Subject: Back Up Fire Pump
Sta
Starting design on a 35 story residential tower. Engineers plans show two
identical fire pumps. Client wants to know if we need two fire pumps. I want to
answer him with the code reference below, but experience has taught me that it
may not be as simple as this ... Am I missing something or is
) 425-1001 x 2
Cell: (612) 759-5556
-Original Message-
From: Sprinklerforum On Behalf
Of John Irwin via Sprinklerforum
Sent: Thursday, August 05, 2021 12:26 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: John Irwin ; Aaron Peck
; Andrew Baldwin ;
Roberto Alvarez
Subject: NFPA 13 8.15.7.2
So I'm going 12 rounds with a local fire marshal who wants to define what
temporary parking means, under a drive through canopy. His logic is that he
doesn't know how long a vehicle will be parked. His exact concerns are as
follows: "Our answer was yes do to deliveries made and not knowing how
e was arguing that it didn't require
sprinklers because it was still under the original year of building code as
a remodel. Letter or spirit?
On Mon, Mar 29, 2021 at 5:32 AM John Irwin via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> John,
>
> I'm also in Fl
John,
I'm also in Florida and we struggle with the same when it comes to sign and
seal. Project engineer of record doesn't want to sign our shops, AHJ demands
signed shops ... always a point of contention.
In your instance, I agree with you and Buddy that technically you are doing a
like for l
sive 20-month program provides a blended
learning environment teamed with robust curriculum created by top industry
leaders. Plus, the first six-months of instruction is online. Now
enrolling for Spring 2021 <https://www.firesprinkler.org/itm>.
On Thu, Mar 18, 2021 at 8:21 PM John Irwin via Sprinkl
NFPA 13 2016 25.2.1.4.2, Modifications that cannot be isolated, such as
relocated drops, shall require testing at system working pressure.
We have a local AHJ that always requires us to pump up tenant improvement
projects to 200 psi if they are over 20 sprinklers. We have a waiver/release
form
doesn't require protection of garages
per the exception in13D, then protect as for a garage in 13R.
Steve Leyton
(Sent from my smartphone; please excuse typos and voice-to-text corruptions.)
Original message ----
From: John Irwin via Sprinklerforum
Date: 1/27/21 6:
We're protecting (4) rows of townhomes per NFPA 13D. Between buildings are
small common areas such as trash storage (132sqft) and mail room (260sqft).
Providing protection in these rooms would come at an additional expense because
the units being protected are fee simple and each has it's own l
I have done a lot of these in many jurisdictions and never protected the
lockers. I have not been asked about it yet.
I do protect the 4x4 or 5x5 lockers that are full height.
John Irwin
Quick Response Fire Protection
"The bitterness of poor quality remains long after the sweetness of low pr
academy.com<http://www.sprinkleracademy.com>>
ce...@sprinkleracademy.com<mailto:ce...@sprinkleracademy.com>
??
OUR STUDENTS SAVE LIVES!!
From: Sprinklerforum on behalf
of John Irwin via Sprinklerforum
Sent: Wednesday, August 19,
fire.com<mailto:philli...@pyebarkerfire.com>
Web :
www.pyebarkerfire.com<http://www.pyebarkerfire.com<http://www.pyebarkerfire.com%3chttp:/www.pyebarkerfire.com>>
-Original Message-
From: Sprinklerforum
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
On Behalf
-7587
Email : philli...@pyebarkerfire.com
Web : www.pyebarkerfire.com<http://www.pyebarkerfire.com>
-Original Message-
From: Sprinklerforum On Behalf
Of John Irwin via Sprinklerforum
Sent: Tuesday, August 18, 2020 6:16 PM
To: Sprinklerforum@lists.firesprinkler.org
Cc: John Irwin
S
Nobody has an informal code interpretation on this? I don't believe we're all
just putting 200 psi on other people's pipe. Anything saved from AFSA, NFSA or
NFPA would be great. Thanks
John Irwin
Quick Response Fire Protection
"The bitterness of poor quality remains long after the sweetness of
Does anyone have a release of liability form for when the owner does decide to
have us pressure test the system rather than argue with the local Marshall.
John Irwin
Quick Response Fire Protection
727-282-9243
Typed on tiny keys, just for you. Please forgive spelling errors, typographical
trans
NFPA 13 2013 25.2.1.6 or NFPA 13 2016 25.2.1.4
We're doing a 200+ sprinkler add and relocate and the new fire marshal has
decided that 200 sprinkler relocates is a lot and that I should put 200 psi on
the existing piping. So we're playing the game of escalation and code
interpretation.
Does an
We installed temporary upright Protection in a partially occupied building
during a major renovation. We then came back and dropped pendent heads in the
new ceiling. We left the uprights above the new ceiling. Fire inspector says we
need to remove the uprights now. Is there a basis for removing
..@comcast.net>
From: Sprinklerforum
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
On Behalf Of John Irwin via Sprinklerforum
Sent: Friday, May 29, 2020 5:55 AM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: John Irwin mailto:jir...@quickresponse
ode to determine the If required.
Mark at Aero
602 820-7894
From: Sprinklerforum
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
On Behalf Of John Irwin via Sprinklerforum
Sent: Friday, May 29, 2020 2:55 AM
To:
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.fi
I have a 3-story, 13R building. Type IIB construction. On the "engineered" bid
set, no sprinklers are shown in the covered parking area. This area is inside
the footprint of the first floor, with 2nd floor units being located above the
parking area. There are no garage doors and the parking spac
25 years in this business ... still new situations every week. Amazing.
Wish I had some guidance for you JD. My gut says there isn't anything specific
to this situation to guide you or absolve you of installing 3 levels of
protection ...
My feeling is that protection ABOVE the fiberboard (along
Where you live does the AHJ have the authority to write his own fire code? In
Florida we would say "that's great that you want that, but no."
13D is two sprinklers. Do you even have 4 sprinklers in a single compartment?
This kind of thing makes me crazy.
John Irwin
West Coast Branch Manager
Qu
We have chapter 23 in NFPA 13 that gives us our checklist of what needs to be
included in our shop drawings.
Is there are similar check list for fire alarms? I don't see anything in NFPA 72
John Irwin
___
Sprinklerforum mailing list
Sprinklerforum@li
PA 72. For example the word “alarm” is likely one
of those words. Constantly reread those NFPA 72 word definitions as you digest
the NFPA 72 sections. You will bump your nose less often.
On Aug 13, 2019, at 4:32 AM, John Irwin via Sprinklerforum
mailto:sprinklerforum@lists.firesprinkler.org>>
I would guess some of you are pretty familiar with fire alarm code as well as
sprinkler code. Our fire alarm division falls under my purview and I really
don't know the first thing about them. They certainly don't seem to follow the
same reasoning we use when determining how we are going to prot
26 matches
Mail list logo