Re: Grounding Classes in Japan

2008-01-13 Thread emc-p...@ieee.org
On Thu, 10 Jan 2008 10:50:38 -0700, Aldous, Scott scott.ald...@aei.com wrote: I've come across specs referencing grounding classes from Japanese customers, i.e A class grounding, D class grounding. Googling doesn't turn up much - it appears that this class is related to the allowable

Re: Grounding Classes in Japan

2008-01-10 Thread emc-p...@ieee.org
Hello Scott, See Article 20 in the link below. http://www.eac.gov.kh/pdf/press-release/Final%20SREPTS%20TD%20July%2021%20_Final_%20rev01.pdf Ted Eckert American Power Conversion/MGE http://www.apc.com/ The items contained in this e-mail reflect the personal opinions of the writer and are only

RE: Grounding Classes in Japan

2008-01-10 Thread emc-p...@ieee.org
...@ieee.org Subject: Re: Grounding Classes in Japan In message 7995b996909d2a40b3cb7d0db4cceaa97e3...@aedcexcvs1.aei.com, dated Thu, 10 Jan 2008, Aldous, Scott scott.ald...@aei.com writes: Googling doesn?t turn up much ? it appears that this class is related to the allowable impedance

Re: Grounding Classes in Japan

2008-01-10 Thread emc-p...@ieee.org
In message 7995b996909d2a40b3cb7d0db4cceaa97e3...@aedcexcvs1.aei.com, dated Thu, 10 Jan 2008, Aldous, Scott scott.ald...@aei.com writes: Googling doesn?t turn up much ? it appears that this class is related to the allowable impedance in the ground path (10 Ohms or less for class A or C, 100

Re: Grounding, Earthing of long cables

2005-03-15 Thread owner-emc-p...@listserv.ieee.org
Pierre, Out of over 2,800 electronics books in my personal library, Grounding and Noise Reduction Practices, published by SDS Data Systems in Pomona, California immediately comes to mind. This book was sponsored by the Air Force Rocket Propulsion Laboratory. I can't find a copyright date

Re: Grounding, Earthing of long cables

2005-03-15 Thread owner-emc-p...@listserv.ieee.org
This (telecoms) isn't my field, so forgive me if I'm barking up completely the wrong tree but is the following of any use? BS EN 50310:2000 Application of equipotential bonding and earthing in buildings with information technology equipment Regards Nick. At 10:25 am + 15/3/05, John Allen

Re: Grounding, Earthing of long cables

2005-03-15 Thread owner-emc-p...@listserv.ieee.org
In article 001901c52949$4d6a7120$0301a8c0@johnallen, John Allen ja014d7...@blueyonder.co.uk writes There used to be an ECMA standard or Technical Report on interconnections between buildings etc., which did address earthing of cables in such circumstances but it no longer seems to be

Re: Grounding, Earthing of long cables

2005-03-15 Thread owner-emc-p...@listserv.ieee.org
Pierre Friends There used to be an ECMA standard or Technical Report on interconnections between buildings etc., which did address earthing of cables in such circumstances but it no longer seems to be available! Can anyone identify which one that was? John Allen (from home - as I have now

Re: Grounding, Earthing of long cables

2005-03-14 Thread owner-emc-p...@ieee.org
In article 656be56e7d48f6419054cc1c8111492704609...@exch01.corp.xl.com , Stone, Richard rst...@excelswitching.com writes and also, for the EU, in terms of signal cable, for ethernet or interface cables (E1/T1) will need to meet the 61000-suite of tests most notibly surge and conducted

RE: Grounding, Earthing of long cables

2005-03-14 Thread owner-emc-p...@listserv.ieee.org
Pierre, There are grounding rules for some LANs, such as Ethernet 10Base2, 10BaseT and others. See the LAN standards for these. Jim _ James L. Knighten, Ph.D. Teradata, a division of NCR http://www.ncr.com 17095 Via del Campo San Diego, CA 92127

RE: Grounding, Earthing of long cables

2005-03-14 Thread owner-emc-p...@listserv.ieee.org
Richard, From: owner-emc-p...@listserv.ieee.org mailto:owner-emc-p...@listserv.ieee.org]On Behalf Of Don Gies Sent: Monday, March 14, 2005 10:38 AM To: Pierre Selva; 'Forum Safety-emc' Subject: RE: Grounding, Earthing of long cables Pierre, For North America, you will need to consider

RE: Grounding, Earthing of long cables

2005-03-14 Thread owner-emc-p...@listserv.ieee.org
Pierre, For North America, you will need to consider the applicability of the following, particularly the long (signal) cable that may go from inside to outside plant: 1. (US) - National Electrical Code - NFPA 70 - Article 800 - Communications Circuits a. Flammability of cable - after 3

Re: Grounding, Earthing of long cables

2005-03-14 Thread owner-emc-p...@listserv.ieee.org
In article 007101c5289b$3ffaa540$0c1ea...@erant.msft, Pierre Selva e.l...@wanadoo.fr writes I know that in UK the BS7671 applies. Not really. BS 7671 applies to electric power distribution inside and outside buildings. It says almost nothing about signal or data cables. The technical reports IEC

Re: grounding and pressure contacts

2004-09-02 Thread owner-emc-p...@listserv.ieee.org
Gary, Chapter 33 of my book Robust Electronic Design Reference Book, Volume 1, discusses bonding. On page 33-2, for direct metal-to-metal bonds it recommends: * 8,300 kilopascals (1,200 pounds/square inch) pressure for soft metals. * Up to 10,300 kilopascals (1,500 pounds/square inch)

RE: grounding and pressure contacts

2004-09-01 Thread owner-emc-p...@listserv.ieee.org
From: Gary McInturff [mailto:gmcintu...@spraycool.com] Sent: Wednesday, September 01, 2004 3:05 PM To: EMC-PSTC (E-mail) Subject: grounding and pressure contacts Gentlemen, I'm looking for some data on pressure versus resistance through metal

RE: Grounding

2003-11-17 Thread Peter L. Tarver
My recollection is that a number of UL standards that explicitly excluded reliance on hinges as bonding conductors. For instance, UL 1459, 3rd ed, explicitly states that hinges and bearings can not be used as current carrying parts. This was interpreted to apply under normal and fault

Re: Grounding

2003-11-17 Thread Ken Javor
@listserv.ieee.org List-Post: emc-pstc@listserv.ieee.org List-Post: emc-pstc@listserv.ieee.org Date: Mon, 17 Nov 2003 08:52:37 -0700 To: ed.pr...@cubic.com, emc-p...@ieee.org Subject: RE: Grounding Perhaps if the added cost of a reliable ground connection is presented to management as insurance from

RE: Grounding

2003-11-17 Thread Doug Massey
home at http://www.acstestlab.com From: owner-emc-p...@majordomo.ieee.org [mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of GARY MCINTURFF Sent: Monday, November 17, 2003 11:06 AM To: ed.pr...@cubic.com; emc-p...@ieee.org Subject: RE: Grounding Morning Ed, This is stated much better than

RE: Grounding

2003-11-17 Thread drcuthb...@micron.com
...@majordomo.ieee.org [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Crabb, John Sent: Monday, November 17, 2003 2:20 AM To: IEEE EMC/Product Safety (IEEE, EMC/Product Safety) Subject: RE: Grounding I might have expected that folk would look for a definition of reliably grounded. I would quote from

RE: Grounding

2003-11-17 Thread GARY MCINTURFF
its a struggle to accept. Gary From: Price, Ed ed.pr...@cubic.com Reply-To: Price, Ed ed.pr...@cubic.com To: 'emc-p...@ieee.org' emc-p...@ieee.org Subject: RE: Grounding Date: Mon, 17 Nov 2003 07:06:30 -0800 -Original Message- From: Gary McInturff [mailto:gmcintu...@spraycool.com

RE: Grounding

2003-11-17 Thread drcuthb...@micron.com
Micron Technology From: owner-emc-p...@majordomo.ieee.org [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Price, Ed Sent: Monday, November 17, 2003 8:07 AM To: 'emc-p...@ieee.org' Subject: RE: Grounding -Original Message- From: Gary McInturff [ mailto:gmcintu...@spraycool.com

RE: Grounding

2003-11-17 Thread Price, Ed
-Original Message- From: Gary McInturff [ mailto:gmcintu...@spraycool.com] Sent: Friday, November 14, 2003 10:46 AM To: 'Crabb, John'; Ned Devine; IEEE EMC/Product Safety (IEEE, EMC/Product Safety) Subject: RE: Grounding John, You are correct, but you have just

RE: Grounding

2003-11-17 Thread Crabb, John
(IEEE, EMC/Product Safety) Subject: RE: Grounding John, You are correct, but you have just presented the conundrum of the thread. Reliably grounded can be determined through test - 25 or 30 amps for a minute. A new hinge will likely pass that test. A used one may likely fail because

RE: Grounding

2003-11-14 Thread Bill Flanigan
Ned, See EN61010-1:20001, 6.5.1.1.d... Movable conductive connections, for example, hinges, slides, etc., shall not be the sole PROTECTIVE BONDING path unless they are specifically designed for electrical inter-connection and meet the requirements of blah...blahhh There are similar provisions,

RE: Grounding

2003-11-14 Thread Gary McInturff
and bean counters. Gary From: Crabb, John [mailto:jo...@exchange.scotland.ncr.com] Sent: Friday, November 14, 2003 9:01 AM To: Ned Devine; IEEE EMC/Product Safety (IEEE, EMC/Product Safety) Subject: RE: Grounding 2.6.1 of IEC 60950-1 refers to parts of equipment shall be reliably

RE: Grounding

2003-11-14 Thread Crabb, John
2.6.1 of IEC 60950-1 refers to parts of equipment shall be reliably connected to the main protective earthing terminal.A hinge would certainly not be regarded as a reliable connection. As far as your door is concerned, is there any single insulated hazardous voltage wiring likely to contact

RE: Grounding

2003-11-14 Thread Gary McInturff
, November 14, 2003 8:13 AM To: ndev...@entela.com; emc-p...@majordomo.ieee.org Subject: RE: Grounding Ned, I know this isn't the standard you are using but I happen to have been using it lately and quickly found a similar situation. EN61010-1:2001, 6.5.1.1 Integrity of protective bonding: d) Movable

RE: Grounding

2003-11-14 Thread Roman, Dan
Ned, You are right, I could not find anything in recent ITE standards specifically stating that hinges are not allowed. Older standards like UL1459 did specifically state that bearings and hinges can not be used. I believe however that the onus would be on the manufacturer to prove that the

RE: Grounding

2003-11-14 Thread Ned Devine
To: Ned Devine; Emc-Pstc Subject: Re: Grounding Ned, I had this discussion with a TUV engineer way back in time. It is not in the UL or IEC standards specifically AFAIK. What the TUV guy asked me to do was consider the life of the product. The door hinge may have good (low) resistance today

Re: Grounding

2003-11-14 Thread Scott Douglas
Ned, I had this discussion with a TUV engineer way back in time. It is not in the UL or IEC standards specifically AFAIK. What the TUV guy asked me to do was consider the life of the product. The door hinge may have good (low) resistance today, but what will it be like in a few years? Hinges

RE: Grounding

2003-11-14 Thread drcuthb...@micron.com
Ned, I know this isn't the standard you are using but I happen to have been using it lately and quickly found a similar situation. EN61010-1:2001, 6.5.1.1 Integrity of protective bonding: d) Movable conductive connections, for example, hinges, slides, etc., shall not the sole PROTECTIVE BONDING

RE: Grounding

2003-10-09 Thread Brian O'Connell
Grounding and Shielding Techniques, 4th Edition Ralph Morrison ISBN: 0-471-24518-6 luck, Brian -Original Message- From: am...@westin-emission.no [ mailto:am...@westin-emission.no] Sent: Thursday, October 09, 2003 2:58 PM To: emc-p...@majordomo.ieee.org Subject: Grounding Hi

RE: Grounding of EUT in EN61000-4-6 conducted immunity test

2003-02-17 Thread Gordon,Ian
Dan et al I have a Word document which I believe gives guidance on this matter. If you would like a copy please let me know. Ian Gordon _ This e-mail has been scanned for viruses by the WorldCom Internet Managed Scanning

Re: Grounding of EUT in EN61000-4-6 conducted immunity test

2003-02-17 Thread Ken Javor
, emc-p...@majordomo.ieee.org Subject: RE: Grounding of EUT in EN61000-4-6 conducted immunity test Mr. Javor, I guess I can't argue your points until I read your paper. Please send me a Word copy. I assure you, I will respect the copyright and destroy the article after I read it. I think

Re: Grounding of EUT in EN61000-4-6 conducted immunity test

2003-02-14 Thread Ken Javor
, Oliver Betz list...@gmx.net, emc-p...@majordomo.ieee.org Subject: RE: Grounding of EUT in EN61000-4-6 conducted immunity test Thanks for the quick response. Please let me explore this further. I have used the special case as the general case where the EUT has many signal lines in which

Re: grounding schemes EMI

2002-10-25 Thread Doug McKean
Hi Dave, I've had this type of discussion at a previous telco company and the only explanation I ever received regarded ground potential differences between equipment through the mains (as we have discussed in a previous thread). And I always seemed to win by saying that if everything was

Re: grounding schemes EMI

2002-10-24 Thread Douglas Smith
Hi David (and the group), Take a look at the Technical Tidbits section of my site at http://emcesd.com where you will find some experimental evidence for your viewpoint. This month's article (at the bottom of the main page) presents some data and links to two other articles. Doug On

Re: grounding schemes EMI

2002-10-11 Thread Cortland Richmond
David, Telecom (Bellcore) usage is to keep signal, surge and power currents off chassis and safety grounds. This is understandable. It is due not only to audio sensitivity, but to the need to protect equipment from substantial peak (hundred of amps) surges at fairly high (thousands of volts)

Re: grounding schemes EMI

2002-10-11 Thread Don_Borowski
A good way to think about this, especially on a larger size board, is to imagine a transmission line resonator. Assume for the moment that the shielding enclosure and the board ground are tied together at one point. In this case, the board will go resonant when the length of the board ground

Re: Grounding architectures for COs

2002-09-11 Thread JPR3
Marko Radojicic writes: Battery Return is also problematic. In NA, it *must* be held isolated from CG/FG. In the EU, it *must* be bonded to the CG/FG! Hi Marko: Thank you for your very informative response. I would just like to clarify any possible distinction between battery return and

Re: Grounding architectures for COs

2002-09-10 Thread Dorin
To: 'Marko Radojicic'; 'John Juhasz'; 'Dorin' Cc: 'EMC-PSTC - forum' Subject: RE: Grounding architectures for COs Hi Marko, I'm curious what measures you and others take to protect against ESD, Lightning, etc when implementing a multi-point bonding scheme of signal ground to frame/chassis

RE: Grounding architectures for COs

2002-09-10 Thread Joe Finlayson
Hi Marko, I'm curious what measures you and others take to protect against ESD, Lightning, etc when implementing a multi-point bonding scheme of signal ground to frame/chassis ground. I can definitely see the advantages for EMI. Thx, Joe -Original Message- From: Marko

Re: Grounding in an operating room environment ...

2002-08-20 Thread jgriver
Doug, You are really asking if the product is Type B (earthed applied part) or Type BF (isolated ground part) according the the classification of IEC 60601-1. The answer is that some types of medical equipment must be Type BF or even Type CF (direct cardiac contact) according to the

RE: Grounding in an operating room environment ...

2002-08-19 Thread Grasso, Charles
Silly Question really - but why are the responses off line?? Would you consider posting a summary, Doug? -Original Message- From: Doug McKean [mailto:dmck...@corp.auspex.com] Sent: Monday, August 19, 2002 4:15 PM To: EMC-PSTC Discussion Group Subject: Re: Grounding in an operating room

RE: Grounding Continuity Testers for UL 60950

2001-11-15 Thread John Shinn
Arc Welder works better. John -Original Message- From: owner-emc-p...@majordomo.ieee.org [mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of John Woodgate Sent: Wednesday, November 14, 2001 10:25 AM To: emc-p...@majordomo.ieee.org Subject: Re: Grounding Continuity Testers for UL

Re: Grounding Continuity Testers for UL 60950

2001-11-14 Thread John Woodgate
I read in !emc-pstc that Loop, Robert rl...@hnt.wylelabs.com wrote (in 81a0ea0cd2a23f439f43a64d24db7d8d08f...@hnt.wylelabs.com) about 'Grounding Continuity Testers for UL 60950', on Wed, 14 Nov 2001: Where in the world can we get a tester that would go up to 200 amps with a 12 V output? Vehicle

RE: Grounding Continuity Testers for UL 60950

2001-11-14 Thread Patricia Knudsen (EWU)
Compliance West USA makes high current continuity testers. I have a 200A model. Their website is: http://www.compwest.com/ Patty Knudsen Ericsson Wireless Communications patricia.knud...@ericsson.com -Original Message- From: Loop, Robert [mailto:rl...@hnt.wylelabs.com] Sent:

RE: Grounding Continuity Testers for UL 60950

2001-11-14 Thread robertj
Note that such a tester may be unnecessary. Note that 2.6.3.3 requires testing only for PROTECTIVE BONDING CONDUCTORS that do not comply with the minimum sizes in table 3B and for protective bonding terminals that do not comply with table 3E. You are unlikely to find a tester of this size on the

RE: Grounding Continuity Testers for UL 60950

2001-11-14 Thread POWELL, DOUG
Robert, We often do high current tests as a type test and on our production line this is a routine test. Some people have used simple arc welders. They are economical but you have to be careful of the strike voltage. Another alternative is that most agencies allow you to do a DC test in which

Re: Grounding Questions

1999-11-17 Thread Robert Macy
damages. - Robert - -Original Message- From: Crabb, John jo...@exchange.scotland.ncr.com To: 'Price, Ed' ed.pr...@cubic.com; 'emc-p...@ieee.org' emc-p...@ieee.org Date: Tuesday, November 16, 1999 3:03 AM Subject: RE: Grounding Questions Ed, we do

Re: Grounding Questions

1999-11-17 Thread Matthew Meehan
. - Robert - -Original Message- From: Crabb, John jo...@exchange.scotland.ncr.com To: 'Price, Ed' ed.pr...@cubic.com; 'emc-p...@ieee.org' emc-p...@ieee.org Date: Tuesday, November 16, 1999 3:03 AM Subject: RE: Grounding Questions Ed, we do not find

Re: Grounding Bond Test

1999-08-26 Thread GASSE
...@sdd.hp.com To: harr...@dscltd.com cc: emc-p...@majordomo.ieee.org (bcc: Volker Gasse/Germany/IBM) Subject: Re: Grounding Bond Test Hi Kevin: Interesting P.S. comment. Surely this can only be so if one is not dealing with a CE country. I don't see how a test agency can waive

RE: Grounding Bond Test

1999-08-26 Thread Crabb, John
The original post said : EN 50116 for ITE specifies the earthing terminal or earthing contact may not exceed 0.1 ohms when 1.5 times the current capacity of hazardous circuits is applied, but not more than 25 A (ac or dc) for 60 seconds. My copy of EN50116 specifies the time as being for the

Re: Grounding Bond Test

1999-08-26 Thread Egon H. Varju
The obvious question I would have is... why couldn't you test at a higher current for longer time meeting both requirements? For example 30A for two minutes. I know the document indicates a maximum current, but does this make sense? Works for me. I can't imagine any agency refusing to

Re: Grounding Bond Test

1999-08-26 Thread Rich Nute
Hi Kevin: Interesting P.S. comment. Surely this can only be so if one is not dealing with a CE country. I don't see how a test agency can waive the requirements for meeting the LVD in Europe. If it is indeed as you say, then where does it put those of us who have in house safety

RE: Grounding Bond Test

1999-08-26 Thread Kevin Harris
: Wednesday, August 25, 1999 4:37 PM To: carmen.fili...@leitch.com Cc: emc-p...@majordomo.ieee.org; fra...@csa.ca Subject: Re: Grounding Bond Test Hi Carmen: You ask how to resolve the difference between two, different production-line (routine) test standards. If your

Re: Grounding Bond Test

1999-08-26 Thread Rich Nute
Hi Rick: The obvious question I would have is... why couldn't you test at a higher current for longer time meeting both requirements? For example 30A for two minutes. I know the document indicates a maximum current, but does this make sense? The original question appeared to me

Re: Grounding Bond Test

1999-08-26 Thread Egon H. Varju
Cameron, The grounding continuity test required by CSA 0.4 is normally intended only for the initial prototype evaluation, to ensure that the basic design is within acceptable parameters. It is not usually intended as a production line test. There may be some exceptions, where non-standard

RE: Grounding Bond Test

1999-08-25 Thread rbusche
; fra...@csa.ca Subject:Re: Grounding Bond Test Hi Carmen: You ask how to resolve the difference between two, different production-line (routine) test standards. If your product is certified by CSA

Re: Grounding Bond Test

1999-08-25 Thread Rich Nute
Hi Carmen: You ask how to resolve the difference between two, different production-line (routine) test standards. If your product is certified by CSA, then you test to the 30-ampere value. If your product is certified by a CB Certificate and Test Report, and the issuing body invokes EN

RE: Grounding of screen room

1998-10-07 Thread Ing. Gert Gremmen
For a screened room to function as a screened room, no earth is required. It's the metal conduit of the shielding material that will be reference potential (if you insist : ground) for all measurements. All external cables (mains) should be filtered to this reference potential, preferably to the

RE: Grounding of screen room

1998-10-07 Thread Bailin Ma
, Barry Ma - Original Text From: ed.pr...@cubic.com, on 10/7/98 9:34 AM: From: Bailin Ma b...@namg.us.anritsu.com Subject: RE: Grounding of screen room Date: Tue, 6 Oct 98 14:35:43 PDT To: emc-p...@ieee.org, TREG t...@world.std.com Cc: Mekonen Buzuayene

RE: Grounding of screen room

1998-10-07 Thread ed . price
--- From: Bailin Ma b...@namg.us.anritsu.com Subject: RE: Grounding of screen room List-Post: emc-pstc@listserv.ieee.org Date: Wed, 7 Oct 98 9:18:11 PDT To: emc-p...@ieee.org, emc-p...@ieee.org Cc: Mekonen Buzuayene

RE: Grounding of screen room

1998-10-07 Thread ed . price
From: Bailin Ma b...@namg.us.anritsu.com Subject: RE: Grounding of screen room Date: Tue, 6 Oct 98 14:35:43 PDT To: emc-p...@ieee.org, TREG t...@world.std.com Cc: Mekonen Buzuayene mbuzuay...@namg.us.anritsu.com Hi Lauren, It is my understanding

RE: Grounding of screen room

1998-10-06 Thread WOODS, RICHARD
Our chamber is grounded via the electrical conduit used with the mains power. Never had a problem. -- From: peterh...@aol.com[SMTP:peterh...@aol.com] Reply To: peterh...@aol.com Sent: Tuesday, October 06, 1998 1:56 AM To: emc-p...@majordomo.ieee.org Subject:

RE: Grounding of screen room

1998-10-06 Thread Crane, Lauren
My guess for a first pass is empty it out, put a spectrum analyzer in with a broadband antenna and see if you can 'hear' anything at a level that is near what you are testing for. Cheers, Lauren Crane -Original Message- From: peterh...@aol.com [SMTP:peterh...@aol.com] Sent: Tuesday,

RE: Grounding of screen room

1998-10-06 Thread Chuck Jackson
Hi Peter. I have always isolated my chambers from any sort of building ground and used a separate grounding grid. The ground was measured using a 'ground megger'. Chuck Jackson -- From: peterh...@aol.com[SMTP:peterh...@aol.com] Reply To: peterh...@aol.com Sent: Monday,

RE: Grounding of screen room

1998-10-06 Thread Randall Flinders
-- From: WOODS, RICHARD Sent: Tuesday, October 06, 1998 5:28 AM To: emc-p...@majordomo.ieee.org Subject: RE: Grounding of screen room Our chamber is grounded via the electrical conduit used with the mains power. Never had a problem. -- From: peterh...@aol.com

RE: Grounding of screen room

1998-10-06 Thread Brumbaugh, David
Peter If you can locate the facility electrical drawings, I would recommend starting with those. It's considered good design practice if you have isolated facility power (air handlers, lights, etc.) and technical power (designated for exclusive use by instrumentation and other equipment requiring

RE: Grounding of screen room

1998-10-06 Thread Bailin Ma
Hi Lauren, It is my understanding that properly grounding the screen room is important in Conducted emission test and have little effect on Radiated emission test. The way you described is a very good and simple method for evaluating the shielding effectiveness (SE) of the screen room. The

Re: Grounding vs. Ground Loops

1997-12-12 Thread Doug McKean
From: Arlen Olive arl...@futuretel.com I've been working on a multimedia board in a standalone box that connects to a PC parallel port. It also has an external DC power supply, and connections for audio and video input and output. To pass FCC class B, I had to: 1. Shield the box