I would suggest that you try to use the option for setting
exp.sys_wide_zip_loads.pw. If you model all loads as constant
admittances by using pw = [0 0 1] you will certainly get a solution with
YSUM since in this case the network is linear and the solution will be
obtained in single iteration. If
Mr. Ray, thanks for the answer!
But in addition to the runpf () function, in what other functions should
I make the change in the number of iterations?
De: bounce-121637368-77188...@list.cornell.edu
em nome de Ray
Dear Mr. Todorovski, thanks for the answer!
De: bounce-121631454-77188...@list.cornell.edu
em nome de Mirko Todorovski
Enviado: quinta-feira, 29 de junho de 2017 21:10
Para: MATPOWER
If you haven’t tried it, certainly try increasing the number of iterations for
the radial methods.
Ray
> On Jul 3, 2017, at 3:15 PM, Andrey Vieira wrote:
>
> for Reconfiguration/Restoration process, ie:
>
> Occurrence of significant concentration of buses/Loads in a
for Reconfiguration/Restoration process, ie:
Occurrence of significant concentration of buses/Loads in a given healthy
region (region that will receive some or all of the disconnected Loads)
Of the feeder (as shown below) via the relocation of disconnected loads
(optimization process) due to the
1. I would simply copy an existing case file and then modify the data to match
your system.
2. For a generator representing a renewable source, you will need to update PG
(for a power flow) or PMAX (for an OPF) to indicate the renewable power
available at the time being simulated by your power
If you have a solved AC power flow, that’s a good start. Normally, the first
step I try when faced with an OPF that won’t converge is to eliminate the
branch flow limits by setting the RATE_A column of the branch matrix to zero
(or by increasing the values by some factor). In your case, you can
The apply_changes() function can be used to disable branches and buses by
setting the BR_STATUS to column to 0 for a branch or the BUS_TYPE column to
NONE for a bus, but it cannot be used to actually delete rows from the branch
and bus matrices.
For example, to disconnect branch 3 and bus 4,
MATPOWER does not use GA for any of its optimizations, so it seems like this is
related to your own code and not to MATPOWER. I suggest checking the
documentation for the GA solver you are using.
Ray
> On Jun 21, 2017, at 4:14 AM, Roshani Thapa wrote:
>
> I
Hi Prem,
If you are solving each island individually, the DC OPF should converge as long
as (1) you have a reference bus in the island, (2) there is adequate generation
to cover the load in the island, and (3) the line constraints do not prevent
the generated power from reaching the loads.
The general power flow formulation does not include a current mismatch version,
though the latest dev version on GitHub does include a current summation method
for radial systems.
Ray
> On Jun 9, 2017, at 6:14 AM, Bone, Gorazd wrote:
>
> Hi all ,
>
> I was
Hi Eran,
Sorry for the delay in responding. I just got back from some time off. You are
right about the matpower-extras. Hopefully, the directions in the README at
https://github.com/MATPOWER/matpower-extras will work for you … namely …
To install, simply place the contents of this repository
There is not necessarily anything unusual about this. If the generators are
relatively expensive and their PMIN value is zero, it may be economical to
dispatch them at 0 MW output.
Ray
> On Jun 9, 2017, at 8:15 PM, Xinwen Ni wrote:
>
> Hi, all
>
> I built a test