> *Subject:* Re: NFPA 13 RESIDENTIAL Exterior Corridor
>
>
>
> Thanks guys... regarding 11.2.3.4.2. I always thought that was only good
> for a single row meaning all the sprinklers were directly on the line. In
> this case the sid
Pipe arrangement is not mentioned in 11.2.23.4.2.
I single line of sprinklers.
Tim
From: Sprinklerforum On Behalf
Of Fire Design
Sent: Friday, July 13, 2018 2:07 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA 13 RESIDENTIAL Exterior Corridor
Thanks guys... regarding
Thanks guys... regarding 11.2.3.4.2. I always thought that was only good
for a single row meaning all the sprinklers were directly on the line. In
this case the sidewalls are fed from armovers coming from a looped main.
Would this still apply?
On Fri, Jul 13, 2018 at 10:28 AM, wrote:
>
Anthony,
Look at 11.2.3.4.2.
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638 TEL: (802) 434-2968
Reliable: F3Res44 Dry good to 175
On Fri, Jul 13, 2018 at 10:21 AM, Fire Design <
fireprotectiondesi...@gmail.com> wrote:
> Hi Guys,
>
> I'm working on an apartment complex that is being designed per NFPA 13
> standards (2016). All the rooms open from an exterior covered corridor that
> is 6