It appears that you are quoting a section about apples but are talking about
oranges. There is NO change regarding the load carried by the structural
member. It is still the weight of the pipe (not 5X) plus 250lbs. The 5X rule
applies to the hanger assembly which was better defined in 2013 to
...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Wednesday, October 30, 2013 1:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pipe supports revisited (Pipe support spacing requirements for
structural supports)
It appears that you
There has indeed been clarification but you have to be part of that tiny sector
of the industry that read the ROPs and ROCs to have been aware of it. Several
cycles ago we attempted to have the 250 lb requirement removed based on the
requirements by the kind and gentle OSHA group that one must
I'm getting tired of going toe-to-toe with every structural and piping engineer
regarding fire protection related pipe support and spacing requirements on
every time I work on a refinery-type project and hoping a hanging and support
committee member might weigh in here. The spacing limitations
...@parsleyconsulting.com
Cc: Leahy, Andrew P aple...@burnsmcd.com,Reene,Kevin
kre...@burnsmcd.com,Eberly, M. David mebe...@burnsmcd.com,Jordan,
David djor...@burnsmcd.com
Subject: Pipe supports revisited (Pipe support spacing requirements for
structural supports)
I'm getting tired
,Jordan,
David djor...@burnsmcd.com
Subject: Pipe supports revisited (Pipe support spacing requirements for
structural supports)
I'm getting tired of going toe-to-toe with every structural and piping
engineer regarding fire protection related pipe support and spacing
requirements
...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rongreenman .
Sent: Tuesday, October 29, 2013 3:23 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: RE: Pipe supports revisited (Pipe support spacing requirements for
structural supports)
I've
Of
craig.pr...@ch2m.com
Sent: Thursday, November 08, 2012 10:31 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe support spacing requirements for structural
supports
If the spacing of pipe rack supports does not meet the spacing
requirements of the NFPA Standards you need
: Pipe support spacing requirements for structural supports
instead of Standard for the Installation of Sprinkler Systems, how about
Benchmark to Determine Just how far from Reality the Actual Situation IS from
what Is Written Here-In, Now let's See the Numbers?
Quoting Ron Greenman rongreen
Subject: Re: Pipe support spacing requirements for structural supports
instead of Standard for the Installation of Sprinkler Systems, how about
Benchmark to Determine Just how far from Reality the Actual Situation IS from
what Is Written Here-In, Now let's See the Numbers?
Quoting Ron Greenman
: Pipe support spacing requirements for structural supports
If the spacing of pipe rack supports does not meet the spacing requirements
of the NFPA Standards you need to supplement with intermediate hangers in
order to have a compliant installation. I just don't use what's given.
Craig L. Prahl
] On Behalf Of
craig.pr...@ch2m.com
Sent: Thursday, November 08, 2012 10:31 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe support spacing requirements for structural supports
If the spacing of pipe rack supports does not meet the spacing requirements
of the NFPA Standards you need
-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Thursday, November 08, 2012 10:31 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe support spacing requirements for structural supports
, 2012 10:31 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe support spacing requirements for structural supports
If the spacing of pipe rack supports does not meet the spacing requirements
of the NFPA Standards you need to supplement with intermediate hangers in
order to have a compliant
...@firesprinkler.org] On Behalf Of Hinson, Ryan
Sent: Tuesday, November 06, 2012 7:07 PM
To: sprinklerforum@firesprinkler.org
Subject: Pipe support spacing requirements for structural supports
I've got a couple projects which have pipe racks for supporting above grade
firewater piping. These rack
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Hinson, Ryan
Sent: Tuesday, November 06, 2012 7:07 PM
To: sprinklerforum@firesprinkler.org
Subject: Pipe support spacing requirements for structural supports
I've got a couple projects which have pipe racks for supporting above grade
Sent: Thursday, November 08, 2012 9:48 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe support spacing requirements for structural supports
I agree that you would have to follow NFPA 13/15 hanger requirements for
spacing of pipe stands you are building to support pipe around like a pump
: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Thursday, November 08, 2012 9:31 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe support spacing requirements for structural supports
If the spacing of pipe
I've got a couple projects which have pipe racks for supporting above grade
firewater piping. These rack supports are spaced at 20' or more on center.
From the NFPA 13 Handbook at the beginning of Chapter 9, pipestands are to have
the same safety factors as hangers. NFPA 15 is suggested for