Fw: Transformer Question

2001-04-25 Thread Chris Wells
- Original Message - From: Wells, Christopher D To: 'Chris Wells' Sent: Wednesday, April 25, 2001 9:19 AM Subject: RE: Transformer Question > Tac Pham - Regarding transformer recognition. > When I have designed a custom power supply like Ken has and the transformer > is made by an out

RE: Request for help RE: NEMA 7

2001-04-25 Thread Dan Kinney (A)
Andy, Supplement A of NEMA250-1997 contains information on NEMA Type 7. It is defined as "Enclosures constructed for indoor use in hazardous locations classified as Class I, Division 1, Groups A, B, C, or D as defined in NFPA 70." It goes on with more information than I am willing to type. Give

RE: Request for help RE: NEMA 7

2001-04-25 Thread Nikolassy, Anton
NEMA 250-1997, Supplement "A" describes applications, features and test criteria of enclosures for hazardous (classified) locations. Certification of products for hazardous (classified) locations is factory mutual research's specialty. If I can be of service, please give me a call, fax or email.

Re: Request for help RE: NEMA 7

2001-04-25 Thread Ted . Eckert
Enclosure ratings 7, 8, 9 and 10 are for hazardous locations. An enclosure rating of NEMA 7 is defined as "Enclosures constructed for indoor use in hazardous locations classified as Class I, Division 1, Groups A, B, C, or D as defined in NFPA 70." NEMA 7 defines an enclosure that will contain a

RE: Request for help RE: NEMA 7

2001-04-25 Thread Michael Taylor
An enclosure rated NEMA-7 is intended for use in Explosive atmospheres (read - big, heavy & VERY expensive). You would need to know the Class, Division & Group to select the correctly rated enclosure. This (more or less) corresponds to the European EEx Zone, CAT. and Group classification. See IEC-

RE: Request for help RE: NEMA 7

2001-04-25 Thread Andrew Wood
Michael, Thanks for the response. I am familiar with many of the European requirements for Hazardous Areas and am also aware of the US Division and Zone classifications (NEC 500 & 505?). However we have not come across NEMA 7 before. Now that I know it is genuine, I can dig deeper. Do

RE: [Fwd: System Laser Safety questions]

2001-04-25 Thread Peter Tarver
Hello, Marko. A remote interlock connector is required when there is potential human exposure to laser radiation, as might be found in labs or industrial environments where the laser is cutting something or marking a product (there may be other applications). In such an environment, there is a n

Request for help RE: NEMA 7

2001-04-25 Thread Andrew Wood
Colleagues I have been contacted by one of our sales engineers who has a request to quote for supplying a product suitable for hazardous areas meeting NEMA 7 rating. He has already spent some time surfing the web. My NEMA to IP rating conversion chart only lists NEMA 1, 2 3, 3R, 3S, 4, 4X, 5, 6

Re: ESD generators max Contact discharge level

2001-04-25 Thread Cortland Richmond
Lower voltages, because of less corona, tend to have more energy, sooner, relative to the total. You might pass a 15 kV air discharge test -- but fail, lower. We ALWAYS want margin, and others ALWAYS want none. My experience in a previous area of the industry is, this lasts until a rash of field

回覆: Requirements in Hungary: Factory-Floor Test Equipment

2001-04-25 Thread 岑國綸
Eric- you can try with the Hungarian Institute for Testing Electrical Equipment (MEEI). website address: http://www.meei.hu/en/jogszab.shtml Alain Sam-Lai Gigabyte Technology -原始郵件- 寄件者: eric.lif...@ni.com [mailto:eric.lif...@ni.com] 寄件日期: 2001年4月25日 AM 06:22 收件者: emc-p...@ieee.org 主旨: R

[Fwd: System Laser Safety questions]

2001-04-25 Thread Dave Heald
Forwarded for Marko Radojicic. Please include Marko in any replies. Dave Heald Original Message Subject: System Laser Safety questions List-Post: emc-pstc@listserv.ieee.org Date: Tue, 24 Apr 2001 14:50:36 -0700 From: Marko Radojicic To: "EMC-PSTC (E-mail)" Greetings, We hav