FM gives a design for installing control mode fire sprinkler under open
grate catwalks in buildings protected by an ESFR system.  However I can no
find anything in NFPA, NFPA 13 2007 8.12.5.3.3 (Section 8.12 addresses ESFR
sprinklers) states "That sprinklers installed under open gratings shall be
of the intermediate level/rack storage type or otherwise shielded from the
discharge of the overhead sprinklers."  It does not give you a design for
the sprinklers under the catwalks.  NFPA 13 2007 16.2.3.5 states "Where ESFR
sprinklers are installed above and below obstructions, the discharge for up
to two sprinklers for one of the levels shall be included with those of the
other level in the hydraulic calculations."  That is if ESFR sprinklers are
installed.  If control mode sprinklers are installed per 8.12.5.3.3., what
is the design requirements?  None are stated.  Do sprinklers have to be
added in or due to being control mode, none are require to be added to
calcs?  Or am I just missing the info in the book?

Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119