Re: [RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread don
Howard- Any voltage drop at the house will be a function of current drawn by the house load. Shut off most loads and there will be minimal voltage drop.  If there was a low voltage issue now before solar is installed, there would be symptoms like florescent lights not working well. That's why they

Re: [RE-wrenches] Which commercial string inverters?

2016-08-16 Thread Jerry Shafer
Wrenches We do lots of bigger systems and our inverter of choice has been SMA, we have seen many manufacturers either fail or be bought out, neither we have any control over but considering issues SMA has had the least of any. We have used fronius, AE, ABB, and satcon some filled with rain water,

[RE-wrenches] Which commercial string inverters?

2016-08-16 Thread Stephen K
Hello RE-Wrenches, I'm a long time recipient of great knowledge, experience and advice from this list, but I've been an infrequent poster. I'm curious about this list's opinion on the current status of the Commercial sized string inverter product options (from ~10kW to 80kW, 600 and 1000VDC fla

Re: [RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread William Miller
Chris: All I know is an application engineer with the transformer manufacturer suggested the higher AIC breaker and it solved the nuisance tripping. William [image: Gradient Cap_mini] Lic 773985 millersolar.com 805-438-5600 *From:* RE-wrenches [mailto:re-

Re: [RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread Ray Walters
My guess is that in your case the GTPV will just help alleviate the volt drop situation. I wouldn't start adding transformers, etc until you are having a problem. Put in the contract that this extra cost may be necessary for proper function, but I would keep it as a backup. Based on the numb

Re: [RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread Chris Mason
Just a note: AIC has nothing to do with breaker trip amperage ratings or nuisance tripping, it has to do with the ability of the switchgear to interrupt very large fault currents for very short periods such as you would find close to a utility transformer with very low impedance in the event of se

[RE-wrenches] Outback radian issues

2016-08-16 Thread Jay
Hi all I was contacted by someone offsite about a 5 stack outback radian, grid connected that is having all sorts of problems. He's been in long contact with OB engineering but still no answers. If anyone has experience with such a critter, please let me know. Thanks Jay Peltz power.

Re: [RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread William Miller
Chris: If you do provide transformers I think they are called step-up/step down. Buck/boost transformers I believe are to make adjustments to voltages. I have learned that you need to account for the current flow and direction. For one-way flow, the upstream transformer has a slightly differ

Re: [RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread Glenn Burt
Maybe a 208v inverter will fit the bill? -Original Message- From: "Howard Arey" Sent: ‎8/‎16/‎2016 12:16 To: "'RE-wrenches'" Subject: [RE-wrenches] Buck-Boost transformer to mitigate high voltage drop? Good day, I have a potential client that has an existing 1,000 foot run from the

[RE-wrenches] Any Exeltech Dealers here?

2016-08-16 Thread Starlight Solar Power Systems
Wrenches, Is anyone setup as a dealer with Exeltech? I need a 22kW MX bi-phase system but they only offer me retail pricing. Please contact off the list: la...@starlightsolar.com Thank you, Larry Crutcher Starlight Solar Power Systems (928) 342-9103

[RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread Howard Arey
Answers to all: No - I did not measure voltage at the house. Right now, only an assumption of voltage drop based on my perception of what "typical" loads might be on this 150-amp service. I wasn't expecting to see such small wires for such a long run from transformer to house when I showed up t

Re: [RE-wrenches] Ballasted Roof Racking?

2016-08-16 Thread William Miller
Nick: We have used Dynoraxx for roof and ground mount. Not great but decent. http://dynoraxx.com/ William [image: Gradient Cap_mini] Lic 773985 millersolar.com 805-438-5600 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behal

Re: [RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread jerrysgarage01
Wrenches We have done transformers for issues just like this with good results, the cost vs the new wire, conduit and trenching must be done to make sure which direction. We have had to use paired mcm 300 to make residentual so run the numbers Jerry Sent via the Samsung Galaxy S™ III, an AT&T

Re: [RE-wrenches] Ballasted Roof Racking?

2016-08-16 Thread Benn Kilburn
We've been using Polar Racking which is pretty light (without ballast). ...from my mobile Benn Kilburn SkyFire Energy Inc. 780-906-7807 > On Aug 16, 2016, at 12:58 PM, Nik Ponzio, Building Energy > wrote: > > Wrenchers, > > Ironridge just pulled plug on their BRM. What are people specifyin

[RE-wrenches] Ballasted Roof Racking?

2016-08-16 Thread Nik Ponzio, Building Energy
Wrenchers, Ironridge just pulled plug on their BRM. What are people specifying for small (<15kW) ballasted roof mount racking for PV? Thanks in advance. ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change list

Re: [RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread Chris Schaefer
Perhaps I missed it but you didn't say what you measured the voltage to be at the clients service entrance panel at his house? Christopher On Tue, Aug 16, 2016 at 1:40 PM, Mac Lewis wrote: > Yes, what current did you use to calculate that voltage drop? How big is > the PV system? > > On Aug 16,

Re: [RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread Mac Lewis
Yes, what current did you use to calculate that voltage drop? How big is the PV system? On Aug 16, 2016 11:38 AM, "Chris Mason" wrote: > How much of the power produced will be self-consumed, how much will be > exported? > > On Tue, Aug 16, 2016 at 12:16 PM, Howard Arey > wrote: > >> Good day, >

Re: [RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread Chris Mason
How much of the power produced will be self-consumed, how much will be exported? On Tue, Aug 16, 2016 at 12:16 PM, Howard Arey wrote: > Good day, > > > > I have a potential client that has an existing 1,000 foot run from the > meter and transformer at the street to the home. This is 4/0 Al and q

[RE-wrenches] Buck-Boost transformer to mitigate high voltage drop?

2016-08-16 Thread Howard Arey
Good day, I have a potential client that has an existing 1,000 foot run from the meter and transformer at the street to the home. This is 4/0 Al and quick calcs show the voltage drop at over 12%. He acknowledges that the wire is undersized to keep voltage at/about 240 volts (I have not measured