Folks,
Here is some more food for thought.  I provide the sprinkler specification
for all of my federal projects.  I use 20 fps velocity as a limit and a
maximum C of 100 to insure that I have a system that has a chance to last
for the life of the building (approximately 50+ years).  Our buildings are
always being changed with the sprinkler system being drained and modified
many many times by all sorts of contractors, from the best to the worst.
Once the building is constructed and occupied, the local GSA service center
does all of the work in the building, usually with the lowest bidder.

Therefore, we need some sort of hedge against all of this.  Once the
building is built, it is out of my control.  I see no problem specifying
these limits as long as everyone is bidding the same job.

Any suggestions?