Greetings Dave,
Which Generac controller is on this 6kW EcoGen? Some of the Generac
controller instructions I have seen state that once the controller
control panel fuse is removed and/or the connections to the starting
battery are disconnected the exercise programming will need to be
re-entered.
Jay I too find this firmware issue questionable. there IS settings on this AGS
& Inverter for disconnect using voltage AND or hz. Again voltage 110/55Hz is
what I will usually start out with.These additional settings; cool down time
and spin down time, I set to the lowest setting possible. Thi
HI Hugh,
Interesting problem your describe which I've not seen before.
I’m curious about your comments on Outback.
I’ve found them to be quite programable in regards to disconnecting from a
generator.
You can set voltage and cycles. Default comes in at 60 cycles which is 1 second
and way to
Does it ruin for 20 mins then stop? Exercise.
On Dec 30, 2016 10:14, "Dave Palumbo" wrote:
> Wrenches,
>
>
>
> I have a 6 kW Generac EcoGen (1,300 hrs on it) with a new problem.
>
> · After swapping in a new battery the other day the generator
> now starts and runs when its start switch