You are crossing the wires on flame spread and limited combustible. IT is amusing that NFPA 13 has an interesting and illogical application of the terms in the 02 edition. For a concealed COMBUSTIBLE space, rigid material with a Class A flames spread OR lumber that has been treated with a fire retardant (which typically creates a Class A flame spread does it not?) allows omission of sprinklers. Limited combustible enters the discussion when we start talking about exterior roofs and canopies. Keep in mind that exterior canopies is just addressing protection BENEATH them. This is where you encounter the requirement for limited combustible construction in order to omit protection from BENEATH the canopy.

The 07 edition has finally acknowledges separation and protection of the concealed spaces makes a difference. It also as incorporated the allowance for fire retardant treated lumber to omit protection so the oddity in how the two characteristics are treated in prior editions has been addressed.

Roland



On Jan 12, 2007, at 7:47 AM, David de Vries/Firetech wrote:

Todd:

That appears to be UL, not ULC.

Whether this product, or any other product listed in that category would turn a ceiling or concealed space that is otherwise combustible into a non-combustible or limited combustible ceiling or space is problematic. The test applied by UL is the one for Surface Burning Characteristics, UL 723. It does not necessarily correlate to the flammability of the material. For example, gypsum board with typical paper face might have a flame spread index of 10 or 15, just like a wood product treated with one of these fire retardants. The difference is that the core material of the gyp board is non-combustible, whereas the wood product is combustible. Once the surface protection is gone, you're back to a combustible concealed space, or combustible ceiling.

--
David de Vries, P.E., CSP
Firetech Engineering Incorporated
[EMAIL PROTECTED]

-------------- Original message --------------
From: Todd Williams - work <[EMAIL PROTECTED]>

Bill,

Is this UL or UL Canada listed?

At 09:23 AM 1/12/2007, you wrote:
This product has a UL listing. I'm not endorsing one way or the other but I think the intent of NFPA 13 would be to accept products like this when
applied properly as Roland indicates.

http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/ showpage.html?name =BMQX.R19565&ccnshorttitle=Coatings,+Fire +Retardant&objid=1078153113&cfgid=1
073741824&version=versionless&parent_id=1073984654&sequence=1

Bill Brooks
Pittsburgh, PA

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Roland
Huggins
Sent: Thursday, January 11, 2007 1:13 PM
To: [email protected]
Subject: Re: Wood Coating


AS we all know, 13 allows fire retardant wood to be used as defined
by NFPA 703. The last time I looked (was nit recently but a year or
3), NFPA 703 addresses both pressure treated wood (as required by the
building code to qualify as treated) AND surface applied (ie field
painted).

IMHO, bad approach.

Roland

On Jan 10, 2007, at 2:09 PM, Todd Williams - work wrote:

I had a architect ask me about using this in a combustible church
attic. I was skeptical and did a little investigating. The tests
that produced the results had a minimum film thickness in order to
work properly. How do you verify the minimum thickness in a field
application? My guess is that the tests shown (by UL Canada only)
were not done on assembled structures, but on individual pieces of
material that were coated under near ideal conditions. What would
happen in a structure coated after assembly? Why is there no UL -
United States or FM tests? Too many questions for me; I'd walk
away. (So did the architect referenced above)

Todd

At 04:15 PM 1/10/2007, you wrote:
Has anyone seen this product?
It touts that it replaces sprinklers in combustible concealed spaces,
under NFPA-13.
If you have seen it, pros and cons?

http://www.eaglecoatings.net/content/safecoatlatex.htm


Wayne Automatic Fire Sprinklers, Inc.
2006 Inductee into "The Players Hall of Fame"
at The Great Games of Business
Wayne Automatic Fire Sprinklers, Inc. "Best Places to Work"
Rated #1 in 2006
Large Business Category
by Orlando Business Journal
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to