[RE-wrenches] Generac EcoGen 6

2016-12-31 Thread Matthew Sirum
Greetings Dave, Which Generac controller is on this 6kW EcoGen? Some of the Generac controller instructions I have seen state that once the controller control panel fuse is removed and/or the connections to the starting battery are disconnected the exercise programming will need to be re-entered.

Re: [RE-wrenches] Conext SW 4024 with bad firmware

2016-12-31 Thread Tump
Jay I too find this firmware issue questionable. there IS settings on this AGS & Inverter for disconnect using voltage AND or hz. Again voltage 110/55Hz is what I will usually start out with.These additional settings; cool down time and spin down time, I set to the lowest setting possible. Thi

[RE-wrenches] Conext SW 4024 with bad firmware

2016-12-31 Thread jay
HI Hugh, Interesting problem your describe which I've not seen before. I’m curious about your comments on Outback. I’ve found them to be quite programable in regards to disconnecting from a generator. You can set voltage and cycles. Default comes in at 60 cycles which is 1 second and way to

Re: [RE-wrenches] Generac EcoGen 6

2016-12-31 Thread Chris Mason