Re: Using Flex Head Connection from CPVV

2022-01-06 Thread John Denhardt via Sprinklerforum
My top of the head guess is that this would be allowed. I have never heard of any concerns or restrictions with this approach. *The above is my opinion and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects. This is provided with

Re: Using Flex Head Connection from CPVV

2022-01-06 Thread Travis Mack via Sprinklerforum
I’ve had customers do it. They seemed to find it quite beneficial when chosen for the correct job. Travis Mack, CFPS, CWBSP, RME-G, COC, SET Senior Engineering Manager MFP Design 480-505-9271 ext. 700 C: 480-272-2471 travis.m...@mfpdesign.com www.mfpdesign.

Using Flex Head Connection from CPVV

2022-01-06 Thread Vince Sabolik via Sprinklerforum
Thoughts? Approved or not? Thanks, Vince -- *Vince Sabolik* *West Tech Fire Protection, Inc.*** 11351 Pearl Road   /   Strongsville, Ohio   44136 Phone 440 238-4800    Fax 440 238-4876   Cell 440 724-7601 ___ Sprinklerforum mailing list Sprinklerf

RE: [EXTERNAL] RE: Open or exterior corridors

2022-01-06 Thread Dane Long via Sprinklerforum
Sorry this is the 2012 IBC. Thanks, Dane Long, AET Engineering Technician | Bamford Fire Sprinkler Co., Inc. P:    785.825.7710 F:    785.825.0667 A:   1383 W. North Street  Salina, KS  67401 -Original Message- From: Prahl, Craig/GVL Sent: Thursday, January 6, 2022 1:51 PM To: s

RE: Open or exterior corridors

2022-01-06 Thread Bob Knight via Sprinklerforum
Dane, "shall be equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 (NFPA 13) or 903.3.1.2. (NPFA 13R)". Based on this wording, the sprinklers in the open exterior corridors are not required since you are providing sprinkler coverage throughout in accordance

Standpipe Hangers

2022-01-06 Thread Taylor Schumacher via Sprinklerforum
There's a rule I remember but cannot find for the life of me. When is a hanger required on the horizontal piping from a standpipe to a hose valve? I believe it's 18" but cannot justify it. Any help is greatly appreciated. Taylor Schumacher CET J-Berd Mechanical/Security Fire Sprinkler/Berd Ele

RE: [EXTERNAL] RE: Open or exterior corridors

2022-01-06 Thread Prahl, Craig/GVL via Sprinklerforum
Dane: What code are you referencing? Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS TEAMS -Original Message- From: Sprinklerforum On Behalf Of Dane Lo

RE: Open or exterior corridors

2022-01-06 Thread Dane Long via Sprinklerforum
They reference section 1026.6 1026.6 Exterior stairway and ramp protection. Exterior exit stairways and ramps shall be separated from the interior of the building as required in Section 1022.2. Openings shall be limited to those necessary for egress from normally occupied spaces. And in particula

RE: Open or exterior corridors

2022-01-06 Thread Prahl, Craig/GVL via Sprinklerforum
Don't forget that corridors are egress paths and have limitations on length if sprinklered versus unsprinklered. To provide sprinklers or not may not necessarily be addressed by NFPA but may be a Building/Fire Code issue. Sometimes as sprinkler designers, it's easy to think NFPA 13 is the all i

RE: Open or exterior corridors

2022-01-06 Thread Mike Morey via Sprinklerforum
What in the IBC is requiring this, the only difference I'm aware of (which is no longer a difference at least in the last cycle or two) is that Type V construction requires protection of porch/patio/decks. I don't believe an exit corridor falls within those requirements? The intent was to coun

Open or exterior corridors

2022-01-06 Thread Dane Long via Sprinklerforum
I have a 13R project with exterior open corridors as seen in 13R (2016) Figure A.6.6.5(a). Per the IBC were being required to provide protection. Can I apply 6.6.5.1.1? 6.6.5.1.1 Where sidewall sprinklers are installed beneath decks or balconies constructed with open wood joists, sprinklers shall