Ken,

If all the sprinklers in the units are within close proximity to a heat source that would normally require the higher temperature, then that would be appropriate. If not, then you should use the temperature ratings as described in NFPA 13. What advantage would there be to using 175 degree sprinklers only? There shouldn't be any problem mixing temperature ratings as long as they are detailed on the drawing as to what to use where.



Todd G. Williams, PE
Fire Protection Design/Consulting