exterior cooler/freezer

2015-03-09 Thread Todd - Work
I am working on a project where they are installing 2 exterior coolers/freezers. The coolers abut the building and there is a doorway cut in the wall to access them. The engineer says they do not need to be sprinklers because they are outside and not part of the building. My claim is that they

RE: exterior cooler/freezer

2015-03-09 Thread Richard Carr
-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work Sent: Monday, March 09, 2015 10:48 AM To: sprinklerforum@lists.firesprinkler.org Subject: exterior cooler/freezer I am working on a project where they are installing 2 exterior coolers/freezers. The coolers abut the building and there is

RE: exterior cooler/freezer

2015-03-09 Thread Steve Sorrell
Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work Sent: Monday, March 09, 2015 10:48 AM To: sprinklerforum@lists.firesprinkler.org Subject: exterior cooler/freezer I am working on a project where they are installing 2 exterior coolers/freezers. The coolers abut the bui

Re: exterior cooler/freezer

2015-03-09 Thread Greg McGahan
ncefire.com > Licensed in NC, SC, VA, TN, GA, AL > > "Performance on Every Level." > > -Original Message- > From: Sprinklerforum [mailto: > sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work > Sent: Monday, March 09, 2015 10:48 AM &g

RE: exterior cooler/freezer

2015-03-09 Thread Craig.Prahl
] On Behalf Of Greg McGahan Sent: Monday, March 09, 2015 11:02 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: exterior cooler/freezer It is attached - per IBC definition therefore sprinkler are required...that is my understanding and what has been enforced locally for years. Greg

RE: exterior cooler/freezer

2015-03-09 Thread Matthew J Willis
...@lists.firesprinkler.org] On Behalf Of Cahill, Christopher Sent: Monday, March 09, 2015 9:17 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: exterior cooler/freezer Hold on a second, there could be a fire wall between the two creating separate buildings, lol. Chris Cahill, PE* Associate Fire

RE: exterior cooler/freezer

2015-03-09 Thread Cahill, Christopher
nkler.org] On Behalf Of Greg McGahan Sent: Monday, March 09, 2015 11:02 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: exterior cooler/freezer It is attached - per IBC definition therefore sprinkler are required...that is my understanding and what has been enforced locally for years.

RE: exterior cooler/freezer

2015-03-09 Thread Craig.Prahl
nklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matthew J Willis Sent: Monday, March 09, 2015 11:18 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: exterior cooler/freezer In that case, see 8.2.5 of NFPA #13 R/ Matt Matthew J. Willis Project Manager

RE: exterior cooler/freezer

2015-03-09 Thread Craig.Prahl
Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, Christopher Sent: Monday, March 09, 2015 11:17 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: exterior cooler/freezer Hold on a second, there could be a fire wall between the

RE: exterior cooler/freezer

2015-03-09 Thread Matthew J Willis
-Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, Christopher Sent: Monday, March 09, 2015 9:25 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: exterior cooler/freezer True, but that's about separate risers/system

RE: exterior cooler/freezer

2015-03-09 Thread Cahill, Christopher
of 100 Best Companies to Work For -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matthew J Willis Sent: Monday, March 09, 2015 10:18 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: exterior cooler/freezer In that c

RE: exterior cooler/freezer

2015-03-09 Thread Cahill, Christopher
um [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matthew J Willis Sent: Monday, March 09, 2015 10:27 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: exterior cooler/freezer Exactly. I think this goes back to... Room or Building? Either way if not separated by fire r

Re: exterior cooler/freezer

2015-03-09 Thread Roland Huggins
8.1.1 talks about sprinklers throughout and A.8.1.1 states including walk-in coolers, freezers etc. I’d say it is a no brainer with interior access from the primary building but even two structures that are together are considered one building (easy to follow if one says fire area) less there i

RE: exterior cooler/freezer

2015-03-09 Thread Jeremy Frazier
-boun...@lists.firesprinkler.org] On Behalf Of Cahill, Christopher Sent: Monday, March 09, 2015 11:17 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: exterior cooler/freezer Hold on a second, there could be a fire wall between the two creating separate buildings, lol. Chris Cahil

Re: exterior cooler/freezer

2015-03-09 Thread Forest Wilson
..@aol.com -Original Message- From: Cahill, Christopher To: sprinklerforum Sent: Mon, Mar 9, 2015 11:25 am Subject: RE: exterior cooler/freezer True, but that's about separate risers/systems not whether the building gets sprinklered. If there is a fire wall the 'engineer' is rig

Re: exterior cooler/freezer

2015-03-09 Thread Norman Arendt
Reviewer and Investigator President Infragard Madison Alliance - Original Message - From: "Forest Wilson" To: sprinklerforum@lists.firesprinkler.org Sent: Monday, March 9, 2015 1:35:52 PM Subject: Re: exterior cooler/freezer If the Project Engineer says they aren't ne

Re: exterior cooler/freezer

2015-03-09 Thread Charles Thurston
gt; craig.pr...@ch2m.com > Sent: Monday, March 09, 2015 10:07 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: RE: exterior cooler/freezer > I concur with if there's a door from the freezer into the building then > sprinkler. > It's no different than if the

RE: exterior cooler/freezer

2015-03-09 Thread Bill Brooks
forum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Charles Thurston Sent: Monday, March 09, 2015 5:50 PM To: Cahill, Christopher; sprinklerforum@lists.firesprinkler.org Subject: Re: exterior cooler/freezer Hello Christopher, That is what the AHJs around here look at it as. They say the closed c

Re: exterior cooler/freezer

2015-03-09 Thread John Drucker
l Brooks -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Charles Thurston Sent: Monday, March 09, 2015 5:50 PM To: Cahill, Christopher; sprinklerforum@lists.firesprinkler.org Subject: Re: exterior cooler/freezer Hello Christopher

Re: exterior cooler/freezer

2015-03-10 Thread John Drucker
urston Sent: Monday, March 09, 2015 5:50 PM To: Cahill, Christopher; sprinklerforum@lists.firesprinkler.org Subject: Re: exterior cooler/freezer Hello Christopher, That is what the AHJs around here look at it as. They say the closed cooler door is like a fire door and no sprinkler needed. They

Re: exterior cooler/freezer

2015-03-10 Thread Todd - Work
ure which one is being referenced here. > > Bill Brooks > > -Original Message- > From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] > On Behalf Of Charles Thurston > Sent: Monday, March 09, 2015 5:50 PM > To: Cahill, Christopher; sprinkle

RE: exterior cooler/freezer

2015-03-10 Thread John Drucker
nklerforum@lists.firesprinkler.org Subject: Re: exterior cooler/freezer I went to the jobsite yesterday to get the full scoop. This is a restaurant in a strip mall. In back, there will be two boxes approximately 9 x 16 x 8(h). One will be liquor storage, which needs to have an inside access. Th

Re: exterior cooler/freezer

2015-03-10 Thread Cahill, Christopher
not sure which one is being referenced here. > > Bill Brooks > > -Original Message- > From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] > On Behalf Of Charles Thurston > Sent: Monday, March 09, 2015 5:50 PM > To: Cahill, Christopher; sprinklerforum@

RE: exterior cooler/freezer

2015-03-10 Thread Matthew J Willis
5.348.0108 -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, Christopher Sent: Tuesday, March 10, 2015 6:07 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: exterior cooler/freezer Its called a backdraft. Look it up or

Re: exterior cooler/freezer

2015-03-10 Thread Greg McGahan
nkler.org] On Behalf Of Cahill, > Christopher > Sent: Tuesday, March 10, 2015 6:07 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: Re: exterior cooler/freezer > > Its called a backdraft. Look it up or watch the movie. Yes it can burn. > Also be careful with statistics

Re: exterior cooler/freezer

2015-03-10 Thread Todd - Work
No offense taken from anyone. I was merely looking for any specific fire history to use as a talking point. I find that is an effective method when trying to convince owners to do something. Sent from my iPad > On Mar 10, 2015, at 8:21 AM, Greg McGahan wrote: > > NFPA #13 is not based on IF

Re: exterior cooler/freezer

2015-03-10 Thread rongreenman .
If it were just on the inside of the wall and rotated 180 degrees would you sprinklers it? Could you could argue it wasn't a part of the building because the door into it led directly outside? On Tue, Mar 10, 2015 at 6:45 AM, Todd - Work wrote: > No offense taken from anyone. I was merely lookin

Re: exterior cooler/freezer

2015-03-10 Thread Todd - Work
No, because if it is inside the building, it is part of the building. If the doorway from the building to the outside cooler remains, then it is another room and has to be sprinklered. No question. However, if the direct doorway is removed and the only access is from outside, then it becomes an

RE: exterior cooler/freezer

2015-03-10 Thread Brad Casterline
t: Re: exterior cooler/freezer If it were just on the inside of the wall and rotated 180 degrees would you sprinklers it? Could you could argue it wasn't a part of the building because the door into it led directly outside? On Tue, Mar 10, 2015 at 6:45 AM, Todd - Work wrote: > No offense take

Re: exterior cooler/freezer

2015-03-10 Thread Tom Wellen
Interesting argument that when an attached cooler or freezer with no direct access to the interior, the AHJs say no sprinklers. Try that theory with an attached noncombustible canopy with storage with no door access direct to the interior nearby - I bet the AHJ says sprinklers are required. To

Re: exterior cooler/freezer

2015-03-10 Thread Todd Williams
Message- > From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] > On Behalf Of rongreenman . > Sent: Tuesday, March 10, 2015 9:28 AM > To: sprinklerforum@lists.firesprinkler.org > Subject: Re: exterior cooler/freezer > > If it were just on the i

Re: exterior cooler/freezer

2015-03-10 Thread Tony Silva
esday, March 10, 2015 5:28:13 AM Subject: Re: exterior cooler/freezer I went to the jobsite yesterday to get the full scoop. This is a restaurant in a strip mall. In back, there will be two boxes approximately 9 x 16 x 8(h). One will be liquor storage, which needs to have an inside acces

RE: exterior cooler/freezer

2015-03-12 Thread David Blackwell
ject: Re: exterior cooler/freezer Interesting argument that when an attached cooler or freezer with no direct access to the interior, the AHJs say no sprinklers. Try that theory with an attached noncombustible canopy with storage with no door access direct to the interior nearby - I bet the AHJ