Gengtlemen: There is no restriction in NFPA 13 on using 175 degree sprinklers. In some cases it is better to use 175 degree sprinklers i.e. A residence that might not be air condition in the hot summer months. Or if the engineer, owner or developer just wanted to use 175 degree sprinklers. Note: Some sprinklers are not available in higher temperatures. Michael L. Brown
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - work Sent: Sunday, January 07, 2007 12:44 PM To: [email protected] Subject: Re: 155 degree -vs- 175 degree Ken, If all the sprinklers in the units are within close proximity to a heat source that would normally require the higher temperature, then that would be appropriate. If not, then you should use the temperature ratings as described in NFPA 13. What advantage would there be to using 175 degree sprinklers only? There shouldn't be any problem mixing temperature ratings as long as they are detailed on the drawing as to what to use where. Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut 860-535-2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum