RE: Transfer Switch Tests

2013-10-30 Thread John Drucker - Home
"More and more I find the committee's saying, well the AHJ can change it" Then why do we need the committee or for that matter the codes and standards they oversee if its going to be left to the ahj anyway ? As for cost impact very much a consideration in the adoption of codes and standards in Ne

RE: 150 gpm pump test

2013-10-30 Thread Steve Leyton
It'll work with roughly 98psi to spare on the first floor. LMAO ... Steve L. -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work Sent: Wednesday, October 30, 2013 2:53 PM To: sprinkler

Re: 150 gpm pump test

2013-10-30 Thread Todd - Work
This is a pump that is not needed at all and should have never been installed. The building is a 3 story retirement home with a system designed per NFPA 13, which includes attic protection. There is 90 psi at the base of the riser and the curve appears to be flat enough to design a system for th

Re: Transfer Switch Tests

2013-10-30 Thread rongreenman .
I've had failures under lees than load, particularly where the electrical guy found he could eliminate his problem by disconnecting the lead to the FP starter, but that failure was immediate. I can't imagine how a pump running at full load wouldn't fail before a couple of minutes at most, then woul

Re: Pipe supports revisited (Pipe support spacing requirements for structural supports)

2013-10-30 Thread Roland Huggins
There has indeed been clarification but you have to be part of that tiny sector of the industry that read the ROPs and ROCs to have been aware of it. Several cycles ago we attempted to have the 250 lb requirement removed based on the requirements by the kind and gentle OSHA group that one must

RE: Pipe supports revisited (Pipe support spacing requirements for structural supports)

2013-10-30 Thread Craig.Prahl
I cannot recall one occasion when the structural engineer has made provision for sprinkler pipe plus 250 lbs when designing the structural steel. 99.9% of pre-engineered buildings can barely support sprinkler pipe over 2"-3" let alone anything bigger and let alone an additional 250 lb. Then wh

Re: Pipe supports revisited (Pipe support spacing requirements for structural supports)

2013-10-30 Thread Roland Huggins
It appears that you are quoting a section about apples but are talking about oranges. There is NO change regarding the load carried by the structural member. It is still the weight of the pipe (not 5X) plus 250lbs. The 5X rule applies to the hanger assembly which was better defined in 2013 to

RE: Transfer Switch Tests

2013-10-30 Thread Tom Duross
So the pump becomes a load bank. -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Denhardt Sent: Wednesday, October 30, 2013 11:43 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Tra

RE: Transfer Switch Tests

2013-10-30 Thread Tom Duross
One other thing. I wonder why the current rating characteristics are less for emergency power than normal power? TD I would love to read the committee's logic for this.  How much water would be wasted in the process? More and more I find the committee's saying, well the AHJ can change it, but i

RE: Transfer Switch Tests

2013-10-30 Thread John Denhardt
The Committee's statement as stated in the ROP is as follows: Committee Statement: Clarifies that a standby generator requires a 30 minute test while carrying peak electric motor fire pump horsepower load. Number Eligible to Vote: 33 Ballot Results: Affirmative: 33 The committee agreed with the

Re: Transfer Switch Tests

2013-10-30 Thread Dwight Havens
I would love to read the committee's logic for this.  How much water would be wasted in the process? More and more I find the committee's saying, well the AHJ can change it, but if it is not practical to perform in the first place (where does one put all the water?) why put the burden on the AH

RE: 150 gpm pump test

2013-10-30 Thread RFletcher
It's probably that we don't normally test beyond 150%. There is no need to go beyond 150%. We did an extended test of a 1500 gpm diesel with PLD just to see what it was capable of. It was still providing boost at 4000 gpm, very impressive. Ron F -Original Message- From: sprinklerforum-bo

Re: Transfer Switch Tests

2013-10-30 Thread rongreenman .
I like that idea. On Wed, Oct 30, 2013 at 8:01 AM, Fairchild, Jack < jfairch...@ballinger-ae.com> wrote: > Maybe it's time to include a "cost impact" line in the public input form > and public comment form. I'll admit this may not be very productive > considering the vast majority of the ICC ch

RE: Transfer Switch Tests

2013-10-30 Thread Fairchild, Jack
Maybe it's time to include a "cost impact" line in the public input form and public comment form. I'll admit this may not be very productive considering the vast majority of the ICC changes "will not affect the cost of construction", even though they clearly do. Does anyone know if the ICC kee

RE: 150 gpm pump test

2013-10-30 Thread Craig.Prahl
Improperly sized pump perhaps? Craig L. Prahl, CET Fire Protection Group Lead CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 craig.pr...@ch2m.com > I did a test on a 150 gpm at 70 psi vertical in

RE: 150 gpm pump test

2013-10-30 Thread John Denhardt
Be careful - make sure the current draw of the electric motor is not too much. You do not want to burn a motor up. John August Denhardt, P.E., FSFPE Strickland Fire Protection Incorporated 5113 Berwyn Road College Park, Maryland 20740 Office Telephone Number: 301-474-1136 Mobile Telephone Numbe

Re: 150 gpm pump test

2013-10-30 Thread Jeff Garrison
In the mechanical world, it's not unheard-of to use pumps at 200% of rating. On Oct 30, 2013 10:29 AM, "Todd - Work" wrote: > I did a test on a 150 gpm at 70 psi vertical inline pump (Aurora) this > morning. When I opened the 2-1/2" hose valve completely, it was flowing at > 355 gpm (net 26 psi).

150 gpm pump test

2013-10-30 Thread Todd - Work
I did a test on a 150 gpm at 70 psi vertical inline pump (Aurora) this morning. When I opened the 2-1/2" hose valve completely, it was flowing at 355 gpm (net 26 psi). I was surprised that I could flow that much water. Is this common for smaller pumps? I've never tested a pump this small before.

RE: Transfer Switch Tests

2013-10-30 Thread Bill Brooks
Not covered on the AFSA webinar either. One of my recurring concerns for the NFPA system is the ratio of People Who Get Paid for Stuff / People Who Actually Pay for Stuff. NFPA 25 is about 10 to 1 but can you consider large organization reps in the category of payers? That would be GSA rep, VA re