Re: [PSES] Internal connection labels in 220VAC systems

2015-12-15 Thread McDiarmid, Ralph
Ask him to reference a clause in an applicable standard. Do you know if spacings from N to PE circuit and to dead metal have been evaluated for 240V ? (in the event it gets cross wired during installation) ___

Re: [PSES] Internal connection labels in 220VAC systems

2015-12-15 Thread Brian O'Connell
Do not disagree in principal, but the Type Tests and construction requirements of L/N/PE terminals vs L1/L2/N terminals can vary with the scoped product safety standards and building code. Brian From: Nyffenegger, Dave [mailto:dave.nyffeneg...@bhemail.com] Sent: Tuesday, December 15, 2015

[PSES] Internal connection labels in 220VAC systems

2015-12-15 Thread John Cochran
Recently a customer has corrected the markings of terminal blocks inside of an industrial control panel my company built. An NRTL has evaluated the system and says the terminal markings for Line (L), Neutral (N), and Ground (G) are incorrect for a 220VAC input condition. Their evaluation says

Re: [PSES] Internal connection labels in 220VAC systems

2015-12-15 Thread Richard Nute
Hi John: If you can, I would include both markings, 90-230 volts: L, N, PE; 220 volts: L1, L2, PE (North America). (I am assuming that the equipment ratings marked on the equipment are wide-range, e.g., 90-240 volts.) The NRTL should not object to a dual

Re: [PSES] Internal connection labels in 220VAC systems

2015-12-15 Thread Nyffenegger, Dave
I've used a lot of small listed/certified DC power supplies that are wide-range voltage input but have the terminals marked L, N, PE. These could also be wired to L1 -L2 or L1-N in the US or L1-N in Europe. -Dave From: Richard Nute [mailto:ri...@ieee.org] Sent: Tuesday, December 15, 2015 2:43

Re: [PSES] Internal connection labels in 220VAC systems

2015-12-15 Thread Rodney Davis
Being familiar with 60950-1 I can tell you there are no Canadian/USA deviations on markings. I would definitely request the NRTL to provide the clauses reference in the standard and to share their Design manual which should help to resolve the issue. Rodney Davis