When a sprinkler contractor gets an inspection contract it is after a
system has been installed under NFPA-13 and the local AHJ has accepted
the building and a Certificate of Occupancy has been given.  Are you
asking the NFPA-25 inspection contractor to second guess your acceptance
process, evaluate the system design, water supply etc.  There has to be
separation between responsibilities of the various parties.  Very often
inspectors for sprinkler contractors have been trained to perform the
specific inspection testing and maintenance requirements of the
standard.  Remember the standard is not named Inspection Testing
Maintenance and Design for a reason.

Top Myers
Myers Risk Services
961 Pottstown Pike
Chester Springs, PA 19425
[EMAIL PROTECTED] Web http://www.myersrisk.com
P- 610-321-2415 X219  C- 610-952-0965
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Thursday, January 11, 2007 12:01 PM
To: [email protected]
Subject: RE: Testing

Rod,


With all due respect, Section 1.1 (Scope) of NFPA-25 reads "This
standard applies to fire protection systems that have been properly
installed in accordance with generally accepted practices".  That's
rather ambiguous but lets just assume that NFPA-25 is speaking of
standards such as NFPA 13 & 13R.  (PS lets hope so because FM Globals
requirements could also be interpreted as "generally accepted
practices")

With that said is it not true that a determination by the maintenance
contractor is needed to assure that the system(s) being maintained "have
been properly installed" in order for NFPA-25 to apply ?.  

The scoping statement is very clear, systems that have not been properly
installed are outside the scope of NFPA-25 so in effect an NFPA-25
inspection of an improperly installed system is null and void. 

My point in this discussion is that the ultimate fire protection goal is
to assure the health, welfare and safety of building occupants and
property protection where applicable.  When a building owner or an AHJ
receives a certificate of inspection from a contractor they assume the
system will control a fire as designed by the applicable standard not
that an unprotected area or deficiency was ignored simply because of the
fine print of the maintenance standard.  If that's the case an annual
inspection by a qualified fire protection engineer is in order.

Sincerely in the interest of Fire Safety,

John Drucker
Fire Protection Subcode Official (AHJ)
Borough of Red Bank, NJ


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of rod
Sent: Thursday, January 11, 2007 11:00 AM
To: [email protected]
Subject: RE: Testing

John,

I agree with you that there are some real problems with the inspections,
inspectors and enforcers. I do not believe however that we can get into
a
situation where even NICET trained certified inspectors are getting into
"protection deficiencies". This is a slippery slope and creates a
liability
for the contractor that NFPA 25 quite frankly puts on the owner. To
transfer
that liability to the contractor for $200 is not equitable. The only
people
with a "false" sense of security are those that do not read the NFPA 25.

Rod DiBona
Rapid Fire 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Wednesday, January 10, 2007 4:34 PM
To: [email protected]
Subject: RE: Testing

New Jersey has extensive certification & licensing regulations for fire
protection contractors. However coordination rarely occurs and flow and
tamper switches are still be "tested" by alarm technicians moving
actuator
arms. I recently attained a flow switch improperly installed in a copper
tee
to the extend the vane wasn't even in the water stream yet the "fire
alarm
inspection report" noted this device as functional even so far as
listing
the time delay.  

Whats need in this situation is a requirement where only alarm companies
and
or sprinkler companies be permitted to perform inspection in testing in
suppressed/alarmed buildings that posess certification in BOTH
disciplines.

The reality is that even with NFPA-13, 72 and 25 gross errors and
omissions
are occuring during periodic inspections and tests.  Inspectors should
know
how to identify protection deficiencies not just installation and
maintenance deficiencies. NFPA-25 certifications give a false sense of
security.

John Drucker
Fire Protection Subcode Official
New Jersey 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Wednesday, January 10, 2007 4:20 PM
To: [email protected]
Subject: RE: Testing

Tennessee where I work requires licensing. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Brown
Sent: Wednesday, January 10, 2007 3:52 PM
To: [email protected]
Subject: RE: Testing

But when you look at the number of states that have a license
requirement
they are few. There are many of the larger cities have requirements but
not
as a state. Look at Oklahoma, They have one of the best licensing
requirements I am aware of and they enforce it well for both the fire
alarm
and fire sprinkler industries. I think every state should be looking at
what
the State of Oklahoma is requiring. Look at the web site for Oklahoma
Department of Health of the requirements if interested. They are doing
the
right thing! Every one associated with fire protection has to be
licensed.


Thank you,

Chris Brown
Fire Protection Designer, Poole Fire Protection
Office: 913.829.8650   Direct: 913.747.2056   Cell: 913.208.3600   Fax:
913.829.8690


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, January 10, 2007 2:37 PM
To: [email protected]
Subject: Re: Testing

there is a fine point you are missing.  The OWNER of a PRIVATE facility
is
typically allowed to do as much of their own work  as they want to.
It's when you hire out to do work for someone else that licensing enters
the
equation.

Roland

On Jan 10, 2007, at 12:29 PM, <[EMAIL PROTECTED]> wrote:

> Chris, Kansas isn't alone on that.  I have a project in a nearby 
> state.
> The owner wanted to do the installation himself.  He has mechanics 
> that know how to use a pipe wrench.  (this guy wanted a detail on his 
> drawings of how to install an upright head, yes we are in
> trouble.......)
>
> Anyway, when I called the state board of licensure and asked the lady 
> if you had to be specifically licensed to install sprinkler systems 
> her words were, "that's a good question, I don't know",  so she passed

> me off to her department manager, who obviously read from the same 
> script
> because he said the same thing.   Seems in their state and local
> municipality don't require permits or system inspections and so anyone

> can install it.
>
> There is no consistency in the laws concerning licensing.
>
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
> 864.599.8439 [EMAIL PROTECTED] http://www.lg.com
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Chris 
> Brown
> Sent: Wednesday, January 10, 2007 3:17 PM
> To: [email protected]
> Subject: RE: Testing
>
> In the state of Kansas all you need is transportation to the site it 
> even could be by mass transit and you can work on any type of fire 
> protection system. Wichita has some requirements and Kansas City 
> Missouri has a sprinkler contractors license requirement but other 
> than that any one can work on any fire protection system. We have 
> plumbers installing sprinkler systems and electricians installing fire

> alarm system. They don't even know what NFPA is.
>
>
> Thank you,
>
> Chris Brown
> Fire Protection Designer, Poole Fire Protection
> Office: 913.829.8650   Direct: 913.747.2056   Cell: 913.208.3600    
> Fax:
> 913.829.8690
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Gregg 
> Fontes
> Sent: Wednesday, January 10, 2007 1:56 PM
> To: [email protected]
> Subject: Testing
>
> Does a C-10 and/or electrical/alarm contractors license allow them to 
> contract the testing of water base fire protection systems?  (I.E.
> opening inspectors test valves, operating control valves, testing of 
> Pre-action/Deluge/Dry systems, generally can they operate any 
> component of a fire sprinkler system that has an alarm affiliated with

> it?)
>
> Gregg Fontes
> Cen-Cal Fire Systems, Inc.
> 209-334-9119
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to