I understand why Tom does that and suggests it.  However, it does not
allow the owner (they are supposed to be checking and draining these) to
know that they have a problem, IMHO, and that problem can, in rare, but
they do occur, result in a claim against the sprinkler contractor that
has the last IT&M tag hanging on the riser.

Scott 

(763) 425-1001 Office 
(612) 759-5556 Cell 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Monday, January 29, 2007 9:36 AM
To: [email protected]
Subject: Re: Drum drip (condensate trap) maintenance in dry system

Tom D. has a good idea for all drum drips. Here in Colorado it is very 
important to know if your air compressor draws air from the garage space
or 
the Mechanical room, or some other conditioned space. Much like
freezers, 
parking garages see below zero temps frequently in the winter. (Sometime

fordays or weeks at a time) We suggest that our customers, pipe their
air 
supply from the un-heated space just like a freezer, and check their
drum 
drips weekly during cold weather. Using Tom D's suggestion this could be

less frequently.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "Robert Tarrall" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Saturday, January 27, 2007 4:55 PM
Subject: Drum drip (condensate trap) maintenance in dry system


>
> We have a recently-installed dry system in a garage in Colorado.
Would
> like to know if we need to do any maintenance on the drum drips - is
> there any sort of standard on how often these should be
checked/drained,
> if at all?
>
> Thanks -
> -Robert.-
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to