We just ripped out a late 60's installtion that had been wet, then
preaction, then wet, and maybe it was something else for awhile. Anyway,
there was sludge that filled the pipes. Office occupancy, single occupant
(major health insurance provider). So larger piping would have helped if
there was a fire, with the mains hopefully less clogged than the 1" arnover
I saw that was almost solid muck. Not solid and brittle, but you'd have to
use Darcy to calc it.

I'd assume that the projects Rahe gets involved in are generally major jobs,
you probably have to screw with showing metric when submitting, etc. anyway,
so changing the C factor- while I'm not a fan of this- is one way to
accomplish building in a cushion, and some "fat" for when Joe Carpetbagger
ties in and runs 6 heads off 1" from it a couple decades from now.

I far prefer to use accepted C factors  so we can discuss the job with
insurance and local AHJs and we all know what we're talking about- instead
of talking to the A/E in his language of 15 PSI cushion using 20% degraded
water supply and with C=70, while the rest of us see a 40 PSI cushion based
on our industry's reality.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Monday, January 15, 2007 2:21 PM
To: [email protected]
Subject: RE: max velocity

Help me out here, while limiting those two items may seem well and good,
I fail to see how limiting the pipe velocity to 20fps will extend the
life of a sprinkler system.  This is not like a plumbing system where
water it flowing constantly.  In the typical 50 year lifespan of the
buildings you know of, how many times has the sprinkler system
discharged?  How long has it been left in a flowing condition?  I dare
say that in most cases you've probably had few discharges and even if
the system is allowed to flow for a couple of hours, in that length of
time and use, the deterioration on the piping couldn't even be measured.


I assume you're specifying that the designer use a C-factor of 100 in
his calcs.  Again, how will that increase the life of the system?  All
that's doing is changing pipe sizes being used because they have to
overcome a fictional friction loss that isn't really there until 50
years from now. If you had that much accumulation it would have to be
based on a system that never saw any maintenance or flushing for 50
years?  

If the systems are modified as often as you say, then it seems like
piping is being changed on a regular basis and the longevity issue is a
moot point.

Might want to reconsider the practicality of requiring the installation
of piping in systems that's larger than necessary.  



Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Monday, January 15, 2007 1:55 PM
To: [email protected]
Subject: RE: max velocity


Folks,
Here is some more food for thought.  I provide the sprinkler
specification for all of my federal projects.  I use 20 fps velocity as
a limit and a maximum C of 100 to insure that I have a system that has a
chance to last for the life of the building (approximately 50+ years).
Our buildings are always being changed with the sprinkler system being
drained and modified many many times by all sorts of contractors, from
the best to the worst.
Once the building is constructed and occupied, the local GSA service
center does all of the work in the building, usually with the lowest
bidder.

Therefore, we need some sort of hedge against all of this.  Once the
building is built, it is out of my control.  I see no problem specifying
these limits as long as everyone is bidding the same job.

Any suggestions?

Thank You

Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to