Subject: RE: [EXTERNAL] RE: Open or exterior corridors
Dane:
What code are you referencing?
Craig Prahl | Jacobs | Group Lead/SME - Fire Protection |
craig.pr...@jacobs.com | www.jacobs.com
1041 East Butler Road Greenville, South Carolina
g]
On Behalf Of Dane Long via Sprinklerforum
Sent: Thursday, January 06, 2022 11:41 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dane Long
Subject: RE: Open or exterior corridors
They reference section 1026.6
1026.6 Exterior stairway and ramp protection. Exterior exit stairways and
ramps sha
Long via Sprinklerforum
Sent: Thursday, January 6, 2022 1:41 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dane Long
Subject: [EXTERNAL] RE: Open or exterior corridors
They reference section 1026.6
1026.6 Exterior stairway and ramp protection. Exterior exit stairways and ramps
shall be
Message-
From: Sprinklerforum On
Behalf Of Mike Morey via Sprinklerforum
Sent: Thursday, January 6, 2022 11:43 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey
Subject: RE: Open or exterior corridors
What in the IBC is requiring this, the only difference I'm aware of (which
is no l
-
From: Sprinklerforum On Behalf
Of Mike Morey via Sprinklerforum
Sent: Thursday, January 6, 2022 12:43 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey
Subject: [EXTERNAL] RE: Open or exterior corridors
What in the IBC is requiring this, the only difference I'm aware o
x 260.487.7991
email mmo...@shambaugh.com
-Original Message-
From: Sprinklerforum On Behalf
Of Dane Long via Sprinklerforum
Sent: Thursday, January 6, 2022 12:38 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dane Long
Subject: Open or exterior corridors
BE ADVISED - This email orig
I have a 13R project with exterior open corridors as seen in 13R (2016)
Figure A.6.6.5(a). Per the IBC were being required to provide protection.
Can I apply 6.6.5.1.1?
6.6.5.1.1 Where sidewall sprinklers are installed beneath
decks or balconies constructed with open wood joists, sprinklers
shall