Karen: There is a lot of information needed in order to help you, but I can't think of any 1'-9" deep floor joist construction what wouldn't require sprinklers with the following exceptions:
1. qualifies for a NFPA 13R design 2. space is filled entirely with noncombustible insulation. 8.14.1.2.1 relates to noncombustible or limited combustible construction, which typically does not include wood floor joists. Mark A. Sornsin, PE Fire Protection Engineer Ulteig Engineers, Inc. Fargo, ND 701.280.8591 [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Karen Purvis Sent: Friday, December 22, 2006 9:56 AM To: [email protected] Subject: Floor Joist question I have a situation where the building has a 1'9" wood floor joist construction and I am being asked if it needs to be sprinkled. If so what type and how many heads. I say that by 8.14.1.2.1 that it does not or may not need to be sprinkled but I just don't know. Any help would be great. Karen Purvis Facility System Consultants _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum