 
concerned about fire sprinklers. We are not sprinkler experts but are aware of 
NFPA standard 13. I'm wondering if you can direct me to any good resources on 
these or other options:

 - Drain system and go without
We are concerned about having no fire protection even if all 
furnishings are removed.
 - Add ethylene glycol or glycerin
Creates some risk if a fire should occur with a person nearby when the 
sprinkler activates.
 - Convert to a dry system
May not meet code unless modified. May require nearly complete 
replacement of system. Is conversion without meeting code a reasonable approach 
if all furnishings are removed?
 - Install heat tape on the lines.
Significant effort and operational expense. Introduces multiple failure 
possibilities.

Thoughts on the relative merits of the alternatives and the relative costs 
would be appreciated.

Thx
SF


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Automated storage machine

2017-05-10 Thread Mike Stossel
Yes, a protected a vertical carousel.  I used FM data sheet 8-33 for guidance.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Wednesday, May 10, 2017 2:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Automated storage machine

I am looking at protecting the interior of an automated storage machine. It has 
lots of small bins in it and you type what you want into a keypad it brings 
that bin down to an access area so you can grab what you need. The machine is 
30 or so feet tall and is designed to take the place of several pick-stations. 
(made by the Modula company – VLM)

Has anyone seen/protected one of these before?

Matt

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sloped Roof in ESFR system

2017-05-10 Thread Mike Stossel
I started in FM data sheet 2-0 section 2.2.1.6 ceiling slope.  This directs you 
to the definition of a false ceiling in appendix A and Data Sheet 1-12.  
Appendix A says that a suitable ceiling would be 3/8” plywood or gypsum board 
or you could also use corrugated or sheet metal.  It also directs you to 1-12 
for the installation procedures.

Best regards,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Wednesday, May 10, 2017 10:37 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sloped Roof in ESFR system

I am not able to find that in my copy of 1-12. Can you direct me to a section? 
I downloaded the May 2008 edition.

Thanks!

Matt


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Wednesday, May 10, 2017 9:14 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Sloped Roof in ESFR system

Data sheet 1-12, they say that the ceiling construction needs to withstand a 
minimum uplift pressure of 3 lb/ft².

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Wednesday, May 10, 2017 9:52 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Sloped Roof in ESFR system

What FM guidelines are you using? I had a project come up that used a drop 
ceiling in a storage location and I had a difficult time finding guidelines for 
ceiling construction.

Matt


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Wednesday, May 10, 2017 8:47 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Sloped Roof in ESFR system

I agree.  I am trying to get them to follow FM’s guidelines for the ceiling 
construction, but they currently have an architect saying that an acoustical 
ceiling will be adequate.  Since FM’s way will be more expensive, and the 
architect is approving it, the owner will most likely be going with the 
acoustical ceiling.  They essentially said that if I cannot produce anything in 
NFPA 13 that doesn’t allow it, then why should they follow FM since they are 
not insured by them.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Pete Schwab
Sent: Wednesday, May 10, 2017 9:40 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Sloped Roof in ESFR system

My concern would be what is the ceiling constructed of. If it is an acoustical 
tile ceiling with no clips I would be concerned with the velocity of the fire 
plume popping tiles before operating a sprinkler.

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com<http://www.waynefire.com/>

[Description: cid:image001.png@01CBEADF.99691B40]

I sleep in a sprinklered home, do you?



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Denhardt
Sent: Wednesday, May 10, 2017 8:02 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Sloped Roof in ESFR system

Confirmed - light hazard.

John August Denhardt, P.E.
Strickland Fire Protection

On May 10, 2017, at 7:13 AM, Richard Carr 
<rc...@coxfire.com<mailto:rc...@coxfire.com>> wrote:
Yes, unused attic is light hazard but you are limited on head spacing.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
rc...@coxfire.com<mailto:rc...@coxfire.com>
904-781-8227

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Wednesday, May 10, 2017 7:11 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Sloped Roof in ESFR system

I am currently working on an old wood building that my client wants to use for 
rack storage.  The building has a sloped roof that exceeds the allowable pitch 
so they will be installing a dropped ceiling to create the flat surface.  The 
area above the ceiling will now be a combustible concealed space that needs 
protection.  Nothing will be stored above th

RE: Sloped Roof in ESFR system

2017-05-10 Thread Mike Stossel
Data sheet 1-12, they say that the ceiling construction needs to withstand a 
minimum uplift pressure of 3 lb/ft².

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Wednesday, May 10, 2017 9:52 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sloped Roof in ESFR system

What FM guidelines are you using? I had a project come up that used a drop 
ceiling in a storage location and I had a difficult time finding guidelines for 
ceiling construction.

Matt


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Wednesday, May 10, 2017 8:47 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Sloped Roof in ESFR system

I agree.  I am trying to get them to follow FM’s guidelines for the ceiling 
construction, but they currently have an architect saying that an acoustical 
ceiling will be adequate.  Since FM’s way will be more expensive, and the 
architect is approving it, the owner will most likely be going with the 
acoustical ceiling.  They essentially said that if I cannot produce anything in 
NFPA 13 that doesn’t allow it, then why should they follow FM since they are 
not insured by them.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Pete Schwab
Sent: Wednesday, May 10, 2017 9:40 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Sloped Roof in ESFR system

My concern would be what is the ceiling constructed of. If it is an acoustical 
tile ceiling with no clips I would be concerned with the velocity of the fire 
plume popping tiles before operating a sprinkler.

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com<http://www.waynefire.com/>

[Description: cid:image001.png@01CBEADF.99691B40]

I sleep in a sprinklered home, do you?



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Denhardt
Sent: Wednesday, May 10, 2017 8:02 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Sloped Roof in ESFR system

Confirmed - light hazard.

John August Denhardt, P.E.
Strickland Fire Protection

On May 10, 2017, at 7:13 AM, Richard Carr 
<rc...@coxfire.com<mailto:rc...@coxfire.com>> wrote:
Yes, unused attic is light hazard but you are limited on head spacing.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
rc...@coxfire.com<mailto:rc...@coxfire.com>
904-781-8227

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Wednesday, May 10, 2017 7:11 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Sloped Roof in ESFR system

I am currently working on an old wood building that my client wants to use for 
rack storage.  The building has a sloped roof that exceeds the allowable pitch 
so they will be installing a dropped ceiling to create the flat surface.  The 
area above the ceiling will now be a combustible concealed space that needs 
protection.  Nothing will be stored above the ceiling, would the area above the 
ceiling be considered light hazard?  From everything that I can find, I believe 
it would be, but I would appreciate the forums input.

Thanks,

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: RE: Sloped Roof in ESFR system

2017-05-10 Thread Mike Stossel
They didn’t say, but I will be recommending it if they decide on the acoustical 
ceiling.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com
Sent: Wednesday, May 10, 2017 9:54 AM
To: Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: Re: RE: Sloped Roof in ESFR system

Clips on the ceiling tiles?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080 (ofc)
860-553-3553 (fax)
860-608-4559 (cell)



On May 10, 2017 at 9:47 AM, mailto:m...@knssprinkler.com>> wrote:
I agree.  I am trying to get them to follow FM’s guidelines for the ceiling 
construction, but they currently have an architect saying that an acoustical 
ceiling will be adequate.  Since FM’s way will be more expensive, and the 
architect is approving it, the owner will most likely be going with the 
acoustical ceiling.  They essentially said that if I cannot produce anything in 
NFPA 13 that doesn’t allow it, then why should they follow FM since they are 
not insured by them.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Pete Schwab
Sent: Wednesday, May 10, 2017 9:40 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Sloped Roof in ESFR system

My concern would be what is the ceiling constructed of. If it is an acoustical 
tile ceiling with no clips I would be concerned with the velocity of the fire 
plume popping tiles before operating a sprinkler.

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com<http://www.waynefire.com/>

[Description: cid:image001.png@01CBEADF.99691B40]

I sleep in a sprinklered home, do you?



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Denhardt
Sent: Wednesday, May 10, 2017 8:02 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Sloped Roof in ESFR system

Confirmed - light hazard.

John August Denhardt, P.E.
Strickland Fire Protection

On May 10, 2017, at 7:13 AM, Richard Carr 
<rc...@coxfire.com<mailto:rc...@coxfire.com>> wrote:
Yes, unused attic is light hazard but you are limited on head spacing.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
rc...@coxfire.com<mailto:rc...@coxfire.com>
904-781-8227

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Wednesday, May 10, 2017 7:11 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Sloped Roof in ESFR system

I am currently working on an old wood building that my client wants to use for 
rack storage.  The building has a sloped roof that exceeds the allowable pitch 
so they will be installing a dropped ceiling to create the flat surface.  The 
area above the ceiling will now be a combustible concealed space that needs 
protection.  Nothing will be stored above the ceiling, would the area above the 
ceiling be considered light hazard?  From everything that I can find, I believe 
it would be, but I would appreciate the forums input.

Thanks,

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___ Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sloped Roof in ESFR system

2017-05-10 Thread Mike Stossel
I agree.  I am trying to get them to follow FM’s guidelines for the ceiling 
construction, but they currently have an architect saying that an acoustical 
ceiling will be adequate.  Since FM’s way will be more expensive, and the 
architect is approving it, the owner will most likely be going with the 
acoustical ceiling.  They essentially said that if I cannot produce anything in 
NFPA 13 that doesn’t allow it, then why should they follow FM since they are 
not insured by them.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Pete Schwab
Sent: Wednesday, May 10, 2017 9:40 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sloped Roof in ESFR system

My concern would be what is the ceiling constructed of. If it is an acoustical 
tile ceiling with no clips I would be concerned with the velocity of the fire 
plume popping tiles before operating a sprinkler.

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com<http://www.waynefire.com/>

[Description: cid:image001.png@01CBEADF.99691B40]

I sleep in a sprinklered home, do you?



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Denhardt
Sent: Wednesday, May 10, 2017 8:02 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Sloped Roof in ESFR system

Confirmed - light hazard.

John August Denhardt, P.E.
Strickland Fire Protection

On May 10, 2017, at 7:13 AM, Richard Carr 
<rc...@coxfire.com<mailto:rc...@coxfire.com>> wrote:
Yes, unused attic is light hazard but you are limited on head spacing.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
6555 Grace Lane.
Jacksonville, Fl. 32205
rc...@coxfire.com<mailto:rc...@coxfire.com>
904-781-8227

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Wednesday, May 10, 2017 7:11 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Sloped Roof in ESFR system

I am currently working on an old wood building that my client wants to use for 
rack storage.  The building has a sloped roof that exceeds the allowable pitch 
so they will be installing a dropped ceiling to create the flat surface.  The 
area above the ceiling will now be a combustible concealed space that needs 
protection.  Nothing will be stored above the ceiling, would the area above the 
ceiling be considered light hazard?  From everything that I can find, I believe 
it would be, but I would appreciate the forums input.

Thanks,

Mike Stossel SET

36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Sloped Roof in ESFR system

2017-05-10 Thread Mike Stossel
I am currently working on an old wood building that my client wants to use for 
rack storage.  The building has a sloped roof that exceeds the allowable pitch 
so they will be installing a dropped ceiling to create the flat surface.  The 
area above the ceiling will now be a combustible concealed space that needs 
protection.  Nothing will be stored above the ceiling, would the area above the 
ceiling be considered light hazard?  From everything that I can find, I believe 
it would be, but I would appreciate the forums input.

Thanks,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Air Relief Time

2017-03-01 Thread Mike Stossel
Brad is actually trying to help me off forum.  It is definitely a difficult 
calculation to run and way beyond me.  At least if it had a dry valve I could 
run an FDT calculation, but it has nothing.  It is a closed system with an air 
compressor only.  A 2 ½” dump valve is located at each FDC with a gauge.  When 
the fire department arrives they open the dump valve and when it hits zero 
starts pressurizing the temporary standpipe.  The air in the system is just 
supervisory.  You have low pressure and high pressure alarms attached just like 
a dry valve, but minus the dry valve.  The air is just to make sure the system 
is always solid for the fire department.  If someone should tamper with it or 
break something the alarm will notify that a repair is needed.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tom Duross
Sent: Wednesday, March 1, 2017 9:07 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Air Relief Time

Sounds like an automatic dry standpipe off a low differential dry valve but 
you’re not concerned about water delivery time or even water pushing out the 
air?  Just a 2 ½” outlet at the top?
Where’s Brad?

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Wednesday, March 01, 2017 9:01 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Air Relief Time

The standing air pressure is a minimum of 13psi and a maximum of 18psi.  The 
gauge located at the FDC must read zero within 3 minutes of full open.  
Compressor is connected and running.  Four 4” stacks top of stack is 70’0”.

Thanks,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tom Duross
Sent: Wednesday, March 1, 2017 7:54 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Air Relief Time

NYC has a requirement for construction standpipes in all high-rises to be 
pressurized and monitored with a placard indicating required FDC pressures for 
required flows at each floor.  Boston adopted this last year.  Roadway 
standpipes are required to be timed for water delivery but are empty and have 
automatic air vents  at the FDV’s.  What’s the application requiring exhaust of 
standing air pressure?  Is there a compressor connected and running?  
Horizontal or vertical installation?
TD

Sidestep the issue. If you can, pull a slight vacuum on the standpipe instead 
of pressurizing it.


On Feb 28, 2017, at 7:17 AM, Mike Stossel 
<m...@knssprinkler.com<mailto:m...@knssprinkler.com>> wrote:

I am trying to calculate the time it will take for a 2-1/2” hose valve to 
relieve a standpipe system of air.  I am designing a temporary standpipe system 
in NYC and the requirement is to fill the entire system with air and a single 
2-1/2” hose valve needs to relieve the pressure within 3 minutes or a second 
will need to be added.  My total system volume will be 1902 gallons and the 
staring air pressure will be at 18psi.  Does anyone know of a way to calculate 
this?

Thanks for the help.

Mike Stossel SET
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Air Relief Time

2017-03-01 Thread Mike Stossel
The standing air pressure is a minimum of 13psi and a maximum of 18psi.  The 
gauge located at the FDC must read zero within 3 minutes of full open.  
Compressor is connected and running.  Four 4” stacks top of stack is 70’0”.

Thanks,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tom Duross
Sent: Wednesday, March 1, 2017 7:54 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Air Relief Time

NYC has a requirement for construction standpipes in all high-rises to be 
pressurized and monitored with a placard indicating required FDC pressures for 
required flows at each floor.  Boston adopted this last year.  Roadway 
standpipes are required to be timed for water delivery but are empty and have 
automatic air vents  at the FDV’s.  What’s the application requiring exhaust of 
standing air pressure?  Is there a compressor connected and running?  
Horizontal or vertical installation?
TD

Sidestep the issue. If you can, pull a slight vacuum on the standpipe instead 
of pressurizing it.


On Feb 28, 2017, at 7:17 AM, Mike Stossel 
<m...@knssprinkler.com<mailto:m...@knssprinkler.com>> wrote:

I am trying to calculate the time it will take for a 2-1/2” hose valve to 
relieve a standpipe system of air.  I am designing a temporary standpipe system 
in NYC and the requirement is to fill the entire system with air and a single 
2-1/2” hose valve needs to relieve the pressure within 3 minutes or a second 
will need to be added.  My total system volume will be 1902 gallons and the 
staring air pressure will be at 18psi.  Does anyone know of a way to calculate 
this?

Thanks for the help.

Mike Stossel SET
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Air Relief Time

2017-02-28 Thread Mike Stossel
The maximum minutes would be three the minimum can be anything, and the ambient 
air I would say place at about 30 since we are headed into Spring.  Yes, you 
can definitely contact me off Forum, I greatly appreciate the help.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brad Casterline
Sent: Tuesday, February 28, 2017 11:08 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Air Relief Time

Mike,

1) Need to know the min. and max. ambient air temperatures.

2) May I contact you off Forum?

Brad


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Tuesday, February 28, 2017 7:17 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Air Relief Time

I am trying to calculate the time it will take for a 2-1/2" hose valve to 
relieve a standpipe system of air.  I am designing a temporary standpipe system 
in NYC and the requirement is to fill the entire system with air and a single 
2-1/2" hose valve needs to relieve the pressure within 3 minutes or a second 
will need to be added.  My total system volume will be 1902 gallons and the 
staring air pressure will be at 18psi.  Does anyone know of a way to calculate 
this?

Thanks for the help.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Owner Info Certicate

2017-02-15 Thread Mike Stossel
Me to please.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jeremy Blocker
Sent: Wednesday, February 15, 2017 10:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Owner Info Certicate

I would like a copy as well please.
JJ
Sent from my iPhone 6

On Feb 15, 2017, at 8:02 AM, rongreenman . 
<rongreen...@gmail.com<mailto:rongreen...@gmail.com>> wrote:
Frank, Roland-- This form in Word might be a good addition to the Member 
Center/Document Center/Other Miscellaneous Forms on the website.

On Wed, Feb 15, 2017 at 6:57 AM, Todd Williams 
<fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com>> wrote:
Actually I wouldn't mind a copy either if you would like to share
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
Office: 860-535-2080<tel:(860)%20535-2080>
Cell: 860-608-4559
Fax: 860-553-3553<tel:(860)%20553-3553>

On Tue, Feb 14, 2017 at 7:25 PM, Paul Cetani 
<pa...@norcalfire.com<mailto:pa...@norcalfire.com>> wrote:
Hey Scott,
I would love a copy of that in Word as well if you wouldn’t mind. It would save 
me the time to create my own….

Paul B. Cetani
Exec. Vice President

Nor Cal Fire, Inc.
16840 Joleen Way, Bldg A
Morgan Hill, CA 95037
T 408-776-1580<tel:(408)%20776-1580>
F 408-776-1590<tel:(408)%20776-1590>
pa...@norcalfire.com<mailto:pa...@norcalfire.com>
www.norcalfire.com<http://www.norcalfire.com/>

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Scott Futrell
Sent: Monday, February 13, 2017 5:24 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Owner Info Certicate

Todd,
We don’t start bid documents without these filled out and signed by the 
occupants – we have a Word document we send them.
We don’t start plan review without them included in the submittal.

Scott

Office: (763) 425-1001 x 2<tel:(763)%20425-1001>
Cell: (612) 759-5556<tel:(612)%20759-5556>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Todd Williams
Sent: Monday, February 13, 2017 10:31 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Owner Info Certicate

Does anyone actually get those?
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
Office: 860-535-2080<tel:(860)%20535-2080>
Cell: 860-608-4559
Fax: 860-553-3553<tel:(860)%20553-3553>

On Mon, Feb 13, 2017 at 11:13 AM, Travis Mack, SET 
<tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>> wrote:
Does anyone have this in a word or excel format that they wouldn't mind
sending me?


--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271<tel:(480)%20505-9271>
fax: 866-430-6107<tel:(866)%20430-6107>
email:tm...@mfpdesign.com<mailto:email%3atm...@mfpdesign.com>

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Ron Greenman

rongreen...@gmail.com<mailto:rongreen...@gmail.com>

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Victaulic IR Fittings

2017-02-15 Thread Mike Stossel
I thought the takeout for the fittings were shorter?  I also heard from my 
client that if you want to go with back to back 90’s you either need to use 
their nipple or a long radius 90, that it doesn’t fit with the shorts.  My 
client is thinking about trying them and asked my opinion, but since I have 
never used them I figured I would tap the massive amount of knowledge on the 
forum.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Todd Williams
Sent: Wednesday, February 15, 2017 8:30 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Victaulic IR Fittings

I have one client who is trying them out on a project. So far the feedback has 
been neutral. At least the takeouts are the same.
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
Office: 860-535-2080
Cell: 860-608-4559
Fax: 860-553-3553

On Wed, Feb 15, 2017 at 8:07 AM, Mike Stossel 
<m...@knssprinkler.com<mailto:m...@knssprinkler.com>> wrote:
I would appreciate the forums opinions and comments on if they have tried 
Victaulic’s IR fittings?  Is it worth switching your fabrication and 
installation strategies over, and does the positives out way the negatives?

Thanks,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Victaulic IR Fittings

2017-02-15 Thread Mike Stossel
I would appreciate the forums opinions and comments on if they have tried 
Victaulic's IR fittings?  Is it worth switching your fabrication and 
installation strategies over, and does the positives out way the negatives?

Thanks,

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Yard FDC Supply Line

2017-02-14 Thread Mike Stossel
I understand the concept of why they are looking for you to provide the 
calculation, but I didn’t think that was the code intent for the FDC.
NFPA 13, 2013
A.6.8.1 The purpose of the fire department connection is to supplement the 
water supply but not necessarily provide the entire sprinkler system demand. 
Fire department connections are not intended to deliver a specific volume of 
water.


Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: Tuesday, February 14, 2017 4:22 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Yard FDC Supply Line

Mike:

If I do that, then it seems to me that I’m not proving the FDC is capable of 
meeting the demand. I already proved the city supply could meet the demand when 
I calc’d  the areas originally. The idea of the FDC supply as a stand alone is 
screwy to me. I have always thought of it as a augmented source of water in 
case the fire outgrows the remote area.

Thanks,
John P

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Stossel
Sent: Tuesday, February 14, 2017 4:17 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Yard FDC Supply Line

Not sure if this would help, but if they won’t accept the code that Brad just 
provided why not include the public supply in you calculation like you would 
with an FDC/standpipe calculation?  I see below that you are currently removing 
it.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brad Casterline
Sent: Tuesday, February 14, 2017 3:56 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Yard FDC Supply Line


John,

Look at 13 (2013) A.8.17.2.3

That should do it, right?
Or is the Evelyn Wood adult ed speed reading course I took years ago messing me 
up here?

Brad
On Feb 14, 2017 2:32 PM, "John Paulsen" 
<j...@crwnfire.com<mailto:j...@crwnfire.com>> wrote:
Afternoon all!

I am trying to respond to a project engineers review letter questioning the 
size of the supply line for the FDC connection.

First, the facts:

Hazard –  Big Box Grocery Store
Systems -3 Wet Grid systems fed by 
2, 3” risers and a 4” riser for the stock room area which is .39 for 2,000 and 
is the  greatest demand.
FDC - 5” Stortz yard 
connection in the parking lot in front of the store. The risers are located in 
the rear. The site contractor has run 6” ductile
From the FDC to a spigot piece at the front of the building and we are 
proposing to connect to the spigot piece and run 4” through the store to the 
riser manifold.
Fire
Department -I contact the local FD and obtained their standard response 
pumper pressures – 150 PSI / 1,500 GPM

I have reviewed NFPA-13 8.17.2 and I am trying to determine the proper 
procedure for calculating the FDC line size. I can configure the source of 
supply as the FDC with the pumper output as the supply curve, remove the 
municipal water supply and the results show that this meets the demand for 2 of 
the 3 systems. The greatest demand system (the Stock Room) is 13 PSI over the 
curve for the FDC supply.

I have always sized the FDC Connection as 4” or the size of the largest riser 
pipe and as a “supplemental supply” to be used in conjunction with the city 
water supply, not an alternative source independent of the municipal supply. 
The only thing that I can find that would seem to support the Engineer’s 
position is 8.17.2.4.7.2 which calls for a sign at the FDC telling the 
responders the required inlet pressure (above 150 PSI) required to meet the 
greatest demand. There is nothing in 8.17.2.3 that says the size is determined 
by the greatest system demand.

The way I am seeing this right now, I have two choices:


1.)Increase the interior 4” to 6” as the engineer wants.

OR

2.)Have a sign installed on the FDC asking for 175 PSI inlet pressure 
(After getting AHJ blessing of course) and hope the engineer will accept it.

Now I ask for other opinions from my learned colleagues.

Thanks,

John Paulsen – SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P – 614-782-2438<tel:(614)%20782-2438>
F – 614-782-2374<tel:(614)%20782-2374>
C – 614-348-8206<tel:(614)%20348-8206>





___
Sprinklerforum mailing list
Sprinklerforum@lists

RE: Yard FDC Supply Line

2017-02-14 Thread Mike Stossel
Not sure if this would help, but if they won’t accept the code that Brad just 
provided why not include the public supply in you calculation like you would 
with an FDC/standpipe calculation?  I see below that you are currently removing 
it.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brad Casterline
Sent: Tuesday, February 14, 2017 3:56 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Yard FDC Supply Line


John,

Look at 13 (2013) A.8.17.2.3

That should do it, right?
Or is the Evelyn Wood adult ed speed reading course I took years ago messing me 
up here?

Brad
On Feb 14, 2017 2:32 PM, "John Paulsen" 
<j...@crwnfire.com<mailto:j...@crwnfire.com>> wrote:
Afternoon all!

I am trying to respond to a project engineers review letter questioning the 
size of the supply line for the FDC connection.

First, the facts:

Hazard –  Big Box Grocery Store
Systems -3 Wet Grid systems fed by 
2, 3” risers and a 4” riser for the stock room area which is .39 for 2,000 and 
is the  greatest demand.
FDC - 5” Stortz yard 
connection in the parking lot in front of the store. The risers are located in 
the rear. The site contractor has run 6” ductile
From the FDC to a spigot piece at the front of the building and we are 
proposing to connect to the spigot piece and run 4” through the store to the 
riser manifold.
Fire
Department -I contact the local FD and obtained their standard response 
pumper pressures – 150 PSI / 1,500 GPM

I have reviewed NFPA-13 8.17.2 and I am trying to determine the proper 
procedure for calculating the FDC line size. I can configure the source of 
supply as the FDC with the pumper output as the supply curve, remove the 
municipal water supply and the results show that this meets the demand for 2 of 
the 3 systems. The greatest demand system (the Stock Room) is 13 PSI over the 
curve for the FDC supply.

I have always sized the FDC Connection as 4” or the size of the largest riser 
pipe and as a “supplemental supply” to be used in conjunction with the city 
water supply, not an alternative source independent of the municipal supply. 
The only thing that I can find that would seem to support the Engineer’s 
position is 8.17.2.4.7.2 which calls for a sign at the FDC telling the 
responders the required inlet pressure (above 150 PSI) required to meet the 
greatest demand. There is nothing in 8.17.2.3 that says the size is determined 
by the greatest system demand.

The way I am seeing this right now, I have two choices:


1.)Increase the interior 4” to 6” as the engineer wants.

OR

2.)Have a sign installed on the FDC asking for 175 PSI inlet pressure 
(After getting AHJ blessing of course) and hope the engineer will accept it.

Now I ask for other opinions from my learned colleagues.

Thanks,

John Paulsen – SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P – 614-782-2438<tel:(614)%20782-2438>
F – 614-782-2374<tel:(614)%20782-2374>
C – 614-348-8206<tel:(614)%20348-8206>





___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Expansion Joints

2017-01-31 Thread Mike Stossel
A flexible coupling within 24" of the joint.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: Tuesday, January 31, 2017 11:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Expansion Joints

Does any consideration need to be given to a Building Expansion Joint? It's not 
a "Seismic Separation Joint" although it does have seismic bracing.

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Funky Wavy Soffit

2017-01-12 Thread Mike Stossel
Can you use the soffit against the wall rule from NFPA 13, 2013
8.6.5.1.2* Sprinklers shall be arranged to comply with one of the following 
arrangements:
(1) Subsection 8.5.5.2, Table 8.6.5.1.2, and Figure 8.6.5.1.2(a) shall be 
followed.
(2) Sprinklers shall be permitted to be spaced on opposite sides of 
obstructions not exceeding 4 ft (1.2 m) in width, provided the distance from 
the centerline of the obstruction to the sprinklers does not exceed one-half 
the allowable distance permitted between sprinklers.
(3) Obstructions located against the wall and that are not over 30 in. (762 mm) 
in width shall be permitted to be protected in accordance with Figure 
8.6.5.1.2(b).
(4) Obstructions located against the wall and that are not over 24 in. (610 mm) 
in width shall be permitted to be protected in accordance with Figure 
8.6.5.1.2(c). The maximum distance between the sprinkler and the wall
shall be measured from the sprinkler to the wall behind the obstruction and not 
to the face of the obstruction.
A.8.6.5.1.2 The intent of 8.6.5.1.2(3) is to apply to soffits that are located 
within the 18 in. (457 mm) plane from the sprinkler deflector. A soffit or 
other obstruction (i.e., shelf) located against a wall that is located entirely 
below the 18 in. (457 mm) plane from the sprinkler deflector should be in 
accordance with 8.6.5.3.3. (See Figure A.8.6.5.1.2.)

[cid:image001.png@01D26CC6.8E3702E0]

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Thursday, January 12, 2017 11:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Funky Wavy Soffit

No. I got up on the wrong side of the bed and that's a face plant into a a 
rough cedar wall. still pulling out splinters, Brian. But do you get my point? 
You may be looking at the reference numbers in the 2007 edition where you are 
and I'm looking at 2013 and the numbers don't match. I always tell my people to 
make it easy for customers to give you their money and that advice applies 
here. When you're asking for free help and looking for code references to argue 
a point make it easy for the other Forumites to help you. I now when I pull out 
the book to help and 8.6.5.3 is not the 48" rule because you're using a 
different edition than I am, then I'm done looking, but tell me the edition you 
are using and I can pull out almost anything back to '68 (I'm missing a 
couple). I think Leyton can tell you I was able to get him a reference to a 
building built in maybe '74 that hadn't changed use and saved his client a pile 
of dough that someone who the Wizard had just bestowed a golden badge upon 
wanted spent.

On Thu, Jan 12, 2017 at 7:44 AM, Brian Harris 
<bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>> wrote:
Ron-
You want my address?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of rongreenman .
Sent: Thursday, January 12, 2017 10:43 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Funky Wavy Soffit

I think that whenever someone posts a reference number and doesn't include the 
text or at least the edition he should be severely beaten.

On Thu, Jan 12, 2017 at 6:24 AM, Brian Harris 
<bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>> wrote:
We have a grocery store that has a wavy kinda soffit (see dropbox file link 
below) around the perimeter of most of the store. The top of this soffit is 
approximately 5’0” below the overhead sprinklers & is less than 48” at the 
widest points. With that being said are additional heads needed in this lower 
soffit? In my opinion 8.6.5.2 would not apply since the pattern development is 
not affected so the next stop would be 8.6.5.3. The only thing that stands out 
to me there would be the 48” width we I do not have. So I say no additional 
heads needed below, what say you?

https://www.dropbox.com/s/3klcgh37fhowmp8/Wavy%20Soffit.pdf?dl=0

Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989<tel:(704)%20896-9989>
Fax: 704.896.1935<tel:(704)%20896-1935>


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Ron Greenman

rongreen...@gmail.com<mailto:rongreen...@gmail.com>

253.576.9700<tel:(253)%20576-9700>

The Universe is monstrously indifferent to the presence

RE: DI Piping

2017-01-06 Thread Mike Stossel
Ductile Iron

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Douglas Hicks
Sent: Friday, January 6, 2017 1:52 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: DI Piping

I am sure DI does not mean De-ionized, so what is Di pipe?  Schedule 10. 7.  5? 
 I do know I cannot thread 10 with my 300 Ridgid, but I can crush 5, 7 and 10 
with the threader.

From: rongreenman .<mailto:rongreen...@gmail.com>
Sent: Friday, January 06, 2017 10:23 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: DI Piping

Yes I meant fittings. Haven't found any DI pipe that can be threaded.

On Fri, Jan 6, 2017 at 10:20 AM Tom Duross 
<tduro...@comcast.net<mailto:tduro...@comcast.net>> wrote:
What Ron said (I think he meant fittings) and I’ve seen many instances of 
grooved unlined DI piping within pump rooms (talk about heavy!) but if used on 
the potable side, I believe like Dave said, cement lined CL52.
TD


In many companies DI has replaced CI for small screwed piping. Grooved fittings 
are DI. The only problem I could see is the connection method and restraint, 
and small leakage if using PE fittings on the pipe.
On Fri, Jan 6, 2017 at 9:24 AM å...  
<eurekaig...@gmail.com<mailto:eurekaig...@gmail.com>> wrote:

I don't know of a many good reasons to deny this design.  If anyone calls you 
on your judgment, preempt their question by caveatting your decision using 
Section 1.5.

Scot Deal
Excelsior Fire & Risk Engineering
gsm:  +420 722 141 478
___

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
--
Sent from Gmail Mobile

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Bracing on vertical sprinkler drops - 15 ft long

2016-11-14 Thread Mike Stossel
Craig,

I don’t know of any requirement for the length of drops, especially in building 
that don’t require seismic restraint.  Drops to a single sprinkler are 
excluded.  The only requirement I know of is for sprigs and not drops, and in 
the commentary it specifies that it is not required on drops.
A.9.3.2.3
 (5) Within 24 in. (610 mm) of the top of drops exceeding 15 ft (4.6 m) in 
length to portions of systems supplying more than one sprinkler, regardless of 
pipe size
Drops to a single sprinkler are not required to be equipped with a flexible 
coupling because of the concern regarding the difficulty of sprinkler 
installation and replacement [see 9.3.2.3(6)]. The rotation inherent in a 
flexible coupling can prevent the development of the torque necessary to 
properly install the sprinkler.
9.3.6.6* Sprigs 4 ft (1.2 m) or longer shall be restrained against lateral 
movement.
Sprig-ups are addressed in 9.3.6.6. A vertical sprig, or a sprig-up, is 
considered the opposite of a pipe drop. A vertical sprig is a pipe rising from 
the branch line to serve an individual  upright sprinkler. They are susceptible 
to rotation during relatively minor seismic events.  The requirement for 
restraint of sprigs was originally instituted for sprigs more than 8 ft (2.4 m) 
in length but was changed in the 1996 edition of NFPA 13 to apply to sprigs 
exceeding 4 ft (1.2 m) in length. The change was based on observations of 
rotated sprigs following the Northridge, CA, earthquake. The additional 
stability gained from this requirement results in time and money saved, because 
sprigs do not have to be manually repositioned after the event. The restraint 
provisions of 9.3.6.6 do not apply to drops to individual sprinklers, because 
gravity acts to pull them back to center.

Hope this helps.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of craig.pr...@ch2m.com
Sent: Monday, November 14, 2016 12:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Bracing on vertical sprinkler drops - 15 ft long

I’ve been hunting the answer to this question and so far have come up short.

I have a case where there are drops off the bottom of 2” branch lines down to 
sprinklers in a ceiling 15 feet below.  They are hard piped to within 2-3 ft of 
the ceiling with a flex drop from that point to the ceiling.

This is seismic design cat. B, so no EQ bracing required.

I’ve been trying to find rules on bracing of vertical drops but find only info 
on unsupported armovers, which this is not.

Also the pump rated pressure is 150 psi so the system will see pressures over 
100 psi.

Any help on locating that elusive one line or paragraph on bracing requirements 
for vertical drops would be appreciated.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.