regarding fusing ac-mains

1996-12-13 Thread DenBleyker, R. (919-543-7251 TL 441)
The important thing to remember is the function of the fuse. 99%+ of the time it is for fire protection, not essential overcurrent protection. Most of us rely on the customer wall outlet to be properly protected per NEC or 950. For this case, electrical position before/after a switch seems not v

IEC1000-3-2

1996-12-02 Thread DenBleyker, R. (919-543-7251 TL 441)
Regarding Fred Waechter comments on table 1 and table 3 in the 1000-3-2 std. In my limited experience there are very few products that exhibit the type 'D' waveform and pass the table 3 limits. This waveform is the result of of a simple rectifier capacitor filter circuit which is so rich in harmo

Reply to fusing of Neutral and /or phase-----

1996-11-19 Thread DenBleyker, R. (919-543-7251 TL 441)
I expect that 99% of us deal with Plugable equipment type 'A', see 950 para 1.2.5.1. per paragraph 2.7.3, 'For PLUGGABLE EQUIPMENT TYPE A, the building insatllation is considered as providing short circuit protection.' Therefore use of a single fuse is ok on smaller equipment using non-industrial

Additional comment re the 240 VA 'hazard'

1996-11-18 Thread DenBleyker, R. (919-543-7251 TL 441)
I believe the original intent of this requirement was to protect the totally technically clueless from harm. The test finger is used simply since it is available to anyone doing safety evaluations. Introduction of a new tool is really a major burden. I have typed out the key phrases in 950 follo

240 VA

1996-11-13 Thread DenBleyker, R. (919-543-7251 TL 441)
The interpretation of 'continuous' is unfortunately a variable and up to the individual test Engineer with some influence by the Test House. Last I checked around, CSA was very rigid with zero tolerance over 240 VA, and UL would allow up to 5 seconds. Bob

A ps on IEC-1000-3-2 75W limits---

1996-11-04 Thread DenBleyker, R. (919-543-7251 TL 441)
Please remember that in the EEA the 75 watt limit for type 'D' waveforms will be reduced to 50 watts. The proposed date is July 1, 1999. It is not probable that there will be a 'grandfather' time period, so all product shipped after that date must be in compliance. Also, in Japan, JEIDA harmonic

Harmonics for products over 16A

1996-09-20 Thread DenBleyker, R. (919-543-7251 TL 441)
Japan has issued harmonic limits for larger products, via JEIDA. I do not have the document number. The title is 'Guidelines for the Suppression of Harmonics in Appliances and General-use Equipment'. These limits are required for JEIDA members Jan 1 1996 for product first shipped to Japan on tha

30A from 120V mains---

1996-08-15 Thread DenBleyker, R. (919-543-7251 TL 441)
John, I suggest you rate your product for 200+ Volts only. Regardless of the rating of the IEC inlet, you are faced with the limits on 120v outlets. Normal outlets (with the parallel blades) are rated at 12A, and normally protected with a 15A breaker. Dedicated outlet (with 1 each horizontal/ver

Power Supply Sources

1996-07-24 Thread DenBleyker, R. (919-543-7251 TL 441)
I know of several power supply manufacturers with active power factor corrected product either availale or very near available. These are intended for various markets and will have varied agency approvals Cherokee International, Tustin Cal., 714-544-6665 Todd Products, Brentwood, NY, 516-345-

IEC-1000-3 and 'the special waveshape'

1996-07-12 Thread DenBleyker, R. (919-543-7251 TL 441)
The limits permitted for Class D equipment, which is the special waveshape of current associated with a full-wave rectifier and capacitor input filter, is given in Table 3 of IEC-1000. Table 3 provides 2 limits for each harmonic, an absolute maximum and a power-weighted maximum based on the real i

In response to the 24 volt SELV level--

1996-07-09 Thread DenBleyker, R. (919-543-7251 TL 441)
Back in the early days, just before dirt was invented, we all used UL-498 for information technology equipment. This spelled out 24 volts peak as the allowed limit. In these early times we also had a telephony industry operating under their own rules--an ok situation since the industry was very t

Response to Jonathan Malton question regarding user accessible fuses

1996-07-03 Thread DenBleyker, R. (919-543-7251 TL 441)
The small off-line switch-mode power supplies are designed without any user replaceable parts. This normally includes the input fuse. This is a sensible practice since the fuse will interrupt only when a serious failure occurs elsewhere, such as a shorted bridge rectifier, or shorted FET, etc. W

Body Impedance

1996-06-18 Thread DenBleyker, R. (919-543-7251 TL 441)
Just several hundred mA of dc current through the chest area is lethal, so please take some care when measuring body impedance. It may be just a tale, but it is told that a physics professor carefully inserted hypodermic needles in each wrist, then applied a 'traditional' VOM using a 9v transitor

Reference Jim Eichner question about automotive fuses.

1996-06-17 Thread DenBleyker, R. (919-543-7251 TL 441)
I recommend the blade style auto fuse, such as LittleFuse. These are diecast parts from a zinc alloy without welds/brazes to fracture or fatigue. The reliability is much improved compared to the ceramic tube fuse with external elements. The blades fit quite snugly into the slip connectors, which

[no subject]

1996-05-17 Thread DenBleyker, R. (919-543-7251 TL 441)
regarding power line harmonics and switched vs linear--- The majority of linear power supplies are TR-packs followed by series regulators. TR is Transformer-Rectifier, which is a line-frequency transformer driving a capacitor-input filter. If the transformer were ideal then the primary current w

JEIDA Harmonic Requirements.

1996-05-10 Thread DenBleyker, R. (919-543-7251 TL 441)
I have a question regarding JEIDA harmonic requirements. When the product in question has real input power less than 75 Watts, what next? Is it necessary to claim compliance via a product lable in Kanji? Or is it ok to just ship the product? from Bob Den Bleyker at IBM-RTP

Australia/New Zealand

1997-03-28 Thread DenBleyker, R. (919-543-7251 TL 441)
For Australia/New Zealand, check that your power system complies with AS/NZS 3260:1993, Appendix 3, DC Component from AC Equipment basically this limits the dc component of the input current to 5 mA or less, with the goal to reduce corrosion at earthing electrodes. Many power supplies use small i

75 Watts and Class D vs. Class A

1997-07-11 Thread DenBleyker, R. (919-543-7251 TL 441)
I agree with 99.9% of the recent note from Rich Nute regarding the competancy and morals of CENELEC BT. I disagree with a technical point. Rich states that his products are less than 75 watts and therefore Class A. This is not correct The exact words are... "For Class D equipment, the limi

Some test information on Zinc-Oxide MOV devices

1997-05-16 Thread DenBleyker, R. (919-543-7251 TL 441)
from--bo...@vnet.ibm.com Several years ago I tested MOV devices from several manufacturers. All had a nominal rating of 70 volts and 10 joules. My testing forced breakover with a 10-ohm limiting resistor. Source voltage was 120 mains and simple fill-wave rectifier. The results were quite inter

Spark-gaps, MOV's and other breakover devices---

1997-04-25 Thread DenBleyker, R. (919-543-7251 TL 441)
In my opinion, any device that shifts from a high impedance to a low impedance to protect an attached, parallel load, needs another part. The additional part is a series energy limiter, examples a PTC device, an inductor, a resistor, a fuse, etc. The resulting circuit is nothing more than a shunt

Martin Garwood Question re galvanized sheet for uniform conductive

1997-08-12 Thread DenBleyker, R. (919-543-7251 TL 441)
plane I don't think galvanized materials are very good for a uniform conductive surface. Zinc forms a 'self-protective' oxide barrier which is terrific for protection against the elements. Unfortunately the oxide thickness is somewhat variable which results in a very variable surface resistivit

Kevin Harris request for Safety assist.

1997-01-03 Thread DenBleyker, R. (919-543-7251 TL 441)
hm. Distance between SELV and Earth? This doesn't compute, per IEC-950 para 2.3 SELV is produced, Method 3, via 'adequate Earthing'. I would try another test house. and a general comment to all. PLEASE include instructions for use of clever data transmission techniques for those of us who a

re Patrick Lawler and linear load in parallel with switcher

1997-01-28 Thread DenBleyker, R. (919-543-7251 TL 441)
In my personal experience looking at just the 3d harmonic is going to get you in trouble. Please take the time to look all the way out to the 39th and be prepared for some unpleasent news. You might be able to create an arguement that the current wave shape falls out of the 'special D' with suffi

Patrick Lawler Dual Function Product

1997-02-05 Thread DenBleyker, R. (919-543-7251 TL 441)
I found a section of Japan MITI-JEIDA documentation that may be of interest. This is probably not the latest information but provides an indication of the thought process. Document is MITI, Division 6, No. 378, dated Oct. 3, 1994. Author is Seija Murata, Director of Public Utilities Department.

Ringing Voltage Hazard Comments--

1997-02-12 Thread DenBleyker, R. (919-543-7251 TL 441)
The USA ring voltage is 66v RMS, as limited by FCC. This is a 54v dc level with superimposed 108v peak-peak ringer at approximately 20 Hz. This is lethal level to any human in a 'low-impedance' state. Low-impedance is the result of skin-breaks, broken lesions, immersion with saline solution etc.

'Cube' form factor power supply

1997-05-01 Thread DenBleyker, R. (919-543-7251 TL 441)
Power Switch has an active power factor corrected 300 watt supply in traditional cube shape with fan. Contact is Danice Donito at 201-478-0300. Location is Lodi, NJ. I have tested to harmonic requirements of 1000-3-2 and it seems ok. bo...@vnet.ibm.com

Seminar on Risk/Hazard

1997-06-12 Thread DenBleyker, R. (919-543-7251 TL 441)
Several years ago, Dr. George Pearsall of Duke University, Durham NC offered an excellent seminar. I took this course and do recommend it. per the Duke website, g...@eng.duke.edu is present address. bobdb at vnet.ibm.com

Moshe Valdmen question regarding leakage current

1997-07-16 Thread DenBleyker, R. (919-543-7251 TL 441)
Just a few precautions--- Leakage current values must be measured per the appropriate standard. Ref IEC-950 Annex D and G. An impedance is placed in series with the current path simulating an adult human body, with bypass capacitors to emphasize human sensitivity to mid-range frequencies. Simpl

Linear Power Supplies and 'Switchers'

1997-07-17 Thread DenBleyker, R. (919-543-7251 TL 441)
Regarding harmonic content and THD over 120% for switching power supply currents. Please let us not forget that the 'linear' power supplies of yesteryear were series regulators fed by TR packs. And the TR part is a transformer driving a full-wave bridge followed by a capacitor input filter. THD

higher voltage dc fans----

1997-07-19 Thread DenBleyker, R. (919-543-7251 TL 441)
1. First a comment. The Duetschesbundepost is the only user to my limited knowledge using 60v nominal battery voltage. I also understood that there was a planned conversion to 48 nominal. This could be important since fans rated at -48 are normally intended for the maximum possible with fully c

GFI Function

1997-09-03 Thread DenBleyker, R. (919-543-7251 TL 441)
In all of the discussions of hair-dryer in a tub scenario, no one has discussed the GFI and how it works. It senses the current in both power leads, and if they are not equal, it trips OFF. Thus it assumes that any current flowing between phase/neutral is good, any current in the phase lead not r

PCB Temperatures

1997-09-16 Thread DenBleyker, R. (919-543-7251 TL 441)
In my opinion, the designer is responsible for the PC board temperature as well as the semiconductor. The PC board is both a structural element of the product maintaining creepage/clearance distances, and an insulator. PC board failure can easily result in a safety problem. Overtemperature will

unsubscribe

1997-12-15 Thread DenBleyker, R. (919-543-7251 TL 441)