RE: Back Up Fire Pump

2021-09-14 Thread John Irwin via Sprinklerforum
Planning | Training -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Irwin via Sprinklerforum Sent: Tuesday, September 14, 2021 8:56 AM To: sprinklerforum@lists.firesprinkler.org Cc: John Irwin Subject: Back Up Fire Pump Sta

Back Up Fire Pump

2021-09-14 Thread John Irwin via Sprinklerforum
Starting design on a 35 story residential tower. Engineers plans show two identical fire pumps. Client wants to know if we need two fire pumps. I want to answer him with the code reference below, but experience has taught me that it may not be as simple as this ... Am I missing something or is

Re: NFPA 13 8.15.7.2 / 8.15.7.5 - Temporary Parking

2021-08-05 Thread John Irwin via Sprinklerforum
) 425-1001 x 2 Cell: (612) 759-5556 -Original Message- From: Sprinklerforum On Behalf Of John Irwin via Sprinklerforum Sent: Thursday, August 05, 2021 12:26 PM To: sprinklerforum@lists.firesprinkler.org Cc: John Irwin ; Aaron Peck ; Andrew Baldwin ; Roberto Alvarez Subject: NFPA 13 8.15.7.2

NFPA 13 8.15.7.2 / 8.15.7.5 - Temporary Parking

2021-08-05 Thread John Irwin via Sprinklerforum
So I'm going 12 rounds with a local fire marshal who wants to define what temporary parking means, under a drive through canopy. His logic is that he doesn't know how long a vehicle will be parked. His exact concerns are as follows: "Our answer was yes do to deliveries made and not knowing how

Re: Shop Drawings vs Design Drawings in Florida

2021-03-29 Thread John Irwin via Sprinklerforum
e was arguing that it didn't require sprinklers because it was still under the original year of building code as a remodel. Letter or spirit? On Mon, Mar 29, 2021 at 5:32 AM John Irwin via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > John, > > I'm also in Fl

RE: Shop Drawings vs Design Drawings in Florida

2021-03-29 Thread John Irwin via Sprinklerforum
John, I'm also in Florida and we struggle with the same when it comes to sign and seal. Project engineer of record doesn't want to sign our shops, AHJ demands signed shops ... always a point of contention. In your instance, I agree with you and Buddy that technically you are doing a like for l

Re: NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread John Irwin via Sprinklerforum
sive 20-month program provides a blended learning environment teamed with robust curriculum created by top industry leaders. Plus, the first six-months of instruction is online. Now enrolling for Spring 2021 <https://www.firesprinkler.org/itm>. On Thu, Mar 18, 2021 at 8:21 PM John Irwin via Sprinkl

NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread John Irwin via Sprinklerforum
NFPA 13 2016 25.2.1.4.2, Modifications that cannot be isolated, such as relocated drops, shall require testing at system working pressure. We have a local AHJ that always requires us to pump up tenant improvement projects to 200 psi if they are over 20 sprinklers. We have a waiver/release form

RE: Townhome - Common Areas

2021-01-27 Thread John Irwin via Sprinklerforum
doesn't require protection of garages per the exception in13D, then protect as for a garage in 13R. Steve Leyton (Sent from my smartphone; please excuse typos and voice-to-text corruptions.) Original message ---- From: John Irwin via Sprinklerforum Date: 1/27/21 6:

Townhome - Common Areas

2021-01-27 Thread John Irwin via Sprinklerforum
We're protecting (4) rows of townhomes per NFPA 13D. Between buildings are small common areas such as trash storage (132sqft) and mail room (260sqft). Providing protection in these rooms would come at an additional expense because the units being protected are fee simple and each has it's own l

RE: Self-storage Lockers

2020-10-15 Thread John Irwin via Sprinklerforum
I have done a lot of these in many jurisdictions and never protected the lockers. I have not been asked about it yet. I do protect the 4x4 or 5x5 lockers that are full height. John Irwin Quick Response Fire Protection "The bitterness of poor quality remains long after the sweetness of low pr

Re: Testing of existing systems (solution!)

2020-08-19 Thread John Irwin via Sprinklerforum
academy.com<http://www.sprinkleracademy.com>> ce...@sprinkleracademy.com<mailto:ce...@sprinkleracademy.com> ?? OUR STUDENTS SAVE LIVES!! From: Sprinklerforum on behalf of John Irwin via Sprinklerforum Sent: Wednesday, August 19,

RE: Testing of existing systems

2020-08-19 Thread John Irwin via Sprinklerforum
fire.com<mailto:philli...@pyebarkerfire.com> Web : www.pyebarkerfire.com<http://www.pyebarkerfire.com<http://www.pyebarkerfire.com%3chttp:/www.pyebarkerfire.com>> -Original Message- From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf

Re: Testing of existing systems

2020-08-19 Thread John Irwin via Sprinklerforum
-7587 Email : philli...@pyebarkerfire.com Web : www.pyebarkerfire.com<http://www.pyebarkerfire.com> -Original Message- From: Sprinklerforum On Behalf Of John Irwin via Sprinklerforum Sent: Tuesday, August 18, 2020 6:16 PM To: Sprinklerforum@lists.firesprinkler.org Cc: John Irwin S

RE: Testing of existing systems

2020-08-18 Thread John Irwin via Sprinklerforum
Nobody has an informal code interpretation on this? I don't believe we're all just putting 200 psi on other people's pipe. Anything saved from AFSA, NFSA or NFPA would be great. Thanks John Irwin Quick Response Fire Protection "The bitterness of poor quality remains long after the sweetness of

Follow up question

2020-08-17 Thread John Irwin via Sprinklerforum
Does anyone have a release of liability form for when the owner does decide to have us pressure test the system rather than argue with the local Marshall. John Irwin Quick Response Fire Protection 727-282-9243 Typed on tiny keys, just for you. Please forgive spelling errors, typographical trans

Testing of existing systems

2020-08-17 Thread John Irwin via Sprinklerforum
NFPA 13 2013 25.2.1.6 or NFPA 13 2016 25.2.1.4 We're doing a 200+ sprinkler add and relocate and the new fire marshal has decided that 200 sprinkler relocates is a lot and that I should put 200 psi on the existing piping. So we're playing the game of escalation and code interpretation. Does an

Uprights in non combustible concealed space

2020-06-18 Thread John Irwin via Sprinklerforum
We installed temporary upright Protection in a partially occupied building during a major renovation. We then came back and dropped pendent heads in the new ceiling. We left the uprights above the new ceiling. Fire inspector says we need to remove the uprights now. Is there a basis for removing

RE: Covered Parking in 13R

2020-05-29 Thread John Irwin via Sprinklerforum
..@comcast.net> From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf Of John Irwin via Sprinklerforum Sent: Friday, May 29, 2020 5:55 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Cc: John Irwin mailto:jir...@quickresponse

RE: Covered Parking in 13R

2020-05-29 Thread John Irwin via Sprinklerforum
ode to determine the If required. Mark at Aero 602 820-7894 From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf Of John Irwin via Sprinklerforum Sent: Friday, May 29, 2020 2:55 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.fi

Covered Parking in 13R

2020-05-29 Thread John Irwin via Sprinklerforum
I have a 3-story, 13R building. Type IIB construction. On the "engineered" bid set, no sprinklers are shown in the covered parking area. This area is inside the footprint of the first floor, with 2nd floor units being located above the parking area. There are no garage doors and the parking spac

RE: Concealed Combustible

2020-01-09 Thread John Irwin via Sprinklerforum
25 years in this business ... still new situations every week. Amazing. Wish I had some guidance for you JD. My gut says there isn't anything specific to this situation to guide you or absolve you of installing 3 levels of protection ... My feeling is that protection ABOVE the fiberboard (along

Re: 13D GPM to use?

2019-11-01 Thread John Irwin via Sprinklerforum
Where you live does the AHJ have the authority to write his own fire code? In Florida we would say "that's great that you want that, but no." 13D is two sprinklers. Do you even have 4 sprinklers in a single compartment? This kind of thing makes me crazy. John Irwin West Coast Branch Manager Qu

Fire Alarm plan checklist

2019-10-23 Thread John Irwin via Sprinklerforum
We have chapter 23 in NFPA 13 that gives us our checklist of what needs to be included in our shop drawings. Is there are similar check list for fire alarms? I don't see anything in NFPA 72 John Irwin ___ Sprinklerforum mailing list Sprinklerforum@li

Re: Fire Alarms

2019-08-13 Thread John Irwin via Sprinklerforum
PA 72. For example the word “alarm” is likely one of those words. Constantly reread those NFPA 72 word definitions as you digest the NFPA 72 sections. You will bump your nose less often. On Aug 13, 2019, at 4:32 AM, John Irwin via Sprinklerforum mailto:sprinklerforum@lists.firesprinkler.org>>

Fire Alarms

2019-08-13 Thread John Irwin via Sprinklerforum
I would guess some of you are pretty familiar with fire alarm code as well as sprinkler code. Our fire alarm division falls under my purview and I really don't know the first thing about them. They certainly don't seem to follow the same reasoning we use when determining how we are going to prot