Hi Ed and the Group,
Ed said: "Did you create a write-up
on what those errors specifically were, and how it happened
that you noticed them in time to control them?"
I have not specifically written them up although I do tell them as
war
On 12/17/2014 5:55 PM, Pettit, Ghery wrote:
Indeed. I’m glad to see that I’m not the only one seeing this.
Ghery S. Pettit
I've also looked over testers shoulders and seen things done wrong.
Often it was because they didn't what was SUPPOSED to be done. We all
learn from mistakes, eh?
Cor
I’m also glad to see that I’m not the only one.
Best regards
Kris Carpentier,
From: Pettit, Ghery [mailto:ghery.pet...@intel.com]
Sent: woensdag 17 december 2014 23:55
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Brick power supplies and test errors (two topics)
Indeed. I’m glad to see th
Indeed. I’m glad to see that I’m not the only one seeing this.
Ghery S. Pettit
From: dward [mailto:dw...@pctestlab.com]
Sent: Wednesday, December 17, 2014 2:50 PM
To: Pettit, Ghery; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] Brick power supplies and test errors (two topics)
Exactly. While
Exactly. While assessors may look over paperwork, that does not actually mean
those involved in testing know what the standard to which they are testing
actually says or if they do that they actually test to them. Cannot tell you
how many times I review reports from supposedly accredited labs
Yes, but the standards I'm thinking of are core to the computer industry.
CISPR 22, CISPR 32, CISPR 24, ANSI C63.4. Really disturbing when you see key
things that aren't set up properly. It makes you wonder what the
qualifications are of the on-site assessors. Paperwork is usually fine, the
The only pathos there is we take ourselves so seriously that a suggestion
like that is rejected out-of-hand.
Ken Javor
Phone: (256) 650-5261
> From: Brian Oconnell
> Reply-To: Brian Oconnell
> Date: Wed, 17 Dec 2014 21:35:37 +
> To:
> Conversation: [PSES] Brick power supplies and test err
Pathos and tragedy, with a bit of comedy, in the EMC lab. Once had the sales
manager for a major lab say "we have never done that test but would give you a
good deal so we could get experience..."
Brian
From: Ed Price [mailto:edpr...@cox.net]
Sent: Wednesday, December 17, 2014 1:29 PM
To: EMC-
Ghery:
I found that business conditions have created large labs which strive to
provide one-stop compliance services, and that this concept is subject to
corruption by enthusiasm. By that, I mean that the labs often have a little
subsection which is tasked with doing nothing but expanding the r
Unless specifically stated in the safety standard used to assess the end-use
equipment, dunno. Might want to look at NFPA70E article 130.
Due to the calculations that must be performed in order properly label
equipment, gonna guess that the 'generic' warnings/cautions and symbols could
be appli
Dave --
ANSI Z535.4 is the standard for warning labels for equipment. Clarion, and
likely other vendors, have samples on their web page.
Mike
- Original Message -
From: "Dave Nyffenegger"
To: "EMC-PSTC"
Sent: Wednesday, December 17, 2014 1:34:29 PM
Subject: Re: [PSES] Arc Flash
So I’m looking at the new NFPA 79 2015 (which you can view on-line for free
now) and they have added 16.2.3 Electrical equipment for industrial machines
such as control panels and disconnects shall be marked according to ANSI Z535.4
to warn of shock and arc flash hazards. I don’t have a copy of
Surprise surprise:)
As long as assessment of labs is being done by people not even in the proper
field of expertise, should we really expect more??
Dennis Ward
This communication and its attachements contain information from PCTEST
Engineering Laboratory, Inc., and I sintended for
I brought up some serious problems with accredited labs at the ASC C63 meetings
in Mesa last month. One accrediting body seems interested in dealing with the
issue, the others not so much. It's so much fun to go into a lab that isn't
properly equipped to perform tests listed on its Scope of Ac
It would appear that the best efforts of lab accreditations are not living up
to expectations?
Or am I expecting too much?
Best Regards
Charles Grasso
Compliance Engineer
Echostar Communications
(w) 303-706-5467
(c) 303-204-2974
(t) 3032042...@vtext.com
(e) charles.gra...@echostar.com
(e2) chasgr
As noted by the Other Brian, some things to pay attention to are if the end
product is subjected to an overvoltage category or pollution degree beyond
what is found in the standard office environment and potential exposure to
liquids.
Some (hopefully) helpful information below found with "the Empe
Brian,
All quite true and it has been a bit of a problem when working with clients who
assume that if the PSU has any kind of an agency monogram, it must be okay.
One other area of concern, often overlooked, is the application of overvoltage
(formerly measurement) categories. Although 60
The IEC/EN/UL 61010-1 3rd Ed. section 1.1.3 has this statement which may be
helpful:
"NOTE Computing devices and similar equipment within the scope of IEC 60950 and
conforming to its requirements are considered
to be suitable for use with equipment within the scope of this standard.
However, so
18 matches