Because we use Hazen Williams for fire sprinkler design, this formula already creates a pressure penalty for excessive velocity, therefore no limit is put on fire sprinkler system velocities.

Just as a side note Backflow preventors are tested and usually listed at 10 Fps, if your exceeding the flow limits of the backflow preventor you can damage it in full forward flow testing.