I’m not sure if the sprinkler will work for your application, but have you 
looked at Victaulic’s LP-46 sprinkler?  If I remember right it can be used on a 
dry system and depending upon what commodity you are protecting it can be used 
in buildings up to 45’0”  high with storage up to 40’0”.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com
Sent: Tuesday, June 13, 2017 8:30 PM
To: Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: RE: Heating cable and 1" wrap.

I gave it the 90 second overview. This was not a detailed analysis. I assumed a 
50 degree temperature differential (+40 to -10?). I'm not even sure where this 
place is.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-553-3553<tel:860-553-3553> (fax)
860-608-4559<tel:860-608-4559> (cell)



On Jun 13, 2017 at 8:16 PM, <Mark.Phelps<mailto:mphe...@aerofire.com>> wrote:
Hey Todd,
On your power calculations, what minimum ambient temperature did you use for 
the water filled pipe.

Mark at Aero
602 820-7894

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com>
Sent: Tuesday, June 13, 2017 4:50 PM
To: Sprinklerforum
Subject: RE: Heating cable and 1" wrap.

Pentairthermal.com has information that you can use to estimate the power 
demand. I went through some numbers (with a lot of assumptions) and came up 
with around 11 kW of power required. Wait until he sees that cost. I think this 
guy is a looney.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-553-3553<tel:860-553-3553> (fax)
860-608-4559<tel:860-608-4559> (cell)




On Jun 13, 2017 at 6:49 PM, <Art Tiroly<mailto:atir...@atcofirepro.com>> wrote:
About 4000 Ft. of pipe, 300 sprinklers.

Art

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Paulsen
Sent: Tuesday, June 13, 2017 6:42 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Heating cable and 1" wrap.

Well, one thing is for sure, your customer would be on AEP’s (American Electric 
Power) Christmas card list the first time they powered the trace system up! 
Hundreds of feet of resistance heating cable…what a “peak” demand that would 
set.

John Paulsen – SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P – 614-782-2438
F – 614-782-2374
C – 614-348-8206



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack, SET
Sent: Tuesday, June 13, 2017 6:25 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Heating cable and 1" wrap.


Yeah...I had some one tell me it was like $5/ft for the materials.  Now, using 
Professor Greenman's qualitative formula, it would be about $10/ft + all the 
extras :-) I don't know how accurate or not, but that sure would keep me from 
doing an entire system in it.

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

email:tm...@mfpdesign.com<mailto:email:tm...@mfpdesign.com>



http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign

LinkedIn: https://www.linkedin.com/in/travismack
On 6/13/2017 3:08 PM, rongreenman . wrote:
Just figure a lot per foot, double it, and then add on the extras.

On Tue, Jun 13, 2017 at 3:05 PM, Art Tiroly 
<atir...@atcofirepro.com<mailto:atir...@atcofirepro.com>> wrote:
Thanks.
How do you determine the cost of operating a heat trace system?
That is important to convey

Ary

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Jeff Normand
Sent: Tuesday, June 13, 2017 5:27 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Heating cable and 1" wrap.

If ceiling is too costly wait until you see the price of heat tracing an entire 
system.



On Tue, Jun 13, 2017 at 4:20 PM, Art Tiroly 
<atir...@atcofirepro.com<mailto:atir...@atcofirepro.com>> wrote:
They need store packaging material, idle pallets.

Ceiling is also too costly.

Art

From: Sprinklerforum 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>]
 On Behalf Of Matt Grise
Sent: Tuesday, June 13, 2017 5:16 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Heating cable and 1" wrap.

What are they storing?

Could they put in a false ceiling?

Matt


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Art Tiroly
Sent: Tuesday, June 13, 2017 3:58 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Heating cable and 1" wrap.

I have a client that is renovating an uninsulated 30,000 SF shed warehouse.
He does not want to heat the building.

Dry system requirements for solid piled storage over 25Ft high in 35 Ft. high 
building are not available.

I am pushing for an ESFR wet system in a heated building.
Rather than heating an uninsulated building owner suggests we heat the 
sprinkler pipe with heat cable and 1” insulation.
This method is in 13. Tyco has a system to apply heating cable to branch lines 
and cross mains.

In over 50 years I have never seen or heard of heat tracing being done. I think 
it is a mistake due to reliability and cost
There must be reasons this heating method is not being installed on a sprinkler 
system.

What arguments can I use to avoid this method of keeping a wet grid system from 
freezing.



Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899<tel:%28216%29%20621-8899>
216-570-7030<tel:%28216%29%20570-7030> cell


[Image removed by 
sender.]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>

Virus-free. 
www.avast.com<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>



_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Ron Greenman

rongreen...@gmail.com<mailto:rongreen...@gmail.com>

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)





_______________________________________________

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________ Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>