[RE-wrenches] schneider xw-Pro issue with genny running

2021-06-28 Thread Chris Schaefer
G'day All, I recently got pulled into someone else's mess on a twin xw-pro 6848 with a Generac 20kw air cooled genny. A little back story. The client is currently off grid with basically an all electric house. I know, I know, lol. The intent is to bring the grid in but that has been slowed for var

Re: [RE-wrenches] schneider xw-Pro issue with genny running

2021-06-28 Thread William Miller
Chris: I have little Schneider experience but I will describe a problem with an Outback system that might be relevant: When the Outback Radian inverters would charge from the generator, in certain modes (there are a several generator utilization settings) the charging circuits would inject lar

Re: [RE-wrenches] schneider xw-Pro issue with genny running

2021-06-28 Thread Mac Lewis
Hi Chris, I recommend enabling Gen support mode and lowering the gen support level until the generator sounds good. I suspect that the generator can't handle full battery charging and loads simultaneously. You may also want to turn down the AC2 In breaker size for the Gen Input, this will determ

Re: [RE-wrenches] schneider xw-Pro issue with genny running

2021-06-28 Thread ericstev
chment was scrubbed... URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20210628/4f362333/attachment-0001.html> -- Message: 2 Date: Mon, 28 Jun 2021 14:13:06 -0700 From: William Miller To: RE-wrenches Su