Re: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Bob Caputo via Sprinklerforum
The committee discussion on this change was the in a 400 cubic foot enclosure, it doesn’t matter where the sprinkler is relative to the shelf. Think about in rack sprinklers and the product loads…. I agree there should be concern for bumping the sprinkler but no one is loading the closet with

RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread BRUCE VERHEI via Sprinklerforum
From an old fire guys perspective I’d be more concerned with accidental head breakage than water dispersal. Best. > On 07/01/2021 3:01 PM Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum > wrote: > > > Thanks for that clarification. I missed that. > > Pete > > -Original

RE: [EXTERNAL] RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
Thanks for that clarification. I missed that. Pete -Original Message- From: Sprinklerforum On Behalf Of Dane Long via Sprinklerforum Sent: Thursday, July 1, 2021 12:51 PM To: sprinklerforum@lists.firesprinkler.org Cc: Dane Long ; Larrimer, Peter A (HEFP\19HEF) Subject: [EXTERNAL]

RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Dane Long via Sprinklerforum
Peter, One thing to emphasize is that it says 400ft3 not ft2. So, the thought is if you have mechanical equipment like a furnace, you're not really going to have much room to store anything in this closet. An example would be a closet with an 8ft. ceiling can only be 7ftx7ft. This is 49sqft or

RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Bob Caputo via Sprinklerforum
Pete, You are correct. Where the closet is less than 400 ft3, no clearance is required below the deflector Bob Caputo -Original Message- From: Sprinklerforum On Behalf Of Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum Sent: Thursday, July 1, 2021 10:36 AM To:

RE: Closets and Clearance from Deflector to Storage

2021-07-01 Thread Mike Morey via Sprinklerforum
My understanding had always been this was mainly related to shelves and the like as an obstruction since the head is going to basically inundate the closet. I believe it was Mr. Huggins that once reminded us that water isn't like light and you don't have to see the head to get wet, as was a

RE: Sprinkler drop sizing

2021-07-01 Thread Ed Kramer via Sprinklerforum
>From the 2016 flavor of NFPA 13: Section 23.4.1.2 says minimum size for steel pipe is 1". The exceptions given in 8.15.20.4 and 8.15.20.5 are for nipples 4" or less in length. Not what your customer will want to hear, but it is what it is . . . Ed Kramer Design Manager | Bamford Fire

Re: Sprinkler drop sizing

2021-07-01 Thread 321 via Sprinklerforum
I think 13 tells us in a round about way that 1/2" and 3/4" steel can only be used as "Pilot Line" detector piping per Chapter 8 and Chapter 6. Look at Note "B" in the allowed pipe size table in Chapter 6...it sends you to the pilot line section in Chapter 8 and restricts those sizes to that

RE: Sprinkler drop sizing

2021-07-01 Thread Dennis Wilson via Sprinklerforum
I have the 1985 book, and it wasn't allowed then. Same rule as now, ½ x 1 ell to 1" drops. -Original Message- From: Sprinklerforum On Behalf Of Jennifer Cornett via Sprinklerforum Sent: Thursday, July 1, 2021 10:45 AM To: Mark Phillips ; Sprinklerforum@lists.firesprinkler.org Cc:

RE: Sprinkler drop sizing

2021-07-01 Thread Jennifer Cornett via Sprinklerforum
The branchlines are 1", 1-1/4", etc. with a tee and the drop is ½" pipe to the sprinkler heads. Where I would normally design a 1" drop, they used ½". Sincerely, Jennifer Cornett, NICET SET Sprinkler Sales Firetrol Protection Systems, Inc. 1001 Ave. B Lubbock, Texas 79401 Ph 806-771-3500 Cell

Re: Sprinkler drop sizing

2021-07-01 Thread Mark Phillips via Sprinklerforum
Code allows you to retrofit that with a 1/2 x1 ell and a 1 “ new drop if the outlets are 1/2” off line Could you elaborate? Sent from my mobile device Please excuse spelling, grammar, and auto correction. Mark Phillips Branch Manager Fire Sprinkler Design, Install, Inspections Service,

Closets and Clearance from Deflector to Storage

2021-07-01 Thread Larrimer, Peter A (HEFP\19HEF) via Sprinklerforum
NFPA 13 (2019 edition) states the following in two sections: 9.5.5.4 Closets. In all closets and compartments, including those closets housing mechanical equipment, that are not larger than 400 ft3 (11 m3) in size, a single sprinkler at the highest ceiling level shall be sufficient without regard

Sprinkler drop sizing

2021-07-01 Thread Jennifer Cornett via Sprinklerforum
I have a customer with an existing system that the fire marshal wants brought up to code. Some is simply adding/relocating heads, but some is that the original installation company used 1/2" drops for the sprinkler heads. The fire marshal wants all of them changed. The customer wants to know

RE: Dry head boot retrofit

2021-07-01 Thread Hinson, Ryan via Sprinklerforum
https://www.tyco-fire.com/index.php?P=detailprod=5910 Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire Protection Engineer O 612-900-3755 \ M 763-688-4045 \  F 952-229-2923 rhin...@burnsmcd.com  \  burnsmcd.com 8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437

RE: Dry head boot retrofit

2021-07-01 Thread Hinson, Ryan via Sprinklerforum
I think you are thinking of the Tyco DSB-2 Sprinkler boot which included one boot, two strap ties, and 1/3 oz. of adhesive. This component is/was found on Tyco's Dry Sprinkler cuts...at least on the old cutsheets TFP500 and TFP550. Not sure if it is still available. Ryan L. Hinson, PE*,