[RE-wrenches] Burned Inverter Technician

2013-10-17 Thread Steven Lawrence
Wrenches, A technician from Solectria was severely burned when he tried to replace a filter on an inverter. You can read it at http://www.nj.com/hunterdon-county-democrat/index.ssf/2013/10/man_medivacked_from_delaware_v.html I hope he's ok and that he makes a full recovery. I also hope

Re: [RE-wrenches] Fronius Installer Support Sucks- but who else?

2013-10-17 Thread August Goers
Don - Unfortunately I believe the Sunny Tripower is only good for 480 V applications. I'm not aware of other 240 V 3-phase inverters on the market (other than the Fronius). We run into a lot of 208 V 3-phase here in the Bay Area and unfortunately can't use these cool new 3-phase inverters from

[RE-wrenches] Trace 2548 intermittent power problem

2013-10-17 Thread SunHarvest
I have encountered a Trace 2548 in seemingly good working condition. I was called out to troubleshoot a Grid-tied, battery back-up system with the following problem: - Upon loss of grid power there is about a 5 second lapse (no power to house) before the BB system engages. Power to the

Re: [RE-wrenches] Trace 2548 intermittent power problem

2013-10-17 Thread Ray Walters
While the problems seem related, I'm guessing the gen set issue is a low coolant or low oil condition. The generator has sensors that shut it down if they don't see fluid (coolant, or oil) after a few seconds. The symptoms fit that. For the inverter, it is either fried or has some

Re: [RE-wrenches] Trace 2548 intermittent power problem

2013-10-17 Thread Allan Sindelar
Eric, A Trace 2548 with automatic generator start? I don't believe there ever was such a thing. I suspect that you're referring to either a SW4048 or SW5548. If so, your first step is to check the error codes, some of which are found in Menu Heading 2 (for

Re: [RE-wrenches] Trace 2548 intermittent power problem

2013-10-17 Thread Steve Higgins
Could be a couple of things... Yes, this sounds like an SW4048... Not a 2548. A 2548 is black only weighs about 60 pounds and doesn't do auto gen start or gen support. Is this a white unit with a green stripe that 2.5 feet long and about 20 inches tall? Right? Does it have a Red or black

[RE-wrenches] Trace 2548 intermittent power problem...55 not 25

2013-10-17 Thread SunHarvest
I was looking at a scratch pad note where I wrote 25 instead of 55...Yes, it is a SW5548. Definitely not set to Search...it's in On mode. I've checked error codes. No Yes messages. I am wondering about a firmware upgrade although I have serious doubt that will clear up the problem. I guess I

Re: [RE-wrenches] Trace 2548 intermittent power problem...55 not 25

2013-10-17 Thread Allan Sindelar
Eric, Ray's suggestion to check the gennie is easy - disconnect the generator's output to the inverter (probably not necessary, but helps to isolate symptoms) and start the generator manually at the gennie. If it shuts down, it's the gennie. Allan

Re: [RE-wrenches] Trace 2548 intermittent power problem...55 not 25

2013-10-17 Thread Steve Higgins
If it's not in search mode, then it sounds like the relay it failing. The SW5548 has two relays, on for grid and one for gen, Does the delay happen using Grid and the Generator? Steve Higgins Technical Services Manager M: +1.206.790.5840 F: +1.902.597.8447 Surrette Battery Company Exclusive

Re: [RE-wrenches] SWWP Whisper 200 - looking for a short to ground.

2013-10-17 Thread Ross Taylor
Hi Ron, Alan, and everyone else... There were good suggestions provided, so I didn't jump in. I was traveling also, so got into this discussion late. But, I'm usually available (and almost always willing) to provide whatever knowledge support I can for Whisper products. Parts will be a problem,

Re: [RE-wrenches] Trace 2548 intermittent power problem...55 not 25

2013-10-17 Thread Eric . Bentsen
Hi Eric, Sounds like a bad control board. Swap the inverter and you should be back in business. Rgds, _ Eric Bentsen | Schneider Electric | Solar Business | UNITED STATES | Technical Support

Re: [RE-wrenches] Fronius Installer Support Sucks- but who else?

2013-10-17 Thread don
Chris Mason wrote:SMA just came out with their Sunny Tripower line for the US. Yes those are interesting. But they are only for 480 Wye, not 240 Delta.Is the Fronius 11.4-3 the only 3-phase inverter that can work with 240 3-phase with a hi-leg (stinger)?

[RE-wrenches] smaller 3-phase commercial inverters

2013-10-17 Thread Marco Mangelsdorf
Yeah, lots more choices out there in the 10+ to 30 kW rangeā€¦.but pretty much all of the larger capacity models only come at 480V. Anyone know why? We have way more 120/208V applications here in Hawaii than 277/480. marco Chris Mason wrote: SMA just came out with their Sunny