Re: Mixed rack storage

2018-11-29 Thread cw bamford
* November-29-18 10:48 AM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* RE: Mixed rack storage > > > > I agree with this, except it calls for one level of in-racks. > > > > John Irwin > > Quick Response Fire Protection > > > > *From:* Sprink

RE: Mixed rack storage

2018-11-29 Thread MFP Design, LLC
ss of low price is forgotten.” From: Sprinklerforum On Behalf Of John Irwin Sent: Thursday, November 29, 2018 10:15 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Mixed rack storage The bulk of the storage area is ceramic or porcelain tile, in wrapped boxes, on wood slat

RE: Mixed rack storage

2018-11-29 Thread John Irwin
Keeping Sent: Thursday, November 29, 2018 12:11 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Mixed rack storage Whoa there! The Chapter 13 only covers plastic to storage to 5 ft in dedicated storage facilities or Miscellaneous Storage of Plastics to 12 ft. My understanding is that

RE: Mixed rack storage

2018-11-29 Thread Larry Keeping
you need to go to Chapter 17. Best regards, Larry Keeping From: Sprinklerforum On Behalf Of John Irwin Sent: November-29-18 10:48 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Mixed rack storage I agree with this, except it calls for one level of in-racks. John Irwin Quick

RE: Mixed rack storage

2018-11-29 Thread John Irwin
I agree with this, except it calls for one level of in-racks. John Irwin Quick Response Fire Protection From: Sprinklerforum On Behalf Of cw bamford Sent: Thursday, November 29, 2018 10:36 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Mixed rack storage Calc seperate areas

Re: Mixed rack storage

2018-11-29 Thread cw bamford
Calc seperate areas. group A plastics on racks UNDER 12’ using 2013 edition of NFPA 2013 Table 13.2.1 Exposed -- Unexpanded -- Rack >10' to 12' OH2 Please check my work. onto Ceramic Floor Tiles It's not just the commodity, It's how they are stored and moved on the racks ? in cardboard ? with

Re: Mixed rack storage

2018-11-28 Thread Sean & Christine Conlin
Not allowed.  If you can’t adhere to the lower hazard pallet limitations then you must design for the most severe hazard present.   FM did testing on mixed commodities and they determined that the mix behaved like the higher hazard commodity.  Regards,Sean Conlin On Wednesday, November 28, 2018,

RE: Mixed rack storage

2018-11-28 Thread John Irwin
I think I follow. And that makes sense. John Irwin Quick Response Fire Protection From: Sprinklerforum On Behalf Of Mark Sornsin [FAR] Sent: Wednesday, November 28, 2018 3:22 PM To: 'sprinklerforum@lists.firesprinkler.org' Subject: RE: Mixed rack storage John, I assume the ceram