Thanks Ray,
I was going along the same lines but had a conflict with sales. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ray Vance
Sent: Wednesday, January 10, 2007 3:55 PM
To: [email protected]
Subject: RE: water supply duration

Sorry Dewayne!

The NFPA-2002 references are:

11.2.3.2.1.1 and A.11.2.3.2.1.1 

Thanks,

Ray Vance
Chief Engineering Tech.
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ray Vance
Sent: Wednesday, January 10, 2007 4:46 PM
To: [email protected]
Subject: RE: water supply duration

Keep in mind that when you have a greater hazard in an otherwise lesser
hazard area, you still need to condier the water supply requirements for
the greater area.

Your design area should include the 800 sq.ft. of storage area (with the
sprinklers discharging at their appropriate density) and then add
sprinklers in the light hazard area (with the sprinklers discharging at
their appropriate density) until you reach your required design area of
discharge.

This will then dictate your required system demand AND your hose demand
as well.

Your hose demand should be appropriate for your larger hazard (ie-250
gpm for ordinary hazard) AND your duration should be that which also
corresonds to your greater hazard.

I know there are times when the "larger hazard" is small, such as ONE or
TWO sprinklers in a SMALLER storage room, and at that time sound
engineering judgements need to be made regarding the statements above,
but the direction from the NFPA standards is pretty clear in this area
when you have different hazards within the same area or areas.

Thanks,

Ray Vance
Chief Engineering Tech.
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Wednesday, January 10, 2007 4:30 PM
To: SprinklerFORUM
Subject: water supply duration

What would the appropriate water supply duration be for a building
overall light hazard occupancy but with a storage room of approximately
800 sq ft in it.  I need to size a water storage tank and 30 vs.. 60 min
makes a difference.  I saw the hose demand exception in NFPA for rooms
less than 400 sq ft. but this did not address the duration.  I tried to
access the archives but they seem to be down.  Any help and possibly a
NFPA reference # would be appreciated.
Thanks
Dewayne
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


Wayne Automatic Fire Sprinklers, Inc.
2006 Inductee into "The Players Hall of Fame"
at The Great Games of Business
Wayne Automatic Fire Sprinklers, Inc. "Best Places to Work"
Rated #1 in 2006
Large Business Category
by Orlando Business Journal
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


Wayne Automatic Fire Sprinklers, Inc.
2006 Inductee into "The Players Hall of Fame"
at The Great Games of Business
Wayne Automatic Fire Sprinklers, Inc. "Best Places to Work"
Rated #1 in 2006
Large Business Category
by Orlando Business Journal
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to