Gengtlemen:

There is no restriction in NFPA 13 on using 175 degree sprinklers.  In
some cases it is better to use 175 degree sprinklers i.e.  A residence
that might not be air condition in the hot summer months.   Or if the
engineer, owner or developer just wanted to use 175 degree sprinklers.
Note:  Some sprinklers are not available in higher temperatures.
Michael L. Brown

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Sunday, January 07, 2007 12:44 PM
To: [email protected]
Subject: Re: 155 degree -vs- 175 degree

Ken,

If all the sprinklers in the units are within close proximity to a 
heat source that would normally require the higher temperature, then 
that would be appropriate. If not, then you should use the 
temperature ratings as described in NFPA 13. What advantage would 
there be to using 175 degree sprinklers only? There shouldn't be any 
problem mixing temperature ratings as long as they are detailed on 
the drawing as to what to use where.



Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 