Karen:

There is a lot of information needed in order to help you, but I can't
think of any 1'-9" deep floor joist construction what wouldn't require
sprinklers with the following exceptions:

1. qualifies for a NFPA 13R design
2. space is filled entirely with noncombustible insulation.

8.14.1.2.1 relates to noncombustible or limited combustible
construction, which typically does not include wood floor joists.

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 