Re: [RE-wrenches] 30 amp disconnect/40 amp breaker

2019-08-21 Thread Greg
All, thanks for the responses.  I greatly appreciate it.  Yes the 30 amp disco is non-fusible and rated for full load.  True, you have to check the manu's specs.  You _always_ should check the manufacturers specs. Anyway, 705.22(4) indicates the disco: /Have ratings sufficient for the maximum

Re: [RE-wrenches] 30 amp disconnect/40 amp breaker

2019-08-21 Thread Brian Mehalic
I agree Blake - you have to check the specs and consult the mfg. The same is true with combiners, some are rated for continuous duty/full load, and some are not. Lots of large systems out there with 200A combiners connected to 250A OCPDs (and 250A conductors, but that’s another story...).

Re: [RE-wrenches] 30 amp disconnect/40 amp breaker

2019-08-21 Thread Greg
All, the engineer came back with 705.22(4) to back up his request. I think that's the end of it.  Per code he is right but since the inverter is only capable of 25 amps, the only time the 30 amp disco would see more than 30 amps is if the inverter was shorted.  If that's the case opening the

Re: [RE-wrenches] 30 amp disconnect/40 amp breaker

2019-08-21 Thread Kristopher Schmid
I have run into this many times and have never found a definitive answer. The disconnect spec typically says that it must be protected with an ocpd at or less than the disco rating, but we are dealing with a current limited device (inverter) in this case so it would seem legal to me. On Wed, Aug

Re: [RE-wrenches] 30 amp disconnect/40 amp breaker

2019-08-21 Thread Christopher Warfel
Not going through the NEC, but it doesn't make sense to me to put in an OCPD greater than the rating of the switch.  I am sure you can find in the spec sheet what the maximum OCPD allowed is. Chris On 8/21/2019 6:12 PM, Greg wrote: Fellow Wrenches,  I'm having a discussion with a utility

[RE-wrenches] 30 amp disconnect/40 amp breaker

2019-08-21 Thread Greg
Fellow Wrenches,  I'm having a discussion with a utility engineer regarding the following situation: Installing a 6kW inverter that has a full rated output of 25 amps. 80% of 30 is 24.  That means to me I need to go up to a 40 amp breaker.  I'm running #8 (continuous load 25 x 1.25 etc.) The

[RE-wrenches] Solarworld warranty

2019-08-21 Thread Marco Mangelsdorf
Hello all, Is there any entity that is covering Solarworld warranties? Thanks, marco ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings:

Re: [RE-wrenches] Mission PVs

2019-08-21 Thread Jason Szumlanski
I have disassembled many of these pallets. On flat ground they stand up very well in their corner protectors. In fact they are a bit difficult to get out. We raise one side of the truck or trailer a bit and let the stack rest against a wall or something heavy and it works just fine. These have

Re: [RE-wrenches] Mission PVs

2019-08-21 Thread Ryan Harkins
Bill, Sometimes we add some duct tape to the corner guards on the side-stacked module skids, so as you unpack you peel tape back one module at a time. Helps them stay together as a unit and not tip. Careful with those Mission modules! We had a couple skids of those and the corner miters of

[RE-wrenches] SunPower 72-cell

2019-08-21 Thread Marco Mangelsdorf
Aloha all, I'm on the hunt for a handful up to a pallet of 72-cell SunPower Corp. mods...215-watt to 250-watt. Please contact me off list if you have any. Mahalo, marco ___ List sponsored by Redwood Alliance List Address:

Re: [RE-wrenches] Mission PVs

2019-08-21 Thread William Miller
Bill: I hope your trailer has side walls. Load the pallet near one side of your trailer. Encourage modules to lean that direction as you cut the bands. If you are worried about travelling with the load off-center, take some extra pallets to stack between the modules and the downhill side of