Joe,

That's why I pointed out that there are two issues, obstructions and air
velocity. The first issue, obstructions, any sprinkler person dealing
with ESFR sprinklers should be fully aware of, hence not much
explanation. The second issue, air velocity, is no more important than
the obstruction but still important. Your statement "A bigass fan is
simply a moving obstruction", is exactly why the air velocity concern
warranted a little more explanation. A bigass fan is not simply a moving
obstruction. It also moves air, the last time I looked at an sprinkler
it needed hot air to set it off. FM has specified a certain air velocity
that in their opinion does not interfere with the sprinkler activation.
Anything out of the ordinary should always be presented to the local
AHJ, authority having jurisdiction, for their approval. Not sure what
the kittens are all about?

Jason

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Hankins
Sent: Monday, November 27, 2006 3:21 PM
To: [email protected]
Subject: Re: Big Ass Fans

Jason,

The air velocity issue is no more important than the obstruction issue. 
The fact that some have succeeded in convincing the fire department to
accept these fans doesn't mean they aren't a problem with ESFRs. An
obstruction doesn't stop being an obstruction just because you call it a
fan, any more than a kitten born in an oven. is a biscuit. A bigass fan
is simply a moving obstruction.

Joe

Jason Norton wrote:

>I have seen them installed with ESFR systems and after some convincing
approved by the fire department. The two issues where with the
obstructions and impact on response time due to increased air velocity.
FM has guidelines on maximum air velocity with ESFR sprinklers in their
data sheets. Big Ass Fans has/can provide air velocity testing to verify
the maximum air velocities. From my experience the fans can easily
provide more air velocity than FM allows and generally needs to have the
speed limited in some fashion that is acceptable to the AHJ. The fans
are at this web site is "bigassfans.com"  The name certainly fits, those
are some really, really big fans.
>
>Jason
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of hughes
rewis
>Sent: Monday, November 27, 2006 12:15 PM
>To: [email protected]
>Subject: Big Ass Fans
>
>Thanks all for your input on the ESFR issue. Seeing as how you were so
helpful with that, maybe you can offer some advise as to the effect a
"Big Ass Fan" has on the ESFR. Not being profane, that's the name of
these fans.
>
>Hughes
>
>_________________________________________________________________
>All-in-one security and maintenance for your PC.  Get a free 90-day
trial! 
>http://clk.atdmt.com/MSN/go/msnnkwlo0050000002msn/direct/01/?href=http:
//clk.atdmt.com/MSN/go/msnnkwlo0050000001msn/direct/01/?href=http://www.
windowsonecare.com/?sc_cid=msn_hotmail
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>  
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to