Re: [RE-wrenches] Fortress Envy E-stop

2024-07-25 Thread Jay via RE-wrenches
Hi Lewis Yes both the 12 and 18 have RSD It’s a button on the left side. Shuts off AC and PV Jay > On Jul 25, 2024, at 7:30 AM, Mac Lewis via RE-wrenches > wrote: > >  > Hello Wrenches, > > Does anyone know if the 12kW Envy inverter has remote stop capability? I > need an external

Re: [RE-wrenches] Identify Inverter / Mango Power

2024-07-24 Thread Jay via RE-wrenches
I don’t know but it’s form factor is very similar to LUX/deye Handles, door latches, disconnects. I wonder if it’s a Ali express special? Jay > On Jul 24, 2024, at 9:42 AM, Jason Szumlanski via RE-wrenches > wrote: > > Can someone help me identify the inverter in the attached picture? >

Re: [RE-wrenches] AGM blew on discharge

2024-07-24 Thread Jay via RE-wrenches
Hi Drake What do you mean it off gassed? Like blew the top off? > On Jul 24, 2024, at 8:40 AM, Drake Chamberlin via RE-wrenches > wrote: > >  > A severely abused bank of Rolls Surrette batteries had one battery off gas > heavily on discharge. It seems like the off gassing happens on

[RE-wrenches] have a laugh

2024-07-23 Thread jay via RE-wrenches
Same person asking about the pump was also asking about the following. I’d never heard of it either. Looks like from a 1970’s sci fi movie https://batteryevo.com/product/walrus-180ah-13-kwh-ac110-220v-72n/ 72v battery, non

Re: [RE-wrenches] workhorse pumps

2024-07-22 Thread jay via RE-wrenches
s apart for fun and says they are built well but has only > about three years with them. I might give one a go since the price is good. > > On Mon, Jul 22, 2024 at 2:01 PM jay via RE-wrenches > <mailto:re-wrenches@lists.re-wrenches.org>> wrote: > Does anyone know

[RE-wrenches] workhorse pumps

2024-07-22 Thread jay via RE-wrenches
Does anyone know anything about this company? https://workhorsepumps.com I have someone asking me about it. thanks in advanced. jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address:

Re: [RE-wrenches] Outback in general

2024-07-21 Thread jay via RE-wrenches
ified PV System Inspector > NABCEP PV Associate > d <mailto:dan.f...@greendustrialtraining.com>anbo...@gmail.com > <mailto:anbo...@gmail.com> > 970-672-4342 > > > > > On Sat, Jul 20, 2024 at 3:22 PM Jay via RE-wrenches > <mailto:re-wrenches@lists.re-wren

Re: [RE-wrenches] Outback in general

2024-07-21 Thread jay via RE-wrenches
LLC > IREC Certified Instructor for PV and Small Wind Installation > NABCEP Certified PV System Inspector > NABCEP PV Associate > d <mailto:dan.f...@greendustrialtraining.com>anbo...@gmail.com > <mailto:anbo...@gmail.com> > 970-672-4342 > > > &

Re: [RE-wrenches] Outback in general

2024-07-20 Thread Jay via RE-wrenches
I just checked the OB forums page and there is nothing current. One thing I found says that the new president of OB is the CEO of Big Battery. I don’t know that to be a fact. Which is also somehow related to signature solar/ EG4. My guess is that if/when OB resurfaces it won’t have the same

Re: [RE-wrenches] Another Mate 3 programming issues

2024-07-19 Thread jay via RE-wrenches
HI Chris, Can you give us more data? Like is this a new problem, or it only started after X? Since its not seeing the port ( NA) it could be the CC or the HUB, or the cable. the hub will show an active LED light if its connecting to anything on that port. You can try plugging into the CC

Re: [RE-wrenches] Mate 3 programming issues

2024-07-18 Thread Jay via RE-wrenches
Hi jim. WilliamMight be right, but what equipment do you have on this system?Doing a cat 5 unplug,plug back might helpJayOn Jul 18, 2024, at 3:18 PM, William Miller via RE-wrenches wrote:Jim:You may be logged in as a limited access user. Try logging in as installer. William MillerMiller

Re: [RE-wrenches] AES RACK MOUNT

2024-07-17 Thread Jay via RE-wrenches
Yes I really like the rack mounts I’m curious about the AES mounts and others that don’t have an enclosure. How does code deal with that?  ThxJayOn Jul 17, 2024, at 9:28 AM, Michael Morningstar via RE-wrenches wrote:Because I work mostly alone, I'm digging the rack mounts. Dealing with 200 lb

Re: [RE-wrenches] VFD drives

2024-07-11 Thread jay via RE-wrenches
ower on a 30 kilowatt will be absolutely no problem. > > -James Jefferson Jarvis > APRS World, LLC > +1-507-454-2727 > > (Sent from my phone. My apologies for spelling errors and brevity.) > > On Thu, Jul 11, 2024, 12:07 PM jay via RE-wrenches > <mailto:re-wrenches@list

Re: [RE-wrenches] VFD drives

2024-07-11 Thread jay via RE-wrenches
erator power. No issues. > Personally, I run numerous old cast iron woodworking machines that all have 5 > and 10hp 3p motors with VFDs from a 15kw Kubota open frame generator. 15 > second ramp up time. And my generator is single phase. > > On Thu, Jul 11, 2024 at 10:06 AM jay via

[RE-wrenches] VFD drives

2024-07-11 Thread jay via RE-wrenches
HI All, I’m being asked to comment about running a 10hp 3 phase well centrifugal pump off of a 30kw single phase generator with a VFD drive. This well pump is located in a tank for fire fighting applications, so its not down a deep well meaning almost no head pressure. And the start time can be

Re: [RE-wrenches] Fortress LFP batteries and Outback charge controller

2024-06-30 Thread Jay via RE-wrenches
The evault doesn’t see the multiple inputs, just like any battery. The envy % reading via web is working well. And yes it’s a bit weird to the solar from the inverter not add up to the daily charge numbers But it’s working fine If you follow oem charge instructions the open loop voltages are a bit

Re: [RE-wrenches] Fortress LFP batteries and Outback charge controller

2024-06-29 Thread Jay via RE-wrenches
No problem at all. I just did a system exactly like that.  Works fine. JayOn Jun 29, 2024, at 5:49 PM, Kirk Herander via RE-wrenches wrote:All,I'm wondering if there are any precautions if charging a Fortress Evault LFP bank using 1 or more OB charge controllers, in tandem with an Envy inverter

Re: [RE-wrenches] Outback app

2024-06-17 Thread Jay via RE-wrenches
lines don't" https://offgridsolar1.com/ e-mail offgridso...@sti.net text 209 813 0060 On 2024-06-17 2:49 pm, Jay via RE-wrenches wrote: Is the Outback app working?I can log into my account but not the app?ThxJay___List sponsored by Redwood A

[RE-wrenches] Outback app

2024-06-17 Thread Jay via RE-wrenches
Is the Outback app working? I can log into my account but not the app? Thx Jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email

Re: [RE-wrenches] Dual battery bank switch for 48 VDC system

2024-06-15 Thread Jay via RE-wrenches
Hi GregHow about this midnite box midnitesolar.comPersonally what I don’t like about single switch A or B is there is an off time. With the midnite box, you switch both on, and turn the off the one you want. That way there is never an off time. Just a thought. JayOn Jun 15, 2024, at 11:19 AM, greg

Re: [RE-wrenches] Two Outback Radian 8048 fails in same week..what is likely wrong in 7+ year inverters?

2024-06-09 Thread Jay via RE-wrenches
Call Zonna energy. It’s most likely 1 of the control boards. And probably not the power modules. Not all that uncommon especially for the non A versions. Jay > On Jun 9, 2024, at 4:50 PM, Scot Arey via RE-wrenches > wrote: > >  > Longtime Outback user but since the experience of this

Re: [RE-wrenches] How many times can a rafter have a lag screw put in and out before it is no longer structurally sound? Some roofs getting their 3rd set of new shingles

2024-05-29 Thread Jay via RE-wrenches
Hi Scot What a fascinating issue. I can’t help as to the structural concerns but I like the deck mounts idea to make sure you don’t have any issues. Jay > On May 29, 2024, at 4:17 PM, Scot Arey via RE-wrenches > wrote: > >  > With all our Texas hail storms, we now have roof solar systems

[RE-wrenches] Discover rack mount battery connectors

2024-05-28 Thread Jay via RE-wrenches
Hi all I’ve noticed that many batteries are now using a different type of battery connector. Almost like a kind of MC4. It has a positive locking mechanism. Discover, EG4, and others. I’m wondering if anyone knows if they are universal or specific to each brand? And is there a name for this

Re: [RE-wrenches] Discover AES exposion

2024-05-28 Thread Jay via RE-wrenches
That is fantastic service!  And it also confirms  that LFP batteries are actually capable of the same explosive energy ( even more actually) as NMC contrary to the claims made by many that it’s impossible. While I’m using LFP batteries in most systems, it does scare me much more than Lead. JayOn

Re: [RE-wrenches] Water system with Grundfos SQFlex

2024-05-27 Thread jay via RE-wrenches
HI Brad, Is this off/on grid? And are the two wells near each other or they just join up at the tank and float switch? If you’ve got the power then I’d install just a standard AC centrifugal pump. Sure uses more power but lasts forever. And is maybe $500 vs $2500 And you’ve said minimal water

[RE-wrenches] offgrid solar installer in anchorage/SE alaska

2024-05-27 Thread jay via RE-wrenches
HI All Any recommendations for a off grid installer in Anchorage or SE alaska? Pls contact me off list thanks jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address:

Re: [RE-wrenches] Water system with Grundfos SQFlex

2024-05-26 Thread Jay via RE-wrenches
Hi JerryWhat equipment are you using to pull steel  from that depth?Jay On May 26, 2024, at 3:18 PM, Jerry Shafer via RE-wrenches wrote:Hey wrenchesWater leaks in wells, I just pulled my well pump out at a mere 390 feet, older galvanized 11/4 « steel, where the Water rose and dropped the pipe

Re: [RE-wrenches] Water system with Grundfos SQFlex

2024-05-26 Thread jay via RE-wrenches
And of course using a torch to soften the tubing just enough so that the barb fitting can insert and then grab into the plastic with the clamps. For 1” its not needed but helpful. For 1.25”- 2” its needed, or at least I’ve never been able to get a solid connection without heat. Jay > On May

Re: [RE-wrenches] Water system with Grundfos SQFlex

2024-05-26 Thread jay via RE-wrenches
Hi Brad, Here is the link.

Re: [RE-wrenches] Water system with Grundfos SQFlex

2024-05-26 Thread Jay via RE-wrenches
  Dave Angelini Offgrid Solar "we go where powerlines don't" https://offgridsolar1.com/ e-mail offgridso...@sti.net text 209 813 0060 On 2024-05-26 4:26 am, Jay via RE-wrenches wrote: Hi Brad With 2 check valv

Re: [RE-wrenches] Water system with Grundfos SQFlex

2024-05-26 Thread Jay via RE-wrenches
Hi Brad With 2 check valves leaking I’d look for a broken pipe or a corroded fitting. If there is anyway to isolate between the 2 check valves then you could measure the pressure drop on both sides which should point to the direction of the leak. Jay > On May 25, 2024, at 7:41 PM, Bradley

Re: [RE-wrenches] Outback Tech Support

2024-05-24 Thread jay via RE-wrenches
Hi Drake, What it says to me is that they either fired everyone or said move to tx. I’ve always joked that if the potential project I’m to work on starts badly it never gets better. I still don’t understand why the owners of EG4 would by a legacy inverter company? Jay > On May 24, 2024,

[RE-wrenches] Outback

2024-05-21 Thread Jay via RE-wrenches
I was talking to signature solar today. Signature solar and EG4 are sister companies. I don’t have info if one owns the other or if they are equal partners? They did admit they bought OB. But didn’t know if signature or EG4 bought them. Jay ___

Re: [RE-wrenches] UL batteries for open loop

2024-05-20 Thread Jay via RE-wrenches
has 3 vaults and a Radian. JohnOn Mon, May 20, 2024 at 7:22 PM jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:HI All I got a call from a fellow installer who needs a UL listed lithium battery.  Say 30-50 kwh.  open loop as its working with existing OB radians. Could be o

Re: [RE-wrenches] Optics

2024-05-20 Thread Jay via RE-wrenches
old.To say I am curious about what is going on is an understatement. Aloha,Lou Russo Ownerl...@spreesolarsystems.com808 345 6762Spree Solar Systems LLC CT-34322On Sun, May 19, 2024 at 2:21 AM Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:I agree with you WilliamWhile there

Re: [RE-wrenches] UL batteries for open loop

2024-05-20 Thread Jay via RE-wrenches
 results allow that.Dan FinkOwner, Buckville Energy Consulting LLCIREC Certified Instructor for PV and Small Wind InstallationNABCEP Certified PV System InspectorNABCEP PV Associatedanbo...@gmail.com970-672-4342 On Mon, May 20, 2024 at 5:22 PM jay via RE-wrenches <re-wrenches@lists.re-wrenches.

[RE-wrenches] UL batteries for open loop

2024-05-20 Thread jay via RE-wrenches
HI All I got a call from a fellow installer who needs a UL listed lithium battery. Say 30-50 kwh. open loop as its working with existing OB radians. Could be outside or inside It so confusing to find the right battery I’d thought I would ask what folks are using/recommending. thanks jay

Re: [RE-wrenches] Optics

2024-05-19 Thread Jay via RE-wrenches
I agree with you WilliamWhile there could be all sorts of valid reasons for the downtime. What’s not acceptable is the lack of communication and notification that it was going to happen or had happened.  If they do have new owners they are not starting well. JayOn May 18, 2024, at 9:42 PM, William

Re: [RE-wrenches] Fortress Avalon

2024-05-15 Thread Jay via RE-wrenches
It’s an interesting design. I went to a seminar on it. Wiring the main power distribution center, is a bit tricky with how they designed or not wire room. Probably want to use cobra wire.  The battery voltage design is unusual in that more batteries increases the voltage, not bad just different. 

Re: [RE-wrenches] Bootstrapping and AC Coupled Sunny Island

2024-05-08 Thread jay via RE-wrenches
HI William, Yes the FM-100 has no problem with keeping the volts pretty tight and i’ve not heard of any lithium related issues, and someone is bound to chime in if there are. jay > On May 8, 2024, at 9:39 AM, William Miller wrote: > > Jay: > > I am considering ditching the Sunny Boys and

Re: [RE-wrenches] Bootstrapping and AC Coupled Sunny Island

2024-05-08 Thread jay via RE-wrenches
Hi William, Since the SOC isn’t being reliable maybe due to not charging correctly? I would recommend going to volts for the relay driver. Thats why I suggested the tristar with RD-1. Because really volts at full is the most accurate. Not knowing how many PV inputs you could do a cascade.

Re: [RE-wrenches] Bootstrapping and AC Coupled Sunny Island

2024-05-08 Thread jay via RE-wrenches
A possible fix. You could run a DC relay on the SB PV input that would be voltage triggered to prevent the battery volts from getting higher than you want. The SI has 2 aux relays I think? Or could do a tristar with RD-1 relay that has 4 channels. Just a thought jay > On May 7, 2024, at

Re: [RE-wrenches] Bootstrapping and AC Coupled Sunny Island

2024-05-08 Thread Jay via RE-wrenches
Hi WilliamHave you talked to fortress about the SOC getting so out of calibration in such a short period of time?JayOn May 7, 2024, at 11:16 PM, William Miller via RE-wrenches wrote:Friends: I am still wrestling with problems integrating a Sunny Island / Sunny Boy AC coupled system to a set of 5

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-05-04 Thread Jay via RE-wrenches
I wanted to follow up on this thread. According to the sol Ark website. The US 8 kw is rated at 120/240. Which I’ve always thought mean 3 wire. L1,L2,N. The US 5kw is 120v only. L1, N Do I have this correct?JayOn May 4, 2024, at 9:15 AM, Tom McCalmont via RE-wrenches wrote:It does not do

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-05-03 Thread Jay via RE-wrenches
Maybe the new 5kw 120v unit is the 8kw at 120v?JayOn May 3, 2024, at 4:22 PM, Tom McCalmont via RE-wrenches wrote:David is correct.  We have some experience with Sol-Ark’s inverter, and it’s a good product.  However, be aware that you can configure it either as a 120V inverter with a max. output

Re: [RE-wrenches] Large transformer losses

2024-04-26 Thread Jay via RE-wrenches
According to the nameplate 6% @ 170°cOn Apr 26, 2024, at 4:33 PM, Darryl Thayer via RE-wrenches wrote:Do you know the transformer impedance?On Fri, Apr 26, 2024, 5:54 PM Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:Hi all. Anyone know what the tare loss and effi

[RE-wrenches] Large transformer losses

2024-04-26 Thread Jay via RE-wrenches
Hi all. Anyone know what the tare loss and efficiency is of a 75 kw transformer? And it would be run mostly at 1-10kw max. This one specifically. hammond SG3L0075PE I’m just curious about it. The situation is 240vac grid at the street, 600’ to the house 400 amps. Why 400 amps on a house

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-26 Thread Jay via RE-wrenches
AC future breaker panel. All lighting was Edison base lamps, and all wiring was NMB Romex.  I wired like a normal house except for a 120-v panel and 12-v panel I relay and momentary switch by appliance for easy turning on of AC inverter.   On Wed, Apr 24, 2024 at 8:49 AM Jay via RE-wrenches <

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-24 Thread Jay via RE-wrenches
Yeah definitely no second battery. On Apr 24, 2024, at 6:41 AM, Howie Michaelson via RE-wrenches wrote:Jason,My vote would be for using a 120 to 12vDC power supply large enough to handle the remaining 12 vDC loads and skip the second battery bank. In my mind, this is simpler, cleaner, and if the

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-24 Thread Jay via RE-wrenches
I agree with John. Most 12v fridges have small compressors. But I don’t know what they have. Personally a major reason to go 120/ac is to get a normal refrigerator. But you can measure the surge/load  and then size the charger accordingly. One feature of going charger is the lights are a lot

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-23 Thread Jay via RE-wrenches
I’ve done this many times I use an Iota or power max charger to run the DC. Jay > On Apr 23, 2024, at 2:42 PM, Jason Szumlanski via RE-wrenches > wrote: > >  > I have an off-grid client who is working on replacing old equipment at a > cabin. He has a lot of 12 volt distribution in the

[RE-wrenches] speaking of batteries

2024-04-23 Thread jay via RE-wrenches
HI All Speaking of batteries I wonder what you all make of this. I was reading the Fortress battery manual and it says they don’t recommend adding new lithium batteries to older lithium batteries if the age is over 1 year difference. Thoughts? thanks jay

Re: [RE-wrenches] PV/Charge Controller Troubleshoot Help

2024-04-23 Thread Jay via RE-wrenches
ler Troubleshoot Help > > It may be the fan. I had an FM 80 where the fan went bad that caused very > limited solar production throughout the day. > > Michael D Nelson > MD Electric & Solar, Inc. > 707-684-0064 mobile > 707-884-1862 office > www.mdelectricsolar.co

Re: [RE-wrenches] PV/Charge Controller Troubleshoot Help

2024-04-23 Thread jay via RE-wrenches
HI Jim, The CC is sure suspect. You didn’t mention what the battery voltage is. Those CC have a hard PV watt input limit. You can try and set it back to factory default and then reprogram, sometimes that works. I don’t use the FM-60, but always the FM-80 because of the fan replacement.

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread jay via RE-wrenches
;> <https://www.youtube.com/RollsBatteryEngineering> >> <https://www.youtube.com/RollsBatteryEngineering> >> <https://www.linkedin.com/company/rolls-battery-engineering> >> <https://www.linkedin.com/company/rolls-battery-engineering> >> &l

Re: [RE-wrenches] Off-grid array far, far from the batteries

2024-04-10 Thread jay via RE-wrenches
Hi Chris, If you run all 6 in series that puts you about 2.6% vd with #4 wire about 200vdc vmp and 10 amps. In cold enough weather you’re probably above the FM-100 so would put you in a 600vdc controller. I’d go with 600v controller vs doing AC coupling. More efficient and the more volt

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread jay via RE-wrenches
t deliver a consistent > specific gravity in range. On the rare occasions you actually need to > equalize, you do it in person. When equalization is complete you return the > settings back to your curated values. > > > > On Wed, Apr 10, 2024 at 7:28 AM jay via RE-wrenches

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread jay via RE-wrenches
Can you explain what changes the eg4 18 inverter has vs the Envy as to LA programming? To me the Envy has a big advantage due to it having AGS warm up/cool down that the EG4 does not. Jay > On Apr 10, 2024, at 7:49 AM, Howie Michaelson via RE-wrenches > wrote: > > John, > If you are

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread Jay via RE-wrenches
Hi scott Yes I think for new larger systems the AIO are the present/future Jay > On Apr 9, 2024, at 9:42 PM, scot.a...@solarcentex.com wrote: > >  > Wow, are we in the golden age of inverter/chargers? If it had 200-a.p pass > thru it would be near perfect. > > Begs the question: are stand

[RE-wrenches] midnite new inverter

2024-04-09 Thread jay via RE-wrenches
Hi All, Does anyone know the pricing and when it’ll be available? The New Midnite MN15-12KW-AIO All in One (AIO) inverter Looks good. thanks jay___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List

Re: [RE-wrenches] Steel pipe purlins

2024-04-03 Thread Jay via RE-wrenches
If your looking to fasten into the steel pipe you look at Dynamicfasteners.comGreat productsJayOn Apr 3, 2024, at 5:34 PM, david quattro via RE-wrenches wrote:because it is an awning seems like you may be able to disturb the roof layer above the purlins, even if temporarily?If so then i think an

Re: [RE-wrenches] Mate3s error vs. event log

2024-04-03 Thread Jay via RE-wrenches
2 things. Maybe you can sell them a service contract and clear/check the events 1x week via optics. I don’t know if there is a way to prioritize events. To me Ive always had good success with the fndc in regards to be pretty accurate for reading %. Getting rid of it seems the wrong way to go. And

Re: [RE-wrenches] Good tech support

2024-03-28 Thread Jay via RE-wrenches
As to the envy not being good for LA batteries. Yes rhe 60v max is just too low. Does it have 3 stage charging?I’m curious to see what the new midnite solar inverter has to offer. It shows up to 64v battery. JayOn Mar 28, 2024, at 6:44 AM, John Blittersdorf via RE-wrenches wrote:Howie,    I

Re: [RE-wrenches] Ballasted ground mounts

2024-03-21 Thread Jay via RE-wrenches
Here is an interesting design. PowerField Energy PowerRack PV solar ballasted ground mount systemsolar-electric.comOn Mar 21, 2024, at 11:08 AM, Bradley Bassett via RE-wrenches wrote:Is Aerocompact still around ?  They had a nice simple ballasted ground mountBrad BassettOn Thu, Mar 21, 2024,

Re: [RE-wrenches] Enohase tech support

2024-03-15 Thread jay via RE-wrenches
ss is not an option. > What kills me about Enphase is that every step of the way over the last 15 > years - EVERY single time they changed their inverter architecture, they > promised that all the new stuff would be backward compatible with old gear. > And every single time, they were full

[RE-wrenches] Enohase tech support

2024-03-15 Thread Jay via RE-wrenches
Hi all Is there anyway to get tech support with remote coms? I got a call just the other day from someone with an envoy. It’s stopped communicating to enohase. Enphase says they need the installer who’s now gone. They just won’t help the customer. It’s about a 5 hr round trip for me. Which is

[RE-wrenches] DC fountain pumps

2024-03-04 Thread jay via RE-wrenches
HI All Any recommendations for quality DC fountain pumps? Brands, suppliers etc thanks jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change

Re: [RE-wrenches] Electrolyte level measurement

2024-02-28 Thread Jay via RE-wrenches
Hi williamFor checking level the best trick I’ve ever seen is a solid glass rod. I can’t remember if you have to grind one end flat or not. When you put the end into the water the top end your looking at changes color. The side you look at would be the one you grind. Mark the rod with tape or use

[RE-wrenches] 30% ITC

2024-02-28 Thread Jay via RE-wrenches
A question maybe someone/s can answer or offer up some thoughts. A neighbor who’s an economist asked me the following question Does the 30% ITC increase the cost of solar? By which he ment that are installers, wholesalers, etc increasing the cost of product and installations because of the

Re: [RE-wrenches] Fwd: Re: $300 + transmission fee!

2024-02-26 Thread Jay via RE-wrenches
Hi williamIs California now doing demand charges? And is it instantaneous or 15 minute average?  JayOn Feb 25, 2024, at 11:23 AM, William Miller via RE-wrenches wrote:Friends:I am pondering a plan to prevent usage spikes. It would involve installing a battery inverter that has true generator

Re: [RE-wrenches] Non-battery string inverter options?

2024-02-22 Thread Jay via RE-wrenches
Hi williamFronius 7.6 kw are in stock. I’ve installed a number of fronius with no issues. JayOn Feb 22, 2024, at 4:56 PM, William Miller via RE-wrenches wrote:Friends: Now that RSS is required on almost every installation, I am having trouble finding a plain old, non-battery, non-MLPE string

Re: [RE-wrenches] Outback Board Repair

2024-02-22 Thread Jay via RE-wrenches
Hi JohnThe work around is to make sure you e got a new enough serial number to at least talk to them about what ever the issue is. But this is a huge new development in a bad way.JayOn Feb 22, 2024, at 6:55 AM, John Blittersdorf via RE-wrenches wrote:I just tried to get Outback tech support and

[RE-wrenches] AP systems contact info

2024-02-21 Thread jay via RE-wrenches
Does anyone have a working phone number for AP systems? I have a system that works but all the LED lights don’t work on the inverters thanks jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread jay via RE-wrenches
A number of people have mentioned strict code compliance. How are lead batteries dealing with this? thanks jay > On Feb 17, 2024, at 12:27 PM, Ray Walters via RE-wrenches > wrote: > > Chris; > > I was definitely moving to the LFP camp for off grid for all the same reasons > you

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Jay via RE-wrenches
fortress is making improvements to their firmware for sure. The fortress envy 12 has generator warmup/cool down which is a really important feature  IMO. The eg4 not. Nor does the Deye sol ark. JayOn Feb 16, 2024, at 8:48 PM, Chris Sparadeo via RE-wrenches wrote:Howie,The EG4 18K and the

Re: [RE-wrenches] Fortress

2024-02-15 Thread Jay via RE-wrenches
Hi williamCould you share the equipment used and what issues you had?ThxJayOn Feb 14, 2024, at 3:13 PM, William Miller via RE-wrenches wrote:Peter: I have only purchased one set of Fortress batteries.  There have been issues, I am sure many of them self-induced.  Fortress has been overall very

Re: [RE-wrenches] XW EQ question

2024-02-12 Thread jay via RE-wrenches
-- > From: RE-wrenches On Behalf Of > jay via RE-wrenches > Sent: February-12-24 11:36 AM > To: RE-wrenches > Cc: jay > Subject: [RE-wrenches] XW EQ question > > HI All, > > I have a client with an older XW 6048 with 2 x XW-60 controllers, SCP etc. > > He

[RE-wrenches] XW EQ question

2024-02-12 Thread jay via RE-wrenches
HI All, I have a client with an older XW 6048 with 2 x XW-60 controllers, SCP etc. He can’t seem to get the EQ to work with either equipment. Its set to 62.4v for Rolls flooded batteries, but it won’t go above 60v. It is charging normally to just at 60v so its not a temp sensor failure. Any

Re: [RE-wrenches] In search of better generator start relay for Outback system

2024-02-09 Thread Jay via RE-wrenches
I would use a sealed relay. The SS one should work. Or a 12v cube relay like in cars.  Super cheap and reliable JayBOSCH 0332209150 Changeover Mini Relay - 5 Pins, 12 V, 20/30 A - Singleamazon.comOn Feb 9, 2024, at 12:55 PM, William Miller via RE-wrenches wrote:Dan: I think a solid state relay

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Jay via RE-wrenches
st? I knew it was time.  Sincerely, Ray Walters Remote Solar On 2/7/2024 9:19 AM, jay via RE-wrenches wrote: One of the things that I’m just now learning is about BMS failure/warranty/fix/replacement.    Some can be field

[RE-wrenches] rolls battery question

2024-02-07 Thread jay via RE-wrenches
Hi All, Can anyone tell me off the top of their head if older Rolls 6CS 25PS Do they have welded or bolted internal connections? I have a site I’m going to, very remote that might have a bad cell or two and I’m just figuring out how I’m going to bypass the bad cells. thanks jay

[RE-wrenches] Lithium batteries

2024-02-07 Thread jay via RE-wrenches
One of the things that I’m just now learning is about BMS failure/warranty/fix/replacement. Some can be field installed some need to go back to the OEM. I guess its something else we need to check on. Jay > On Feb 7, 2024, at 9:06 AM, Bradley Bassett via RE-wrenches > wrote: > >

Re: [RE-wrenches] Schneider Insight Home and Insight Cloud

2024-02-07 Thread jay via RE-wrenches
I guess the SCP is back in production. But if I understand correctly you still need the insight to program the XWPRO versions? thx jay > On Feb 7, 2024, at 8:50 AM, Drake Chamberlin via RE-wrenches > wrote: > > My experience with using Insight and Xanbus is that the projects never end.

[RE-wrenches] Lorentz pumps

2024-01-22 Thread Jay via RE-wrenches
Does anyone know if Lorentz pumps still exist in the US. Someone is looking for a PS200 control box. It seems to be intermittent Thx Jay ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address:

Re: [RE-wrenches] Recommendation on DC Breaker

2024-01-18 Thread Jay via RE-wrenches
I’d use an IMO disconnect as you don’t have any current limitations. I think sometimes things get lost in translation. Jay > On Jan 18, 2024, at 8:43 AM, Jason Szumlanski via RE-wrenches > wrote: > >  > I am installing an EG4 off-grid 3k inverter for the first time, and the > manual

[RE-wrenches] sol ark 15kw

2024-01-13 Thread jay via RE-wrenches
HI All, I have some sol ark 15 questions, and I’m sure someone out there has the answer as I can’t seem to find it in their literature How much can it output AC with solar: offgrid and ongrid in sell back mode. What I read was 15kw, but I can’t figure out if thats both on/off grid or not?

Re: [RE-wrenches] Odd battery charging behavior with Outback inverters

2024-01-12 Thread Jay via RE-wrenches
There is or was a setting in the mate 3/s that the rebulk volts has a trigger. If the voltage doesn’t get below it it won’t charge (absorb) properly. Fix is to set the rebulk up higher than the charge voltsI don’t know if that’s your issue or not but I have fixed this  on systems. JayOn Jan 12,

Re: [RE-wrenches] Recommendations for A/B battery switch

2024-01-03 Thread jay via RE-wrenches
HI Ron, I prefer to use two ON/OFF switches rather than A/B. That way you can always have power to the loads if you want. I can’t say they are the best but the Perko 9703 seems high quality and has been around for years. Its just a single on/off rated at 450 amps continuous and UL marine.

Re: [RE-wrenches] SMA TL-22 insulation resistance error

2023-12-13 Thread Jay via RE-wrenches
I think that using a megger etc to test the panels and wires is what I’d do before I yanked out  all the Wires. They are not that expensive anymore and maybe possible to rent one?JayOn Dec 13, 2023, at 8:53 AM, Dave Tedeyan via RE-wrenches wrote:Hi All,I am curious to hear if anyone else has run

Re: [RE-wrenches] 48 V DC temp sensing relay

2023-12-13 Thread Jay via RE-wrenches
Hi Drake Try this one. I get a lot of equipment from supply house. Since you need on with temp rise it’s an AC type. This one will do 8 amps at 120v so a small amp dc fan won’t hurt the relay. Jay

Re: [RE-wrenches] Mate 3s with legacy FX inverters

2023-12-12 Thread Jay via RE-wrenches
Agreed to all said. Numerous systems with mate 3/3s and every inverter and stacking is all fine. New hub 10:3 required. MX CC don’t appear on the mate 3/s. Few of my systems are on optics so can’t comment on that. JayOn Dec 12, 2023, at 1:15 PM, Roland Shackelford via RE-wrenches wrote:We have

[RE-wrenches] Hydraulic KO tool

2023-12-11 Thread Jay via RE-wrenches
I’m wondering if anyone has recommendations for an inexpensive hydraulic KO tool. I have a project where I need to punch some 4” holes in gutter. I can’t get a jig saw or anything in there and a 4” hole saw bit is crazy expensive. There are many inexpensive hydraulic tools out there that

Re: [RE-wrenches] Integrating Fortress E-vault maxes into an SI AC-coupled system

2023-11-12 Thread Jay via RE-wrenches
via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:Maybe someone else knows differently but it was explained to me that the fortress batteries have a relay that disconnects the battery if the voltage gets to high or low. There isn’t any electronic  device to change battery impedance b

Re: [RE-wrenches] Integrating Fortress E-vault maxes into an SI AC-coupled system

2023-11-12 Thread Jay via RE-wrenches
Maybe someone else knows differently but it was explained to me that the fortress batteries have a relay that disconnects the battery if the voltage gets to high or low. There isn’t any electronic  device to change battery impedance besides what the actual cells are doing. JayOn Nov 12, 2023, at

Re: [RE-wrenches] Cable sizing for high current modules? NEC interpretation/guidance?

2023-11-10 Thread Jay via RE-wrenches
I’ve wondered what other variables are at work given that mostly these connectors work as they should. I’d like to see them come with plugs covering the openings. This would keep dirt, salt air, moisture, etc  out until they are connected. As to if there were lots of failures with SW modules then

Re: [RE-wrenches] Small Diesel generator recommendation off-grid

2023-11-04 Thread jay via RE-wrenches
It depends a lot on the what you want. open chassis sound enclosed super quite tier 4 prime/standby built in 2 wire start etc. MQ power make great units. https://www.mqpower.com/whisperwatt.html jay > On Nov 4, 2023, at 7:45 AM, Mac Lewis via

Re: [RE-wrenches] Radian Question

2023-11-01 Thread Jay via RE-wrenches
. ---   Drake Chamberlin Athens Electric LLC Ohio Electrical Contractor’s License 44810 NABCEP Certified PV Installation Professional On 2023-10-31 12:14, Jay via RE-wrenches wrote:   Is the radian connected to grid sell?     If so then I'd say yes the higher grid voltage is preventing

Re: [RE-wrenches] Radian Question

2023-10-31 Thread jay via RE-wrenches
based >> on the reading of 251 and higher when the inverter would not connect. >> >> Thanks, >> >> Drake >> >> >> >> Drake Chamberlin >> >> Athens Electric LLC >> >> Ohio Electrical Contractor’s License 44810 >> &

Re: [RE-wrenches] Radian Question

2023-10-31 Thread Jay via RE-wrenches
on the reading of 251 and higher when the inverter would not connect. Thanks, Drake Drake Chamberlin Athens Electric LLC Ohio Electrical Contractor’s License 44810 NABCEP Certified PV Installation Professional ---   On 2023-10-30 20:37, Jay via RE-wrenches wrote:   Drake I forgot to ask, but I'm

Re: [RE-wrenches] Radian Question

2023-10-30 Thread Jay via RE-wrenches
0? (IE 140 V X 2). Thanks for your help. Drake Drake Chamberlin Athens Electric LLC Ohio Electrical Contractor’s License 44810 NABCEP Certified PV Installation Professional ---   On 2023-10-29 15:45, Jay via RE-wrenches wrote:   Hi drake   The early mate 3 has a glitch which I think they c