*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
"A switch, outside of the building, opening the PV circuit to the power
electronics, and functioning as the pv s
s/o0ukef>
*From:* RE-wrenches on
behalf of Jeremy Rodriguez
*Sent:* Tuesday, February 1, 2022 8:31:16 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
What about the PV circuits tha
y 1, 2022 8:31:16 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
What about the PV circuits that leave the combiner and are ran on or in a
building to the CC
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 812
To: RE-wrenches
Subject: Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
What about the PV circuits that leave the combiner and are ran on or in a
building to the CC
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iP
t;
CA Lic. 773985
From: RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>]
On Behalf Of Ray
Sent: Tuesday, February 1, 2022 10:11 AM
To: re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>
Subject: Re:
-top or ground-mount. Although the 2020 code includes
>>> some differing language, I don’t see it as exempting ground mount systems.
>>>
>>>
>>>
>>> The moral of the story is this: For ground-mounts: either install RSS or
>>> put your equipme
38-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Ray
> *Sent:* Tuesday, February 1, 2022 10:11 AM
> *To:* re-wrenches@lists.re-wrenches.org
> *Subject:* Re: [RE-
ary 1, 2022 10:11 AM
> To: re-wrenches@lists.re-wrenches.org
> Subject: Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
>
> Ground mounts do NOT require RSS. We hashed this out years ago on the
> Wrenches list, when NEC 2017 came out.
>
> See Figure 690.1(B) Note (2): "
2017 NEC, we were very careful to carve out all batteries and loads,
>>> that were previously part of PV systems, and place them in their own
>>> articles.
>>>
>>> I have not read through the battery sections of the code to verify this, I
>>
...@lists.re-wrenches.org] *On
Behalf Of *Ray
*Sent:* Tuesday, February 1, 2022 10:11 AM
*To:* re-wrenches@lists.re-wrenches.org
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
Ground mounts do NOT require RSS. We hashed this out years ago on the
Wrenches list, when NEC 2017 came out
llersolar.com/>
CA Lic. 773985
*From:*Jay [mailto:jay.pe...@gmail.com]
*Sent:* Tuesday, February 1, 2022 6:07 AM
*To:* will...@millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
2017 code has a specific exception/clarification for ground mount
solar
ttp://www.millersolar.com/>
CA Lic. 773985
*From:*Jay [mailto:jay.pe...@gmail.com]
*Sent:* Tuesday, February 1, 2022 6:07 AM
*To:* will...@millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
2017 code has a specific exception/clarification for ground mount
07 AM
*To:* will...@millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
2017 code has a specific exception/clarification for ground mount
solar that it does not need RS.
It’s in the first line after 690.12
Jay
On Feb 1, 2022, at 12:13 AM, William Miller
wrote:
: [RE-wrenches] Rapid Shutdown for Off-grid systems
William
Are you sure RSD is required on a non habitable building, historically its
not required. Now that being said we use fire raptor with the best results,
yes it takes an extra conduite and might require a button and power supply
depending
Monday, January 31, 2022 7:21 PM
> To: William Miller; RE-wrenches
> Subject: Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
>
> William
> Are you sure RSD is required on a non habitable building, historically its
> not required. Now that being said we use fire raptor w
www.millersolar.com
CA Lic. 773985
*From:* Kirpal [mailto:solarwo...@gmail.com]
*Sent:* Monday, January 31, 2022 5:21 PM
*To:* RE-wrenches; William Miller
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
Hi William.
We have had good luck with the AP Smart Rapid shutdown system
...@gmail.com]
*Sent:* Monday, January 31, 2022 7:21 PM
*To:* William Miller; RE-wrenches
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
William
Are you sure RSD is required on a non habitable building, historically its
not required. Now that being said we use fire raptor with the best
William
Are you sure RSD is required on a non habitable building, historically its
not required. Now that being said we use fire raptor with the best results,
yes it takes an extra conduite and might require a button and power supply
depending on inverter application.
Jerry
On Mon, Jan 31, 2022, 9
I also recently used the Tigo with Sol-Ark to provide the 12V signal with
good success. The Tigo transmitter can also (barely) fit inside the Sol-Ark
wiring compartment, so you do not need the whole Tigo enclosure for it.
Cheers,
Dave
On Mon, Jan 31, 2022 at 8:21 PM Kirpal wrote:
> Hi William.
>
Hi William.
We have had good luck with the AP Smart Rapid shutdown system. It is
similar to the Tigo in that it sends a "heartbeat" signal to the units up
behind each solar panel over the power wires. I haven't tried the Tigos yet
but would be open to it if the opportunity presented itself. The t
William,
We did one this year, offgrid, Outback Radian with Simpliphi batteries.
Used the outback rapid shutdown option which is probably similar to the
fire raptor system.
Cheers!,
Vic Guillot
Vic Guillot
Sol Sierra, Inc.
209.795.3554 office
209.768.3560 mobile/text
On Mon, Jan 31, 2022 at 9:5
Hi William,
We have a half dozen plus off grid systems using SolArk inverters and
TIGO optimizers. They work well and the TIGO's, from my experience,
have been really reliable. The necessary 12 volt signal can come
directly from the relay in the SolArk inverter.
Best,
Daryl DeJoy
NABCEP Certifi
Hi William,
I have had good luck with the Tigo TS4-AF. Although it does require a 12VDC
power supply for it's RSD transmitter, Outback, Sol Ark and Schnieder have
a straight forward integration not requiring dependency of AC output from
inverter.
Best,
Chris
On Mon, Jan 31, 2022 at 12:57 PM Wil
Friends:
It is quite rare for us to install off-grid systems on roof-tops. We have
one coming up with about 20kW on a large barn roof. This will be our first
off-grid with a module-level rapid shutdown requirement. I see no
exemptions from RSS for off-grid systems in the code. I have looked