We have a 100 ft high rise residential bldg. with major renovations. There
are two existing 4" standpipes. The building will be retrofitted with a
sprinkler system per NFPA 13. From NFPA 14 2003,can 5.4.1.3 be used to not
require a fire pump to supply the standpipe 100 psi pressure since this
existing 80 year old bldg is being sprinklered? Is the fire pump required to
supply 750 gpm with 500 gpm at 100psi at the most remote standpipe?
Art Tiroly
ATCO Fire Protection


Roland Huggins wrote
excellent question.  I put my money on Steve's answer.   The NFPA  
committees that I am on (or familiar with) are aggressively moving  
away from encouraging occupants to use a hose (which correlates  
nicely with OSHA requirements).

Roland

On Jan 30, 2007, at 1:02 PM, Steve Leyton wrote:

> I think that the sections I referenced are quite clear:
>
> "For Class III systems installed without hose, the water supply  
> requirements shall be as specified for Class I systems."
>
> That would be ALL of the water supply design criteria, including  
> both maximum and minimum pressures.
>
> Steve Leyton
> Protection Design & Consulting
>
> The foregoing is the opinion of the writer alone, and does not  
> necessarily represent the intent of the NFPA 14 Technical  
> Committee, nor constitute a formal or informal interpretation of  
> the standard.
>
>