the inclusion (or rather exclusion) of a mezzanine from a calculation
of the ceiling is not my question. IF including the additional 540
sf below the mezzanine is causing a problem, it sounds like you are
calc'ing just the 15X51. What happened to the 3000 sf remote
area or does this new room qualify for the room design?
Roland
On Nov 30, 2006, at 6:36 AM, Greg McGahan wrote:
Normally we error on the side of caution but we have a situation
with calcs
that are not working with more than a 2.4% cushion so I have to ask.
Existing building with existing 3" water supply with new room and new
mezzanine. The new room is 51' by 15' with a lower mezzanine that
is 36' x
15'. The remote area is specified at 3,000 sqft so there is no
reductions
etc.
Question: Do I need to calculate the entire area with the mezz.? I
need
something concrete to submit if I do not have to include them.
Thanks,
Greg McGahan