Re: [RE-wrenches] 2014 NEC 705-100 (A)

2017-03-22 Thread billbrooks7
Jay, You need to provide more information. The 2014 NEC is a significant improvement in the language related to single-phase inverters on a 3-phase service. To read it any other way shows a very large misunderstanding of the language. It should be much better on the 2014 NEC, not worse. Where

Re: [RE-wrenches] SMA 40 series DC disconnect

2016-12-15 Thread billbrooks7
William, I was also surprised to see SMA go down this road (ala Fronius IG). I can’t speak to why they did this. I’m installing my first 40 series right now. I have never supported covering the array as a viable method of removing voltage. It is far safer to unplug the strings on the roof

Re: [RE-wrenches] SMA $0 series DC disconnect

2016-12-14 Thread billbrooks7
William, I’m not sure you meant to imply this, but carports and groundmounts do not need any RS equipment unless you were to bring the dc conductors into a building, which would not be smart. The 2017 NEC allows connectors to be used as isolation devices for equipment as long as the circ

Re: [RE-wrenches] Undercurrent Protection?

2016-11-01 Thread billbrooks7
Eric, No worries on the education side. I’ve been educating for nearly 30 years in this field. I’m learning new stuff every day so I expect others to have the same commitment to learning. I’m glad to see that you do. One personal frustration with the listing label on inverters is that the

Re: [RE-wrenches] Undercurrent Protection?

2016-10-31 Thread billbrooks7
Eric, Your reasoning sounds logical, but it is missing the point. Transformers have to be protected by overcurrent devices, similar to wire. Inverters are current limited devices so they only have to be able to withstand a certain size circuit breaker. The current from the inverter is consider

Re: [RE-wrenches] NRTL certification question

2016-08-29 Thread billbrooks7
Steven, Although you are correct that OSHA certifies NRTLs for specific test standards, I have not run into jurisdictions in California that reject products listed to UL standards by ETL, TUV, and CSA. There have been specific cases where the County and City of LA have questioned various pro

Re: [RE-wrenches] 120% rule for hybrid inverters

2016-08-12 Thread billbrooks7
All, The 2011 NEC reference for stand-alone systems is 705.12(D)(2) Exception: Exception: Where the photovoltaic system has an energy storage device to allow stand-alone operation of loads, the value used in the calculation of bus or conductor loading shall be 125 percent of the rated uti

Re: [RE-wrenches] Siemens P4JF 75 watt PV module spec sheet

2016-04-29 Thread billbrooks7
Dana, Reaching back into my brain archives, having done a few projects with these modules, I know that many, if not all, of these modules were rated for a maximum system voltage of 48-volts. They can’t be used on higher voltage PV arrays. This was a budget version of their standard produ

Re: [RE-wrenches] reflective label maker?

2016-04-01 Thread billbrooks7
Chris, Where sign requirements (whether in NEC, IBC, IFC, IRC, etc) have specific requirements for specific signs that may not agree with the basic ANSI rules, the code requirement applies. Where no color requirement accompanies the sign, then the ANSI color designations would be most appropria

Re: [RE-wrenches] reflective label maker?

2016-04-01 Thread billbrooks7
Chris, Just to add a fine point of clarification, 690.31(G)(4) requires that the "warning" sign on conduit be Reflective, Capitalized, with white lettering on Red background. This intentionally does not match the ANSI color schemes for signs. The NEC overrules ANSI in this case. If AHJs req

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread billbrooks7
Ray, I guess I have to step in after that acknowledgement. PV system circuit is a self-defined term and therefore cannot be defined unless you are going to develop a meaning that is different from the self-definition. It means ANY circuit in a PV system. This includes battery and stand-alone circu

Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for center-fed panelboards

2016-03-03 Thread billbrooks7
Chris, While John’s article may seem like a logical interpretation of the 2014 NEC, if you lived in the western half of the United States where these panels are common, you would have a very different view of his choice of articles. His article sites a technicality that is not a safety co

Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for center-fed panelboards

2016-03-03 Thread billbrooks7
Howie, To clarify what the 2017 NEC states, it allows for either end of the bus. There is some value to having loads in between the PV breaker and the main breaker. Also, by putting the PV breaker as far away from the main as possible, the heat of both breakers are likely to affect each othe

Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for center-fed panelboards

2016-03-03 Thread billbrooks7
Phil, I think you already understand how to apply the “120% rule.” All this is saying is that the breaker can go at either end of a center-fed panel for dwellings. Do you understand now? To summarize—a 200A center-fed panel would allow a 40-amp PV breaker to be installed at either end to

Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for center-fed panelboards

2016-03-02 Thread billbrooks7
All, Here is the new language that has been approved for the 2017 NEC (more authoritative than JW). 705.12(B)(3)(d) (d) A connection at either end, but not both ends, of a center-fed panelboard in dwellings shall be permitted where the sum of 125 percent of the power source(s) output

Re: [RE-wrenches] Aquion Batteries

2016-01-29 Thread billbrooks7
Dan, I concur with your basic assessment. After listening to an Aquion presentation, and reviewing the operating curves, this battery has a very narrow application. Most off-grid houses these days have significant surge loads. That is why we spend so much time and effort making sure our

Re: [RE-wrenches] Plastic washers

2016-01-27 Thread billbrooks7
William, It appears that most (not all) of the damage you show on your website is due to incidental contact of bare copper with the aluminum. Also, dripping from bare copper to aluminum is a problem particularly in a marine environment. Lastly, the Coast Guard has been using unframed modules

Re: [RE-wrenches] traveling with digital meters

2015-11-09 Thread billbrooks7
Jay, I always try to carry on meters. This includes I-V curve tracers and such. TSA will often ask you to turn them on. Bill. -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay Sent: Monday, November 09, 2015 3:50 PM To: RE-wrenches

Re: [RE-wrenches] Guarding against live parts 690.7 (D)

2015-09-05 Thread billbrooks7
William, You can always quote me to an AHJ, as long as I actually said it or wrote it. I have been accused of saying all kinds of things that I never said—people just misunderstood what I said and “quoted” me incorrectly. All the best—and stay safe. Always tragic to hear of electrocutions

Re: [RE-wrenches] Guarding against live parts 690.7 (D)

2015-09-04 Thread billbrooks7
William, I’m shocked and offended (a tiny bit) that you would prejudice yourself to not agree with me ;-). First of all I have been heavily involved in the revising of the language in 690.31(A) to make it clear that we cannot walk up and touch cables operating at 600V. The term guarded is

Re: [RE-wrenches] Guarding against live parts 690.7 (D)

2015-09-04 Thread billbrooks7
Craig, This one is easy to misinterpret. You missed the words “live parts”. This has been removed from the 2017 NEC because it is actually referring to load circuits being fed directly by a PV system on the dc side. All references to loads and batteries are being removed from 690. This is

Re: [RE-wrenches] Cable tray

2015-08-31 Thread billbrooks7
Brian, I don’t know that I have a lot of good news for you. I have looked into this and I really don’t see a good way out of making some pretty conservative assumptions. You can read what I wrote in my IAEI article on Support of Exposed Cable earlier this year. I get into ampacity briefly tho

Re: [RE-wrenches] Rapid Shutdown Battery Systems

2015-08-27 Thread billbrooks7
Ray, Do you have a massive battery bank and 3, 8kW inverters inside the house? Is this in a garage or power shed. If it is a power shed, then 690.12 is not intended to relate to the power shed. That will be clarified in the 2017 NEC. The area for discussion is what constitutes the length of batte

Re: [RE-wrenches] Using the North Facing Roof

2015-07-31 Thread billbrooks7
Jarmo, Your intent was laudable, but simple trigonometry just flat out fails with the complexity of solar geometry. PVWatts is so easy to use that anyone, without any knowledge of trigonometry, can use it with far more accurate results. Take advantage of nice, free software that your tax doll

Re: [RE-wrenches] Using the North Facing Roof

2015-07-28 Thread billbrooks7
Larry and Peter, You are too old-school to think outside the box. It’s not about direct sunlight—it’s all about kWh/m^2/day and those numbers don’t lie. Your analysis is not correct and this is why simple analyses will always give you a wrong answer. North-facing arrays have been financial

Re: [RE-wrenches] Using the North Facing Roof

2015-07-28 Thread billbrooks7
Jarmo, Unfortunately, simple is wrong in this case—and detrimental to the PV industry that needs all the roof real estate it can find. Bill. Bill Brooks, PE Principal Brooks Engineering From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jarmo.venalai.

Re: [RE-wrenches] Using the North Facing Roof

2015-07-28 Thread billbrooks7
Jarmo, The sun’s geometry is not nearly that simple. To understand the impact of north-facing arrays, you have to perform a simulation. PV:WATTS does this just fine and it is easy to show that a 18-degreed North-facing tilt produces 75% of a perfect 30-degree south-facing array. Far more than

Re: [RE-wrenches] SMA 1800u not generating power

2015-07-24 Thread billbrooks7
Glenn, While the installation may not claim exact compliance with the current NEC (debatable), you can easily show that the TL inverter is much safer than the older 1800U. The TL has arc-fault detection and much better ground-fault detection. Conduit is not the answer since it breaks several