You should have a mobile number directly into support. I just used it last
week. If not you are going to have get one from them. If you write me off
list I will try and help you get in.. I am cc'ing Sandra also at Schneider.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
This is why I use the XW! They start just about anything and they are
one 6.8KW inverter, not multiple like the Radian. I do like the radian and
use it. For large motors, XW is hard to beat. The battery needs to be at
least 800 AH for this large motor app.
Dave Angelini Offgrid Solar
"we go
Hey Chris and Wrenches,
So I talked to Steve at Gen Pro and he says that his soft starts are
intended to be used for LRA conditions where there is a load against the
shaft on start-up - although they do do some well pumps. See below -
still searching!
Thanks though cause he is going to
Hey Dave,
Okay I'm hearing you now after you said it twice! :) So let's compare
Radian and XW:
Radian:
Continuous - 33.3 Amps - 8000 Watts
30minute - 9 kVA - 37.5 Amps
5 Secs - 12 KVA - 50 Amps
100 mS RMS - 16.97 kVA - 70.7 AMPs
1 mS Peak - 100 Amps
XW:
Continuous - 28 Amps 6800 Watts
30
Hi all,
I have been registered as an installer for Schneider tech support for
quite a while. I no longer have a way to contact them. The number I
received refers me to internet support. Any help out there. I have a
bad out of the box off grid Conext SW 2524.
Thanks for any help,
Daryl
Hi about 20 years ago we used to build a soft start, it was a reduced
voltage starter, composed of AC capacitors and a relay. Upon start from
pressure switch the power would flow through capacitors? And shortly there
after the relay would close after motor started to turn. It seems to me we
Given the DC voltage sag I have to wonder how a bank of lithium batteries
would react as if I understand correctly they maintain the same voltage
through out their entire range of SOC.
Christopher
On Fri, Jul 26, 2019 at 1:19 PM Ray wrote:
> I've run a 3 Hp pump on a pair of VFX 3648s, but
Hi Chris,
Thanks so much for the reference. I still am at an impasse. I have an
unhappy customer and want to proceed cautiously - Tech support at Radian
will only promise 1/2hp per 4 KW radian module - so only 1.5 HP for an
8048 - It's a 2 HP but as you know HP is not a definitive
I've been following this post with great interest. I was looking at an
off-grid project a couple years back that was being run entirely by large
diesel generators and had two massive AC units where the LRA was 104 Amps.
I found a company that makes what amounts to a soft start. I don't recall
the